Home  5  Books  5  GBEzine  5  News  5  HelpDesk  5  Register  5  GreenBuilding.co.uk
Not signed in (Sign In)

Categories



Green Building Bible, Fourth Edition
Green Building Bible, fourth edition (both books)
These two books are the perfect starting place to help you get to grips with one of the most vitally important aspects of our society - our homes and living environment.

PLEASE NOTE: A download link for Volume 1 will be sent to you by email and Volume 2 will be sent to you by post as a book.

Buy individually or both books together. Delivery is free!


powered by Surfing Waves




Vanilla 1.0.3 is a product of Lussumo. More Information: Documentation, Community Support.

Welcome to new Forum Visitors
Join the forum now and benefit from discussions with thousands of other green building fans and discounts on Green Building Press publications: Apply now.




    • CommentAuthorHerodotus
    • CommentTimeDec 6th 2019
     
    We're putting in a solar thermal system in southern spain to power a radiant floor. The design load is 35 kwh/day (small house, lots of insulation, triple glazing). We're hoping to supply most of our needs just from the sun, so we're going to be installing 10.8k (nominal) of solar thermal. In order to keep the system efficient, we're looking at a solar store tank of 1000l, which should allow us to operate in a temperature range of 35-65 degrees. To keep things simple, my preference is to use a drainback system pumped directly into the main tank rather than mucking about with glycol, pressurized circuits and a coil.

    The concern I have - largely driven by advice from suppliers/plumbers here - is that it's a really bad idea to mix circuits that contain air with UFH - because it's a recipe for corrosion, part failure and things filling up with sludge; this would imply that it's a bad idea to pump the water from the main tank directly around the floor if it's also being used as the drainback circuit water. Is this something people here have opinions on?

    Assuming that it *is* a bad idea, do people think I'd be best off moving to an isolated circuit for the solar - I could make my own drainback vessel easily enough and put a solar coil in the main tank; or should I extract the heat from the tank for the floor using a coil instead? I'm still toying with the idea of making the main tank myself so I'd potentially have some flexibility in this regard.
    • CommentAuthorgyrogear
    • CommentTimeDec 6th 2019
     
    FWIW, I am installing a system where the drainback tank is pumped through the floor, I used oxygen-barrier PEX and will be using a plastic tank and a bronze circulator.

    gg
    • CommentAuthorHerodotus
    • CommentTimeDec 6th 2019
     
    @gyrogear - that's interesting. Are you using the same spec pipe/pump for the solar side as well then?
    • CommentAuthorgyrogear
    • CommentTimeDec 6th 2019 edited
     
    Yes the PEX is the same : 100 meters in the floor, and 66 meters from tank to collector and back...

    http://certipubli.cstb.fr/2016/138/2935-153-2113.pdf

    Not got the pumps sorted yet, but they will be Salmson becos that's what my oppo has got and he told me to go to the same route !

    http://www.salmson.com/fileadmin/user_upload/UPLOAD/product/notice_technique/SXS_NT_FR_50Hz.pdf

    My tank is supposedly good to 90°C, I doubt it will get anywhere near that ! (especially in December) :devil:

    gg
  1.  
    Herodotus, I'm wondering which parts of the system are expected to have corrosion? It won't be in the UFH pipes themselves as they are plastic. If it's the flow/return pipes and pumps, then they will be much the same as the supply pipes for the solar system, so that line of thought might suggest that you should not have drain back at all?

    For bacteria buildup (sludge) the water should be treated with anti floculants, and you ought to have a strainer in the system pre-UFH to catch lumps.

    I've used drainback often, but on a separate loop with coil in the thermal store. That was not for any corrosion reasons, but rather because the solar collectors/drain back tank are at the highest point in the building, and so difficult to get the F&E tank and open vent above that.

    I'd have thought having say a log boiler stove linked to a thermal store with UFH would be a much greater source of lumpy bits in the water, as it's likely a steel jacket on the stove, going through quite large temp fluctuations.

