Home  5  Books  5  GBEzine  5  News  5  HelpDesk  5  Register  5  GreenBuilding.co.uk
Not signed in (Sign In)

Categories



Green Building Bible, Fourth Edition
Green Building Bible, fourth edition (both books)
These two books are the perfect starting place to help you get to grips with one of the most vitally important aspects of our society - our homes and living environment.

PLEASE NOTE: A download link for Volume 1 will be sent to you by email and Volume 2 will be sent to you by post as a book.

Buy individually or both books together. Delivery is free!


powered by Surfing Waves




Vanilla 1.0.3 is a product of Lussumo. More Information: Documentation, Community Support.

Welcome to new Forum Visitors
Join the forum now and benefit from discussions with thousands of other green building fans and discounts on Green Building Press publications: Apply now.




    • CommentAuthorIan1961
    • CommentTimeMay 29th 2020
     
    Posted By: tonyIt has nothing to with filling floor voids with insulation.


    Ive also seen dry rot in the timber joists of floor voids where the owner of the house had blocked the ventilation pathways on one half of the house.
    • CommentAuthortony
    • CommentTimeMay 29th 2020
     
    A very dangerous and silly thing to do but very different from adding insulation
    • CommentAuthorKenny_M
    • CommentTimeMay 29th 2020
     
    Posted By: gyrogearmaybe the solution is a good covering of lime on the floor of the void...

    gg


    I've been giving this some thought, but not sure if that would help or hinder. I suppose it depends on whether most of the vapour is coming up from the ground or down from the house.

    Posted By: tonyA very dangerous and silly thing to do but very different from adding insulation


    I agree with you that this is not the same, but is it completely different? If I block the air vents then I have a large unventilated void. If I then fill that void with EPS I have lots of tiny unventilated voids.

    Obviously this is the same in EPS filled cavity walls, except that surface area of the ground is a higher ratio to the space and there is no wood in there to rot and feed the mould.

    I keep relating this to my risky decision to fully fill my flat roof void, but my flat roof is south facing and at some times of the year the sun will be driving vapour in the other direction, while the uf void is cold all of the time.

    I note the theory that the areas where the joists are is warmer, but the data from the research appears to show high RH in the upper levels of EPS.

    What do you make of this Pelsmaker's research results Tony?
    •  
      CommentAuthorfostertom
    • CommentTimeMay 29th 2020
     
    V important study you've come up with there Kenny_M - a lot to read and digest.

    I note in the Conclusion (about all I've read thoroughly), all emphasis is on the real Uvalue benefits of UF insulation and no cautions at all about high RH in the joists zone - they don't seem to think the latter is v important.

    I did wonder, when (you say) RH is over 80% in the zone just under the floorboards, whether they recorded room RH just above the floorboards? It seems inconceivable that RH just below should be much different from RH just above the floorboards, assuming the latter are vapour permeable. Any RH gradient, presumably to 'very high' at subsoil, must begin in the room above. I suspect that the RH of over 80% in the zone just under the floorboards may be due to room conditions above, not any 'fault' of the full-fill method. Any idea what the study says on that?
    • CommentAuthorKenny_M
    • CommentTimeMay 29th 2020
     
    Tom,
    From what I can gather, the RH sensors were mostly placed near the external wall, they say due to access restrictions, so it doesn't give a full picture of conditions throughout the void.

    The sensor with the consistent high RH, was near top of joists and in beads. Another sensor is labelled as at top of joists, not in beads, which I would take to mean above the former. The latter had a consistently lower RH. I would take it from this that the moisture levels are not coming from the room above.

    It does say somewhere something about further research required to better understand the impact of moisture sources.

    What I would be interested to see is them taking one of the uninsulated floors that show a consistently low RH, and doing a full fill of EPS and monitoring the change in RH.


    Posted By: fostertomAny RH gradient, presumably to 'very high' at subsoil, must begin in the room above.

    Isn't possible that the high RH here is coming up from the subsoil?
    • CommentAuthorgyrogear
    • CommentTimeMay 29th 2020
     
    Posted By: Kenny_Mnot sure if that would help or hinder.


    cannot see how lime would ever HINDER ?

    It is THE humidity controller par excellence !
    acts two ways (absorbs falling humidity (condensation) and rising humidity (from the ground)
    (and the latter is *always* wet!)

