Home  5  Books  5  GBEzine  5  News  5  HelpDesk  5  Register  5  GreenBuilding.co.uk
Not signed in (Sign In)

Categories



Green Building Bible, Fourth Edition
Green Building Bible, fourth edition (both books)
These two books are the perfect starting place to help you get to grips with one of the most vitally important aspects of our society - our homes and living environment.

PLEASE NOTE: A download link for Volume 1 will be sent to you by email and Volume 2 will be sent to you by post as a book.

Buy individually or both books together. Delivery is free!


powered by Surfing Waves




Vanilla 1.0.3 is a product of Lussumo. More Information: Documentation, Community Support.

Welcome to new Forum Visitors
Join the forum now and benefit from discussions with thousands of other green building fans and discounts on Green Building Press publications: Apply now.




    • CommentAuthorGreenfish
    • CommentTimeSep 3rd 2014
     
    Any one care to share their experiences of building air tightness testing and the results?

    Just had our door blower test run, not got results yet, but was underwhelmed by the experience. Pretty sure we are well within Part L requirements, but was hoping to get below 1 (units confused!) and have a chance to feel and listen for any tiny leaks. In the end the guy was happy things were "good enough", well of course they were, and the fan was on and off in minutes. More worrying he did not seal the MVHR input/output grilles, wish I had done it before hand. He said switching it off was enough, but I am convinced it seals just because the fan isn't running. Also the seal of the fan into the door didn't look that great, I could see daylight around the cracks (no tape).

    So I will get a number, but not a true measure of what we have achieved, and no indication of the weak points. Was I hoping for too much?
    • CommentAuthortony
    • CommentTimeSep 3rd 2014
     
    Trouble with sub contractors on a price is that they are always in a hurry to go home!

    I have two done and both times I was moderately happy as they did offer advice and even helped to trace leeks.

    The first guy had loads of trouble as he wasn't expecting a masonry house to so air tight and had to reduce his blower fan aperture several times and slow it down a lot too.

    I forgot to seal up the cooker hood duct the first time and found a couple of unsealed service penetrations by listening for the sound of wind whistling through the gaps, noted and sealed later on.

    They both drew graphs at various pressures and sent a report

    Second guy's result was less than one 0.98

    I asked about their worse results and both told me that had been to new houses where their fan could not raise the pressure to 50Pa plenty of poor results.

    One problem is that a pass is hopelessly leaky and so their standards are low and OK is not OK
    • CommentAuthorsnyggapa
    • CommentTimeSep 3rd 2014
     
    I used a chap called Martin Gill from here http://www.etophouse.com/ , I found him very good and spent time with me skipping around the house feeling for draughts , checking what he had found in other houses as "problem areas" and generally helpful rather than in a hurry. He did my sap calcs too which was an interactive process rather than just a dump n run.

    We ended up with a score of about 3, most of which was leaking out of the quirky, wonky, sash windows ..
    • CommentAuthorborpin
    • CommentTimeSep 4th 2014
     
    Guy I had, had a TI camera and a smoke stick. Spent the morning here.
    • CommentAuthorTriassic
    • CommentTimeSep 4th 2014
     
    I once worked on a research project, during which BRE pressure tested 25 homes of various ages and construction. It was interesting go see air infiltration through poorly constructed concrete slabs, floating carpets in houses with uninsulated suspended timber floors, loft hatches lifting under the pressure etc.

    Rather than a quick and dirty job done to a price, maybe you should ring round and see how much a day would cost, might be cheaper than you think.
    • CommentAuthorEd Davies
    • CommentTimeSep 4th 2014
     
    Maybe it's best to separate out the diagnosis bit and the testing bit. Make up your own crude fan arrangement to allow finding problems while you're building. No need to make accurate (or any) actual measurements. Then a test once it's built to verify the required level has been reached.

    Testing on the final structure is, IMHO, flawed anyway. E.g., you might have areas which are only sealed by the plasterboard with dreadful thermal bypass behind which is, at the end of the process, undetectable and would be very expensive to fix even if it was detectable but would have been trivial to find and sort out if the basic shell of the house had been tested earlier.
    • CommentAuthorneilu
    • CommentTimeSep 4th 2014
     
    The tester should have been able to tell you your test result there and then.
    He will have been using a software package that controls the fan and runs the test.
    The test does only take 5 minutes and the software gives the result immediately.
    So the only reason I can think of as to why he couldn't give you the result was if he hadn't calculated the envelope area, which he should do before doing the test.

