Green Building Forum - Electric cables Tue, 19 Dec 2023 05:52:51 +0000 http://www.greenbuildingforum.co.uk/newforum/ Lussumo Vanilla 1.0.3 Electric cables http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=14056&Focus=236428#Comment_236428 http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=14056&Focus=236428#Comment_236428 Mon, 15 Feb 2016 17:18:59 +0000 tony
Then fiddle about with earth sleeve?

Should be all three inners are insulated, blue, brown and green/yellow.

When will we progress?]]>
Electric cables http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=14056&Focus=236429#Comment_236429 http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=14056&Focus=236429#Comment_236429 Mon, 15 Feb 2016 17:48:34 +0000 ringi Electric cables http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=14056&Focus=236430#Comment_236430 http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=14056&Focus=236430#Comment_236430 Mon, 15 Feb 2016 17:57:33 +0000 Paul in Montreal Posted By: tonyWhy do we still have twin and Earth?

The only reason the non-earth conductors have insulation is to protect them against shorting to each other or shorting to earth. The earth conductor is already at earth potential so there's no impact if it shorts to earth.

I now like the North American colour codes (which work well for colour blind people). Earth is uncovered, white is neutral and black and/or red are live. So even if you can't see red, you can see that it's not white and anything that's darker than white is live. The colour coding carries over to devices such that the silver screws are for the neutral connection and the brass screws are for the hot connection.

Paul in Montreal.

p.s. plus the outer sleeve insulation is nylon so there's no worry with passing through polystyrene insulation]]>
Electric cables http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=14056&Focus=236456#Comment_236456 http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=14056&Focus=236456#Comment_236456 Mon, 15 Feb 2016 23:45:40 +0000 Gotanewlife Electric cables http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=14056&Focus=236469#Comment_236469 http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=14056&Focus=236469#Comment_236469 Tue, 16 Feb 2016 10:18:11 +0000 Simon Still Electric cables http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=14056&Focus=236473#Comment_236473 http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=14056&Focus=236473#Comment_236473 Tue, 16 Feb 2016 10:48:14 +0000 djh
I confess I've never seen a house with the wiring in conduits. It's sort of appealing from an over-engineering neatness point of view, but if I think back to wiring our house I think there are a lot of places where having to route conduits would have been awkward.]]>
Electric cables http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=14056&Focus=236484#Comment_236484 http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=14056&Focus=236484#Comment_236484 Tue, 16 Feb 2016 12:33:40 +0000 Simon Still Posted By: djh

I confess I've never seen a house with the wiring in conduits. It's sort of appealing from an over-engineering neatness point of view, but if I think back to wiring our house I think there are a lot of places where having to route conduits would have been awkward.

My guess is that the reason you never see it in the UK is that it's next to impossible to pull solid core T&E cable through (15 or 20mm) conduit. You can get it through before it's installed but once a conduit has a few bends in it you can't. On the continent, if they're using stranded singles it's much easier.]]>
Electric cables http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=14056&Focus=236485#Comment_236485 http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=14056&Focus=236485#Comment_236485 Tue, 16 Feb 2016 12:41:10 +0000 ringi
Remember on the continent, their plugs don't have fuses, so each socket has to connect back to the consumer unit with its own cable.]]>
Electric cables http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=14056&Focus=236487#Comment_236487 http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=14056&Focus=236487#Comment_236487 Tue, 16 Feb 2016 12:54:33 +0000 Simon Still Posted By: ringiRemember on the continent, their plugs don't have fuses, so each socket has to connect back to the consumer unit with its own cable.

I'm pretty sure that's not the case. They use radials rather than rings but there will be a number of sockets on each radial.

The principle of fuses is that they protect the cable beyond the point of the fuse. A UK radial on 2.5mm will normally have a 20A MCB at the Consumer Unit. That protects the 2.5mm cable between the CU and the socket. The fuse in the plug protects the cable between the socket and the appliance.

Even if a continental radial has a 16A MCB that's still more than many appliance cables could handle. That said, most of the plugs I've looked at in the UK have the wrong fuses in (including extension leads clearly marked as 5A with 13A fuses in the plugs).]]>
Electric cables http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=14056&Focus=236489#Comment_236489 http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=14056&Focus=236489#Comment_236489 Tue, 16 Feb 2016 13:27:20 +0000 djh :devil:]]> Electric cables http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=14056&Focus=236495#Comment_236495 http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=14056&Focus=236495#Comment_236495 Tue, 16 Feb 2016 13:59:29 +0000 Ed Davies quickly. It's fairly easy to have a fault which makes the case of some appliance high voltage but, particularly with the resistance of thin flex, will take a considerable time to trip an MCB (more than a few tens of milliseconds) so delivering enough energy (power for long enough) to stop somebody's heart.

