Home  5  Books  5  GBEzine  5  News  5  HelpDesk  5  Register  5  GreenBuilding.co.uk
Not signed in (Sign In)

Categories



Green Building Bible, Fourth Edition
Green Building Bible, fourth edition (both books)
These two books are the perfect starting place to help you get to grips with one of the most vitally important aspects of our society - our homes and living environment.

PLEASE NOTE: A download link for Volume 1 will be sent to you by email and Volume 2 will be sent to you by post as a book.

Buy individually or both books together. Delivery is free!


powered by Surfing Waves




Vanilla 1.0.3 is a product of Lussumo. More Information: Documentation, Community Support.

Welcome to new Forum Visitors
Join the forum now and benefit from discussions with thousands of other green building fans and discounts on Green Building Press publications: Apply now.




    • CommentAuthorJeremy S
    • CommentTimeFeb 10th 2013 edited
     
    Hi,

    we've had some trouble finding a heating engineer locally with sufficient experience of solar thermal, so I'm hoping for some feedback on our proposed circuit (attached as PDF).

    We've overspecified the collectors and the store in order to a) gain a greater winter contribution, and b) to offset the lower contribution on frequent cloudy days in western Perthshire.

    We've been heating our well-insulated and air-tight 57sq.m 2-bedroom cabin with the occasional use of a 2kW electric radiator on the cold (sub-zero) nights - installing a 4kW solid fuel stove (c/w 1kW back-boiler) will a) reduce reliance on electricity, b) contribute to DHW, c) improve air-flow (via window trickle-vents), and d) be cosy!

    Due to roof pitch and topography, we're intending to install the collectors on a shed some 25m from the store (see below); 12vDC thermal differential control, pump, expansion vesel, and pressure relief will be in the shed, with solar PV alongside the collectors. Thermal store, other valves, and heat exchanger for stagnation-preventing heat dump will be in the cabin.

    Any comments are welcome, bur specific questions are:
    1) can anyone recommend a H.E. in 50-mile radius of Crieff?
    2) are there any safety concerns with the proposed schematic?
    3) how does a 'filling loop' work? what's the procedure and hence, required plumbing?
    4) for the 25m run, we thought to not use std s/s corrugated due to pressure loss; should we go for copper and just deal with thermal expansion somehow, or instead use s/s tube at extra expense?
    5) suggestions for valves?

    Links to kit:
    Thermal store: http://jouleuk.co.uk/Cyclone_Thermal_Stores/299
    Collectors: http://www.kingspansolar.co.uk/products/16/df100.aspx
    Stove: http://shop.salamanderstoves.com/small-stoves/hobbit-stove
    Pump: http://www.solarproject.co.uk/page2.html
    Thermal differential controller: http://www.reuk.co.uk/buy-SOLAR-PUMP-CONTROLLER-CIRCUIT.htm or http://www.solarproject.co.uk/controller%20detail.html
    Plate heat exchanger: http://www.ebay.co.uk/itm/Stainless-Steel-Heat-Exchanger-Plate-Heat-Exchanger-20-Plates-44-kW-/330867777183?pt=UK_Home_Garden_Hearing_Cooling_Air&hash=item4d09419e9f

    In the longer term, I'm looking to investigate programming a dedicated 12v Linux 'intelligent' controller using Raspberry Pi (http://www.raspberrypi.org/) - see: http://www.raspberrypi.org/phpBB3/viewtopic.php?t=31455&p=272911

    best wishes - Jeremy
    •  
      CommentAuthorSteamyTea
    • CommentTimeFeb 10th 2013 edited
     
    Posted By: Jeremy SIn the longer term, I'm looking to investigate programming a dedicated 12v Linux 'intelligent' controller using Raspberry Pi
    Playing with that myself, quite good fun when I have enough time.

    May be teaching Granny to suck eggs but if you have a a large store you need a lot more input at a higher temperature then the store. So are you at risk of not getting the store temperature up high enough with just solar and/or not being able to top the tank up with solar because it has been heated by the wood burner.
    Do you know your expected DHW usage already,this is what really governs the size of system.

    There was some chat on here about someone wanting to ST on a shed 15 metres from the house, I suggested that PV may be easier, cheaper and more effective. Have you costed out that option?
  1.  
    The panels to which you refer say they are 'direct flow'? I take it these are the type where the fluid is circulated through the tubes, rather than the heat-pipe type. I appreciate your array will be pretty close to the ground, and thus good for access, but our experience with (Schott) 'through-flow' tubes at South Yorkshire Energy Centre was that when the local 'little dears' used the array for target practice, the entire system drained down (of course). Because we had them on a frame on the gable, the access was more tricky, and it cost over £500 just for the access equipment and 2 engineers. If we'd had heat-pipes the system would have carried on working, albeit a bit less efficiently.