    Did the plumbers give any reason behind their theory?
  2.  
    To keep people happy why not put in a heat exchanger some where to separate the solar thermal from the UFH.
    Options
    Tube heat exchanger in the heat store to feed UFH
    Plate heat exchanger external to the heat store to feed UFH
    Tube heat exchanger in the heat store to to take the output from the solar thermal.

    If you use the tube heat exchanger in the heat store to to take the output from the solar thermal then water volume will be fairly small so it would be economical to use antifreeze/inhibitor in the solar thermal and not have a drain back system.
    • CommentAuthorHerodotus
    • CommentTimeDec 14th 2019
     
    So i'm tying myself up in knots with this now. In the end the drainback option has gone by the wayside: we're using too many panels now and it's going to be too much of a PITA to arrange a consistent fall across the whole array back to the store, so we're just going to have a closed glycol-filled circuit and be done with it.... But we *are* going to be using a log boiler as a backup heat source, and this creates it's own set of problems.

    AFAICT most log boiler manufacturers recommend heating the primary thermal store directly using the boiler rather than using an indirect coil. I've seem some designs from UK stove manufacturers showing an open-vented gravity-fed primary circuit heating a DHW cylinder via a coil, but these all seem designed for relatively low output back boilers in the 2-10kw range rather than a dedicated 20+kw log boiler. I'm concerned that a coil - particularly one positioned in the middle or higher of the store - is going to struggle to keep up with the heat output of the log boiler, particularly once the stop of the store starts to warm up. It seems like for both safety and efficiency reasons we'd be a lot better off pumping/gravity feeding the store water directly... does anyone have any thoughts on this?

    If we do feed the store water directly through the boiler, we've got potential sludge issues, since it will obviously need to be open vented. A PHX on the UFH side has been suggested as an option above, but I've read that it can be a problem due to the fact that UFH wants a relatively small temperature difference between flow and return, so return temps on the primary side of the PHX tend to be higher than you'd want to maintain good stratification in the store.

    With appropriate filters/magnaclean/inhibitors is it practical to combine an open-vented store + log-boiler with UFH pumped directly from the store? Can anyone with long-term experience with this sort of setup comment on the corrosion/sludge aspect?

    Thanks again for the all the input!
    • CommentAuthorgyrogear
    • CommentTimeDec 15th 2019 edited
     
    Posted By: Herodotusit's going to be too much of a PITA to arrange a consistent fall across the whole array back to the store


    Just a thought - do you know about the Tichelmann system ?

    https://uk.grundfos.com/service-support/encyclopedia-search/tichelmann-system.html


    Maybe watch this first !
    https://www.youtube.com/watch?v=VlAfTYTA0Z0

    gg
    • CommentAuthorHerodotus
    • CommentTimeDec 15th 2019
     
    Interestingly, here in Spain it seems like the whole open-vented thing is not actually required or even recommended by the manufacturers of solid-fuel appliances. Mechanically activated quench valves are mandated along with pressure relief valves and expansion vessels. Here's a hydronic installation diagram from a Domusa gasification boiler:
      Screenshot from 2019-12-15 09-26-35.png
    • CommentAuthorHerodotus
    • CommentTimeDec 15th 2019
     
    @gyrogear. Yeah, you've reminded me why I didn't want to use glycol in the first place. We're going to have 6 panels for a total nominal output of 10.8kw. Our plumber says he doesn't recommend using drainback with this number of panels.

    Does anyone know if there's a practical limit on how many panels you can have in series and still have drainback working effectively? Do we need to do two sets of 3 in parallel or will 6 drain ok in series? They're the flat plate style panels. It's also complicated because we're running entirely on PV electric, and there's a ~4.5m height difference between the store and the top of the panels - which entails quite a powerful pump, particularly if we put all the panels in series (higher frictional losses). Oh, and we're at 1200m of altitude, so the underpressure thing is potentially going to mean our panels boil at a lower temperature as well :confused: . Although I really like the idea of drainback in principle (simple is good) I wonder if in practice we're just going to encounter a bunch of other, less obvious complexity. See https://backend.orbit.dtu.dk/ws/files/140025523/drain.pdf for example.
  3.  
    Posted By: HerodotusSo i'm tying myself up in knots with this now. In the end the drainback option has gone by the wayside: we're using too many panels now and it's going to be too much of a PITA to arrange a consistent fall across the whole array back to the store, so we're just going to have a closed glycol-filled circuit and be done with it.... But we *are* going to be using a log boiler as a backup heat source, and this creates it's own set of problems.

