Home  5  Books  5  GBEzine  5  News  5  HelpDesk  5  Register  5  GreenBuilding.co.uk
Not signed in (Sign In)

Categories



Green Building Bible, Fourth Edition
Green Building Bible, fourth edition (both books)
These two books are the perfect starting place to help you get to grips with one of the most vitally important aspects of our society - our homes and living environment.

PLEASE NOTE: A download link for Volume 1 will be sent to you by email and Volume 2 will be sent to you by post as a book.

Buy individually or both books together. Delivery is free!


powered by Surfing Waves




Vanilla 1.0.3 is a product of Lussumo. More Information: Documentation, Community Support.

Welcome to new Forum Visitors
Join the forum now and benefit from discussions with thousands of other green building fans and discounts on Green Building Press publications: Apply now.




    • CommentAuthorRobinB
    • CommentTimeOct 4th 2009
     
    Optimistic? Yes! If anyone know where I can find small pieces - anything from 15mm strips to 600 x 1000mm at a reasonable price I'd be very grateful.
    thanks!
    Robin
  1.  
    you can make Aerogel yourself at home.
    • CommentAuthorSaint
    • CommentTimeOct 4th 2009
     
    RobinB,

    Try Polyformes in Leighton Buzzard for offcuts, they fabricate Aerogel for all sorts of smaller applications, many non construction. 1000 x 600 would not be an offcut though.
    Bot de paille, please tell us more!!!!
  2.  
    Flower resting on a slab of aerogel over a flaming bunsen burner.
    Making Silica Aerogels

    The discussion below relies upon the following terms:

    Hydrolysis:
    The reaction of a metal alkoxide (M-OR) with water, forming a metal hydroxide (M-OH).
    Condensation:
    A condensation reaction occurs when two metal hydroxides (M-OH + HO-M) combine to give a metal oxide species (M-O-M). The reaction forms one water molecule.
    Sol:
    A solution of various reactants that are undergoing hydrolysis and condensation reactions. The molecular weight of the oxide species produced continuously increases. As these species grow, they may begin to link together in a three-dimensional network.
    Gel Point:
    The point in time at which the network of linked oxide particles spans the container holding the Sol. At the gel point the Sol becomes an Alcogel.
    Alcogel (wet gel):
    At the gel point, the mixture forms a rigid substance called an alcogel. The alcogel can be removed from its original container and can stand on its own. An alcogel consists of two parts, a solid part and a liquid part. The solid part is formed by the three-dimensional network of linked oxide particles. The liquid part (the original solvent of the Sol) fills the free space surrounding the solid part. The liquid and solid parts of an alcogel occupy the same apparent volume.
    Supercritical fluid:
    A substance that is above its critical pressure and critical temperature. A supercritical fluid possesses some properties in common with liquids (density, thermal conductivity) and some in common with gases (fills its container, does not have surface tension).
    Aerogel:
    What remains when the liquid part of an alcogel is removed without damaging the solid part (most often achieved by supercritical extraction). If made correctly, the aerogel retains the original shape of the alcogel and at least 50% (typically >85%) of the alcogel's volume.
    Xerogel:
    What remains when the liquid part of an alcogel is removed by evaporation, or similar methods. Xerogels may retain their original shape, but often crack. The shrinkage during drying is often extreme (~90%) for xerogels.

    Sol-Gel Chemistry

    The formation of aerogels, in general, involves two major steps, the formation of a wet gel, and the drying of the wet gel to form an aerogel. Originally, wet gels were made by the aqueous condensation of sodium silicate, or a similar material. While this process worked well, the reaction formed salts within the gel that needed to be removed by many repetitive washings (a long, laborious procedure). With the rapid development of sol-gel chemistry over the last few decades, the vast majority of silica aerogels prepared today utilize silicon alkoxide precursors. The most common of these are tetramethyl orthosilicate (TMOS, Si(OCH3)4), and tetraethyl orthosilicate (TEOS, Si(OCH2CH3)4). However, many other alkoxides, containing various organic functional groups, can be used to impart different properties to the gel. Alkoxide-based sol-gel chemistry avoids the formation of undesirable salt by-products, and allows a much greater degree of control over the final product. The balanced chemical equation for the formation of a silica gel from TEOS is:

    Si(OCH2CH3)4 (liq.) + 2H2O (liq.) = SiO2 (solid) + 4HOCH2CH3 (liq.)

