Green Building Forum - Basic MVHR schematic and materials Required Plan? Lossnay Tue, 19 Dec 2023 08:26:16 +0000 http://www.greenbuildingforum.co.uk/newforum/ Lussumo Vanilla 1.0.3 Basic MVHR schematic and materials Required Plan? Lossnay http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=13732&Focus=230856#Comment_230856 http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=13732&Focus=230856#Comment_230856 Tue, 20 Oct 2015 11:26:35 +0100 Victorianeco
I acquired a Mitsubishi Lossnay unit which I intend to utilise in my terraced house. This was more of an afterthought so full ducting isn't possible.

In simple terms, will the following be okay:

Extract
One from kitchen (ground floor)
One from bathroom (first floor)

Input
One in attic conversion entrance way (third floor)

I guess there will be plenty of air movement and diffusion so all rooms will benefit and anything is better than nothing.

If this sounds plausible it leads me onto the next part....

Materials required....

A - 3 vents (2 for extract, one for input). What size diameter should these be? The more discrete the better? Link to supplier? Do they need some form of balancing? Aim is to run them both at the same time
B - Ducting? Size from each vent to the lossnay unit?
C - Rectangular ducting - I'll need rigid ducting ideally rectangular from the kitchen through to the unit, something I can wallpaper over or box in, what size and supplier?

Supply Wire....

I have a feed for an extractor fan in the bathroom already wired ready to go, will this be sufficent for the Lossnay unit?

Positioning...

I assume the Lossnay unit will suffice in an uheated attic and just throw mineral wool over it, can I exhaust and supply it from a roof tile vent or even a disused chimney??

Thanks]]>
Basic MVHR schematic and materials Required Plan? Lossnay http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=13732&Focus=230861#Comment_230861 http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=13732&Focus=230861#Comment_230861 Tue, 20 Oct 2015 13:04:51 +0100 tony
I would plug unit in to a socket

Might need a condensate drain on it, mount on eps platform.]]>
Basic MVHR schematic and materials Required Plan? Lossnay http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=13732&Focus=230867#Comment_230867 http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=13732&Focus=230867#Comment_230867 Tue, 20 Oct 2015 13:43:01 +0100 Victorianeco Basic MVHR schematic and materials Required Plan? Lossnay http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=13732&Focus=230869#Comment_230869 http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=13732&Focus=230869#Comment_230869 Tue, 20 Oct 2015 13:49:43 +0100 djh
Positioning - don't forget you will need easy access to change the filters - again, consult the manual for details. MVHR is better inside the thermal envelope but it can go outside. Make sure you have some mounting to minimise noise transmission.

Ducts - the manual should tell you acceptable sizes. It's all about keeping the air speed in the ducts down to a level where it's not noisy, which in turn depends on the flow rates of the unit. You'll probably want the same area of supply ducts and terminals as extracts. You'll also want one or two attenuators. As you say, anything is better than nothing but putting supply vents in living rooms and/or bedrooms will be better than the hall if possible. And yes, you'll need to balance it so you'll need some adjustable valves of some kind.

Part F has tables and things on how it is supposed to be done along with the Domestic Ventilation Compliance Guide. Both worth reading. There are other things like this as well:

http://www.encraft.co.uk/wp-content/uploads/2012/08/Viewpoint-August-2012-MVHR-Designing-and-implementing-a-robust-and-effective-ventilation-system3.pdf]]>
Basic MVHR schematic and materials Required Plan? Lossnay http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=13732&Focus=230893#Comment_230893 http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=13732&Focus=230893#Comment_230893 Tue, 20 Oct 2015 23:09:38 +0100 cjard
http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=12026]]>
Basic MVHR schematic and materials Required Plan? Lossnay http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=13732&Focus=230894#Comment_230894 http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=13732&Focus=230894#Comment_230894 Tue, 20 Oct 2015 23:12:46 +0100 cjard
mvhr really need the same air pressure on both their world streams, if you fit one to the roof and one to the side of the house you can establish an imbalance in the streams (in the same way a chimney draws air to make a fire go) when the wind blows]]>
Basic MVHR schematic and materials Required Plan? Lossnay http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=13732&Focus=230920#Comment_230920 http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=13732&Focus=230920#Comment_230920 Wed, 21 Oct 2015 12:02:06 +0100 Victorianeco
The issue I have is the walls are stone and clad in 90mm eps. Hard to drill through high level]]>
Basic MVHR schematic and materials Required Plan? Lossnay http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=13732&Focus=230924#Comment_230924 http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=13732&Focus=230924#Comment_230924 Wed, 21 Oct 2015 12:54:41 +0100 willie.macleod
This unit comes with 8" ducts. Anything else you will need to drop down with adapters. I compromised with coring 6" holes in my walls.

