Green Building Forum - Build tight ventilate right Tue, 19 Dec 2023 05:51:48 +0000 http://www.greenbuildingforum.co.uk/newforum/ Lussumo Vanilla 1.0.3 Build tight ventilate right http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=15102&Focus=258370#Comment_258370 http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=15102&Focus=258370#Comment_258370 Thu, 25 May 2017 11:49:45 +0100 tony
What does it mean now

How tight is tight, in ACH/h at 50Pa is. It 10, 5, 2, less than 1 or some multiple of 0.1? What does tight mean?

Then what is right in terms on ventilation? Depressurising an air tight building with an extract fan? Opening windows, trickle vents, PIV, MVHR, using poor levels of air tightness?

Anyone like to put numbers on ACH and acceptable heat losses due to ventilation?]]>
Build tight ventilate right http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=15102&Focus=258371#Comment_258371 http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=15102&Focus=258371#Comment_258371 Thu, 25 May 2017 12:17:45 +0100 DarylP Air tightness testing is for uncontrolled ventilation - leaks.
Controlled ventilation is sealed during tests: trickle vents, int. extracts, etc etc
Losses due to ventilation can range from v small, to considerable, depending on the m3 of the dwelling, the numbers/types of vents.
:smile:]]>
Build tight ventilate right http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=15102&Focus=258374#Comment_258374 http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=15102&Focus=258374#Comment_258374 Thu, 25 May 2017 13:06:15 +0100 tony Build tight ventilate right http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=15102&Focus=258376#Comment_258376 http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=15102&Focus=258376#Comment_258376 Thu, 25 May 2017 13:28:31 +0100 djh Posted By: DarylPControlled ventilation is sealed during tests: trickle vents, int. extracts, etc etc
Trickle vents should not be sealed - they should be closed but not sealed. Ventilation systems and extract fans should be sealed, but only the ducts themselves, not the connections to the walls or windows. As usual, this is if the job is being done properly, not according to English tradition.]]>
Build tight ventilate right http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=15102&Focus=258377#Comment_258377 http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=15102&Focus=258377#Comment_258377 Thu, 25 May 2017 13:57:27 +0100 barney
Both are achievable in practice without complex detailing etc - but are dependent on "type" of construction

Values above are about 1/10th of what's considered traditional however so it does need some attention from designers and builders - basically there needs to be a clear air tightness strategy from the beginning and someone to champion that on site

I wouldn't depressurise any building personally - if you want control (and that may include filtering the incoming air to achieve reasonable indoor AQ) then you want positive overpressure - the degree of which will and should vary IMO depending on what's to be achieved

For all buildings with mech ventI would put in G4/F7 filtration as a starting point - then enhance from there depending on location

That said, I like windows that open - people aren't stupid - they will use them but in shared spaces often need an indicator that the AQ is dropping and a bit of fresh is needed

I'm still not convinced by the need for MVHR in pretty airtight domestic properties - windows are perfectly capable of being used to maintain IAQ without presenting a significant energy burden

Regards

Barney]]>
Build tight ventilate right http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=15102&Focus=258378#Comment_258378 http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=15102&Focus=258378#Comment_258378 Thu, 25 May 2017 14:07:46 +0100 Sigaldry
Below 3m³/m²/hr @ 50 Pa is best practice (combined with a mechanical ventilation system (with a low fan power and heat recovery - essential below this level; recommended below AT=5).

See EST GPG 224 and EST GPG 268 for some good practice guidance on ventilation and low air tightness.

Attention to detail can get you below 1m³/m²/hr @ 50 Pa with a SIPs dwelling (and AT=2-3 is relatively easy it seems), Timber frame seems to be able to get below AT=3-4 reasonably with airtightness layers, attention to detailing/filling gaps; Most masonry dwellings seem to be able to get AT=5-7 easily enough with some care and attention and lower levels doable with a parge coat or plaster. All down to workmanship and thinking about it.]]>
Build tight ventilate right http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=15102&Focus=258382#Comment_258382 http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=15102&Focus=258382#Comment_258382 Thu, 25 May 2017 16:08:41 +0100 tony
I call 5 bad practice and 2 not quite good enough!

In Canada they only want low decimal points]]>
Build tight ventilate right http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=15102&Focus=258385#Comment_258385 http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=15102&Focus=258385#Comment_258385 Thu, 25 May 2017 18:25:53 +0100 gyrogear
One should be comparing apples with apples, no ?

gg]]>
Build tight ventilate right http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=15102&Focus=258389#Comment_258389 http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=15102&Focus=258389#Comment_258389 Thu, 25 May 2017 19:49:09 +0100 fostertom Posted By: gyrogearGuess it just goes to show that we all live in different places on the Planet, with different climates and requirementsTell that to PHPP - which adjusts physical requirements to account for climate - but airtightness not negotiable.]]> Build tight ventilate right http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=15102&Focus=258395#Comment_258395 http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=15102&Focus=258395#Comment_258395 Thu, 25 May 2017 21:22:02 +0100 gravelld Posted By: djh
Trickle vents should not be sealed - they should be closed but not sealed. Ventilation systems and extract fans should be sealed, but only the ducts themselves, not the connections to the walls or windows.Similarly, do you not think 'common or garden' dumb on demand extract fans should be left off but not sealed? They contribute to the leakiness of the house day-to-day do they not?

