Home  5  Books  5  GBEzine  5  News  5  HelpDesk  5  Register  5  GreenBuilding.co.uk
Not signed in (Sign In)

Categories



Green Building Bible, Fourth Edition
Green Building Bible, fourth edition (both books)
These two books are the perfect starting place to help you get to grips with one of the most vitally important aspects of our society - our homes and living environment.

PLEASE NOTE: A download link for Volume 1 will be sent to you by email and Volume 2 will be sent to you by post as a book.

Buy individually or both books together. Delivery is free!


powered by Surfing Waves




Vanilla 1.0.3 is a product of Lussumo. More Information: Documentation, Community Support.

Welcome to new Forum Visitors
Join the forum now and benefit from discussions with thousands of other green building fans and discounts on Green Building Press publications: Apply now.




    • CommentAuthorjamesingram
    • CommentTimeOct 23rd 2012 edited
     
    Just brought myself a CO2 monitor
    http://www.kane.co.uk/online-catalogue/ambient-co-a-co2/kane-alert-co2
    What levels ppm of CO2 should I be expecting in my home ?

    As a side question ,any good links for a novice guide to CO2 and ventilation rates ?
    found these so far
    Ventilation and good indoor air quality in low energy homes
    Finding proven good practice
    http://www.goodhomes.org.uk/downloads/news/VIAQ%20final%20120220%20-%20PUBLICATION.pdf
    MHRV how many air changes per hour?
    http://www.greenbuildingforum.co.uk/forum114/comments.php?DiscussionID=4443
    with Pauls link to http://oee.nrcan.gc.ca/Publications/infosource/Pub/hrv/contents.cfm?attr=4
    Why Measure Carbon Dioxide Inside Buildings?
    By Rich Prill, Washington State University Extension Energy Program 2000
    http://www.energy.wsu.edu/Documents/CO2inbuildings.pdf
    CO2
    http://www.dhs.wisconsin.gov/eh/chemfs/fs/carbondioxide.htm

    seems the North Amercians are more up on this than the UK/EU ?
    or are they just 'burger eating worry monkeys'
  1.  
    "Carbon dioxide
    Carbon dioxide (CO2) is a surrogate for indoor pollutants emitted by humans and correlates with human metabolic activity. Carbon dioxide at levels that are unusually high indoors may cause occupants to grow drowsy, get headaches, or function at lower activity levels. Humans are the main indoor source of carbon dioxide. Indoor levels are an indicator of the adequacy of outdoor air ventilation relative to indoor occupant density and metabolic activity. To eliminate most Indoor Air Quality complaints, total indoor carbon dioxide should be reduced a difference of less than 600 ppm above outdoor levels. NIOSH considers that indoor air concentrations of carbon dioxide that exceed 1,000 ppm are a marker suggesting inadequate ventilation. ASHRAE recommends that carbon dioxide levels not exceed 700 ppm above outdoor ambient levels.[15] The UK standards for schools say that carbon dioxide in all teaching and learning spaces, when measured at seated head height and averaged over the whole day should not exceed 1,500 ppm. The whole day refers to normal school hours (i.e. 9.00am to 3.30pm) and includes unoccupied periods such as lunch breaks. European standards limit carbon dioxide to 3500 ppm. OSHA limits carbon dioxide concentration in the workplace to 5,000 ppm for prolonged periods, and 35,000 ppm for 15 minutes."
    from http://en.wikipedia.org/wiki/Indoor_air_quality#Carbon_dioxide
    • CommentAuthorjamesingram
    • CommentTimeOct 23rd 2012 edited
     
    My external CO2 is currently measuring ( 17.30 ) around 510ppm , so according to the above I should be looking for around 1100-1200ppm as a maximum average for indoors ?
  2.  
    Aprrox. reading for 21:00-21:30 (bedroom windows open slightly through out day till just before sunset) no central heating on
    Lounge/kitchen/diner: 1800ppm (no ventilation)
    Bed 1 , small double room, 2 occupant 2200ppm (window open on first latch)
    Bed 2, box room, 1 occupant 2100ppm (no ventilation)
    Bed 3 , main bedroom, unoccupied 1910ppm (no ventilation)
    Bathroom, 1850ppm (window open on first latch)

    all looking a bit high, any thoughts, other than open some more windows and stick the heating on :bigsmile:
    cheers
    • CommentAuthorRobL
    • CommentTimeOct 23rd 2012
     
    I got a CO2 meter a bit over a year ago. I think it starts to feel a little stuffy to me over 1500ppm, and by 2500ppm I would feel obliged to open a window. I suspect that having a CO2 meter "tunes" you to the sensation, like some sort of biofeedback sensor - ie. I may now be more sensitive to a stuffy atmosphere, now there's a number associated with it.

