Home  5  Books  5  GBEzine  5  News  5  HelpDesk  5  Register  5  GreenBuilding.co.uk
Not signed in (Sign In)

Categories



Green Building Bible, Fourth Edition
Green Building Bible, fourth edition (both books)
These two books are the perfect starting place to help you get to grips with one of the most vitally important aspects of our society - our homes and living environment.

PLEASE NOTE: A download link for Volume 1 will be sent to you by email and Volume 2 will be sent to you by post as a book.

Buy individually or both books together. Delivery is free!


powered by Surfing Waves




Vanilla 1.0.3 is a product of Lussumo. More Information: Documentation, Community Support.

Welcome to new Forum Visitors
Join the forum now and benefit from discussions with thousands of other green building fans and discounts on Green Building Press publications: Apply now.




    • CommentAuthorTigoDog
    • CommentTimeApr 28th 2023
     
    Hi all,

    I'm helping my dad convert a 19th century hay barn into a 3 bed home that he'll live in. We're aiming for Band A EPC, so a very high level of insulation and air tightness, if not quite PassivHaus standard.

    We effectively have a blank slate, so I'm interested in the GBF hive mind's opinion on the best heating solution. We are expecting to use an air-source heat pump, and I know the most commonly done method is an air-to-water system, heating water for UFH and general use. However, there is no existing wet heating system and I'm interested in air-to-air systems, particularly ducted systems (not wall mounted units). My thinking is that it should be more efficient to use the warm air created by the ASHP to heat the home directly, rather than losing energy in converting warm air to warm water. Also, UFH is expensive to install and ducted air should be cheaper(?). I'm also interested in how it could interact with Mechanical Ventilation. I imagine it would add complexity, but for the money I've seen quoted for UFH, I'd guess you could get a very high-end warm air/ventilation setup.

    I know warm air systems were wide spread in residential buildings in the 70s - but were not popular as I understand it. They are common in commercial buildings (HVAC) and I assume they have come along way in the last 50 years, but most contractors I speak to seem to be pushing wet UFH. I'm trying to understand if this is just 'what they're used to' installing, more profitable, or if it is genuinely a better solution.

    I appreciate he'd need a separate solution for hot water if we use the warm air system. He has space for solar, or if not, would an electric water heater would do the trick, or would that negate the efficiency gains? I've seen this system which does both in another thread, but according to the Daikin installer I spoke to, it isn't yet available in the UK market. https://www.daikin.eu/en_us/product-group/air-to-air-heat-pumps/multiplus.htm

    My dad is relatively open to both options, but I wouldn't want to push something on him that doesn't work well, or 'feel nice'.

    The barn is in the South of England (Berkshire). I include plans, which I have permission to post.

    I'd welcome your opinions, or alternatively suggestions of contractors that can help.

    Thanks in advance!
      Screenshot 2023-04-28 at 16.23.29.png
    • CommentAuthorTigoDog
    • CommentTimeApr 28th 2023
     
    •  
      CommentAuthordjh
    • CommentTimeApr 28th 2023
     
    Hello and welcome.

    I wouldn't try to aim for any particular EPC band. It bears very little relation to the real world :( Personally I would suggest using PHPP since it is pretty accurate and measures something quantifiable and achievable. By all means pick a different target than PH level, but be aware of the differences if you do.

    Posted By: TigoDogWe are expecting to use an air-source heat pump, and I know the most commonly done method is an air-to-water system, heating water for UFH and general use. However, there is no existing wet heating system and I'm interested in air-to-air systems, particularly ducted systems (not wall mounted units). My thinking is that it should be more efficient to use the warm air created by the ASHP to heat the home directly, rather than losing energy in converting warm air to warm water. Also, UFH is expensive to install and ducted air should be cheaper(?). I'm also interested in how it could interact with Mechanical Ventilation. I imagine it would add complexity, but for the money I've seen quoted for UFH, I'd guess you could get a very high-end warm air/ventilation setup.
    A heat pump doesn't create warm air, it creates warm refrigerant. Whether that is changed into warm air or warm water depends on what type of heat exchanger is used indoors.

