Green Building Forum - 50mm cavity wall - would adding 50mm EWI be worth it? Tue, 19 Dec 2023 08:31:00 +0000 http://www.greenbuildingforum.co.uk/newforum/ Lussumo Vanilla 1.0.3 50mm cavity wall - would adding 50mm EWI be worth it? http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=17798&Focus=300981#Comment_300981 http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=17798&Focus=300981#Comment_300981 Tue, 28 Mar 2023 13:48:35 +0100 Osprey
Would it be worth adding 50mm EPS EWI (ie get a substantial insulation improvement)?

I realise the pebbledash would need smoothing for good EWI attachment. More than 50mm EWI would be difficult for various reason.

Thanks]]>
50mm cavity wall - would adding 50mm EWI be worth it? http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=17798&Focus=300992#Comment_300992 http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=17798&Focus=300992#Comment_300992 Tue, 28 Mar 2023 18:33:39 +0100 Peter_in_Hungary
Adding 50mm of EPS EWI will improves your wall from a u value of 0.5 to 0.3 Putting on 100mm EWI improves it to 0.21 Guesstimate based on a brick both sides cavity wall with 50mm EPS inside. Your original wall structure may differ from my assumption.

The difference in cost between 50mm and 100mm EWI is just the extra 50mm of EPS, other costs remain the same.

You can play around with different insulation options at
https://www.ubakus.de/en/r-value-calculator/?
Use the demo version.

You can put EWI on to pebbledash without a 'smoothing coat' if you attach the EPS with a fillet of adhesive all the way around the edge of the EPS sheet and 4 dollops in the centre. The EPS sheet is then pushed on to the wall firmly to seat the adhesive. This method uses a bit more adhesive but saves the cost of a smoothing render coat. Of course the pebbledash needs to be in good condition to take the EWI with no hollow patches. (if there are a few hollow patches then knock off the pebbledash and attach the EPS as above with perhaps a thicker fillet to account for no pebbledash)

To get a dust free pebbledash surface for EWI a pressure washer is a good option.]]>
50mm cavity wall - would adding 50mm EWI be worth it? http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=17798&Focus=300994#Comment_300994 http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=17798&Focus=300994#Comment_300994 Wed, 29 Mar 2023 09:13:06 +0100 Osprey Yes I appreciate 100mm ewi would be better than 50 (and 150mm better still) but there are some practicalities that may not allow it.]]> 50mm cavity wall - would adding 50mm EWI be worth it? http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=17798&Focus=301012#Comment_301012 http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=17798&Focus=301012#Comment_301012 Wed, 29 Mar 2023 18:20:19 +0100 Jeff B 50mm cavity wall - would adding 50mm EWI be worth it? http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=17798&Focus=301014#Comment_301014 http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=17798&Focus=301014#Comment_301014 Wed, 29 Mar 2023 19:00:02 +0100 Osprey I am pretty sure bonded eps beads injected into the cavity would pretty much eliminate air movement there, or am I missing something?]]> 50mm cavity wall - would adding 50mm EWI be worth it? http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=17798&Focus=301018#Comment_301018 http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=17798&Focus=301018#Comment_301018 Wed, 29 Mar 2023 20:19:45 +0100 Peter_in_Hungary Posted By: OspreyJeff
I am pretty sure bonded eps beads injected into the cavity would pretty much eliminate air movement there, or am I missing something?
Depends totally upon the workmanship of the person doing the injection and unfortunately there is no easy way to check the results of the work.]]>
50mm cavity wall - would adding 50mm EWI be worth it? http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=17798&Focus=301021#Comment_301021 http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=17798&Focus=301021#Comment_301021 Wed, 29 Mar 2023 23:04:54 +0100 Jeff B I am pretty sure bonded eps beads injected into the cavity would pretty much eliminate air movement there, or am I missing something?</blockquote>