    AFAICT most log boiler manufacturers recommend heating the primary thermal store directly using the boiler rather than using an indirect coil. I've seem some designs from UK stove manufacturers showing an open-vented gravity-fed primary circuit heating a DHW cylinder via a coil, but these all seem designed for relatively low output back boilers in the 2-10kw range rather than a dedicated 20+kw log boiler. I'm concerned that a coil - particularly one positioned in the middle or higher of the store - is going to struggle to keep up with the heat output of the log boiler, particularly once the stop of the store starts to warm up. It seems like for both safety and efficiency reasons we'd be a lot better off pumping/gravity feeding the store water directly... does anyone have any thoughts on this?

    Your 20kw log boiler will need a loading valve to maintain the boiler temp. at about 70 deg (laddomat or similar) otherwise you will over cool the boiler which will give burning efficiency and chimney problems. These valves incorporate a pump and also allow gravity circulation if the pipework is installed to promote this. IMO the boiler should be connected to the thermal store (TS) directly and not via a heat exchanger.

    IMO a reasonable installation would be
    Have the boiler feed the TS directly and the boiler temp. controlled by a loading valve. The boiler and the TS would be open vented and the boiler would be fitted with a mechanical quench valve although these are of little value unless you have mains water.

    Have the solar panels on a closed glycol-filled circuit feeding the TS via a coil in the TS (so indirectly connected to the TS)

    Have the UFH fed from the TS via either a coil in the TS or an external plate heat exchanger (PHX) with a recirculation valve to maintain the required UFH temp. (IMO a coil would be better than a PHX because there is one less pump and less chance of disturbing the stratification within the TS)

    Have the DHW fed from the TS via a coil in the TS although if you have the space a seperate DHW tank would be better but adds a floor space demand and some plumbing complications.

    With this setup you have 3 independent water volumes, 1 open vented - the boiler and the TS and 2 sealed with pressure vessels, the solar panels (with glycol) and the UFH (with inhibitor?). The DHW if included would be a 4th independent circuit.
    • CommentAuthorHerodotus
    • CommentTimeDec 15th 2019
     
    @Peter - I have been thinking seriously about this option. There are a couple of practical challenges/ downsides with it:

    1) I had hoped to avoid the glycol closed solar circuit. Apart from the intrinsic efficiency downsides of glycol + coil, and the additional components required, it's going to create a bunch of problems in summer. The system is being designed to provide a decent proportion of our space-heating requirements during the winter; during the summer when we have more sun and no space heating needs, it will be massively oversized. A pressurized glycol system is going to give us a bunch of headaches here. We'd probably need to think about splitting the system into two parts and draining one of them, or having some sort of heatsink to dissipate the excess in summer - neither of which I'm very excited about. One possible compromise here is an indirect drainback system with a coil. It's not ideal because most of the efficiency benefits of drainback systems come from losing the heat exchanger component, but at least it avoids the overheating issues.

    2) Stores with 3 coils - two supply and one DHW exchanger - are not that common. Those that exist pretty much all, AFAICT, have one configuration: the DHW coil runs the full height up the middle, then there's a solar coil at the bottom and a smaller, secondary coil towards the upper middle of the store. The primary use case for this is to have an additional, higher temperature heat source input - e.g. a boiler. Running the UFH through this coil isn't ideal because you're skipping the whole of the bottom half of the store - which is exactly where you want to be working for a low-temperature circuit like UFH. This is certainly still better than returning overly hot water to the bottom of the store as would most likely happen with a PHX on the UFH circuit, but it's still not great.
  4.  
    Herodotus
    What are your plans for DHW?
    Any solar thermal (ST)system designed for space heating in the winter is IMO going to have overheat issues in the summer especially in Spain.
    It is not unusual for annual DHW demands to be somewhere about the winter space heating demands - depending upon the insulation values of the house DHW could be higher than space heating requirements.