    Posted By: TigoDogI know warm air systems were wide spread in residential buildings in the 70s - but were not popular as I understand it.
    Indeed my first house, which I bought in the 1970s, had a warm air heating system, and it was fine for me since I lived alone and liked loud music, so I didn't care how much noise the heating system made. Most people do, and I would nowadays. The house I live in now is also heated by warm air, but the heating system is inaudible. The difference is that my house is a PH and needs so little heat that it can be heated by blowing warm air through the ventilation system. The PH standard was specifically chosen so that is possible! If you're not at that level, you won't be able to do it.

    Looking at the plans (which it's not possible to see properly, unless there's some means to download them?) one immediate comment is that you'll have trouble meeting PH with the glazing arranged as it is. I can't tell which direction is north.

    If you're thinking about a ventilation system and/or a warm air heating system, where will the ducts run? What type of joists and ground floor do you have?
    •  
      CommentAuthorfostertom
    • CommentTimeApr 29th 2023 edited
     
    Posted By: djhmy house is a PH and needs so little heat that it can be heated by blowing warm air through the ventilation system
    That needs slight qualification - the point about a PH is that for the vast majority of the year it doesn't need any heating (or cooling) at all, but at extremest cold times it does need a little heating boost, and this is so small that it can be delivered by the very lo-capacity MVHR system. And adds up to so little heat that on-peak electric element in the duct is simple, controllable and affordable, so no other, expensive heat source, whether boiler or heat pump, and no expensive heat emittere, whether rad system or UFH, are necessary in a PH.
    • CommentAuthorowlman
    • CommentTimeApr 29th 2023
     
    I have a ducted air to air system and I wouldn't hesitate for a moment to install it again. The noise aspect isn't a problem IMO, if installed correctly. The system controls are excellent, as is the response time. Fitting registers with filters keeps circulating indoor air pleasant. The cooling option is a boon on the odd occasion. If there are areas where ducting becomes a bit difficult you also have the option of a large choice of other indoor air supply units. You will most likely need assistance with system design though.
    With your "blank slate", the most onerous bit,- i.e. fitting and insulating the ducting,- is easily accomplished. On the water front I think too much is made of DHW supply. It's an easy problem to solve and again with your blank slate you have loads of cheaper options, that don't involve an expensive air to water unit.
    •  
      CommentAuthordjh
    • CommentTimeApr 29th 2023
     
    Posted By: owlmanI have a ducted air to air system and I wouldn't hesitate for a moment to install it again. The noise aspect isn't a problem IMO, if installed correctly.
    I'm curious to know some more detail. What's the heat output of the system, and the duct speed used? What diameter ducts? Do you happen to know what the noise level is?
    • CommentAuthorowlman
    • CommentTimeApr 29th 2023
     
    These are the outdoor and indoor units. They are part of Toshiba light commercial range.

    https://data.toshiba-klima.at/en/Super%20Digital%20Inverter%20R32%20-%207,10%20kW%20-%20R32%20-%20RAV%20RAV-GP801AT-E%20en.pdf

    https://data.toshiba-klima.at/en/Standard%20duct%20unit%20R32_R410A%20-%207,10%20kW%20-%20R410A%20-%20SET64%20-%20RAV%20RAV-RM801BTP-E%20-%20RAV-GP801AT-E%20en.pdf



    The indoor unit I immediately handed over to a local sheet metal company who fabricated inlet and outlet plenums each with two spigots for me to attach the initial ducting flows and returns. I suspended the unit from the rafters with threaded studs before directing the ductwork. In my case this was a pain because of my restricted attic roof-space, also because I chose to fit rigid spiral steel ducting in order to get smooth airflow.
    The ducting overall is the difficult bit, both in fitting and design. I taught myself with some initial guidance from Paul in Montreal and by asking lots of questions from various suppliers and fitters.
    Duct sizing and system design is a bit of a black art and I most likely erred on the side of caution which gave me extra grief. The end result however works fine and the oversized ductwork most likely aids any noise issues. I also had bespoke inlet and outlet ceiling registers and plenums made with removable filter medium screens.
    •  
      CommentAuthordjh
    • CommentTimeApr 29th 2023
     