    This may not be an issue for you if access is easy and any labour DIY (and also if you have no vandals!), but others may find it worth noting. Out of interest, if I am right that they are the 'through-flow' type, why did you choose these against the heat-pipe type?
    • CommentAuthorEd Davies
    • CommentTimeFeb 10th 2013 edited
     
    Clever scheme for running the solar loop through the plate exchanger for the heat dump all the time and just turning the cool side flow on if it gets too hot. Two concerns I'd have with that though: 1) it'll increase the thermal mass of the solar loop further making use of short bursts of sunshine more problematic and 2) I read somewhere that such 'total loss' heat dumps weren't allowed by water regulations. Obviously you don't expect the heat dump to cut in often so it shouldn't be a problem in practice but it might be worth checking if what you plan is actually legal if there's any question of anybody looking at the system in detail later.

    I'd echo Nick's question of your choice of collectors. With the long run to the cabin from the collectors it's already hard to make use of short bursts of sun. Having a “wet” collector tube with a higher thermal mass will make the problem worse, I'd have thought. Just curious but how much those Kingspan collectors cost?
    • CommentAuthorJeremy S
    • CommentTimeFeb 10th 2013
     
    @Steamy: as mentioned, store is over-specified for reasons listed; also, in the schematic you'll see that we're hoping to use both the lower (solar) coil and the upper (primary) coil for the solar circuit, but diverted by hydraulic temperature valve (right name? see http://www.danfoss.com/United_Kingdom/Products/Categories/List/HE/Domestic-Control-Valves/Miscellaneous-Controls/RAVK/bcd81841-0aa9-417a-a06a-53552b1bae78.html - possibly the least helpful website?) depending on temperature, to maintain stratification.

    Any failure to achieve ~50degC at top of tank results in extra heat being delivered by inline electric heater, i.e. only heating the water we use, not the whole tank (CEX-U from http://www.zipheaters.co.uk/zip-hot-water).

    Nevertheless, point taken. Calculations suggest at least 7.5hrs at peak solar output, with no system losses, to heat whole tank from 10 to 60degC. However, once warmed above 25degC electric load is significantly reduced, and large volume should attenuate variation due to draw-off; during winter, the ~daily top up with solid fuel should further reduce electric load, by being introduced at top of tank.

    @Nick: access is good; the only vandals I'd envisaged are home-grown and armed with footballs - I'd intended to screen the tubes with chicken wire, being concerned more about the glass than the actual pipes.

    @Ed: point taken re: thermal mass - maybe an option is to introduce a short-circuit that diverts solar flow past store until fluid exceeds store temp. The long run is unavoidable. Price from Kingspan: £1500 for 3m2. (cf. £1880 for heat pipes). In short term heat 'dump' (on rare occasions - ~5x p.a.) will be to 'solar paddling pool'; longer term, we're considering massive (up to 20m3) inter-seasonal storage for UFH, i.e. low-grade heat, with attendant lower heat-loss over time.
    • CommentAuthorEd Davies
    • CommentTimeFeb 10th 2013 edited
     
    Posted By: Jeremy SPrice from Kingspan: £1500 for 3m2. (cf. £1880 for heat pipes)

    Ta. Not as bad on the Kingspan prices as I thought.

    Still, that's a bit of a high price for the heat pipes - perhaps 1.5 times what's available. I got 10 m² for just over £1700 (incl VAT and delivery for 8 panels, 20 tubes of 47 mm x 1.5m, 1.25 m² aperture per panel) but that was a particularly good deal - more normal prices might be £900 to £1200 for 3 m² (if you could get exactly that size - e.g., Navitron SFB30-58, aperture 2.84 m², for £940 incl VAT).
    • CommentAuthorMegacycles
    • CommentTimeFeb 10th 2013
     
    6.5kWp seems high for 3m2 of panel. I'm not far away from you and have 60 47mm navitron tubes (around 4m2) and these work into 180 litres first and then 120 litres in a secondary tank (only on decent days does this get heated). I doubt theres much difference in panel efficiency and I have a shorter run (30m circuit), so I think you need more collector area for 500 litres, oversizing is needed around here!

    You can fill the system with one of those weed/paint sprayer tank things you get at DIY stores, no need for a filling loop.
    I wouldn't bother with an AAV if the panels are accessible, I just loosened one of the compression elbows on the panel to remove air although I did arrange pipework to have a constant rise to the panels. I've never had to remove air (or add water) to the system in over 6 years now - very much fit and forget. I did check a few times for air after installing but never found any.

