Mike 1
So far as I'm aware, that has only been reported in older / lower spec timber frame buildings - for example those that rely on an external building paper wind barrier for airtightness. I don't recall reading any reports of significant variation when a fully taped dedicated vapour barrier has been correctly installed.
djh wrote:
It'd be nice if you provided links to these studies you mention so other people can refer to them.
djh
I'm not sure it would make much difference. Yes, sure, the humidity in a hygroscopic house will behave differently to the humidity in a 'plastic' house but hygroscopicity doesn't affect other pollutants.
SimonD
I understand that, my point was more to do with how human perception of and relationship with the environment will affect behaviour, consciously or unconsciously, and thus impact on overall energy consumption of the house.
djh
I'm not sure I understand that, so again a link to some explanatory material would help.
SimonD
Now, I'm referring to a tendency to design & build houses in the same way regardless of the environment within which they are going to be placed and how they're likely to be used
djh
It depends what you're talking about. Obviously designers tend to use techniques and materials that builders and regulators are familiar with, and reuse parts of designs where they can to a greater extent than I and many others would prefer (as a matter of cost-reduction). But all the planning applications I've seen recently of any scale have talked about orientation with regard to solar input and street design and so forth. Some are better designed than others but that is inevitable.
SimonD
airtightness in a timber frame building is likely to vary across the seasons, with airtightness reducing during the winter months
djh
I don't see why that would be the case, given that the timber frame doesn't contribute to the airtightness?
djh
This all depends on the building techniques that are used and again its clear there are preferences to use techniques and materials that require less effort and thus cost, because cost is important and so is reliability.
Posted By: SimonDPosted By: Mike 1Here’s the link to the study and unless you read Swedish, you may need google translate:
So far as I'm aware, that has only been reported in older / lower spec timber frame buildings - for example those that rely on an external building paper wind barrier for airtightness. I don't recall reading any reports of significant variation when a fully taped dedicated vapour barrier has been correctly installed.
https://www.chalmers.se/en/projects/Pages/LufttQthetens-variation-Qver-Qret.aspx
Posted By: SimonDMy particular interest is how not necessarily how occupants’ everyday practices affect energy consumption of a building as I think given the research, that is a given, but rather how our relationship with both the building and immediate natural environment affect those practices, some of which we may not be aware of.I take a similar view; any technological system doesn't stop with the technology; it needs to include the people using it and the environment in which they, and it, operate.
And for me, the approach to simply provide a technical solution is inadequate. The same PHD suggests something similar:
“.. the ability of these systems to provide adequate indoor air quality depends on many factors such as the existence of user friendly controls (Stevenson et al. 2013) maintenance of the system (Lowe & Johnston, 1997), performance (Kurnitski et al. 2007) and operation."
Posted By: Mike1An interesting RH link, though not very significant in impact (compared to studies of older homes that I've read), and not sure what 'disc' refers to, but the overall message is that airtightness is important, most leaks are at junctions, so get your details right.
Posted By: SimonDI don’t mean all of this to become some evangelical rant, more that when it comes to ventilation, we’ve got a lot more to understand in terms of how it sits with the whole house design and those living within it, the energy actually consumed, health and comfort.
Posted By: djhThe other paper about numerical modelling that predicts the transfer of water vapor, CO2, and SF6 between the building envelope and air seems a little strange. Why would SF6 be considered?Good question., The only thing that I can spot in a quick Google search is a report from 2001 mentioning that that SF6 was used in double glazing in some countries - Mainly outside Europe, but Germany gets a mention (https://ec.europa.eu/clima/sites/clima/files/eccp/docs/eccp_wg_final_report_en.pdf)
Posted By: djhI'm not convinced about humidity and hygroscopicity though. I think we understand humidity pretty well but I'm less convinced about our knowledge of hygroscopicity and how it interacts with other factors. We know enough to know that humidity can be dangerous, or just uncomfortable, and so the tendency is to simply design out those risks.In addition, buildings built with hygroscopic material require their inhabitants to understand the nature of the building and how to maintain it. You wouldn't want them painting the walls with plastic paints, for example. And if it's difficult for people to understand what a MVHR unit does and how to operate and maintain it, despite being able to physically see it, how well will they cope with a building that looks like any other, but isn't?