    Your CO2 levels do sound higher than I would tolerate. We keep our house now at or below 1000ppm with MVHR - which is probably the best house improvement I have done - it avoids the whole healthy house versus saving the planet compromise.

    Now you have the CO2 meter, next step will be MVHR :-)
    • CommentAuthorRobur
    • CommentTimeOct 23rd 2012
     
    Hi James, Those figures do look very high, it would feel uncomfortably stuffy at about 2000ppm. Also a good idea to look at CO2 over time so you see what's happening - CO2 levels change readily in response to internal and external conditions... for example our attic room fills up with CO2 overnight despite no-one sleeping up there but on a windy night much less so. I use one of the units below hooked up to a PC or Arduino to data log over time so as to get a picture of what is happening. Also, I would expect a reading of low 400's for external CO2? Looking at CO2, especially when refurbishing older properties is very valuable as it is quite easy to reduce the air change rate to below where it should be for building and occupant health without compensating with vents or MVHR.

    http://www.airsensor.co.uk/index.php?page=shop.product_details&category_id=1&flypage=flypage.tpl&product_id=10&vmcchk=1&option=com_virtuemart&Itemid=2
    • CommentAuthorSprocket
    • CommentTimeOct 23rd 2012
     
    Just backing up what the Robs said really.
    Our (admittedly not very airtight) house seems to rest at around 550ppm normally.
    This rises when a room is occupied but I rarely see it over 800.
    Outside clean air should be around 450ppm. Do you see 400~500 outside?

    I bought the same unit that RobL uses and previously recommended. It seems to work well and the readings correspond pretty well with an Elektor CO2 meter and with a homebrew detector using some COZIR sensors that I bought (with the intention of using them to control my MVHR... but not in the leaky house).
  3.  
    Thanks for the info , I'll monitor over a week or so doing what we normally do re. venting and see what levels are .
    Got a small HRV I've been meaning to fit to upstairs, so be interesting to see before and after values
    06:30-07:00
    Outside : 508
    Lounge/kitchen/diner: 1780ppm (no ventilation)
    Bed 1 , small double room, 2 occupant 2750ppm (window open on first latch)
    Bed 2, box room, 1 occupant 2200ppm (no ventilation)
    Bed 3 , main bedroom, 2 large occupant 2250ppm (no ventilation) went to 2930 overnight on window sill near bed
    Bathroom, 1790ppm (window open on first latch)
    • CommentAuthorRobur
    • CommentTimeOct 24th 2012
     
    Ouch, those numbers are too high..... I suspect they are not that high in reality. Are you holding the unit whilst taking the measurements perhaps? Just breathing near them will swing the sensor value - best leave it in a room for a bit and come back to it to take a reading before you get too close and handle the monitor. Hmmm, I just re-read your post, sounds like your measurements might be taken over time in which case they could be right and your new monitor is highlighting an air quality problem.... money well spent in that case.

    @ Sprocket, the COZIR sensor looks interesting, is it expensive?
    •  
      CommentAuthorfostertom
    • CommentTimeOct 24th 2012
     
    Posted By: jamesingramCarbon dioxide (CO2) is a surrogate for indoor pollutants emitted by humans and correlates with human metabolic activity
    Hopng not to hijack the thread, but I'd had humidity in mt mind as the best surrogate for all the other pollutants?
  4.  
    Opening a single window on the first latch in an unheated room may not be providing adequate ventilation in all conditions, especially the still air conditions we have at the moment. It normally takes heating, cross/stack ventilation &/or wind to get a reasonable air change rate.

    David
    •  
      CommentAuthorfostertom
    • CommentTimeOct 24th 2012 edited
     
    May be splitting hairs, but cd help to be clear - why does CO2 have to rely on bulk air movement to disperse?

