Generally, 0.5 mm² cords should be the smallest size connected to plugs fed by 30 A or 32 A ring circuits.Apart from the following sentence, which discusses cords longer than 10 metres, it doesn't say anything more about minimum cord CSA for ring final circuits. Page 136, talking about radial circuits, says:
The minimum cross-sectional area for flexible cords should be:Obvious question, why is is acceptable to plug a 0.5 mm² cord into a 32 A ring final circuit but not into a 20 A radial circuit?
0.5 mm² where the radial circuit is protected by a 16 A fuse or circuit breaker,
0.75 mm² for a 20 A fuse or circuit breaker,
or 1.0 mm² for a 30 A or 32 A fuse or circuit breaker.
Where the cord length must be 10 m or greater, the minimum size should be 0.75 mm² and rubber-insulated cords are preferred to those that are PVC insulated.It's not completely clear if that applies just to ring final circuits or all socket circuits - it's in the more general section but immediately follows and qualifies a sentence which is specific to rings rather than radials.
Posted By: markocosicShort 0.5mm^2 cords can draw enough current in a fault condition to trip the breaker quickly before things get too hot. Long 0.5mm^2 cords are too high impedance to trip the breaker quickly enough to meet the regs.Ah, that makes sense: it'd be an awfully long cord to stop 32 A flowing but it's easy to believe that the cable or whatever's actually shorting might catch fire before the breaker tripped at 50 amps or so. At 32 amps the temperature of the cable would initially rise by about
Ring mains are an awful idea …Indeed, a desperate war-time fail-dangerous invention we should have got rid of long ago.
We should be designing for 16A socket circuits as many continental market/chinese market devices commonly sold in shops do not have large enough conductors to trip the 32A breakers used in (UK only) ring circuits.Yep - who needs or wants more than 6 kW on sockets? I'm planning 6, 10 or 16 amp MCBs on my low power radials and 16 or 20 A on the few high power socket pairs.
1 to 7 of 7