    The above reaction is typically performed in ethanol, with the final density of the aerogel dependent on the concentration of silicon alkoxide monomers in the solution. Note that the stoichiometry of the reaction requires two moles of water per mole of TEOS. In practice, this amount of water leads to incomplete reaction and weak, cloudy aerogels. Most aerogel recipes, therefore, use a higher water ratio than is required by the balanced equation (anywhere from 4-30 equivalents).
    Catalysts

    The kinetics of the above reaction are impracticably slow at room temperature, often requiring several days to reach completion. For this reason, acid or base catalysts are added to the formulation. The amount and type of catalyst used play key roles in the microstructural, physical and optical properties of the final aerogel product.

    Acid catalysts can be any protic acid, such as HCl. Basic catalysis usually uses ammonia, or, more commonly, ammonia and ammonium fluoride. Aerogels prepared with acid catalysts often show more shrinkage during supercritical drying and may be less transparent than base catalyzed aerogels. The microstructural effects of various catalysts are harder to describe accurately, as the substructure of the primary particles of aerogels can be difficult to image with electron microscopy. All show small (2-5 nm diameter) particles that are generally spherical or egg-shaped. With acid catalysis, however, these particles may appear "less solid" (looking something like a ball of string) than those in base-catalyzed gels.

    As condensation reactions progress the sol will set into a rigid gel. At this point, the gel is usually removed from its mold. However, the gel must be kept covered by alcohol to prevent evaporation of the liquid contained in the pores of the gel. Evaporation causes severe damage to the gel and will lead to poor quality aerogels
    Single-Step vs. Two-Step Aerogels

    Typical acid or base catalyzed TEOS gels are often classified as "single-step" gels, referring to the "one-pot" nature of this reaction. A more recently developed approach uses pre-polymerized TEOS as the silica source. Pre-polymerized TEOS is prepared by heating an ethanol solution of TEOS with a sub-stoichiometric amount of water and an acid catalyst. The solvent is removed by distillation, leaving a viscous fluid containing higher molecular weight silicon alkoxy-oxides. This material is redissolved in ethanol and reacted with additional water under basic conditions until gelation occurs. Gels prepared in this way are known as "two-step" acid-base catalyzed gels. Pre-polymerized TEOS is available commercially in the U.S. from Silbond Corp. (Silbond H-5).

    These slightly different processing conditions impart subtle, but important changes to the final aerogel product. Single-step base catalyzed aerogels are typically mechanically stronger, but more brittle, than two-step aerogels. While two-step aerogels have a smaller and narrower pore size distribution and are often optically clearer than single-step aerogels.
    Aging and Soaking

    When a sol reaches the gel point, it is often assumed that the hydrolysis and condensation reactions of the silicon alkoxide reactant are complete. This is far from the case. The gel point simply represents the time when the polymerizing silica species span the container containing the sol. At this point the silica backbone of the gel contains a significant number of unreacted alkoxide groups. In fact, hydrolysis and condensation can continue for several times the time needed for gelation. Failure to realize, and to accommodate this fact is one of the most common mistakes made in preparing silica aerogels. The solution is simple--patience. Sufficient time must be given for the strengthening of the silica network. This can be enhanced by controlling the pH and water content of the covering solution. Common aging procedures for base catalyzed gels typically involve soaking the gel in an alcohol/water mixture of equal proportions to the original sol at a pH of 8-9 (ammonia). The gels are best left undisturbed in this solution for up to 48 hours.

    This step, and all subsequent processing steps, are diffusion controlled. That is, transport of material into, and out of, the gel is unaffected by convection or mixing (due to the solid silica network). Diffusion, in turn, is affected by the thickness of the gel. In short, the time required for each processing step increases dramatically as the thickness of the gel increases. This limits the practical production of aerogels to 1-2 cm-thick pieces.