Or are they considered to be offering background ventilation when turned off? Seems a bit finger-in-the-air.

Mine were even worse chimneys than my downlighters, fortunately far fewer of them.]]>
Build tight ventilate right http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=15102&Focus=258396#Comment_258396 http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=15102&Focus=258396#Comment_258396 Thu, 25 May 2017 21:22:26 +0100 Ed Davies
Heating degree days to 20 °C for RAF Benson in Oxfordshire is just over 3500 so, without heat recovery, heat loss would be 70 kWd (1680 kWh) per year or about 190 W or nearly a tenth of a 2000 W society person's use. Heating with mains gas, that'd be about £84/year.

Seems worth reducing to me.]]>
Build tight ventilate right http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=15102&Focus=258397#Comment_258397 http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=15102&Focus=258397#Comment_258397 Thu, 25 May 2017 22:01:42 +0100 tony
Any view on air tightness number?]]>
Build tight ventilate right http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=15102&Focus=258399#Comment_258399 http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=15102&Focus=258399#Comment_258399 Thu, 25 May 2017 22:15:42 +0100 djh Posted By: gravelldSimilarly, do you not think 'common or garden' dumb on demand extract fans should be left off but not sealed?
It doesn't really matter what I think; it's what ATTMA thinks that matters. But personally, yes I agree, any extract fan should have its duct closing mechanism tested as part of the test.]]>
Build tight ventilate right http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=15102&Focus=258402#Comment_258402 http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=15102&Focus=258402#Comment_258402 Fri, 26 May 2017 09:26:06 +0100 fostertom Posted By: djhany extract fan should have its duct closing mechanism testedif any - traditionally these are just on open hole in the wall.]]> Build tight ventilate right http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=15102&Focus=258403#Comment_258403 http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=15102&Focus=258403#Comment_258403 Fri, 26 May 2017 09:45:18 +0100 Ed Davies
What's difficult is knowing how the airtightness tests relate to infiltration in practice.

E.g., 50 Pa corresponds (via ½ρv² [¹]) to a wind speed of 8.77 m/s (19.6 mph; Beaufort force 5, fresh breeze [²]) which is probably a bit higher than average but not at all exceptional, particularly during the parts of the year when the heating matters. Of course, wind only blows from one direction but then it tends to produce a negative pressure on the other side of the house. But then many houses are sheltered from direct wind by trees, other buildings, etc.

Plus there's stack effect.

So it's hard to say but I think that if the results of the airtightness test are an order of magnitude more than the ventilation requirements then something's likely wrong. Subject to more information, my guess would be that PH 0.6 AC/h or similar (e.g., 1 m/h) seems a sensible target. Lower if you're somewhere windy.

What I worry about more is lack of windtightness on the outside of the insulation.

[¹] https://en.wikipedia.org/wiki/Stagnation_pressure
[¹] https://en.wikipedia.org/wiki/Beaufort_scale#Beaufort_Number_5]]>
Build tight ventilate right http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=15102&Focus=258404#Comment_258404 http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=15102&Focus=258404#Comment_258404 Fri, 26 May 2017 09:53:08 +0100 Ed Davies
1) It's probably the most cost-effective step.

2) It's, in some ways [¹], easier to check that it's been done properly.

So I'm interpreting the question as what level of airtightness is needed to make sensible use of MHRV (i.e, to recover a significant proportion of the ventilation heat loss). There's the separate issue of not over ventilating on windy days which applies if you're aiming for natural ventilation only but can be ignored if you're aiming for MHRV levels.

[¹] Easy to check at completion, harder to know how it'll last.]]>
Build tight ventilate right http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=15102&Focus=258405#Comment_258405 http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=15102&Focus=258405#Comment_258405 Fri, 26 May 2017 11:04:52 +0100 fostertom Posted By: Ed Davies50 Pa corresponds (via ½ρv²) to a wind speed of 8.77 m/s (19.6 mph; Beaufort force 5, fresh breeze)and (correct me if wrong) about 10mm water. We can easily suck orange squash up a straw 150mm or even 300mm or more, so have at our instant disposal a test rig capable of 30x the 50Pa standard, for a small sample (give it a wipe first!)]]> Build tight ventilate right http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=15102&Focus=258407#Comment_258407 http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=15102&Focus=258407#Comment_258407 Fri, 26 May 2017 11:29:51 +0100 gravelld Posted By: fostertom
Posted By: djhany extract fan should have its duct closing mechanism tested
if any - traditionally these are just on open hole in the wall.I think Dave, from the point of view of measurement, was rightly identifying that the duct can be closed anywhere from 0 to 100% (ignoring the surely immaterial impact of the fan blades), and you're right, a vast, vast majority are at 0%.]]>
Build tight ventilate right http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=15102&Focus=258408#Comment_258408 http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=15102&Focus=258408#Comment_258408 Fri, 26 May 2017 12:02:59 +0100 Ed Davies
Less than that, about 5 mm.