    Posted By: owlmanthe oversized ductwork most likely aids any noise issues
    Thanks for the info. Yes, that was why I was interested to know the duct diameter? I see from the indoor unit spec that the minimum flowrate is 870 m³/hr, which is significantly more than an MVHR system (seven times as much air as mine), so I expect much larger ducts are needed.
    • CommentAuthorowlman
    • CommentTimeApr 30th 2023
     
    It worked out fine in the end and because of the restricted attic space it was easiest to take two delivery and return ducting spigots. I was further hindered by only having ceiling space for both flow and return registers. On a new build I'd most likely put flows at floor level and returns in the ceiling and with modern rectangular ducting that's easily achievable into stud walls, but like I said room air movement and system design can be a bit of a black art.
    In the end I think mine worked out OK.
    I positioned one of the returns high up in the wall separating the glazed sun room from the sitting room. This allowed the system to drag in some warm roof level air which was then re-circulated aiding the overall system temperature modulation. In Summer if we use reverse cooling mode it keeps the sun room pleasant by dissipating any overheating.
    I have no idea on the running costs because my home is virtually all electric and the thought of teasing out one device usage makes me queasy. I tend to simply round up incomings FITs, and outgoings power supply contracts and at the moment I live comfortably, and I'm still winning. Any wood I burn to supplement other non- A/A ducted areas or for occasional aesthetic reasons is from my own property tree prunings. Quite a bit of any heat so generated gets sucked into the A/A and is modulated as before.
    •  
      CommentAuthordjh
    • CommentTimeApr 30th 2023
     
    Posted By: owlmanthe thought of teasing out one device usage makes me queasy.
    If the device has a plug then it's quite easy - just get an energy-monitoring smart plug. If it is hardwired then you need a clamp-on current/power meter, which tend to be a bit more expensive.
    • CommentAuthorMike1
    • CommentTimeApr 30th 2023 edited
     
    Posted By: TigoDogUFH is expensive to install and ducted air should be cheaper [than ducted air heating](?)
    I've not done a comparison, but I wouldn't expect there the be a huge difference. I've lived happily in homes with both systems, but personally I'd choose UFCH because it produces a very even temperature gradient in a room and a pleasantly warm floor to sit on. If the pipes are reasonably close together (minimum 150mm, it seems) it can be used for / upgraded later to provide cooling too.

    Interestingly, the first major use of UFCH in the UK was to heat public air-raid shelters during WW2 - see https://digital-library.theiet.org/content/journals/10.1049/ji-2.1942.0002 (£)

    Posted By: TigoDogI know warm air systems were wide spread in residential buildings in the 70s - but were not popular as I understand it.
    It was popular for a decade or so in new-builds in England & Wales, partly because of attractive off-peak electricity tariffs, partly because the alternatives were limited to coal, oil or wood, or town gas in cities. With the 1973 energy crisis the economics looked rather different.

    1970s era promo: https://www.youtube.com/watch?v=l9dZQumYqtI
  1.  
    Nice paper from 1942!

    What have the Romans ever done for us?

    Introduced underfloor central heating to (southern) Britain, using ducted warm air, though apparently they borrowed the idea from the ancient Chinese.

    https://www.romanobritain.org/12_innovations/inv_central_heating.php

    There are Victorian greenhouses surviving with piped hot water UFH, good for growing pineapples it seems.
  2.  
    Back on the OP:
    An EPC "A" is defined in SAP as an annual energy cost below a certain threshold, works out around £250 for a medium-large house, including heating/water/cooking/lights/etc. The heating part of that will have to be pretty minimal to meet the threshold.

    It hardly seems worth spending £10k+ on a heat pump and distribution ducts or ufh. Better just to have a couple of small panel heaters, or heated MHRV?

    The alternative would be to spend less on insulation, so consume more heat, but generate the heat cheaper with solar thermal or a heat pump. That would also meet the EPC-"A" cost threshold and deliver the same low operational carbon, but might not comply with building regs insulation levels which were tightened last year, and might not be cheaper overall as the heat pump would need replacing every decade or so.
    •  
      CommentAuthordjh
    • CommentTimeApr 30th 2023
     
    Posted By: Mike1It was popular for a decade or so in new-builds in England & Wales, partly because of attractive off-peak electricity tariffs
    The warm air heating in my house was gas-powered. Built by the local council.
    •  
      CommentAuthordjh
    • CommentTimeApr 30th 2023
     
    Posted By: WillInAberdeenAn EPC "A" is defined in SAP as an annual energy cost below a certain threshold, works out around £250 for a medium-large house, including heating/water/cooking/lights/etc. The heating part of that will have to be pretty minimal to meet the threshold.
    I don't believe an A is defined so simply, since a common technique for gaming them is to add a load of PV to improve them.

    works out around £250 for a medium-large house
    The standing charge accounts for about half that! And 1 kWh per day for the other half. What it tells me is that the EPC is a pile of steaming **** and best ignored.