    After aging the gel, all water still contained within its pores must be removed prior to drying. This is simply accomplished by soaking the gel in pure alcohol several times until all the water is removed. Again, the length of time required for this process is dependent on the thickness of the gel. Any water left in the gel will not be removed by supercritical drying, and will lead to an opaque, white, and very dense aerogel.
    Supercritical Drying
    Graph of temperature in degrees centigrade and pressure in psi versus time in hours, for alcohol drying and carbon dioxide drying.

    Process conditions for both the carbon dioxide substitution/drying process and the alcohol drying process.

    The final, and most important, process in making silica aerogels is supercritical drying. This is where the liquid within the gel is removed, leaving only the linked silica network. The process can be performed by venting the ethanol above its critical point (high temperature-very dangerous) or by prior solvent exchange with CO2followed by supercritical venting (lower temperatures-less dangerous) It is imperative that this process only be performed in an autoclave specially designed for this purpose (small autoclaves used by electron microscopists to prepare biological samples are acceptable for CO2 drying). The process is as follows. The alcogels are placed in the autoclave (which has been filled with ethanol). The system is pressurized to at least 750-850 psi with CO2 and cooled to 5-10 degrees C. Liquid CO2 is then flushed through the vessel until all the ethanol has been removed from the vessel and from within the gels. When the gels are ethanol-free the vessel is heated to a temperature above the critical temperature of CO2 (31 degrees C). As the vessel is heated the pressure of the system rises. CO2 is carefully released to maintain a pressure slightly above the critical pressure of CO2 (1050 psi). The system is held at these conditions for a short time, followed by the slow, controlled release of CO2 to ambient pressure. As with previous steps, the length of time required for this process is dependent on the thickness of the gels. The process may last anywhere from 12 hours to 6 days.

    At this point the vessel can be opened and the aerogels admired for their intrinsic beauty.
    Typical Recipes
    Single-Step Base Catalyzed Silica Aerogel

    This will produce an aerogel with a density of approx. 0.08 g/cm3. The gel time should be 60-120 minutes, depending on temperature.

    1. Mix two solutions:
    1. Silica solution containing 50 mL of TEOS, 40 mL of ethanol
    2. Catalyst solution containing 35 mL of ethanol, 70 mL of water, 0.275 mL of 30% aqueous ammonia, and 1.21 mL of 0.5 M ammonium fluoride.
    2. Slowly add the catalyst solution to the silica solution with stirring.
    3. Pour the mixture into an appropriate mold until gelation.
    4. Process as described above.

    Two-Step Acid-Base Catalyzed Silica Aerogel

    This will produce an aerogel with a density of approx. 0.08 g/cm3. The gel time should be 30-90 minutes, depending on temperature.

    1. Mix two solutions:
    1. Silica solution containing 50 mL of precondensed silica (Silbond H-5, or equivalent), 50mL of ethanol
    2. Catalyst solution containing 35 mL of ethanol, 75 mL of water, and 0.35 mL of 30% aqueous ammonia.
    2. Slowly add the catalyst solution to the silica solution with stirring.
    3. Pour the mixture into an appropriate mold until gelation.
    4. Process as described above.
    • CommentAuthorSaint
    • CommentTimeOct 4th 2009
     
    Bot de Paille,
    You've got an autoclave in your home? you must live in some gaff
    Cut and paste is cool but a link is even quicker http://eetd.lbl.gov/ECS/aerogels/sa-making.html
  3.  
    "Bot de Paille,
    You've got an autoclave in your home? "

    Yes Saint I have, its called a pressure cooker

    Teengaers have been making this stuff in their kitchen for their science projects

    Loads and loads of stuff on th einternet about DIY AEROGEL, google it
    • CommentAuthorSaint
    • CommentTimeOct 5th 2009
     
    Mmmm.... not quite the same pressure (by a factor of 100) so may take a little longer to dry and then there's the 60 year old issue of how to make it useable, the fleece form works pretty well, but here's the deal, you make it I'll sell it
    • CommentAuthorRobinB
    • CommentTimeOct 6th 2009
     
    I LOVE the idea of cooking my own! Is it really practical at home? Dangerous? Poisonous? Expensive?