    Lime also stops pathogens dead !

    gg
    • CommentAuthortony
    • CommentTimeMay 29th 2020
     
    On a couple of occasions I have inspected floor voids there they had water, from a high water table above the level of the oversite, yet the joist were in perfect condition and dry. The void was ventilated and the wall plates were on sleeper walls with EPC’s


    I did an experiment where I filled a box with eps beads with four Temperature/humidity sensors dead centre, 1/4, half, 3/4 up and on top. Sat it in an ice bath about 25mm deep and fed ice in constantly

    Humidity and temperature allowed me to calculate partial vapour temperatures - highest at the top where it was warm and lowest at the bottom. Moisture movement down into the ice

    Repeated with cold water instead of ice, same result, lower gradient.
    •  
      CommentAuthordjh
    • CommentTimeMay 29th 2020
     
    Posted By: gyrogearcannot see how lime would ever HINDER ?

    Well, calcium is a requirement for the growth of dry rot, apparently?
    •  
      CommentAuthordjh
    • CommentTimeMay 29th 2020
     
    Posted By: tonyOn a couple of occasions I have inspected floor voids there they had water, from a high water table above the level of the oversite

    According to previous statements, the floor needs to be 150 mm above the oversite, which must be above existing ground level. So how can that occur?

    PS I'm glad those regs apparently didn't apply to our passive slab, which is level with the outside at one point in accordance with Part M. :) It's 200 mm or so above at the other side of the building, to be fair.
    •  
      CommentAuthorfostertom
    • CommentTimeMay 29th 2020 edited
     
    Posted By: Kenny_MIsn't possible that the high RH here is coming up from the subsoil?
    Sure it is - the RH gradient goes from moderate to high in the room, to very high at the subsoil. Which means the low RH is going down from the room! Actually RH 'going' anywhere makes no sense, unlike heat, which definitely 'goes' somewhere.
    •  
      CommentAuthordjh
    • CommentTimeMay 30th 2020
     
    Posted By: fostertomActually RH 'going' anywhere makes no sense

    It makes sense, but a very complicated sort of sense since it's a combination of many factors. Changing the temperature changes the RH without anything moving. Changing the absolute humidity changes the RH and does involve movement of water often as vapour by diffusion but it can also be as liquid by capillary or straightforward gravity flow followed by evaporation, which itself can also affect the temperature. And of course the wind or other air pressure difference can move both vapour and liquid.
    • CommentAuthorKenny_M
    • CommentTimeMay 31st 2020
     
    Posted By: fostertomSure it is - the RH gradient goes from moderate to high in the room, to very high at the subsoil. Which means the low RH is going down from the room! Actually RH 'going' anywhere makes no sense, unlike heat, which definitely 'goes' somewhere.


    I meant, the water/vapour coming up from the subsoil to cause the high RH.



    Posted By: gyrogear
    Posted By: Kenny_Mnot sure if that would help or hinder.


    cannot see how lime would ever HINDER ?

    It is THE humidity controller par excellence !
    acts two ways (absorbs falling humidity (condensation) and rising humidity (from the ground)
    (and the latter is *always* wet!)

    Lime also stops pathogens dead !

    gg


    I am presuming that by lime we mean lime mortar. What I meant was, reading different comments in this thread there seems to the suggestion from some that the water vapour is coming from the house, and others that it is coming from the subsoil. If its coming from the subsoil then sealing the solum would help, but if the aim is to drive it down into the subsoil, as was suggested earlier in the thread, then its going to hinder - maybe not a lot, but more hindrance than it not being there at all. It may absorb humidity, but only up to a saturation point, so while it can act as a buffer it obviously can't soak up vapour indefinitely.


    Posted By: djh
    Posted By: fostertomActually RH 'going' anywhere makes no sense

    Changing the temperature changes the RH without anything moving.


    This is the thing that I think makes this very complicated, and is related to what I was trying, perhaps badly, to say in an earlier post. The current RH underneath my floor is 85%. The currently fairly warm air at a relatively low RH will be coming in the vents to a very cool area and the RH will rise, so there is every chance that the under floor RH will be above 85% over the whole of the summer, and so would be in the red according to Pelsmakers paper.

    It seems that there are so many factors from the water content in the soil, whether the room faces south or north, humidity in the room above, DPC present or not, vapour barrier on the interior floor or not, currently ventilated well or badly, and a host of other factors, that would impact whether this would be successful or not, making it a bit of a hit or miss.
    •  
      CommentAuthordjh
    • CommentTimeMay 31st 2020 edited
     
    Posted By: Kenny_MI meant, the water/vapour coming up from the subsoil to cause the high RH.

    Yes, but you have to understand the physics first.

    The current RH underneath my floor is 85%. The currently fairly warm air at a relatively low RH will be coming in the vents to a very cool area and the RH will rise, so there is every chance that the under floor RH will be above 85% over the whole of the summer, and so would be in the red according to Pelsmakers paper.