    If you have a drain back system to avoid the overheating in the summer you are still looking at inefficiencies, think about the amount of surplus ST capacity that will only be used in the winter and the redundant investment cost of this for a good part of the year.

    Are you wedded to a ST system? PV is reducing in price/Watt and if you use PV and an immersion heater for the DHW when the tank is up to temp - you can always use the spare power to feed the grid or power freezers etc. With this approach if you had a separate DHW tank then in winter you can prioritise the DHW and when this is up to temp divert the PV to an immersion heater in the TS. If you run on just the TS then the PV heats the TS all year around. (Although it is generally recommended to separate space heating and DHW heat storage).

    The TS configuration of the DHW coil running the full height up the middle, then there's a solar coil at the bottom and a smaller, secondary coil towards the upper middle of the store, I would use the upper middle coil as the UHF coil and the boiler running direct. This means that the DHW has a priority amount of heat at the top of the store that is not available for space heating.
    • CommentAuthorgyrogear
    • CommentTimeDec 15th 2019 edited
     
    Posted By: HerodotusDoes anyone know if there's a practical limit on how many panels you can have in series and still have drainback working effectively? Do we need to do two sets of 3 in parallel or will 6 drain ok in series?


    The answers to those questions are in here :

    https://www.youtube.com/watch?v=CW9YVaPW9wU

    "collector arrangements" at cue 12':49''

    especially important = linear expansion on long systems : ends at 15:41...

    relatively explicit :devil:

    gg
    • CommentAuthorHerodotus
    • CommentTimeDec 15th 2019
     
    @gyrogear - thanks that's brilliant, i will take a look now. I tend to forget about youtube because I default to reading rather than watching to learn stuff!

    @peter. I don't think PV is a credible solution. We already have 3750w of PV panels and we're not going to have much spare in the winter. Our heat losses will be around 35kwh / day during the colder parts of the winter - possibly slightly less given passive gain, but that's most likely offset by the failure of our builders here to make anything to the specification I actually asked for. With a 6 hour solar day and typical efficiencies I reckon we'd need *at least* another 6k of PV to meet our heat requirements. I literally don't have enough roof space for that, let alone factoring in the cost of new charge control etc. If you need heat, ST is *much* more space efficient than PV; and ST is cheap here anyway: 10.8k of panels, including plumbing fittings and support framework will set you back about 1.5k euros. Obviously most of it's going to be wasted in summer, but it's not *that* much money and TBH I'm struggling to think what we'd do with the surplus PV output in summer either!

    Economic efficiency is also not a primary motivation here. Economically speaking, by *far* the cheapest option would have been a dedicated thermosyphon solar water heater with backup gas boiler and a LBS in the living room. Wood is free and gas is dirt cheap (12.80 for a 12.5kg butane cylinder). We would have saved thousands in costs and a lot of heartache but we're prioritising long-term convenience and avoiding burning things as much as possible over saving money.

    Our DHW energy requirements are relatively small - at most 10kwh / day, and usually more like half that I'd imagine. I'd imagine that annual DHW requirements are not massively different to the space heating requirements.

    I was planning on having some separate DHW storage which could be heated by the log boiler independently. I'd hope that most of the time it'd be unnecessary. See attached. (And before anyone jumps on me for having a closed circuit on a solid fuel appliance, this is the recommended plumbing from the boiler manual. See the picture higher up the thread.)
      heating system.jpeg
  5.  
    Posted By: HerodotusOne possible compromise here is an indirect drainback system with a coil. It's not ideal because most of the efficiency benefits of drainback systems come from losing the heat exchanger component, but at least it avoids the overheating issues.

    Sounds like this would be the way to go
    • CommentAuthorgyrogear
    • CommentTimeDec 15th 2019 edited
     
    Posted By: HerodotusST is cheap here anyway: 10.8k of panels, including plumbing fittings and support framework will set you back about 1.5k euros. Obviously most of it's going to be wasted in summer


    unless you can somehow inject it into your subsoil...