    Did you go to one of the big companies to do the test or a smaller company?
    I know that some companies have people in the office that calculate the envelope areas from drawings rather than it being done by the tester themselves.
    • CommentAuthordickster
    • CommentTimeSep 4th 2014
     
    So, we scratched around for an air test company. with the builder abroad and really worried that we might fail the test.

    I sealed all openings beforehand. Architect arrived to witness his first test on site.

    Fan in doorway, computerised read out. Didn't work at first, more fiddling and result just over one. Considering there was nowhere for the air to go, I was disappointed, then I noticed that the seal around the door had blown apart. Bloke basically said, well you've passed by a mile so it doesn't matter. I was too slow and didn't voice my objections, bloke went off, architect (and builder, who phoned up for result whilst on holiday) all very pleased.

    Hey ho, I wonder what the real result would have been?
    • CommentAuthorEd Davies
    • CommentTimeSep 4th 2014 edited
     
    Posted By: dickster… then I noticed that the seal around the door had blown apart …
    Yes, I've wondered about that - the test does test the temporary seal made by the blower door but doesn't test the actual seal made by the real door. Not ideal.
  1.  
    Posted By: Ed Davies
    Posted By: dickster… then I noticed that the seal around the door had blown apart …
    Yes, I've wondered about that - the test does test the temporary seal made by the blower door but doesn't test the actual seal made by the real door. Not ideal.
    Unless you go for dodgy cheap doors you shouldn't have a problem Ed. Our front door and utility room door are almost identical save for a small glazed panel in the front door. I made sure to check the seals on the utility room door with a smoke pen when the house was both pressurised and depressurised and didn't find a hint of a leak.

    I'd echo your sentiments about testing the house before the plasterboard is in place so that if there is a problem it can be found and fixed. It did cause us some problems however as the software got upset due to the change in internal volume due to the airtightness layer getting sucked in/blown out. It was also quite scary to witness the pressure put on the foil and the taped joints, it was tight as a drum at 50Pa, but thankfully all held together, the tester told me he had left another house in tatters when testing in similar circumstances for a "professional" builder.
    • CommentAuthorShevek
    • CommentTimeSep 4th 2014 edited
     
    Posted By: Ed DaviesMaybe it's best to separate out the diagnosis bit and the testing bit. Make up your own crude fan arrangement to allow finding problems while you're building.

    Would a petrol powered garden blower be powerful enough?

    Is this too powerful?
    http://www.ebay.co.uk/itm/Stoney-Racing-16-120W-Electric-Radiator-Fan-Universal-12v-Slimline-/181428101106

    Fan speed: 2100-2390rpm
    NTP airflow rating*: 1575cfm
    Maximum airflow rating*: 2650cfm
    Outer dimensions: 437mm x 405mm x 66mm
  2.  
    • CommentAuthorGreenfish
    • CommentTimeSep 4th 2014
     
    Posted By: Ed DaviesMaybe it's best to separate out the diagnosis bit and the testing bit. Make up your own crude fan arrangement to allow finding problems while you're building.

    Can you hire the fan kit (without the operator) from anywhere?
    • CommentAuthorEd Davies
    • CommentTimeSep 4th 2014
     
    Difficult to tell without a proper performance curve (flow rate against back pressure) but if it was 25% efficient it would produce roughly 50 Pa at the rated flow rate so it's probably in the right ballpark.

    Posted By: Chris P BaconIt was also quite scary to witness the pressure put on the foil and the taped joints, it was tight as a drum at 50Pa, but thankfully all held together, the tester told me he had left another house in tatters when testing in similar circumstances for a "professional" builder.
    That's also scary in a different way - windy weather can produce a lot more than 50 Pa. I wonder how many installations pass the pressure test then are reduced to tatters (unseen behind the plasterboard) by the next winter storm.

    E.g., 20 m/s (only a Beaufort scale “fresh gale”) would produce a dynamic pressure of ½ρv² = 0.5 * 1.3 * 20 * 20 = 260 Pa and that's just the steady pressure without the effects of momentum and gusts.
    • CommentAuthorneilu
    • CommentTimeSep 5th 2014
     
    You need to do a quick calculation.
    Work out your envelope area see ATTMA guide below:

    http://www.bindt.org/downloads/ATTMA%20TSL1%20Issue%201.pdf

    Lets say its 400m2.
    If the air tightness is 3.00 m3/h.m2 at 50 pascals then the fan would run at a flow rate of 1200 m3/h (cubic metre per hour) at 50 pascals.
    An online conversion says that 1200m3/h equals 706 cfm (cubic foot per minute) so well within the range of the radiator fan.