    The alternative would be to spend less on insulation, so consume more heat, but generate the heat cheaper with solar thermal or a heat pump.
    solar thermal suffers from the same problem as PV - the time of maximum demand is the time of least supply (not coincidentally). So that leaves a heat pump, and even then AIUI we're going to be hard-pressed to generate enough stable electricity, so I continue to believe that minimising energy usage is a laudable social goal.
  3.  
    You can read the definition for yourself, it's in SAP 10.2.

    "The SAP rating is related to the total energy cost by the equations:

    ECF = deflator × total cost / (TFA + 45) ....

    SAP rating = 100 – 16.21 x ECF

    where the total cost is calculated at worksheet (255) or (355) and TFA is the total floor area of the dwelling at
    worksheet (4). The deflator is given in Table 12a."

    "SAP rating: 92 or more : Band A"

    Using these equations, a 150m² house using £250 of energy will have a SAP rating of 92 (band A).


    At risk of stating the obvious:

    -adding lots of solar panels will reduce the energy cost and so improve the EPC;

    -south facing windows are good for solar gains in winter but need shading in summer.;

    - if one house uses 3x more heat than another, and gathers that heat with a heat pump of CoP=3, then both houses will require exactly the same amount of "stable electricity".

    - Manufacturing insulation now is damaging to the environment, and so is manufacturing heat pumps, but electricity will become net zero early in the lifetime of any building from now.
    •  
      CommentAuthordjh
    • CommentTimeApr 30th 2023 edited
     
    "Calculating the SAP — or Standard Assessment Procedure — score offers the only government-approved methodology for compliance with Part L of Building Regulations, and for ascertaining the cost of supplying the home with sufficient energy for heating and lighting.

    "The score will typically fall between 1-100, and will be calculated based on the construction itself, lighting, heating, and any renewable technologies (such as solar) that will be installed on the property. A score of 100 indicates that the dwelling will have no energy costs, and a score of 100+ means that the property is exporting more energy than it uses."

    from https://www.atlanticrenewables.co.uk/news-blog/your-guide-to-meeting-sap-requirements-with-solar.html

    "Will I need solar PV panels for the New Part L 2021 SAP?
    ...
    "If you’re looking for a way to pass the SAP calculation with flying colours, then you should consider installing PV panels. PV panels have many benefits that make them an ideal choice for those looking to improve their energy efficiency.

    "However, under the new Part L 2021 and SAP 10, PV is now in the new building regulations for the notional assessment. This means that when assessing a dwelling, it will be compared with having solar PV and therefore, if PV is not installed, it will be very difficult to pass the SAP assessment.
    ...
    "Although, this based on using a gas boiler. If you were to install an electric Air Source Heat Pump or Ground Source Heat Pump, then it will be much easier to pass the SAP assessment and there would be no need to install PV! This is due to the high efficiency of the heat pump system."

    from https://www.baseenergy.co.uk/knowledge-base/will-i-need-solar-pv-panels-for-the-new-part-l-2021-sap/

    Manufacturing anything is damaging for the environment.

    And if you believe that UK electricity will be net zero any time in the near future, I've got a brifge you might like to buy. Manufacturing nuclear power stations and solar panels and wind turbines and batteries damages the environment, as does demolishing fossil-fuel power stations. Not to mention costing a lot of money. I'm afraid I don't think the government is competent to deliver it all. So I don't base my planning on assuming it will.
  4.  
    You're getting confused I think (or those salespeople are trying to confuse you) - that stuff is about the English building regs, which use the SAP software to calculate the DER and TER (CO2 emissions) to see if the building complies with the regs.