Sorry I missed reading the "bonded" bit! Maybe it'd be ok, I wouldn't like to say definitely. I must admit we have Rockwool fibres in our cavity walls so the risk of air movement maybe quite high. The only way to be 100% sure would be to seal the tops of the cavity which in our case was not possible access-wise.]]>
50mm cavity wall - would adding 50mm EWI be worth it? http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=17798&Focus=301022#Comment_301022 http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=17798&Focus=301022#Comment_301022 Thu, 30 Mar 2023 08:01:47 +0100 fostertom Posted By: OspreyI appreciate 100mm ewi would be better than 50 (and 150mm better still) but there are some practicalities that may not allow it.Can you outline those practicalities? might make a difference. On a project with 200EPS EWI on cavity walls with unknown-quality previous cavity fill, it's made a huge difference, as you'd hope with 200 EWI. No attempt to seal top of cavity wall.]]> 50mm cavity wall - would adding 50mm EWI be worth it? http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=17798&Focus=301026#Comment_301026 http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=17798&Focus=301026#Comment_301026 Thu, 30 Mar 2023 10:39:19 +0100 RobL
We have pro fitted fluff filled narrow cavity walls, and 150mm diy EWI. It has been a battle to stop air leakage via the cavity - there were no cavity closers at the top, lots of holes all over - massive ones hidden by PVC T&G panelling. Big holes you could fit your hand into between floors! If you can't see it, it will be wrong...]]>
50mm cavity wall - would adding 50mm EWI be worth it? http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=17798&Focus=301034#Comment_301034 http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=17798&Focus=301034#Comment_301034 Thu, 30 Mar 2023 14:06:22 +0100 fostertom
Yes, you can't rely on rendered EWI as 'airtight layer' but it's still quite good at it. If that EWI is applied on extg render, then that's also quite good at it, as long as you fill render cracks before EWIing. Ditto internal plaster, as long as you deal with gaps in it - inter-floors, elect boxes etc.

Can add up to a fair wind-barrier, even if there's no formal 'airtight layer'. So where's the big 'draw' of outside air?]]>
50mm cavity wall - would adding 50mm EWI be worth it? http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=17798&Focus=301035#Comment_301035 http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=17798&Focus=301035#Comment_301035 Thu, 30 Mar 2023 17:05:39 +0100 Osprey
Narrow driveway is one thing, if existing drainpipes were moved out to accommodate EWI. I guess EWI could be fitted around drain/sewage pipes without losing TOO much insulation (as wall cavities would be filled) but may look a bit odd.]]>
50mm cavity wall - would adding 50mm EWI be worth it? http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=17798&Focus=301036#Comment_301036 http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=17798&Focus=301036#Comment_301036 Thu, 30 Mar 2023 17:08:28 +0100 Osprey </blockquote>
My cavities are vented to the underfloor air bricks and and also have a couplemof their own airbricks.]]>
50mm cavity wall - would adding 50mm EWI be worth it? http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=17798&Focus=301037#Comment_301037 http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=17798&Focus=301037#Comment_301037 Thu, 30 Mar 2023 17:11:00 +0100 Osprey
Sorry I missed reading the "bonded" bit! Maybe it'd be ok, I wouldn't like to say definitely. I must admit we have Rockwool fibres in our cavity walls so the risk of air movement maybe quite high. The only way to be 100% sure would be to seal the tops of the cavity which in our case was not possible access-wise.</blockquote>

My house cavity tops are accessible from the loft. If fact they provide the sole loft ventilation, which will have to be addressed when I do the walls..]]>
50mm cavity wall - would adding 50mm EWI be worth it? http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=17798&Focus=301038#Comment_301038 http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=17798&Focus=301038#Comment_301038 Thu, 30 Mar 2023 18:20:17 +0100 Peter_in_Hungary Posted By: OspreyMy cavities are vented to the underfloor air bricks and and also have a couplemof their own airbricks.
Posted By: OspreyMy house cavity tops are accessible from the loft. If fact they provide the sole loft ventilation, which will have to be addressed when I do the walls..