AIUI, this is the reason there's a higher minimum conductor CSA for flexes plugged into radial circuits than there is for rings for with the same fuse or MCB.]]>
Electric cables http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=14056&Focus=236499#Comment_236499 http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=14056&Focus=236499#Comment_236499 Tue, 16 Feb 2016 14:26:46 +0000 Paul in Montreal Posted By: djhThankfully there aren't too many electrical failure modes that lead to a failure current greater than the fuse in the plugtop but less than the fuse/MCB in the CU and which also don't also blow something in the appliance itself.:bigsmile:" alt=":bigsmile:" src="http:///newforum/extensions/Vanillacons/smilies/standard/bigsmile.gif" >:devil:" alt=":devil:" src="http:///newforum/extensions/Vanillacons/smilies/standard/devil.gif" >

Actually, it is precisely this failure mode that, thanks to several fires, lead to the introduction of arc fault circuit interrupters (AFCIs) that are now mandated for all bedroom circuits here in North America. The failure mode is something like a lamp cord behind a piece of furniture where the insulation gets crimped/damaged over time. Arcs form between the now exposed conductors, but the current in the arc isn't enough to trip a normal circuit breaker, but it is enough to cause a fire. Earth Leakage Circuit Breakers (ELCBs / RCDs) cannot detect this fault either, but AFCIs can.

Paul in Montreal.]]>
Electric cables http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=14056&Focus=236500#Comment_236500 http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=14056&Focus=236500#Comment_236500 Tue, 16 Feb 2016 14:50:09 +0000 Simon Still Posted By: Ed DaviesPart of the point of plug fuses, though, is to blowquickly. It's fairly easy to have a fault which makes the case of some appliance high voltage but, particularly with the resistance of thin flex, will take a considerable time to trip an MCB (more than a few tens of milliseconds) so delivering enough energy (power for long enough) to stop somebody's heart.

AIUI, this is the reason there's a higher minimum conductor CSA for flexes plugged into radial circuits than there is for rings for with the same fuse or MCB.

So continental circuits just don't have any protection over this type of fault? A 16A or 32A MCB isn't going to make any difference there is it (or is that situation covered by the RCD in both countries now?)]]>
Electric cables http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=14056&Focus=236504#Comment_236504 http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=14056&Focus=236504#Comment_236504 Tue, 16 Feb 2016 15:29:06 +0000 Ed Davies Electric cables http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=14056&Focus=236505#Comment_236505 http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=14056&Focus=236505#Comment_236505 Tue, 16 Feb 2016 15:37:14 +0000 ringi
If the case is earthed the RCD will trip as soon as the case becomes lives.

However RCD do fail more work more often, hence they should be tested every 3 months.]]>
Electric cables http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=14056&Focus=236521#Comment_236521 http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=14056&Focus=236521#Comment_236521 Tue, 16 Feb 2016 22:32:18 +0000 bot de paille
Conduit costs about 25 euros for 100m, peanuts.
Earth, Phase and Neutral costs about 20 euros each for 100m.

The MCBs are grouped together under and protected by RCDs which are rated to 30milliamps.

When you have this modern setup there really is no need to for a fuse in the plug as far as I can tell. the slightest leak to earth or short circuit and the RCD will trip within fractions of a second.

I bought all Schneider for the fuse board components, sockets, switches. Really nice gear and everything is push fit.

All circuits runs back to a central hub/box in the loft where it is all individually labeled and connected together with WAGOs.
Sockets and lighting can be daisy chained or have their own conduit run depending on the layout of the house, as long as you stay within the 8 or 5 double socket limits for each circuit you can do what you want.

lighting circuits can be run using either 3 core double insulated cable or conduit with insulated individual insulate wires.


This includes the wires for any two way light switches so that hey are just connected as needed as you kneel over the hub.

Old French wiring is beyond frightening. SO glad my family dont have to live in a house with the kind of wiring now that was considered acceptable then....]]>
Electric cables http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=14056&Focus=236526#Comment_236526 http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=14056&Focus=236526#Comment_236526 Wed, 17 Feb 2016 00:41:17 +0000 Gotanewlife
This is our forever home, I just hope if I ever sell (or my son comes to sell!) so many years have passed that there won't be any problems 'cos it's all done DIY - no supervision or documentation beyond the 3 consumer units. I was able to buy the house with outrageous in-situ electrics so I hope this indicates it will all work out fine in the end.]]>
Electric cables http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=14056&Focus=236539#Comment_236539 http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=14056&Focus=236539#Comment_236539 Wed, 17 Feb 2016 10:19:42 +0000 djh Posted By: bot de pailleWhen you have this modern setup there really is no need to for a fuse in the plug as far as I can tell. the slightest leak to earth or short circuit and the RCD will trip within fractions of a second.
Many electricians in the UK criticize the 17th edition wiring regs because of what they regard as its over-reliance on the 'miracle' of RCDs. As Ringi said:

Posted By: ringiHowever RCD do fail more

And sometimes in quite Byzantine ways! In my own experience, it's fairly common that a fuse in the plugtop will blow without tripping the RCD, even without the RCD being faulty. So I'm still happy with defence in depth.