    If you are trying to find leaks then you want to be running the fans as fast as possible.
    When I'm finding leaks in buildings I take all the rings out of the fan and run it at top speed which gives a flow rate of about 7500m3/h. 2650cfm equates to 4500m3/h so not as powerful but still reasonable.
    If you think that your house is very airtight then 4500m3/h should be good enough to find the leaks.

    There are companies that hire out the equipment (I'm not sure if I'm allowed to mention them on here). I'm not sure if they will hire out to anybody not qualified plus I've no idea of the cost.
    • CommentAuthorGreenfish
    • CommentTimeSep 9th 2014
     
    I have been told that we achieved just over 1, not bad given the MVHR was not sealed and there were obvious leaks around the fan itself, paper report to follow. Tester thinks it is an amazing result, but I feel quite disappointed. The build is better than that, but I don't know by how much, nor do I know if there are any leaks we could fix.

    Other than self satsfaction, is there any thing to gain from another test? Would a DIY test be able to locate leaks in such an air tight build? Depressure at max fan speed and feeling for leaks wth a hand? Worth hiring someone specfically to run the fan while we look for leaks rather than just generate a number for building control? Should I wait a year and test then showing how the building is settling in too?

    If it had been below 1 then the beers would be on me!
    • CommentAuthorTriassic
    • CommentTimeSep 9th 2014
     
    Posted By: Greenfishachieved just over 1, not bad given the MVHR was not sealed and there were obvious leaks around the fan itself
    I'd say the beers are on you..
    •  
      CommentAuthordjh
    • CommentTimeSep 9th 2014
     
    Posted By: GreenfishI have been told that we achieved just over 1, not bad given the MVHR was not sealed and there were obvious leaks around the fan itself, paper report to follow. Tester thinks it is an amazing result, but I feel quite disappointed. The build is better than that, but I don't know by how much, nor do I know if there are any leaks we could fix.

    I'm trying to organize my first test. Who did your test, so I can avoid them? (whisper if you don't want to publically shame). I think it is key to check up front that they know how to do a PH test rather than a building regs one. Can you get him to come back?

    Other than self satsfaction, is there any thing to gain from another test? Would a DIY test be able to locate leaks in such an air tight build? Depressure at max fan speed and feeling for leaks wth a hand? Worth hiring someone specfically to run the fan while we look for leaks rather than just generate a number for building control? Should I wait a year and test then showing how the building is settling in too?

    I think it's definitely worthwhile to have access to a fan for leak location. Crank it up to max and use a smoke pencil or cigarette or back of the hand etc etc. I figured it was cheap and easy enough to build a simple system to help with leak location. Cetainly cheaper than paying for somebody to come in with their own kit, although you should get the benefit of their experience if you do the latter. The ability to repeat tests later is also something I like the idea of my own lash-up for.
    •  
      CommentAuthorfostertom
    • CommentTimeSep 9th 2014
     
    Yes I intend to get one, once someone else sorts out the best deal or best DIY system!

    Wind pressures - think of a yacht - enormous pressure to create force to drive it through water and waves at speed - look at the engineering to withstand that pressure and force, which sometimes still breaks - look at the quality of the 'membrane' - any sticky tape there? - know that your house will suffer all those forces over a long lifetime, over very large 'sail area'. A sail generally only experiences forces in one direction; a house's membrane experiences frequent fatiguing pressure reversals, with a yank every time.

    I don't rate anything less that glued and screwed OSB, for air barrier. And why not - cheap, ordinary builders merchant materials, ordinary chippy skills, easy and foolproof (though "fools are so damn ingenious" - Mark Twain), robust, repairable, durable.
  3.  
    Posted By: fostertomA sail generally only experiences forces in one direction; a house's membrane experiences frequent fatiguing pressure reversals, with a yank every time.
    Unless I misunderstand then there won't be "a yank" on the membrane unless there is a void on one side. A membrane sandwiched between solid layers of construction just won't experience anything like the same forces as a sail in the wind.
    •  
      CommentAuthorfostertom
    • CommentTimeSep 9th 2014
     