How wonderful - outside air flowing through the cavity to ventilate your loft with air that will have been warmed by the inner leaf of the cavity wall-----------Hmmm

BTW if you select the Html button at the bottom of the comments box then quotes come out in blue, which makes the post easier to read.]]>
50mm cavity wall - would adding 50mm EWI be worth it? http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=17798&Focus=301039#Comment_301039 http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=17798&Focus=301039#Comment_301039 Thu, 30 Mar 2023 18:31:47 +0100 fostertom Posted By: OspreyMy cavities are vented to the underfloor air bricksbut I guess you're looking at insulating, even full-filling your u/floor, as per much discussion on here? Then those air bricks can be sealed.
Posted By: Ospreyand and also have a couple of their own airbricks
Bung them up too - the EWI will do that anyway.
Posted By: OspreyI guess EWI could be fitted around drain/sewage pipes without losing TOO much insulation (as wall cavities would be filled) but may look a bit odd
Should be possible - tragic to half-measure your EWI investment just for a want of a bit of creative design!]]>
50mm cavity wall - would adding 50mm EWI be worth it? http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=17798&Focus=301048#Comment_301048 http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=17798&Focus=301048#Comment_301048 Thu, 30 Mar 2023 21:22:37 +0100 Osprey Posted By: Peter_in_Hungary
Posted By: OspreyMy cavities are vented to the underfloor air bricks and and also have a couplemof their own airbricks.

Posted By: OspreyMy house cavity tops are accessible from the loft. If fact they provide the sole loft ventilation, which will have to be addressed when I do the walls..

How wonderful - outside air flowing through the cavity to ventilate your loft with air that will have been warmed by the inner leaf of the cavity wall-----------Hmmm

BTW if you select the Html button at the bottom of the comments box then quotes come out in blue, which makes the post easier to read.

Agreed, but loft, and everywhere else is very dry, and in good condition for 100year old house. Not the warmest though.
(Thanks for html hint)]]>
50mm cavity wall - would adding 50mm EWI be worth it? http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=17798&Focus=301049#Comment_301049 http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=17798&Focus=301049#Comment_301049 Thu, 30 Mar 2023 21:25:53 +0100 Osprey Posted By: fostertom
Posted By: OspreyMy cavities are vented to the underfloor air bricks
but I guess you're looking at insulating, even full-filling your u/floor, as per much discussion on here? Then those air bricks can be sealed.
Posted By: Ospreyand and also have a couple of their own airbricks
Bung them up too - the EWI will do that anyway.
Posted By: OspreyI guess EWI could be fitted around drain/sewage pipes without losing TOO much insulation (as wall cavities would be filled) but may look a bit odd
Should be possible - tragic to half-measure your EWI investment just for a want of a bit of creative design!

Re airbricks - yes just stating current arrangement. Proceeding with under floor insulation soon, as part of which will be isolating airbricks from cavity. Still needed for underfloor, imo.]]>
50mm cavity wall - would adding 50mm EWI be worth it? http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=17798&Focus=301054#Comment_301054 http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=17798&Focus=301054#Comment_301054 Fri, 31 Mar 2023 09:11:09 +0100 fostertom Posted By: OspreyStill needed for underfloor, imoAFAIK, the consensus here was no, an old myth, not needed, provided any water entering from outside has been fixed.

Do these comments help allay worries of outside air blowing around in the cavity? What you say, Peter, Rob and Jeff?]]>
50mm cavity wall - would adding 50mm EWI be worth it? http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=17798&Focus=301060#Comment_301060 http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=17798&Focus=301060#Comment_301060 Fri, 31 Mar 2023 11:59:48 +0100 Osprey Posted By: fostertom
Posted By: OspreyStill needed for underfloor, imo
AFAIK, the consensus here was no, an old myth, not needed, provided any water entering from outside has been fixed.

Do these comments help allay worries of outside air blowing around in the cavity? What you say, Peter, Rob and Jeff?