    I use a danfoss 3 way motorised valve for tank switching , from memory these have a higher temp rating , 95'C maybe.
    I don't know any decent plumbers around here as I DIY everything, if you are practical and have the time you can do the same.

    Can you use the solid fuel burner as a heat dump somehow? The long pipe run will help limit the output.
    • CommentAuthorJeremy S
    • CommentTimeFeb 10th 2013 edited
     
    @ Ed: short-circuit, to reduce impact of thermal mass, like this...
    would need to be fail-safe, i.e default to route through PHE and store
    (edited to attach PDF as PNG is a bit titchy)
    ... or maybe put short-circuit after PHE so that thermal inertia is overcome prior to routing via store?
    • CommentAuthorJeremy S
    • CommentTimeAug 27th 2014 edited
     
    Hi,
    updated plan.
    I've ditched the 12V (solar PV powered) pump
    Still intending to use Raspberry Pi to control, so all diverter valves are now actuated and hope to gradually develop optimised switching dTs, T thresholds, and pump cycle.

    Important design change: heat upper coil until >60degC, and don't run through lower coil, i.e. don't try to extract maximum heat, but maintain transfer fluid temp in order to achieve maximum temp.

    (WBS circuit removed for clarity - it's in and working well, although cool tank causes tar build-up on back boiler, which should be reduced once solar thermal is in place - PNG is illegible, and I can't upload SVG, so PDF is further down...)
    • CommentAuthorJeremy S
    • CommentTimeAug 27th 2014 edited
     
    (seems PDF can't be uploaded from Firefox any more...)
    •  
      CommentAuthordjh
    • CommentTimeSep 2nd 2014
     
    Posted By: Jeremy S(seems PDF can't be uploaded any more...)

    Dunno, but it's not a size limit is it?
    • CommentAuthorJeremy S
    • CommentTimeSep 2nd 2014 edited
     
    (edited out)
    •  
      CommentAuthordjh
    • CommentTimeSep 2nd 2014
     
    Posted By: Jeremy SYou are not allowed to upload (140830CultyMS_SolarTS_12.pdf) the requested file type: application/.pdf

    I don't know what's changed, and it seems stupid that it has, but it might be worth renaming the files with a .txt ending instead of .pdf - that's worked for some spreadsheets in the past. Simple-minded rules!
    •  
      CommentAuthorSteamyTea
    • CommentTimeSep 2nd 2014
     
    There was something about using /forum114/ or not a while back.
    Do a search on here and you should find out what the issue is.
    • CommentAuthorJeremy S
    • CommentTimeSep 3rd 2014 edited
     
    • CommentAuthorJeremy S
    • CommentTimeSep 3rd 2014 edited
     
    So, to discussion...

    It seems 'pretty ordinary' to place expansion vessel (EV) in return to collector, which would avoid issues of steam reach, as the shed is ~25m from house, but:

    1. the plate heat exchanger (PHEx) heat dump should cut in and reduce transfer fluid temp well before this becomes a real risk
    2. I'm planning to use Watts STS20/Honeywell TS130(if it's still available)/Danfoss BVTS to control heat dump via PHEx - the last comes in various preset temp models (P/Ns: 003N3349, 003N3352,003N3300), the highest being 100degC - since the transfer fluid will definitely have cooled by the time it reaches the store, what's to stop me using this model rather than, say, 97 or 95degC?,
    3. is there a risk associated with placing EV ~50m from collector, ie. boiling fluid in collector being prevented from expanding by need to displace 13L (not all of it, but thinking about friction &c.)?
    4. therefore: is EV better placed between collector and pump, after PHEx, say?
    5. Also, I've seen mention of fitting isolating ball valve to the automatic air vent (AAV), and just opening it up during periodic maintenance - surely this defeats object of AAV - or is a different kind of 'automatic'?
      http://www.bes.co.uk" > BES stock at least 4 variations on the theme, (AAV/de-aerator/airstop) - what's the difference/(dis)advantages of each? (I couldn't find any discussion of this elsewhere on GBF)


    any comments welcome - thanks
  2.  
    Ref Q 5 - the AAVs (the solar rated ones) usually leak eventually - I think all do leak eventually. Leave the isolating valve open for 2 or 3 days after all 'work' and then close the valve until next time more air has a chance to get in. Think of it as a commissioning tool rather than as a full-time AAV. Once or twice a year I open the isolating valve and any air that has caught under the valve (it is still the highest point) can then escape.