    The prime vehicle for vapour dispersal is not bulk air movement, but dispersal of each vapour present through still air, driven by ea vapour's PVP (partial vapour pressure).

    A local concentration of a vapour creates a local vapour pressure that's 'visible' to that vapour alone, and that pressure tails off outward, in other words a PVP (partial vapour pressure) gradient exists, within still air, and molecules of that vapour move outward through the still air, driven by their private vapour pressure gradient. That could be the PVP gradient established between indoors and outdoors, as soon as a window is opened a crack.

    Volatility is the measure of how strong the PVP is, at given concentration, for ea vapour substance. Perfume has very high volatility - you can smell it (molecules of it reach your nose) as soon as she walks into the room (or even he - yuk), even without any bulk air movement to carry them.

    It must be (I don't know) that CO2 has such low volatility that it's insufficient to drive adequate CO2 dispersal by PVP alone, hence Plan B has to come in - moving the whole array of CO2 molecules bodily within bulk air movement.

    Lecture over.
  5.  
    Hi James, can you calibrate it for 380ppm outside?
    • CommentAuthorEd Davies
    • CommentTimeOct 24th 2012 edited
     
    Posted By: Viking House: “Hi James, can you calibrate it for 380ppm outside?â€Â

    Trouble is, outside tends to be pretty variable on short time scales and distances. See for example some measurements in Paris:

    http://www.realclimate.org/index.php/archives/2007/05/beck-to-the-future/

    That's why Keeling's measurements were made on the top of Mauna Loa, not at more convenient locations like his lab in California.
  6.  
    Hi,
    What about gas cooker and rings ? These can easily be in the kW range and even if on for a short time will produce a large increase in CO2. Also occupancy levels will have an effect. My better half and I work at home and also have a dog so the house is occupied most of the time.

    So glad I have seen this interesting thread - it has prompted me to check my own CO2 levels which in winter will probably be a lot higher.

    Richard
    • CommentAuthorjamesingram
    • CommentTimeOct 24th 2012 edited
     
    Robur , measurements taken after meter in area for a least 10 minute and straight away, before I get time to pervert reading with breath . Yes i did breath on it to see what would happened, when I first got it , It just said "HI" :) (>5000ppm)

    So outdoor still reading 505ppm ( 19:30 )
    took it to job today just to check it wasn't misreading
    outside was reading 480 ( slight more rural ( Chalfont ))
    Internal was reading 550-800ppm , though house was empty all day
    Please to say bathroom with single room mhrv I fitted was reading 650-700 first thing , after client had just left.
    as was kitchen.

    I'm slightly concerned its mis-reading
    It's been pretty damp, overcast , all most misty and still , I live next to a moderately busy road .
    , perhap it's just because I live in Slough
    I haven't noticed stuffyness or poor air , though my wife does/has
    As for negative symptom, i always wake up knacker and aching , but then I'm a builder .

    I'll monitor for the next few days , see if I can get a better outside reading in fine windy weather
    before I worry to much about my indoor readings, might well be misreading.

    most rooms at home are currently around 1400ppm
    • CommentAuthorjamesingram
    • CommentTimeOct 24th 2012 edited
     
    Posted By: Viking HouseHi James, can you calibrate it for 380ppm outside?

    If I get a minute I'll contact the manifacturer, see what they think re outside ppm measurements I'm getting.
    • CommentAuthorjamesingram
    • CommentTimeOct 24th 2012 edited
     
    this is the property for those interested ( half done refurb of a 1960s poured concrete council house )
    http://www.greenbuildingforum.co.uk/forum114/comments.php?DiscussionID=6234&page=1#Item_29
    • CommentAuthordickster
    • CommentTimeOct 25th 2012
     
    Very interesting stuff, might get a monitor, any recommendations as to which one?
    • CommentAuthorSprocket
    • CommentTimeOct 25th 2012
     
    > @ Sprocket, the COZIR sensor looks interesting, is it expensive?

    Hi Rob

    I bought three (wanted five but the price put me off)
    A bit pricey. £118 each (and add another 20% for vat).
    That was for the 5000ppm version including the optional temp and humidity sensor.

    They are neat though. Pretty low power (just a few ma every 0.5s to run the LED). The output is plain 9600 baud serial ascii at 3.3V TTL levels; which is not so convenient for me (would have preferred SPI or I2C so I can use the normal serial port on my controller for modbus).

