Posted By: williamdThe previous owner had fitted solar PV panels with eligibility for feed in tariff commencing in May 2013.
My relative intends to build on an extension and wonders whether fitting further solar PV panels to this extension would be worthwhile financially. I assume that FIT will not apply to the new panels so is there any alternative subsidy available and how will this work in practical terms as it would presumably make sense if the existing panels are to remain on FIT.
Posted By: philedgeIm pretty sure the inverter limits its output to 16A on standard domestic installs so adding panels cant add anything to the maximum system output.
Posted By: revorYou can generate more than 3.6 Kw but obviously you would need an inverter for the size of panels and you can get a device which limits what you can send to the grid to 3.6 kw. So if DNO won't allow you to export more than you 3.6 kw I suppose you could use the extra generation yourself and maybe store it in a battery.
Posted By: djh
You can't add panels to the current inverter without losing FIT.
Posted By: jamesingramIve a fits system and a non fits systems.
the no fits systems doesnt require MCS registration so can be fitted by a compedent roofer and a electrician rather than a specialist company , this may save on cost. if going over 16A potential export a G99 is required prior to connection , this may have a cost implcation.
Posted By: philedgeHave you got a reference for that?
Posted By: nigelPosted By: jamesingramIve a fits system and a non fits systems.
the no fits systems doesnt require MCS registration so can be fitted by a compedent roofer and a electrician rather than a specialist company , this may save on cost. if going over 16A potential export a G99 is required prior to connection , this may have a cost implcation.
I have two PV systems one fit eligible and the other not. I have signed up to Agile outgoing where they pay for exported energy, they will only accept this if both the systems are Mcse installed. So long term unless you will never export I would try and get an MCSE installed system.
Posted By: philedgeHad a bit of a search round and found the following on the Ofgem site
https://www.ofgem.gov.uk/publications-and-updates/feed-tariffs-guidance-renewable-installations-version-15
The section on modification refers to not exceeding the Total Installed Capacity which is defined as
“the maximum capacity at which an Eligible Installation could be operated for a
sustained period without causing damage to it (assuming the Eligible Low-carbon Energy
Source was available to it without interruption), a declaration of which is submitted as
part of the processes of ROO-FIT Accreditation and MCS certified Registration.â€Â
The way I read this is that if an inverter has a restricted output of 16 amp, the installations maximum operating capacity is the 16 amp limit regardless of the PV panels input capacity. Anyone read that differently???
Posted By: jamesingram
From memory the issue with expanding and existing system that receives FITs is it then requires an update to its registration which then in turn results in it being classified under the current FITs band.
The result of this when FITs rates were dropping regularly was you would end up on a lower tariff after registering.
Now FITs has stopped to new installs Im not sure what the situation is.
At the time I personally thought it wise just to leave any eixisting system receiving funding alone and to not rock the boat and risk loss of tariff
Posted By: revorI need to get my head around these regs as well. My proposed installation is gathering pace now and my inverter is G98 G 99 and G 100 compliant It seems that the G100 bit is about export limitation. The inverter can be programmed to not export or export what you want. However my system will be 6Kw and the proposal I think from the installer is to limit the output to 3.6 so don't need to make a G99 application although I would like to export everything I cannot use. Think that historically in our area everyone with SPV has been limited because of grid capacity.
Posted By: revorHowever my system will be 6Kw and the proposal I think from the installer is to limit the output to 3.6 so don't need to make a G99 application although I would like to export everything I cannot use.Is that limitation on the power output of the inverter or on the export? I.e., is it sensed at the inverter or is there a separate current sensor near the meter?
Posted By: revorWhat we need now is to be able to tap into the EV battery to power the house.
Posted By: revorHave looked into the leaf trials it will be some time before it is generally available and only then if trials are deemed a success and worthy of a rollout. From what I was told the system cannot power the house in a power cut as the V2G charger which is the "clever" bit needs to have a permanent connection to grid.
Posted By: revorMy G99 G100 application gone in today hope they will allow the 6kw if not will see the cost involved in increasing the size of the battery. This where being able to use a car battery for the house would be great as car is idle most of the time but house always consuming power somewhere.