I have seen a discussion whereby, if the underfloor void is filled with insulation, no ventilation is required. However, with my setup, the joist 'bottoms' would be exposed.]]>
50mm cavity wall - would adding 50mm EWI be worth it? http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=17798&Focus=301717#Comment_301717 http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=17798&Focus=301717#Comment_301717 Fri, 26 May 2023 15:16:02 +0100 wookey
So yes, as others have said, 50mm EWI is a very good idea, but only if you also fill the cavity. Filling it in more airtight ways will likely work better. And sealing off as many holes as you can find will also improve it. All of this is quite hard to quantify (i.e just filling the cavity will probably allow the EWI to work 'adequately', but the more hole-bunging the better, espescially the bottom-vents as those will generate significant stack ventilation).

In general the continuous EWI layer will be better insulation than the cavity layer as that often ends up with gaps and is bridged by wall ties and cement spillage and usually about 300mm of crap at the bottom. So I'd expect it to be _more_ than twice as good as just filling the cavity. You could also use PIR insulation for better U-values, given that your thickness is restricted to 50mm. There is a system for that (weber maybe?)

I would strongly advise spending the extra time/money to move your drainage goods outside the EWI so as to have a continuous layer, and it just looks way better. Yes, to some degree the fact that you also have cavity insulation means you don't _need_ to do this from a thermal point of view, but it still looks cheap if the insulation just stops around plumbing goods, and it makes rendering difficult and is likely to let water in.]]>
50mm cavity wall - would adding 50mm EWI be worth it? http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=17798&Focus=301719#Comment_301719 http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=17798&Focus=301719#Comment_301719 Sat, 27 May 2023 08:35:37 +0100 tony 50mm cavity wall - would adding 50mm EWI be worth it? http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=17798&Focus=301731#Comment_301731 http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=17798&Focus=301731#Comment_301731 Tue, 30 May 2023 15:17:25 +0100 wookey
One approach where 'narrow driveway/passage' is the problem is to step it out above head height so the mediocre area is minimised. And the option remains for some IWI too one day to compensate.]]>
50mm cavity wall - would adding 50mm EWI be worth it? http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=17798&Focus=301734#Comment_301734 http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=17798&Focus=301734#Comment_301734 Wed, 31 May 2023 17:56:20 +0100 tony 50mm cavity wall - would adding 50mm EWI be worth it? http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=17798&Focus=301737#Comment_301737 http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=17798&Focus=301737#Comment_301737 Thu, 01 Jun 2023 08:35:10 +0100 dathi 50mm cavity wall - would adding 50mm EWI be worth it? http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=17798&Focus=301739#Comment_301739 http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=17798&Focus=301739#Comment_301739 Thu, 01 Jun 2023 08:47:58 +0100 Peter_in_Hungary Posted By: tonyWould it pass building regs?
Is there still the get-out clause where insulation limits can be ignored if it is not practical or too expensive (pay back within a certain time) to fit?]]>
50mm cavity wall - would adding 50mm EWI be worth it? http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=17798&Focus=301745#Comment_301745 http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=17798&Focus=301745#Comment_301745 Thu, 01 Jun 2023 11:20:45 +0100 WillInAberdeen
There is a further get-out that insulation should be "technically and functionally feasible and have a simple payback no more than 15 years", in which case U= 0.7 would also be acceptable.]]>
50mm cavity wall - would adding 50mm EWI be worth it? http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=17798&Focus=302009#Comment_302009 http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=17798&Focus=302009#Comment_302009 Thu, 15 Jun 2023 08:55:42 +0100 Osprey I suppose I could have 50mm ewi under the pipework (in addition to cwi), and 100mm elsewhere: may be impractical though.
Stepping the sewer pipe out above charge height might work, and notmlook TOO bad. Will investigate.
(I found one website where the manufacturer (from diagrams anyway) had come up with a 3 sided profile to handle sewer pipes, with high performance insulation behind the pipe. Website seems defunct, and I can't find it now)

Edit: found it! It is called Thermo-pro from Enviroform]]>