Water has a density of about 1000 kg/m³ so 1 m³ weighs 10'000 newtons (if we round gravity from 9.81 m/s² to 10). The pressure at depth h in millimetres is therefore 10'000 N/m² × h/1000 = 10·h Pa. So 50 Pa is just 5 mm of water.

http://www.kylesconverter.com/pressure/pascals-to-millimeters-of-water agrees, give or take the rounding.

But I agree with Tom's basic point that testing at 50 Pa is pretty weedy.]]>
Build tight ventilate right http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=15102&Focus=258409#Comment_258409 http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=15102&Focus=258409#Comment_258409 Fri, 26 May 2017 12:36:52 +0100 fostertom
I've yet to try sucking on a piece of OSB - could be a good check at the builders merchant, as air permeability is said to vary from batch to batch.]]>
Build tight ventilate right http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=15102&Focus=258410#Comment_258410 http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=15102&Focus=258410#Comment_258410 Fri, 26 May 2017 12:41:25 +0100 djh Posted By: Ed DaviesBut I agree with Tom's basic point that testing at 50 Pa is pretty weedy.
It's based on average wind pressures, I think. Some places with a more serious climate test at 75 Pa or even 100 Pa. In this country, testing at more than 100 Pa is deemed to possibly damage the building's fabric!

There's a good summary of airtightness from the passivhaus point of view, including testing and what they think should be sealed, at:
http://www.passivhaus.org.uk/filelibrary/Primers/Passivhaus-Airtightness-Guide.pdf]]>
Build tight ventilate right http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=15102&Focus=258412#Comment_258412 http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=15102&Focus=258412#Comment_258412 Fri, 26 May 2017 12:58:00 +0100 goodevans Build tight ventilate right http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=15102&Focus=258414#Comment_258414 http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=15102&Focus=258414#Comment_258414 Fri, 26 May 2017 13:34:18 +0100 fostertom Build tight ventilate right http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=15102&Focus=258415#Comment_258415 http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=15102&Focus=258415#Comment_258415 Fri, 26 May 2017 13:36:19 +0100 Ed Davies Posted By: goodevanswhen you look at SAP average infiltration is assumed at 1/20th of the 50Pa m3 valueBut is that assumption reasonable given that 50 Pa seems not to be huge compared with plausible air pressures on a house (even though those pressures wouldn't uniform in the way that a pressure test is)?

E.g., 4 km/h might be average over the whole year in the south of England but seems very low as the average for the worst parts of the heating season when it matters most.]]>
Build tight ventilate right http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=15102&Focus=258421#Comment_258421 http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=15102&Focus=258421#Comment_258421 Fri, 26 May 2017 16:09:38 +0100 goodevans
At 50Pa infiltration for an average new build house may be say 5 m3/hour/m2env@50Pa which for my planned house (370m2 env) equals 513 litres/second. A house leaking that much air would be loosing around 600 Watts per degree C temp difference (adding the equivalent of 1.6 to the U values of the house). Obviously a new build house does not leak that much air.

I therefore propose that the test at 50Pa is too high to represent average infiltration for a typical house (but may be about right on the windiest days) - however testing at a lower pressure would mean that the test would only be valid if taken on a windless day - 50Pa is probably about right for testing. because of the non-linearality of infiltration it means that small holes and cracks are under represented and larger cracks and holes are over represented compared to average conditions.

Test value can be adjusted by dividing be a number (e.g. 20 for SAP) or using a formula for calculating heat loss though infiltration. The number 20 is questionable for it's simplicity but it seams about right - the real number would be different for each mix mix of small and large cracks for any given tested house.]]>
Build tight ventilate right http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=15102&Focus=258422#Comment_258422 http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=15102&Focus=258422#Comment_258422 Fri, 26 May 2017 16:15:59 +0100 fostertom Build tight ventilate right http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=15102&Focus=258425#Comment_258425 http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=15102&Focus=258425#Comment_258425 Fri, 26 May 2017 16:31:00 +0100 goodevans Build tight ventilate right http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=15102&Focus=258427#Comment_258427 http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=15102&Focus=258427#Comment_258427 Fri, 26 May 2017 16:41:00 +0100 djh Build tight ventilate right http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=15102&Focus=258428#Comment_258428 http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=15102&Focus=258428#Comment_258428 Fri, 26 May 2017 16:55:30 +0100 goodevans
stack affect for a 5m height difference and 20 deg C temp difference would be 5Pa. Assume 2.5 sucking at the bottom and 2.5 blowing out the top balanced at mid height - strangely about 1/20th of the blower test.

In cold still weather stack affect would be significant.]]>
Build tight ventilate right http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=15102&Focus=258429#Comment_258429 http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=15102&Focus=258429#Comment_258429 Fri, 26 May 2017 17:20:13 +0100 fostertom
Posted By: goodevans5m height difference and 20 deg C temp difference would be 5Pa
is a bungalow with walk-height loft, or a v skimpy flat roof 2 storey. 2 storey with loft more like 7m, so 14C - not just deep winter. A 2-storey maisonette above shop say with GrdFl entrance would be 9m, 11C.]]>