Posted By: djhPosted By: Mike1An interesting RH link, though not very significant in impact (compared to studies of older homes that I've read), and not sure what 'disc' refers to, but the overall message is that airtightness is important, most leaks are at junctions, so get your details right.
Thanks for the translation, Mike. The study seems to be of three unremarkable houses - it's a pity they don't state the actual airtightness numbers as well as the percentage change.
I found the abstract for one of his other papers 'Moderating Indoor Conditions with Hygroscopic Building Materials and Outdoor Ventilation' ASHRAE Transactions . 2004, Vol. 110 Issue 2, p804-819. It says: 'In general, increasing the ventilation has a stronger impact on the average indoor conditions than applying hygroscopic materials, but the impacts of ventilation and hygroscopic materials can be similar during certain operating conditions.' which seems reasonable to me. The other paper about numerical modelling that predicts the transfer of water vapor, CO2, and SF6 between the building envelope and air seems a little strange. Why would SF6 be considered?
Posted By: djhPosted By: SimonDI don’t mean all of this to become some evangelical rant, more that when it comes to ventilation, we’ve got a lot more to understand in terms of how it sits with the whole house design and those living within it, the energy actually consumed, health and comfort.
Me neither, and I suspect we agree about many things but are just looking at them from different viewpoints.
I'm not convinced about humidity and hygroscopicity though. I think we understand humidity pretty well but I'm less convinced about our knowledge of hygroscopicity and how it interacts with other factors. We know enough to know that humidity can be dangerous, or just uncomfortable, and so the tendency is to simply design out those risks. Hence the prevalance of non-organic materials, for example, since they simply don't carry the same risks. I think you may find it interesting to read some of Tim Padfield's writing.
For myself, having chosen to build one of the most hygroscopic houses I'm aware of, I didn't feel that taking additional risks with the ventilation strategy was sensible. And I'm not convinced there's that much to be gained from the possible alternatives, TBH.
Posted By: Mike1In addition, buildings built with hygroscopic material require their inhabitants to understand the nature of the building and how to maintain it. You wouldn't want them painting the walls with plastic paints, for example. And if it's difficult for people to understand what a MVHR unit does and how to operate and maintain it, despite being able to physically see it, how well will they cope with a building that looks like any other, but isn't?
Posted By: Mike1You wouldn't expect to operate a car without taking lessons, nor run it without servicing, and you would expect it to come with a suitable user interface and easy-to-read handbook.Yes. It was interesting chatting with one of the BioRegional people [¹] about BedZED. They initially had a lot of problems with flats overheating because when it got a bit warm residents threw open the doors/windows to the glass atriums making the problem much worse. They put out a leaflet explaining the need to keep those openings closed in warm weather and this solved the problem. People will modify their behaviour when they understand what needs doing and why.
Posted By: SimonDAt a ventilation rate of 0.5 ach, the peak humidity is typically reduced by 10% to 25% RH. The reduction is slightly greater in Toronto than in Vancouver and Saskatoon. At a ventilation rate of 1 ach
Posted By: Mike1There must be scope for some researchers to do likewise and build a reliable model for hygroscopicity that can be readily and reliably applied in the real world.
Posted By: WillInAberdeenAFAICT they assumed that if a very-leaky building was fitted with MHRV, then a corresponding number of air leaks would be fixed at the same time, to keep exactly the same airflow through the building.Sorry, I'm being dim but where do you see them making that assumption?
Posted By: djhApologies for adding to an old discussion, but it seems as good a place as any ...
I've just come an interesting paper (not an academic, peer-reviewed paper but it says it's a paper) that makes the case for MVHR in buildings with any airtighness and recalculates their carbon emissions:
https://www.passivhaustrust.org.uk/UserFiles/File/research%20papers/MVHR/2020.04.27-The%20Case%20for%20MVHR-v7%20new%20cover.pdf" rel="nofollow" >https://www.passivhaustrust.org.uk/UserFiles/File/research%20papers/MVHR/2020.04.27-The%20Case%20for%20MVHR-v7%20new%20cover.pdf
It agrees with a lot of what people on here have found.