    That's not the same as the EPC rating. No particular EPC band rating is required to pass building regs, EPCs come from different legislation. EPCs are not "pass" or "fail", the bands are based on estimated £ costs.

    The only thing they have in common is that the same SAP software is also used to calculate the EPC rating.

    (Edit: and that adding PV will reduce both CO2 and energy cost, so will improve DER and separately EPC)

    (For interest, houses in Scotland that have heat pumps have a different TER calculation in Scottish Building Standards, they do not require PV, whereas gas heated houses must have PV. All-electric houses do not have to meet a TER at all, because electricity in Scotland is already considered to be low carbon by the government, if not yet by me!)
    • CommentAuthorTigoDog
    • CommentTimeApr 30th 2023 edited
     
    Thanks all for the comments so far - the subscription fee has paid for itself already!

    I've created a folder with access to the plans. The proposed site layout shows the orientation: https://drive.google.com/drive/folders/1ThgZxF907N8oUZi3QHArHBuv93cMJbRf?usp=sharing

    Posted By: djhI wouldn't try to aim for any particular EPC band. It bears very little relation to the real world

    Yes, fair point. This focus comes more from the language we used in our planning application (which took 6 years to gain approval!), and is more of a guide than a requirement. But i take the point that PH standards are a better guide.

    Posted By: djhyou'll have trouble meeting PH with the glazing arranged as it is. I can't tell which direction is north.

    I think it is unlikely we could achieve PH, there is a neighbouring barn adjacent to ours on the south side, the spots most suitable for glazing are on the north and east faces.

    Ducting is possible, I believe, in spite of the timber frame of the main barn. I was imagining something like what Owlman describes, with lower vents for heat/cooling distribution and ceiling vents for return.

    Posted By: WillInAberdeenIt hardly seems worth spending £10k+ on a heat pump and distribution ducts or ufh. Better just to have a couple of small panel heaters, or heated MHRV?

    An interesting point, I suppose I'm concerned about leaving the building 'under heated' and my dad being cold and grumpy! Would the consultant who provided the U values also instruct how much heating will be required?

    Part of the attraction of the HVAC-style systems is that they can provide cool air efficiently too, which may become increasingly important with the way things are going.

    Do people have insights on installation costs? I was expecting heat pump + ducting to be significantly cheaper than heat pump + UFH, although no BUS government grant for air-to-air system would counter balance somewhat.

    So far I'm reading that either system could work, and it could just be down to costs/personal preference. Are there any particular specialists that members would recommend?

    Thanks again all
    • CommentAuthorTigoDog
    • CommentTimeApr 30th 2023
     
    Posted By: djhIf you're thinking about a ventilation system and/or a warm air heating system, where will the ducts run? What type of joists and ground floor do you have?


    GF is having a new insulated slab with screed. I believe the FF will have posi joists between the existing timber frame. Open to suggestions here, as everywhere!
    •  
      CommentAuthordjh
    • CommentTimeMay 1st 2023
     
    Posted By: TigoDogDucting is possible, I believe, in spite of the timber frame of the main barn. I was imagining something like what Owlman describes, with lower vents for heat/cooling distribution and ceiling vents for return.
    That was why I was keen to discover what size Owlman's ducts actually are.

    Posi joists are good, until the pipe is too big!

    Would the consultant who provided the U values also instruct how much heating will be required?
    Depends entirely on the particular consultant's qualifications etc. You'll need to ask. I would expect the architects to be able to tell you that. But I'd treat any figures with scepticism unless they're produced using PHPP or one of the dynamic models and the user is properly trained.

    The drawings don't seem to show a particularly well-insulated building? Also there seem to be multiple SVPs penetrating the thermal envelope; there was a recent thread about SVPs. There are extractor fans; what are the plans for ventilation?
    • CommentAuthorowlman
    • CommentTimeMay 1st 2023
     
    @djh apologies I forgot to say, for initial duct size I chose 10" I believe could have got away with 9" or possibly even 8" but in my case no smaller. I was mindful of increasing fan speed or air velocity too much, I admit I was guessing though.

    Ducting layout with ( Y ) pieces to several registers would determine the initial indoor unit take off size. My runs were fairly short which obviously helps with ultimate performance. System design is uppermost and from that the location of the indoor unit needs to carefully planned, to ensure short duct runs.