    (FWIW, what stage is your construction at ? What type of foundations ?)

    gg
    • CommentAuthorGreenPaddy
    • CommentTimeDec 16th 2019
     
    Herodotus,

    can I ask why you have a 20kW log boiler? At 35kWh/day heat loss in winter, you're looking at 2kW power input. 20kW seems a lot. Maybe you inherited it with the house, or want to do a single batch burn to charge the TS once, and then forget about the boiler? Even so, about 2 hours running would fully load the TS from totally cold (looks like 750 litre on drawing?).

    In terms of solar thermal, I always install drainback, to avoid a pressurised system, with summer boiling, winter freezing, pressurised charging with glycol, and the typical conditions in UK of sun/cloud/sun/cloud, whereby drainback holds the heated water inside the thermal envelope, not out on the roof. Not suggesting pressurised is wrong, or worse, just my opinion as the person the client will call if there's ever an issue.

    6 panels in series will give a very high output temp, even in winter. Like you, I'm wondering about 2 triples or even 3 pairs in parallel? If you have a variable speed pump, the solar controller would vary the pump speed / flow rate to suit.

    Whilst I mention solar controller, I assume you will use your solar controller to manage the boiler pump?

    Your separate (duplicate) DHW cyl worries me a bit, in terms of legionella control. The 100 L could sit unused at uncontrolled temps for periods of time. Would you consider NOT taking DHW from the thermal store? Use it as a buffer tank to receive the boiler and solar input. Then draw UFH and a hot feed to the DHW cyl? 100 litres seems a bit small anyway.

    I think a better answer, (maybe?), install two solar coils, one top and one bottom, with a solar transfer valve. That will direct hottest solar input to top, with cooler towards the base. That way you'll make better use of high temp solar input, having better DHW reservoir at the top of the TS. NoGets rid a separate DHW cyl, a couple of3 port valves, and some control logic to decide when to draw DHW from which cyl.

    So essentially as per your drwg, but remove the DHW cyl and the two 3-ports, and add a second solar coil above the lower one, plus a solar transfer valve.

    The high lift to the solar panels - could you just put 2 cheap domestic circ pumps in series, avoiding going to a much more expensive "commerical" high pressure pump?

    Hope there's something amongst that of use to you?
    • CommentAuthorborpin
    • CommentTimeDec 16th 2019
     
    As a matter of interest (as I have looked and not found one), what drainback systems & components are being considered? For various reasons I have some ST that I have ever connected up - it needs to be an indirect drain back system (i.e. ST water passes through coil in tank via diverter).
    • CommentAuthorGreenPaddy
    • CommentTimeDec 17th 2019
     
    I personally don't buy a "system". It's only 4 or 5 components, so why pay someone else to group those in a box?

    - panel capable of draining (no that many which the manuf actually state as drainback, but some do state it, and others are drain back but manuf doesn't state it. Does the water run out under gravity in your chosen orientation?). Look for suppliers of drain back complete systems, then buy that panel, or find the manufacturer of that panel. Get the manuf internal pipe work/connection drwg,and confirm for yourself that it's drainable.

    - circ pump

    - drainback tank (get this made by the therm store manufacturer Ne**rk Cop Cyl). It's only a little insulated pot with a few ports, one with a dip leg

    - solar controller (take your pick. I choose ones that also allow me to run a log boiler stove, and have 3 temp sensors for the TS)
    • CommentAuthorborpin
    • CommentTimeDec 18th 2019 edited
     
    Posted By: GreenPaddyI personally don't buy a "system"
    No I wasn't intending to. The panels less the tubes are already mounted, the SS ribbed pipes are run less the final connections. It is the tank, pump and controller that I have been trying to find someone to offer advice on.

    Panels are EconNomical(?) ones but they seem to have vanished. EV tubes into a manifold.
    • CommentAuthorHerodotus
    • CommentTimeFeb 1st 2020 edited
     
    Slightly necro-ing my own thread... but hey. I'm still puzzling this out and really running out of time to make decision on this now.

    Posted By: GreenPaddycan I ask why you have a 20kW log boiler?