Posted By: SimonDPassivhaus Trust should be ashamed of themselves
Posted By: John WalshPosted By: SimonDPassivhaus Trust should be ashamed of themselves
A sadly typical example of spoiling the GBF armchair?
Posted By: John Walsh
The PHT 'report' is written by a staffer and peer-reviewed by eight members from the field. Under what circumstances, then, is it reasonable to trash their work - including the grossly anti-intellectual "No need to go any further.... " - on the stated basis of dismissing one aspect of one of four references for the widely accepted premise that natural ventilation in homes is problematic?
To boot, it's followed up with a 'spurious' (is this a valid usage) reference to another field ('commercial and office buildings'). And then the glorious UK climate: would that be the weather in the 1950s?
How might it be possible for us to re-learn how to discuss research in the field?
Posted By: John Walsh
And then the glorious UK climate: would that be the weather in the 1950s?
Posted By: John WalshTo boot, it's followed up with a 'spurious' (is this a valid usage) reference to another field ('commercial and office buildings')
Posted By: WillInAberdeenBecause the slope of the lines in their charts are parallel, but the intercept for the MHRV line is lower than the natural ventilation line.I think you're overlooking that in a 'normal' building without MVHR the ventilation is done not by infiltration (lack of airtightness) but by deliberate holes in the walls (ventilators) and by opening windows some of the time. The air exhange that results has to be heated by the assumed gas heater and I believe that accounts for the additional emissions. The deliberate holes in the walls do not exist and the opening of windows does not occur in houses with MVHR during the heating season.
(If MHRV were added without also fixing leaks, then the building's total ventilation and hence energy usage would increase, so the MHRV intercept would be greater. If the MHRV flowrate were adjusted to account for the leak rate, the lines would not be parallel.)
Agree it is not very clear how this was done.
Posted By: djhI think you're overlooking that in a 'normal' building without MVHR the ventilation is done not by infiltration (lack of airtightness) but by deliberate holes in the walls (ventilators) and by opening windows some of the time. The air exhange that results has to be heated by the assumed gas heater and I believe that accounts for the additional emissions. The deliberate holes in the walls do not exist and the opening of windows does not occur in houses with MVHR during the heating season.
So I suppose that, yes, they have assumed that some leaks have been fixed, because that is the case by deliberate building design. No trickle vents; no extractor fans; and windows that stay closed.
Posted By: WillInAberdeenThat is the previous thinking, that infiltration had to be reduced to a low enough level, before MHRV is effective, such that windows/vents would be opened in winter.Exactly, what I'm saying is that I believe SAP assumes windows are opened and trickle vents are fitted in order to meet the ventilation rates mandated by Part F. So a building without MVHR will always be heating the ventilation air in addition to whatever infiltration there might be. The reality of how people use buildings might be completely different.
if the building already has sufficient (accidental) air ingressI don't think it's possible to rely on a building having sufficient accidental air ingress. It is possible to design a naturally aspirated system that achieves the desired air exchange rates, as Simon has been at pains to point out, and it is possible to achieve the rate by mechanical ventilation. But what Building Regs require frequently leads to buildings that although in theory are adequately ventilated do not achieve that in reality, with consequent risks for the occupant's health.
Posted By: djhSimon, I'm sorry I posted the link here nowhttp:///newforum/extensions/Vanillacons/smilies/standard/cry.gif" alt="" title="" >
When I read the document (and yes, I don't know what to call it either) it didn't even occur to me that it could be seen as attacking natural ventilation. I believe it simply set out to explain a particular error in the way MVHR is accounted for by Building Regulations that has resulted in them not being installed in some circumstances where they would have been appropriate.
I don't think there's any consideration of the merits of the better natural ventilation designs versus the usual rubbish of trickle vents etc with no thought to airflow at all. I think that's a completely separate subject and outside the scope of the document.