Installing in a cold loft will require extensive insulation of the ductwork and unit. These are huge units, will not go through a standard loft hatch.]]>
Basic MVHR schematic and materials Required Plan? Lossnay http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=13732&Focus=230935#Comment_230935 http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=13732&Focus=230935#Comment_230935 Wed, 21 Oct 2015 16:49:52 +0100 Victorianeco
I guess so long as the unit is above the external vents, all is good.

I will be able to install the unit in the envelope, but the vent hose wont be... that will be fine surely?

And just throw mineral wool over the ducts from the extracts to the unit ?]]>
Basic MVHR schematic and materials Required Plan? Lossnay http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=13732&Focus=230936#Comment_230936 http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=13732&Focus=230936#Comment_230936 Wed, 21 Oct 2015 16:52:26 +0100 Victorianeco Basic MVHR schematic and materials Required Plan? Lossnay http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=13732&Focus=230959#Comment_230959 http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=13732&Focus=230959#Comment_230959 Wed, 21 Oct 2015 21:03:54 +0100 willie.macleod Basic MVHR schematic and materials Required Plan? Lossnay http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=13732&Focus=231028#Comment_231028 http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=13732&Focus=231028#Comment_231028 Thu, 22 Oct 2015 23:23:03 +0100 Victorianeco Basic MVHR schematic and materials Required Plan? Lossnay http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=13732&Focus=231029#Comment_231029 http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=13732&Focus=231029#Comment_231029 Thu, 22 Oct 2015 23:30:20 +0100 Gotanewlife
Of course you could get lucky and any condensate might evaporate away....]]>
Basic MVHR schematic and materials Required Plan? Lossnay http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=13732&Focus=231229#Comment_231229 http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=13732&Focus=231229#Comment_231229 Mon, 26 Oct 2015 18:08:35 +0000 cjard Basic MVHR schematic and materials Required Plan? Lossnay http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=13732&Focus=231231#Comment_231231 http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=13732&Focus=231231#Comment_231231 Mon, 26 Oct 2015 18:13:17 +0000 Victorianeco
Any reason I couldn't use the input air from within the attic space? At least it will be pre heated of sorts? And the exhaust vent to a wall vent?]]>
Basic MVHR schematic and materials Required Plan? Lossnay http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=13732&Focus=231246#Comment_231246 http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=13732&Focus=231246#Comment_231246 Mon, 26 Oct 2015 22:29:17 +0000 Gotanewlife Posted By: VictorianecoAny reason I couldn't use the input air from within the attic space? At least it will be pre heated of sorts? And the exhaust vent to a wall vent?
Not an expert but provided the attic space is well ventilated (in that it will not adversely increase pressure in the system) then I can't see why not. Strictly speaking though, the input and output should face the same way to avoid differential pressure from wind - and you can imagine how strong that might be if you think about what happens if the front and back doors are left open and there is a gust be quiet.

In short: all the MVHR advice, best practice documentation and installation instructions I have read say cold air input and exhaust pipes should slope down way from the MVHR unit and be on the same wall/subject to the same wind pressure - you either have the accept this and make it work or reject it and have a sub-optimal installation. No-one is going to say "Yes you can ignore one of these points"....]]>
Basic MVHR schematic and materials Required Plan? Lossnay http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=13732&Focus=231248#Comment_231248 http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=13732&Focus=231248#Comment_231248 Mon, 26 Oct 2015 23:12:43 +0000 willie.macleod Basic MVHR schematic and materials Required Plan? Lossnay http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=13732&Focus=231258#Comment_231258 http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=13732&Focus=231258#Comment_231258 Tue, 27 Oct 2015 09:41:54 +0000 djh Posted By: cjard(in lay terms) surely it's condensate because the air was oversaturated with moisture and some of it "fell out", so not quite sure how more inbound air that is also oversaturated will carry away any condensation..
It wouldn't but the idea would be that it sat there until conditions changed such that the air wasn't saturated. Which is how everything outside dries after it rains. But it's not an ideal situation - almost guaranteed to grow something over time - so best not to design it in. So best to follow Willie's advice IMHO.]]>
Basic MVHR schematic and materials Required Plan? Lossnay http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=13732&Focus=231308#Comment_231308 http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=13732&Focus=231308#Comment_231308 Tue, 27 Oct 2015 21:46:25 +0000 Victorianeco
Easiest way to fit a vent of sorts from inside out?]]>
Basic MVHR schematic and materials Required Plan? Lossnay http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=13732&Focus=231507#Comment_231507 http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=13732&Focus=231507#Comment_231507 Sun, 01 Nov 2015 12:18:36 +0000 cjard Basic MVHR schematic and materials Required Plan? Lossnay http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=13732&Focus=231521#Comment_231521 http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=13732&Focus=231521#Comment_231521 Sun, 01 Nov 2015 16:30:30 +0000 Gotanewlife Posted By: VictorianecoEasiest way to fit a vent of sorts from inside out?