    I will get my chemistry friend to take a look. If I could mould specific items to do away with some of the thermal bridges I'll be super-happy!
    thanks bot de paille!
    And thanks to Saint too.
    • CommentAuthorSaint
    • CommentTimeOct 6th 2009 edited
     
    RobinB,
    At best you will create a substance so delicate that if you sneeze it will disintegrate. This would be, although somewhat unlikely, like Kistlers "invention" from the 1930s which stayed on the lab shelf until 2001 when NASA thought it would be good to somehow combine it into a textile so it could be sewn into space suits. That is the fleece format that you see available from Aspen Aerogels. At worst it will just collapse in on itself and be totally unuseable. Check out the website www.aerogel.com and look at the "frozen smoke"
    • CommentAuthorRobinB
    • CommentTimeOct 6th 2009
     
    Oh, Saint, you crush my aerogel-fragile dreams! I sneeze a lot so that wouldn't be a good idea, and I'm not sure it would be good to inhale it either. Still intriguing to have a go - something for when the house is finished and I'm twiddling my thumbs.
    •  
      CommentAuthorDAI_EVANS
    • CommentTimeOct 6th 2009
     
    Why is that Saint? What makes it less stable than the stuff off the shelf? Is there any way to make it stable in home production? The use of Aerogel in construction is very costly but if you could home produce quantities of the stuff to use in areas of cold bridging etc as well as a primary insulation for the main construction it may be possible to produce a fully insulate building without any insulation breaks in areas where this would normally be problematic.
  4.  
    How about a light weight material made from clay, a kind of clay aerogel?

    this university is making it....
    http://www.youtube.com/watch?v=9Pj3-G9eI_k
    •  
      CommentAuthorfostertom
    • CommentTimeOct 7th 2009
     
    Great if it could be made in situ?
    • CommentAuthorRobinB
    • CommentTimeOct 7th 2009
     
    I might start a new "home made aerogel " thread, I think could have much wider interest than my original "offcuts wanted" Thanks to all for moving a basic question in a really interesting direction... To be able to make small bespoke parts or to mould it in situ as fostertom suggests could be fantastic!
    Robin
    • CommentAuthorSaint
    • CommentTimeOct 7th 2009 edited
     
    Dai,
    When you say stuff off the shelf, the two major formats are either in bead form from Cabot which is used sometimes in filling glazed units or the fleece format from Aspen Aerogels. Here the sol has been allowed to diffuse and then gel into a reinforcing fabric matrix. This latter format has finally allowed aerogel to be used commercially and very successfully in industrial, military and construction applications.
    Pure silica aerogel is extremely fragile, pieces larger than petri dishes are not practical and even those have minimal survival rates.

    PS Dai, relating to your other postings there is a company in Essex now lining out shipping containers with an aerogel laminate
    •  
      CommentAuthorDAI_EVANS
    • CommentTimeOct 8th 2009
     
    Saint,
    is it possible to make a stable form at home? In regards to shipping containers what company? Dissertation results tomorrow :confused:
    • CommentAuthorSaint
    • CommentTimeOct 8th 2009 edited
     
    Dai, I really don't know but if it were possible then I'm sure there would have been significant development in that respect since its conception back in the 1930s.
    Its taken a huge investment to get it to the fleece stage and that has only happened due to NASA pushing for it.

    The company with the newly developed container lining product is Paraclad based in Harlow 01279 701010
    • CommentAuthorcookie
    • CommentTimeOct 10th 2009
     
    Robin.... lol..... I'm not installing home made aerogel without a data safety sheet to say its safe to do so. :bigsmile:
Add your comments

    Username Password
  • Format comments as
 
   
The Ecobuilding Buzz
Site Map    |   Home    |   View Cart    |   Pressroom   |   Business   |   Links   
Logout    

© Green Building Press