    Two reasons: firstly because for dedicated boilers (as opposed to a LBS with a back boiler) it's actually quite hard to find anything under 15-20kw. I don't want anything that burns wood in the house because it takes up loads of space and it makes mess/dust. Secondly, as you surmised, because I'd rather be able to load it once a day, do a fast, hot, efficient burn and dump that heat into the TS. i don't want to be popping out to the boiler room all day to keep it stoked up.

    I take the point about legionella. The tricky thing here is balancing having a guaranteed supply of DHW with avoiding legionella problems. Since we don't have an automatic heat source that is guaranteed to produce > 60 degree temperatures there's no perfect solution to this problem. The safest option, as you say, is to dispense with the secondary hot water tank, and this was always my preference. The downside is that if we have a really cold night and the floor sucks up a lot of heat, we could wake up in the morning with little/no hot water. I guess some extra intelligence in the control programme could help to avoid that (I'm building my own controller from a Raspberry PI + a bunch of 1-wire thermo sensors). Maybe the best fix for this is just a cheap gas backup for emergencies.

    The health of the floor is still concerning to me. It's the one thing that is utterly inaccessible and almost impossible to fix if it goes wrong, so it makes sense to take all possible precautions against it becoming clogged up with crap. I know there are different schools of thought on this but there do seem to be a lot of plumbers (and most of the manufacturers/suppliers) who strongly recommend having a sealed system for the floor. I'm wavering between: Peter's suggestion of running the floor through a coil and leaving the rest of the system unpressurized; or alternatively keeping just the solar circuit unpressurized with a coil of some sort into the TS. The choice basically comes down to what the log boiler needs. At the moment we're looking at one that wants a pressurized circuit so I think the second option is probably better.
    • CommentAuthorgyrogear
    • CommentTimeFeb 1st 2020
     
    "The downside is that if we have a really cold night and the floor sucks up a lot of heat, we could wake up in the morning with little/no hot water".

    Er, I don't think that that is how the floor is supposed to work...

    The idea of the floor is to produce a thermal flywheel effect: if it was built right with (notably the correct level of edge insulation ), the raison d'être of the floor is to GET you through the stated "cold night"... by relying on the heat already stored in the slab.

    gg
    •  
      CommentAuthordjh
    • CommentTimeFeb 1st 2020
     
    If you use the TS (or even a separate TS) for DHW then you don't have to worry about legionella.

    If you use a coil in the bottom half of the TS to supply a closed-circuit UFH system then you'll answer most of your rust etc worry and a filter will fix the rest. A coil in the bottom shouldn't take heat from the top of the store, as long as it stays stratified.

    So if you use a coil in the top half of the store for DHW you should be OK ordinarily. An immersion halfway up the store will provide backup for DHW, or alternatively an inline heater could be used.

    Coil(s) for the solar input as well. Then the TS could be unpressurised with an open-vented stove or could be pressurised with your proposed model.

    I say bottom half and top half, but sizing the volumes appropriately may mean some different ratio. Or you could have two separate TS in parallel, which some seem to prefer.
    • CommentAuthorHerodotus
    • CommentTimeFeb 2nd 2020
     
    Posted By: gyrogear

    Er, I don't think that that is how the floor is supposed to work...

    The idea of the floor is to produce a thermal flywheel effect: if it was built right with (notably the correct level of edge insulation ), the raison d'être of the floor is to GET you through the stated "cold night"... by relying on the heat already stored in the slab.

    gg


    Sorry, I was simplifying somewhat. Yes, there's lots of insulation, and yes there's a screed with tiled floors on top that will act as a thermal mass that evens out the variations. But the thermal capacity of the floor itself is still significantly lower than that of the thermal store because it's cement not water, and because it isn't being heated to 70+ degrees. It provides a limited buffer of ~10kwh of energy, but to be honest that's not really the point, because the control system will general try and avoid letting the floor temperatures drop significantly, so that buffer only really comes into play when the TS has run out of energy anyway.