Not easy but I managed! String, pre-siliconed vent of the type with spring fitting that goes inside the pipe - long bit of wood. Of course I planned it so I had a stub pipe out to outside that was short enough to reach through.]]>
Basic MVHR schematic and materials Required Plan? Lossnay http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=13732&Focus=231533#Comment_231533 http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=13732&Focus=231533#Comment_231533 Sun, 01 Nov 2015 20:51:54 +0000 Victorianeco
It's above a pitched roof, two storeys up.... A ladder won't go on the roof and would be too steep...]]>
Basic MVHR schematic and materials Required Plan? Lossnay http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=13732&Focus=232404#Comment_232404 http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=13732&Focus=232404#Comment_232404 Sat, 21 Nov 2015 02:03:35 +0000 wookey Basic MVHR schematic and materials Required Plan? Lossnay http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=13732&Focus=232405#Comment_232405 http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=13732&Focus=232405#Comment_232405 Sat, 21 Nov 2015 02:36:48 +0000 wookey
http://www.bpc-direct.com/cgi-bin/olscgi?cgi_req=102|66 shows both.]]>
Basic MVHR schematic and materials Required Plan? Lossnay http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=13732&Focus=232406#Comment_232406 http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=13732&Focus=232406#Comment_232406 Sat, 21 Nov 2015 06:09:16 +0000 willie.macleod Posted By: Victorianeco
It's above a pitched roof, two storeys up.... A ladder won't go on the roof and would be too steep...

Cherry picker is the fast and easy way. Find someone local with one, electricians sometimes have one.]]>
Basic MVHR schematic and materials Required Plan? Lossnay http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=13732&Focus=232492#Comment_232492 http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=13732&Focus=232492#Comment_232492 Sun, 22 Nov 2015 16:45:28 +0000 djh Posted By: wookeyFor the external terminals why would I chose stainless cowls vs (cheaper and more discreet) plain louvred vents? Is it mostly about not having the wind blowing straight up the pipe too badly? Not entirely sure I like the look of those cowls (shortest runs have them coming out the front wall of the house so 'not too ugly' is in order)
I'm a fashion victim so I've got stainless cowls. I think it's as much about keeping the rain out of the ducts as it is the wind. They're supposed to be held in place by two screws into the little holes that you can see in the photo. In my case, it's insulated foam duct behind they're so the screws are bu**er all use and they're siliconed on or whatever was in the nearest tube to hand at the time. But they're still there and looking fashionable :bigsmile:]]>
Basic MVHR schematic and materials Required Plan? Lossnay http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=13732&Focus=249980#Comment_249980 http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=13732&Focus=249980#Comment_249980 Mon, 14 Nov 2016 10:07:40 +0000 Victorianeco
1. Not to use slate vents, he did you can but not ideal
2. He also said not to connect to a wet area such as a bathroom....

So that kind of rules out my idea.

Unless anyone has installed one using roof vents and also ducted from a shower room?]]>
Basic MVHR schematic and materials Required Plan? Lossnay http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=13732&Focus=263129#Comment_263129 http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=13732&Focus=263129#Comment_263129 Thu, 16 Nov 2017 22:07:15 +0000 Victorianeco
Being a mid terrace there's no other place to route the pipework unless I go roof vents or vent into a bedroom below and out the wall that way which I think would be too invasive.

So, should I scrap the lossnay and get something else? Or just vent to roof slates but ensure the runs are lower than the unit?]]>