Posted By: Nick Parsonslambda of over 0.44Yeah, that'd be poor. ITYM 0.044.
Posted By: VictorianecoInternal insulation and flat finish, approximately 75m2
What's the u value, prices and is it truly DIYable? If a wall is 8m long hours do you do it in one go? With batons and sections?
Posted By: Nick ParsonsEarlier in this thread there is reference to a lambda value of 0.068W/mK. On my 225 solid brick wall this would, for example, give me a u value of around 1.2W/m2K compared to an as-built u value of 2.1W/m2K.
Posted By: VictorianecoSo better off using PIR then surely?
Posted By: Nick ParsonsIf you can use PIR 'safely' after a rigorous risk assessment. The big problem is embedded timbers and interstitial condensation generally. A water-vapour-permeable insulant is more sympathetic to older buildings. However I would not normally use anything with a lambda of over 0.044 if I could help it.
Posted By: Nick ParsonsAlexander,
I am sorry, I should have said that I was talking about like-for-like thicknesses.I assumed a 'base-case' U value of 2.1W/m2K and 25mm of your insulating plaster with a lambda of 0.068W/mK. Yes, it is really too thin, but if I were looking to go with thick insulation I would (a) lose the nice ceiling mouldings and (b) choose to use wood-fibre or cork with a lambda of 0.042W/mK.
You referred on another thread (http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=14393&page=1#Item_9) to:
''other aspects of thermal performance after installation, which includes thermal bridges for boards, breathability and condensation issues, which impacts real thermal performance after the installation but it is a different topic..''
I agree wholeheartedly that mitigation of thermal bridges is very important indeed, but why do you feel that there is any more of a likely issue with ''thermal bridges for boards'' than with insulated plaster? Poorly-detailed insulation board will leave thermal bridges which could have been mitigated, as will poorly-detailed insulating plaster. On the other hand, good detailing (good practice) with either material will help to keep thermal bridges to a minimum.
Posted By: VictorianecoPosted By: BauwerPosted By: Nick ParsonsEarlier in this thread there is reference to a lambda value of 0.068W/mK. On my 225 solid brick wall this would, for example, give me a u value of around 1.2W/m2K compared to an as-built u value of 2.1W/m2K.
Hello Nick,
Your statement is only correct for 30mm Bauwer Light application thickness, which is really too thin.
30mm of Bauwer Light applied to 225 solid brick wall, would give you an improved U value of 1.2 W/m2K compared to an as-built U value of 2.75W/m2K, eg. 2.3 times improvement. This calculation assumes 5mm of Bauwer Finish.
As I posted above, higher thickness option should be considered, as 50mm or 100mm (2 layers application).
Regards, Alexander.
Can you give figures for the 50mm and 100mm application to the same reference wall? And also advise on price for each method?
Posted By: GotanewlifeI have to say I am with Alexander on this. A U value of 0.9 and a loss of space of 50mm with vastly reduced risk of poor detailing compared to boards (incl wood fibre), and no risk of damaging those solid walls with condensation issues and all DIYable is a worthy target - except it is not.....
and the price?
Posted By: VictorianecoPrice seems excessive unfortunately, 50mm IWI will give me a U-Value of approximately 0.3 and will cost £9.03 per square metre using composite boards (£26 per sheet)
Posted By: GotanewlifeI have to say I am with Alexander on this. A U value of 0.9 and a loss of space of 50mm with vastly reduced risk of poor detailing compared to boards (incl wood fibre), a durable finish that can't be damaged with one un sealed screw, and no risk of damaging those solid walls with condensation issues and all DIYable and not even mentioning the eco bit is a worthy target, - except it is not.....
but the price?
Posted By: SteamyTeaYou can add multiple images to a single post by initially adding one image and posting, then using the 'edit' function, add another image, then save changes (repost). You can do that for as many images as you like.
Posted By: MarkyPhas anyone ever tried mixing their own insulating plaster? Perlite is available (100 litres for about £20), likewise vermiculite. I wonder if some experiementation with these, an aggregate base and lime would lead to a nice, lightweight plaster at a cheap price. If I had the time, I'd give it a go.