    Many places there will be a void, intended or not. Pulled taut, inelastic membrane, the slightest bellying force on membrane yanks sideways considerably on tiny sharp edged staple shanks; or if clamped by batten, which shrinks microscopically, allows unclamped movement to reach the nail shanks. Particularly at tricky corners, membranes will be asked to bridge, imperfectly supported. Wherever there's a L-section tape joint e.g. to window frame, pipe etc, by definition it's unsupported, relying on tape adhesive not deteriorating and not creeping, over a lifetime.
    • CommentAuthorGreenfish
    • CommentTimeSep 10th 2014 edited
     
    Posted By: djhI'm trying to organize my first test. Who did your test, so I can avoid them? (whisper if you don't want to publically shame).
    Used a local guy, you should be OK if not in my part of the world. To be fair he was nice enough, just didn't get (no matter what I said) that I was interested in more than passing. In 7 years of testing he said I was one of the few even interested in the test process. Mostly he was just worn down by the abusive atttude of most builders and architects he encountered daily. Great shame, and my mistake for not putting my test requrements e.g. seeking leaks even if they are small, and nialing as small a value as possible, on paper as contractual.

    I think it is key to check up front that they know how to do a PH test rather than a building regs one. Can you get him to come back?
    Yes, simply telling them my design aims for air tightness was not enough. Find someone intereted in their job rather than jaded. Sure he would come back if I paid him, but I doubt he has accuracy in his skill set.

    Have found a place where I can hire a fan for leak testing, but not the manometers, software etc. and didn't get the price. However they advsed that seeking leaks in such an air tight build would be rather futile. Anyone agree?
    • CommentAuthorEd Davies
    • CommentTimeSep 10th 2014
     
    I think there's a lot to be said for your idea of testing again in a year - or, at least, after the winter.
  4.  
    @Greenfish you can probably estimate what the savings would be if you were to say halve your air tightness result. Although I'm not sure how you get figures for hourly wind speeds at your location and then relate them to the temperature differential at the same time. Sounds like a job for ST!

    Maybe just take a worst case scenario of a cold and windy day and figure out what the potential difference will be.

    That would be an interesting exercise.
    •  
      CommentAuthordjh
    • CommentTimeSep 10th 2014
     
    Greenfish quoth: "Have found a place where I can hire a fan for leak testing, but not the manometers, software etc. and didn't get the price. However they advsed that seeking leaks in such an air tight build would be rather futile. Anyone agree?"

    I posted the bits that I've bought at the bottom of this page:
    http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=7396&page=5

    It's a very useful thread. For finding leaks, I don't think you need any software, or even a manometer, or an adjustable power supply. Just a fan and something to power it and a smoke pencil or something to find the leaks. Actually, if you have MVHR then you can use it to depressurise the house. I think the details are in that other thread.

    I don't see why it's futile to look for leaks. I think it just speaks to a difference between their knowledge and expectations and yours.
    •  
      CommentAuthorSteamyTea
    • CommentTimeSep 10th 2014
     
    Posted By: Chris P BaconSounds like a job for ST!
    Greenfish is local too, and the weather data is easy to get hold off (and I can take down my new weather station and bring that along).

    I think we had a thread on here about DIY testing and our old mate J S Harris told us how to make a manometer and control a fan.
  5.  
    I was thinking more along the lines of a theoretical calculation ST.

    Based on historical weather data how many litres of heated air will be lost from the house on a particularly cold and windy day?

    How many kWhrs that represents calculated for both 1ACH and 0.5ACH so Greenfish (and others) can figure out how much effort it is worth going to to achieve the absolute best result possible.

    A ballpark figure is all that is required. Is the difference going to cost an extra 10p a day or £2 a day?

    So given a heating season of around 120 days what is the total cost impact of better airtightness likely to be each year?
    •  
      CommentAuthorSteamyTea
    • CommentTimeSep 11th 2014
     
    Posted By: Chris P BaconI was thinking more along the lines of a theoretical calculation ST.

    Like I did here with windspeed.
    http://www.greenbuildingforum.co.uk/forum114/comments.php?DiscussionID=11624&page=1
  6.  
    •  
      CommentAuthordjh
    • CommentTimeSep 11th 2014
     
    Posted By: Chris P BaconHow many kWhrs that represents calculated for both 1ACH and 0.5ACH so Greenfish (and others) can figure out how much effort it is worth going to to achieve the absolute best result possible.

    Sadly perhaps, the reason quoted for such a tight airtightness level in PH isn't to do with the energy or cash saved directly. The point as I understand it is to avoid drafts and to maintain internal surface temperature everywhere. That in turn allows you to reduce the internal air temperature by a degree or two whilst maintaining the same level of comfort, and that is what saves the energy and cash.
   