    To experiment with it on a PC for now I just plugged it into one of these cables (available pretty cheaply from RS or Farnell).

    http://www.ftdichip.com/Products/Cables/USBTTLSerial.htm
    • CommentAuthorSprocket
    • CommentTimeOct 25th 2012
     
    Hi Dickster

    The prices are unfortunately a bit high because the NDIR (IR absorption) CO2 sensor is an expensive part.
    The monitor that RobL recommended elsewhere on GBF is this one:-

    http://www.ebay.co.uk/itm/330803980004

    They are £75 on ebay.
    It is a "Green Life" model 7787.
    There is also a model 7788 knocking about out there that has a relay output in addition to the alarm.

    I bought one back in June and it's been running in my office most of the time since.
    It shipped from Hong Kong but it arrived very quickly. It seems to work very well.
    I've not been able to find anything cheaper. It does have an NDIR sensor and I can't even find any decent NDIR sensors for that price.
  7.  
    Sprocket and others , fancy seeing what your meters give for CO2 ppm outside .
    cheers
    • CommentAuthorRobL
    • CommentTimeOct 26th 2012
     
    I just got 395-399ppm outside here in Cambridge at 8pm with our "Green Life" meter from ebay.
    Getting 850ppm inside, it will probably dither around 1000ppm throughout the night whilst we're in as it kicks the MVHR between 5 and 20%.
    Definately recommend this meter for anybody seriously air-tightening their house.
    • CommentAuthorGaryB
    • CommentTimeOct 27th 2012
     
    374 ppm was recorded indoors via 4 calibrated sensors on one morning last week at a visitor centre in Co Antrim which I monitor. This is a rural coastal location about 2 miles ftom the nearest town.

    The sensors are used to control ventilation on occupancy. The internal levels have not exceeded 900 ppm, occupancy rates have been at design + 25%. Design ventilation rate is 12 l/s per person.

    Ventilation is held off until 450 ppm is reached, then operates at 33%. The next ventilation stages are 600 ppm = 66%, 800 ppm = 100%.
    •  
      CommentAuthorSteamyTea
    • CommentTimeOct 27th 2012
     
    Current atmospheric level is 391.07 ppm.
    So if you have a higher internal level and your walls are slightly warm and you apply the physics behind global warming, you will not have to heat your house :wink:
  8.  
    Sent CO2 ppm meter for recalibration as noticed temperature was out and am unsure about CO2 ppm readings, so we'll see what reading i get on it's return.
    I've fitted a small single room MHRV unit to bathroom and split incoming air vent to two north facing bedrooms that were not vented at night due to traffic noise and suffered from condensation and mold last winter.
    I'll monitor with system on an off once I get the meter back. Already room air quality has noticably improved first thing regarding odours etc. but be interesting to see CO2 concerntration relative to the high reading I was getting 3 weeks ago with no/low night ventilation.
    • CommentAuthorjamesingram
    • CommentTimeJan 9th 2013 edited
     
    So I got my meter back .
    Fitted mhrv, extracts 70m3/h from bathroom / input 70m3/h on boost, split to 2 NW facing front bedrooms
    (humidistate controlled boost on most the time)
    (so approx 35m3/h each, probably more to main bedroom due to the way I've adjusted the outlet valves)

    25m3 Main bedroom (2 adults) windows closed , now reads around
    600-800pmm if during the day if windows left close and unoccupied
    goes up to 1200ish during the evening when where up and downstairs . baths , kids to bed etc.
    then in the first thing in morning averages around 1200-1400ppm.

    I've been opening windows fully for 15-30 minute around 11am over the holiday to give the house a full vent then close them again. this drops ppm to 450-600 and it'll stay there abouts unless room occupied

    Only windows left on vent at night is rear bedroom with no MHRV outlet
    Mhrv seems to have solved mold problem and now only slight condensation on windows when cold , though it's been very mild, relative to this time last year.

    Outside CO2 around 450ppm

    Seems if I wanted to keep CO2 ppm around 800ish I'd have to vent constantly or increase mhrv input to a level
    where airchanges would force indoor temperature drop and heating to be on more.
    • CommentAuthorjamesingram
    • CommentTimeJan 22nd 2013 edited
     