The latest madness is the insistence on metal CUs; supposedly to fix a fire risk that everybody knows is actually due to the use of single screws on connections instead of two screws. Though a better connection scheme to replace screws altogether would be even better.]]>
Electric cables http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=14056&Focus=236545#Comment_236545 http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=14056&Focus=236545#Comment_236545 Wed, 17 Feb 2016 11:06:22 +0000 SteamyTea Electric cables http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=14056&Focus=236546#Comment_236546 http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=14056&Focus=236546#Comment_236546 Wed, 17 Feb 2016 11:10:21 +0000 bot de paille Electric cables http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=14056&Focus=236549#Comment_236549 http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=14056&Focus=236549#Comment_236549 Wed, 17 Feb 2016 11:22:19 +0000 SteamyTea Not the same as failing to 'off'.]]> Electric cables http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=14056&Focus=236551#Comment_236551 http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=14056&Focus=236551#Comment_236551 Wed, 17 Feb 2016 11:25:48 +0000 bot de paille Electric cables http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=14056&Focus=236553#Comment_236553 http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=14056&Focus=236553#Comment_236553 Wed, 17 Feb 2016 11:28:16 +0000 Gotanewlife Posted By: djhit's fairly common that a fuse in the plugtop will blow without tripping the RCD, even without the RCD being faulty.Exactly right - no fault to earth just fault from live to N making for too much current and blowing fuse, if fuse wasn't there then either there would be catastrophic failure of electrical elements breaking bad circuit (and fire invariably) OR the consumer unit MCB would turn off - but this type of fault would never cause the RCD to trip. Though it might as melted wires and arcing caused some current to flow to earth, except perhaps not in a double-insulated laptop.

DIYers - You need to know these things if you do any electrics; they are on page 1 of the things DIYers must know before touching a screwdriver.]]>
Electric cables http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=14056&Focus=236555#Comment_236555 http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=14056&Focus=236555#Comment_236555 Wed, 17 Feb 2016 11:30:13 +0000 ringi Posted By: djhAnd sometimes in quite Byzantine ways! In my own experience, it's fairly common that a fuse in the plugtop will blow without tripping the RCD, even without the RCD being faulty. So I'm still happy with defence in depth.

A RCD will not trip on a L to N fault, or a overload.]]>
Electric cables http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=14056&Focus=236557#Comment_236557 http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=14056&Focus=236557#Comment_236557 Wed, 17 Feb 2016 11:33:27 +0000 Paul in Montreal Posted By: ringiA RCD will not trip on a L to N fault, or a overload.

The ones we have over here will trip on both ground faults and over-current faults. The breakers we have are a combination of over-current and earth-leakage (or arc fault detection). We don't have separate RCDs except for special sockets that go in places like bathrooms or outside where the overall circuit doesn't have earth fault detection. In my bathroom the socket has RCD protection and all the lighting circuits are fed from the downstream output of the RCD so that all the switches in the bathroom are protected rather than having the whole radial circuit that the bathroom sits on having an RCD breaker.

Paul in Montreal.]]>
Electric cables http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=14056&Focus=236558#Comment_236558 http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=14056&Focus=236558#Comment_236558 Wed, 17 Feb 2016 11:33:38 +0000 SteamyTea Posted By: bot de pailleWhats the difference?The fault condition is what it is designed to sense, a fault, which in the case of an RCB is an imbalance between the live and the neutral, and or earth.
An RCD failure is when the actual unit fails, so it may be unable to detect the imbalance or may be physically impeded from reacting to the imbalance. Then it may fail in either the on or the off position.
They are not intrinsically safe devices.]]>
Electric cables http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=14056&Focus=236561#Comment_236561 http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=14056&Focus=236561#Comment_236561 Wed, 17 Feb 2016 11:58:29 +0000 Paul in Montreal
This is why they (should) have a test button that should be tested regularly.

RCD breakers are still supposed to act as overcurrent breakers, just like regular ones - though maybe in the UK the RCD is a separate thing and isn't bundled into a "MCB"?

Now with mandated arc-fault breakers, the two functions (earth leakage and arc detection) have been integrated into one circuit breaker device, such as: http://www.schneider-electric.us/en/product-range/62274-qo-dual-function-circuit-breakers/

See also http://download.schneider-electric.com/files?p_Reference=RP19520116&p_EnDocType=Brochure&p_File_Id=1713692785&p_File_Name=Square+D+Advanced+Function+Breakers.pdf which gives more details about arc faults etc.

Paul in Montreal.]]>
Electric cables http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=14056&Focus=236563#Comment_236563 http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=14056&Focus=236563#Comment_236563 Wed, 17 Feb 2016 12:04:49 +0000 SteamyTea Electric cables http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=14056&Focus=236567#Comment_236567 http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=14056&Focus=236567#Comment_236567 Wed, 17 Feb 2016 13:19:42 +0000 ringi
It will be very hard to damage "twin and earth" in a way that gives a N/L fault without getting a L/E fault. But I would still expect Arc faults on cables attached to plugs.]]>
Electric cables http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=14056&Focus=236568#Comment_236568 http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=14056&Focus=236568#Comment_236568 Wed, 17 Feb 2016 13:21:41 +0000 ringi Posted By: SteamyTeaRCBO is the one that does residual current and over current.

Why don't we have consumer units with 3 bus bars (N,L,E) that a RCBO can plug into, rather then the number of wires you have when you use a lot of RCBO in a UK consumer unit?]]>