    The point is that during a cold period with limited sun, there will most likely come a stage - perhaps after a delay of a day or two - where the heat losses from the house have pulled more heat out of the TS than the panels have put back in. In principle, the room stats and control system will keep the floor running to keep the house temperatures where we want them until the store temperature drops below 35.

    Our backup heat source (log boiler) requires manual intervention to work. If for some reason we don't anticipate the heat demand correctly, or we're out for more than a day, it's possible that we're going to run into a situation where the TS has dropped to 35C or thereabouts. If it stratifies well we should end up with a little bit of hotter water at the top for DHW production, but there are no guarantees with this, particularly since we're using an internal finned SS coil rather than an external PHX (which I don't want for lots of reasons).

    So we have to light the log boiler. It now has to heat a big 800l tank of water by at least 15 degrees before we start getting hot water again. Again, if we're lucky with stratification, when the boiler starts running and we start feeding 70+C water into the top of the TS, we may be able to start producing hot-ish water quicker. But there's most likely going to be a 30-45 minute delay.

    It's possible that I shouldn't be worried about this. The local Spanish plumbers/suppliers have a horror of the idea that you might end up without immediately available hot water. Having grown in the UK with a household full of people that preferred baths over showers, and a 200l tank that got heated on a timer twice a day, this actually doesn't phase me so much; but I'm being made to feel that I'm being somewhat primitive in this regard. My wife isn't exactly keen on the idea of having to go and load a log boiler and wait for 45 minutes to have hot water either.

    Perhaps the easiest thing is to buy a cheap on-demand gas boiler for a couple of hundred euros, and stick it on a gas bottle for emergencies and be done with it.
    • CommentAuthorHerodotus
    • CommentTimeFeb 2nd 2020
     
    Posted By: djhIf you use the TS (or even a separate TS) for DHW then you don't have to worry about legionella.

    If you use a coil in the bottom half of the TS to supply a closed-circuit UFH system then you'll answer most of your rust etc worry and a filter will fix the rest. A coil in the bottom shouldn't take heat from the top of the store, as long as it stays stratified.

    So if you use a coil in the top half of the store for DHW you should be OK ordinarily. An immersion halfway up the store will provide backup for DHW, or alternatively an inline heater could be used.

    Coil(s) for the solar input as well. Then the TS could be unpressurised with an open-vented stove or could be pressurised with your proposed model.

    I say bottom half and top half, but sizing the volumes appropriately may mean some different ratio. Or you could have two separate TS in parallel, which some seem to prefer.


    This is more or less what I'm leaning towards. I'm not going to have two TS in parallel, although this is probably ideal, because (1) money and (2) space.

    I'm looking at something like this: https://biomasalamanca.es/depositos-hygienico-2-serpentin/291-tanque-hygienico-con-serpentin-de-acero-inox-800-litros2-apoyo.html

    It has a coil at the bottom for solar input, one in the middle that I could use to extract heat for the floor, and then a third SS coil with a preheat at the bottom and main coil at the top. The only thing I don't like is that it's uncoated steel (which is surprisingly common here). But I guess with appropriate inhibitor that's not an issue, particularly if I go with a closed pressurized circuit for the boiler.

    The main downside with this approach is that there are two coil heat exchangers between the panels and the floor. That's a lot of inefficiency, particularly as nothing here gets made of copper :sad: If the boiler is on a closed pressurized circuit then in theory there's nothing stopping me pulling the floor water directly from the store itself.

    Or there's the really radical option, where I buy an 800l PP rain water tank, immerse a copper coil for DHW water production and another one to pull out floor heat, and then run the boiler and the solar drainback directly from the water in the tank. I'll need to find a different boiler that will operate at atmospheric pressure though. And I'm probably opening myself to a world of potential boiler failure nonsense there as well since the drainback circuit of necessity has a lot of oxygen in it. That and the sketch factor of building it all myself from scratch.
    • CommentAuthorHerodotus
    • CommentTimeFeb 2nd 2020
     
    I'm guessing that in some regards a lot of my problems would go away if i was willing to use a PHX for DHW production but (1) I'm trying to limit the number of pumps that I need (money, maintenance, limited PV energy) and (2) I just don't trust things that produce hot water based on pressure switches. I'm so fed up with not being able to turn my kitchen tap on just a little bit because the gas boiler cuts out when the flow rate drops.