    There is no such thing as "the RH under the floor". The RH depends on the temperature, so will be varying everywhere. You only care about the RH wherever you have mould-sensitive construction materials.
    • CommentAuthorKenny_M
    • CommentTimeJun 1st 2020 edited
     
    Posted By: djh
    Posted By: Kenny_MI meant, the water/vapour coming up from the subsoil to cause the high RH.

    Yes, but you have to understand the physics first.


    What do you mean by that, what is it you don't think I understand?

    Posted By: djh
    Posted By: Kenny_MI meant, the water/vapour coming up from the subsoil to cause the high RH.

    The current RH underneath my floor is 85%. The currently fairly warm air at a relatively low RH will be coming in the vents to a very cool area and the RH will rise, so there is every chance that the under floor RH will be above 85% over the whole of the summer, and so would be in the red according to Pelsmakers paper.

    There is no such thing as "the RH under the floor". The RH depends on the temperature, so will be varying everywhere. You only care about the RH wherever you have mould-sensitive construction materials.


    How can there be "no such thing as RH under the floor"? There is an RH anywhere that there is air. If I put an RH meter into the void under the floor, which is what I did, and it gives me an RH reading then that signifies the RH under the floor. I know it varies with temperature, this is what I was getting at in my post, warm air of say 80% RH enters a cold under floor void and cools down, raising the RH in the void

    According to Pelsmaker mould will grow on EPS with long term exposure to >97 RH, which is presumably why they were measuring throughout the void. Even if that is not a concern, the paper reports >85% over extended periods beside the timber joists, which are without doubt mould-sensitive construction materials. Obviously I am less concerned about the possibility of mould growing on the EPS at the subsoil, but I would be concerned about an RH that is consistently over 85% at the joists.
    • CommentAuthorgyrogear
    • CommentTimeJun 1st 2020 edited
     
    One thing to consider maybe, is to create a conditioned void, if you have got access: entails blowing (drier) house air through the crawlspace, and ejecting it to exterior.

    One recommendation is to install continuously operated mechanical exhaust ventilation at a rate equal to 1 cfm for each 50 square feet of crawl space floor area. (I do somewhat more...).

    Entails first insulating the crawl periphery walls, and treating the floor (either encapsulation or limecrete slab etc.)

    gg
    •  
      CommentAuthordjh
    • CommentTimeJun 1st 2020
     
    Posted By: Kenny_MHow can there be "no such thing as RH under the floor"?

    I didn't say that. You omitted the vital word 'the'. RH is a quantity that varies everywhere in space. There is no single value that you can call "the RH under your floor" since that volume has air currents and varying temperatures as well as varying moisture sources, so it doesn't make sense to talk about a single number for the whole space. Just as it doesn't make sense to talk about the RH being the same everywhere in a room. It will be higer in corners and behind furniture etc. It does generally make sense to talk about the RH in a room, since air currents are small, the temperature is fairly uniform, and we know to restrict the meaning to the central space. But you can't make the same assumptions underfloor.
    • CommentAuthorEd Davies
    • CommentTimeJun 2nd 2020 edited
     
    Posted By: gyrogear: “…entails blowing (drier) house air…”

    Typically house air is damper than outdoor air in that it'll have more water vapour per kg or m³, though it'll usually have a lower RH because it's warmer. The extra water comes from people breathing and things drying out.

    E.g., in my study now it's 20°C with an RH of 65%. Looking at this psychrometric chart: https://en.wikipedia.org/wiki/Psychrometrics#/media/File:PsychrometricChart.SeaLevel.SI.svg that shows an absolute humidity of about 9g of water vapour per kg of dry air. Run up green 20°C line to the point half way between the red 60% and 70% then parallel to the blue lines (horizontal) to the scale on the right-hand axis.

    50 minutes ago Wick Airport, about 20km ago, was reporting 100% humidity and temperature 10°C which, using the chart in a similar way corresponds to about 8g/kg humidity ratio.

    100% RH is a bit extreme, so often the outdoor air is drier still, but overall those are quite typical conditions for the UK.
  1.  
    I agree! though I think gyrogear lives in a much warmer French(?) climate than the one we 'enjoy' at the top of the UK.

    Ed's study has a dewpoint of 16degC, so any surface colder than that will condense water.

    I like to think of the soil here as a big cold dehumidifier, that helps draw moisture from the suspended floor of the house. The soil is near to our average climate temperature of 9degC.