    A mix and match approach may be best with ducting to say a large open plan area; as mine is. You could then use a multi-split wall, floor, or ceiling hung solution to other problem, or more difficult, or smaller areas. Refrigerant pipework is small, and drainage isn't too difficult an issue to solve.

    I think much of the bad press from years ago regarding warm air heating could be laid at the door of poor design and poor insulation of both the property and the ductwork, together with poor controls. Correctly installed Air/Air heat pumps are from my experience highly efficient and very responsive. The occasional cooling is on occasion a real boon. I have the advantage of PV to supplement running costs and it's why I don't hesitate to use Summer cooling if needed, it runs for free, just at a time when the sun shines and it's needed; a win-win I believe.

    Reverse cycle ASHPs are simple, relatively cheap, generally trouble free, and a versatile way of providing a comfortable interior. Their failure to attract any form of installation subsidy, as Air/Water, seems to be based solely on their ability to cool as well as heat. Tweaking regulations to insist on the installation of accompanying PV could allay fears there; just a thought.
    Oh BTW I have no connection to the ASHP industry in any way.
    • CommentAuthorTigoDog
    • CommentTimeMay 2nd 2023
     
    Posted By: djhThe drawings don't seem to show a particularly well-insulated building?

    What would be considered well-insulated?


    Posted By: djhAlso there seem to be multiple SVPs penetrating the thermal envelope; there was a recent thread about SVPs.

    The barn is not on mains sewage, so will have a septic tank.


    Posted By: djhThere are extractor fans; what are the plans for ventilation?

    I'm keen to use MVHR and was interested how this might work alongside an air-to-air heat pump.

    thanks!
  5.  
    Just looking at the EPCs for recent new houses, the majority are "B" with some at "C".

    Only a small number make it to "A", less than 3% of new houses last year, so that is a very demanding target.

    Posted By: TigoDogWhat would be considered well-insulated?
    To meet the bogstandard building regs insulation levels in England, needs very roughly 200mm of polystyrene or woodfibre insulation on the walls (U≤0.18) , and 400mm of rock wool in the ceiling (U≤0.11), and 300mm of polystyrene under the floors (U≤0.13). The joins need care to avoid bridges, there needs to be minimal air leakage, and the doors windows appliances need to be good quality, and lots of solar panels.

    However to get into the 3% that gain EPC "A" you'd need to go further than that.

    The environmental impact of that polystyrene and slab and render, will be quite a big chunk of the lifetime impact of the building, so needs careful thought not to overdo it.



    Posted By: TigoDogleaving the building 'under heated' and my dad being cold and grumpy!
    You could err on the safe side and fit panel heaters in every room, and it would still cost much less than UFH+heatpump!

    A bit of a different mindset is helpful for this kind of very low energy building. Most of the heat will not be coming from the heating system.

    Instead it will come from solar gains through the windows and roof and from the people and appliances.

    Rather than thinking about the heating system up front, the design needs to begin with a careful balancing of the amount and direction of glazing and the insulation and airtightness values, to give enough heat in the winter and not too much in the summer. Probably you'll need to lose some windows on the North and the roof, and add some on the south.

    Once that balancing act is as good as possible, then whatever remaining imbalance is left, gets taken up by a minimal and simple heating/cooling system, measured in Watts not Kilowatts.

    There are architects with experience of thinking in this way, that might be the quickest way to get up to speed?
    • CommentAuthorrevor
    • CommentTimeMay 3rd 2023
     
    Posted By: TigoDogThe barn is not on mains sewage, so will have a septic tank.

    We are on a septic tank, That is open vented some are not but best if they are, Our is and an outside loo is as well. All the internal soil pipes have AAV fitted and for extra security all the sink traps also. If you look at this product by McAlpine

    https://mcalpineplumbing.com/air-admittance-valves/ventapipe/vp100-ventapipe-100

    It allows a large quantity of air in and is approved for use instead of open vented. (That way I was able to avoid unnecessary holes in the roof and unsightly pipes on the house elevations. My BCO was ok with my plan. Coincidentally I have just replaced this valve as the original was sometimes malfunctioning it lasted about 7 years. Taking it off and giving it a shake would fix it for a while.