    I'm sure the proponents of PHX would say that modern fancy ones don't have these problems but I remain sceptical and it just seems like a complex solution with multiple points of potential failure compared to a coil in a tank.
    • CommentAuthorCWatters
    • CommentTimeFeb 3rd 2020
     
    Just for info.. We have an open vented thermal store and unpressurized UFH. Same water circulates through the boiler. Dosed the system with Fernox F1 corrosion inhibitor. No worries. Just make sure you put enough in. Don't just tip a bottle in, calculate the number of bottles needed based on the volume and recommend concentration. You might need 3-6 bottles if you have a big thermal store. I was advised not to drain and refill too frequently as that introduces oxygen.
  6.  
    Hi, we built some Solar Enhanced Passive Houses using 40m2 and 60m2 Solar Drain-Back arrays and no heat exchangers.
    http://viking-house.ie/solar-enhanced-passive-house.html#prettyPhoto
    http://viking-house.ie/solar-enhanced-passive-house-louth.html
    These houses remain in Ireland's top 5 most energy efficient houses with annual heating, hot water and electricity costs of less than €200 per annum.
    • CommentAuthorfreemp31
    • CommentTimeFeb 4th 2020
     
    I don't know why, but I get the impression there are people here who are fighting shy of pressurized systems. All you need is an expansion vessel 10% the size of your total capacity, pressure relief valves and a 8 bar meter and you're away.
    I have a 48kw gasification boiler feeding a 3000L TS with a coil for DHW take off (not yet connected) and a Solar coil (in the process of ng now)
    This is directly fed from the boiler via a Laddomat which opens at something like 62C and progressively bleeds back less and less of the hot to the boiler return as the temp rises. The output from the TS is mixed down with sufficient of the returning cold (cool) to deliver at about 68C

    I have a mix of rads and UFH (3 discrete manifolds the largest of which has 3 separate zones) each of these manifolds has a thermostatic mixer valve and pump so the temp of the UFH circuits are reliably constant - vital in my opinion if the TS is being fired from a non-automatic source like a maunually filled gasification boiler. The components are 3.5bar rated, and I run it at 0.5bar (cold) and even when the TS is fully charged to about 75-85C the system doesn't climb much higher than 1.5 to just under 2 bar with an expansion tank of 250L.
    The system has been up and running for about 10 years now and I have recently flushed the crud out of biggest (and lowest) UFH manifold in order to find why it was getting less and less efficient. Jet black, of course, but not a vast amount of mush in the actual loops. Turned out the problem was a pair of flexibles connecting the manifold were crudded up completely (this was a solution to a first fix/second fix/trying to plumb with a house full of other trades chasing me/scenario and was never meant to be permanent! A change to 22mm CU fixed that!)

    There is nothing to be gained by under-sizing a Gasification boiler/TS combo (apart from the cost). There's something very satisfying about popping out to the barn to check on the TS thermometers on a mild day, only to discover you don't have to do a firing at all today, and on the other hand, a system only *just* big enough for the heat demand, requiring loading/firing 2 or 3 times a day in very cold weather, is a daily routine which gets old very quickly!

    The solar panels will be 4 x 18 evac. tubes (again pressurized), obviously a separate sealed system feeding the coil in the TS, switchable to a swimming pool heat exchanger, and to a smaller 300L TS for a new DHW system pre-heat coil. At the moment the switching will be manual, but future-proofing all this with mororized valves!
    I'm looking to this addition to affect the 'shoulders' of the heating system: there is perhaps a 2 or 3 weeks in the Spring and Autumn when a full burn isn't necessary every day, but the o/night temps are still low. Added to which I have long grieved at the waste of free heat every time I stand by this south-facing wall barn wall and (even in January after a sunny day) I can feel the heat being radiated off it.
    It will be interesting to see just how much contribution 12 sqm of panels makes when I get it up and running.

    As my old English teacher, Henry Thomas, used to say, "our policy, like Fords, is one of continuous improvement" !
   