    The wind through the crawl space does the same when its dewpoint is colder than the house air dewpoint, which is for most of the year for us, though maybe not for GG. The wind's dewpoint is 10degC in Wick today, and 18degC in Paris.

    So Ed's study would dry out in drizzly Wick, but get wetter in balmy Paris, which takes some thought!

    If we insulated the crawl space walls like GG, the soil surface would warm up, maybe warmer than 16degC.

    Moisture would then have to go somewhere else, either permeating down to condense deeper in the soil, or through the insulation to condense behind on the crawl space walls, or condense somewhere else in the ground floor structure, whichever was its route of least resistance to find somewhere colder than 16deg.

    GG's climate often has warm air with a warmer dewpoint outside than inside, so he mentioned 'drier house air'. Cross ventilation would bring moisture into his crawl space those days, rather than carry it out like it does here. It also carries less heat out, so GG's crawl space is naturally warmer than ours and less able to dehumidify the ground floor.

    Vive la différence, as they say in Caithness.
    • CommentAuthorKenny_M
    • CommentTimeJun 2nd 2020
     
    Posted By: djh
    Posted By: Kenny_MHow can there be "no such thing as RH under the floor"?

    I didn't say that. You omitted the vital word 'the'. RH is a quantity that varies everywhere in space. There is no single value that you can call "the RH under your floor" since that volume has air currents and varying temperatures as well as varying moisture sources, so it doesn't make sense to talk about a single number for the whole space. Just as it doesn't make sense to talk about the RH being the same everywhere in a room. It will be higer in corners and behind furniture etc. It does generally make sense to talk about the RH in a room, since air currents are small, the temperature is fairly uniform, and we know to restrict the meaning to the central space. But you can't make the same assumptions underfloor.


    I don't really see what difference "the" makes. Of course measurements of anything, whether it be RH, temp, light, air quality, they all vary at different points in space, but its a pretty normal generalisation to give a value for a space. My initial statement was "The current RH underneath my floor is 85%", in the context that I was talking about the space under a single room. I don't know if that is where the confusion has arisen. Of course I can't say that the RH under the floor over the the whole of the house is x, because this will be made up of different spaces with walls in between, but its not unreasonable to summarise the RH for an unrestricted air space of about 5m2.

    I feel that I already have a sufficient understanding of absolute and relative humidity, and how the latter varies with temperature and pressure. Its this variation that I am pointing to as the source of the complexity. In a single unrestricted air space, the measured RH is not going to change significantly as the air is constantly circulating. When you fill that space with EPS the air flow is deliberately being restricted, as is the point of that type of insulation, so it must follow that the RH could be more significantly different at different points in the same space.

    I went through a lot of this before when discussing my flat roof space and I previously posted research that indicated that its often better to fully fill (with insulation) and seal poorly ventilated roof spaces, especially if they are south facing.

    A lot of the same must apply to ventilated floor spaces and insulation, except that the south facing aspect will probably have less of an impact. In the climate I live in, the RH of the air outside is usually quite high for most of the year. In the winter, the fact that the temp in the house is higher, means that ventilation tends to lower the RH in the house. In the subfloor void, in the winter the temp is not as significantly different, so the RH might only be slightly lower under the floor than the outside ear (not withstanding any other factors). In the summer, the temp in the void will most often be lower, so the RH is probably slightly higher than the outside air.

    It might be that fully filling the void with EPS would reduce the RH, and reduce the seasonal variations, especially with a vapour barrier to the interior. In Pelsmakers paper the RH is high at a number of measurement points in the EPS installation, and that could be a problem, but what we don't know is what the RH measurements were for the year before the EPS was installed. Maybe its better, maybe it is worse. That to me is the main flaw with that piece of research. In some ways I find it a bit disappointing that publicly funded research is allowed to be designed in this way, with no requirement to follow up on the outstanding questions.

    In my specific situation, I know that although the RH is high under there right now, its probably lower when the outside air is colder. I presume that because there is no sign of mould or deterioration in the timber that I believe has been there for at least 30 years. In any case, there are currently no mould or timber decay problems and adding EPS may or may not change that. Its a gamble, if I was to look at this as a business decision the relatively small saving wouldn't justify the risk, although if I was only in this to save money I wouldn't be doing any of these things, with the exception of maybe loft insulation and draught proofing.
    • CommentAuthorcc64
    • CommentTimeMar 4th 2023
     
    I was intrigued to discover "energystore superbead has been approved by NHBC Accepts as an insulation method for underneath beam and block floors. The innovative insulation solution for beam + block floors enables project savings, thermal optimisation and real-life performance."

    Looked at the details' ah - DPM under the beads.

    ah well
    • CommentAuthortony
    • CommentTimeMar 4th 2023
     
    Strange to have dpm on the cold side of insulation, it is acting as a vapour barrier and could in some circumstances ‘sweat’
    •  
      CommentAuthordjh
    • CommentTimeMar 4th 2023 edited
     
    tony said: "Strange to have dpm on the cold side of insulation, it is acting as a vapour barrier and could in some circumstances ‘sweat’"

    It's normal to have the DPM underneath most of the insulation in a passive slab, for example. Ours has one layer (of 100 mm EPS) underneath and three on top. If you're in a radon area I think you also want it near the outside.

    I assume Matthew is referring to something like https://www.energystoreltd.com/news-professional/nhbcacceptsbeamandblock in which there's a VCL above the insulation so that should mean the DPM isn't so much.
    • CommentAuthorNRDigger
    • CommentTimeApr 3rd 2023 edited
     
    This thread is incredible - I am seriously impressed by the level of analysis that's gone on.
    The URL for the Pelsmakers study seems to have changed but available (open access) https://doi.org/10.1016/j.enbuild.2017.07.085

    I'm interested to know what you did at the end, Kenny? Did you chuck in the EPS beads? And has your house fallen down yet? Love the idea of putting in nails to test conductance...

    Am seriously considering the same thing - as it is we've got not enough cross ventilation in any case. I'd just be chucking them on subsoil above a 300mm-ish gap so very interested to hear how you got on.

    Direction of travel also relevant as we have MVHR retrofit so presumably can be a little less worried about internal moisture...

    I suppose one variable is how tricky are they to remove once they're down... I mean, it's a LOT of beads!
    • CommentAuthortony
    • CommentTimeApr 4th 2023
     
    It is a mistake to think that MVHR will help, it is a good idea and lovely but won’t reduce problems of condensation on very cold/below dew point places in the structure, sorry

    Beads very easy to remove if not glued together , garden vac with massive bag and 75mm pipe connected to the business end - so reversible
  2.  
    I presented 4 Passivhaus renovation projects at the first UK Passive House Conference, think it was 2010, 2 houses had 400mm pumped EPS under the floor, Sofie came to chat afterwards, said she's like to do her PhD on it.
    My own 1880's house is done 15 years now without issues. I've a thermocouple and 2 steel rods for ground humidity testing beneath the insulation, the temperature's constantly 14 degrees, warmer than before so less likely for condensation to occur and also drier which proves that. We modeled it in Therm and added some drylining, because heatloss was focused to the joist ends in the wall, they were warmer than before the floor was pumped, so less likely to decay. I also did my neighbours 1880's house and removed some 5 years later to fit a wine store, the earth beneath was drier than before, the previous rising damp issues were gone, so insulating one side of a rising wall heats it and drives out damp, a 2 degree difference is sufficient to reverse capillary pull according to the Scandinavians. I also checked the electric cables and saw no sign of brittleness.
    I purchased a foam concrete machine recently and am quite impressed with it, I thought it could also be used for insulating floor voids, satisfy the regulations easier and remove the need to modify cables.
    • CommentAuthortony
    • CommentTimeApr 23rd 2023
     
    I want one of those too!

    I reckon downrating cables in the insulation is a possible good way forward, (can’t do that for mains in, cooker, shower or other heavy loads)
  3.  
    Posted By: djhtony said: "Strange to have dpm on the cold side of insulation, it is acting as a vapour barrier and could in some circumstances ‘sweat’"
    It's normal to have the DPM underneath most of the insulation in a passive slab, for example. Ours has one layer (of 100 mm EPS) underneath and three on top.
    A Passive Slab'S DPM's usually on the warm side of the Dew Point, 100mm EPS above the DPM and 200mm EPS below.
    • CommentAuthortony
    • CommentTimeApr 25th 2023
     
    Yes, great way to go, sadly others including designers and inspectors put them on the cold side and at risk of collecting dew.
    • CommentAuthordathi
    • CommentTimeApr 26th 2023
     
    for any of you that are mad enough you could shred your own polystyrene https://www.youtube.com/watch?v=TdpaMzGhSp4&t=87s
    •  
      CommentAuthorfostertom
    • CommentTimeApr 26th 2023 edited
     
    Gotta hand it to Americans - so can-do, backyard-resourceful about so many worthy new-thinking ideas, while also (it looks from here) other Americans so dangerously clueless about other important things. So huge that what's admirable leads the world, while what's deporable drags the world down. Take your pick as to which one to 'believe' about America!"
   