Posted By: pmccWould a reasonable option be to replace item 4 (rigid insulation between rafters) with some kind of breathable membrane filled with cellulose?
Posted By: ali.gilli believe sarking in scotland is just standard timber with no bitumen but welcome correction on this. (An idea of build date to check relevant b.con spec would be useful)
50mm vent void in rafters, spec'd by b.con is 25mm void and 25mm to allow for sagging of the felt. In the o.p's case sarking is rigid so you may be able to go 3)25mm 4)75mm or maybe safer 3)40mm and 4)60mm.
Then i'd counterbatten 50mm x 50mm and insulate between using pir cavity batts to gauge spacing and save cutting. If screwing through rigid foil-faced insulation to rafters use 50x50 of duck tape at screw location to prevent penetration of screw head and retain vcl quality as best as can be hoped.
Then over that fix a laminated osb/pir hybrid board onto the 50x50 c'batten. Mark (hi-vis) fixing lines on the osb to suit the plasterboard sheet size - place a clear polythene vcl and staple up (only on the fixing line) - apply a silicone mastic over staple holes (full length of fixing line) and fix directly over the mastic a 2x1 or 3x1(d.i.y) batten for fixing plasterboard and to provide a service cavity.
Counterbattening 50 x 50 reduces thermal bridging compared to battening directly over rafter but also gives body for mechanical fixing of what comes after. Spec further up the thread assumes fixing p'bd directly onto vcl and through 100mm insltn then into a seasoned rafter.
fostertom has a spec that includes multifoil in the mix so thats also worth considering.
Posted By: Mike GeorgeThe reference details a rate of around 1.5ach@50Pa, which is not very good at all.What do you mean it's not very good? None of the Stamford Brook properties achieved this level of air tightness. Maybe you're not seeing the @50Pa - at regular pressure this is 0.075ACH. 1.5ACH@50Pa is the R2000 maximum allowed air leakage for certification. Doesn't the current UK Part L suggest something like 5ACH@50?
Posted By: tonyIt is still a good idea to have a vb even with a vented roof.
Posted By: Paul in MontrealPosted By: Mike GeorgeThe reference details a rate of around 1.5ach@50Pa, which is not very good at all.What do you mean it's not very good? None of the Stamford Brook properties achieved this level of air tightness. Maybe you're not seeing the@50Pa- at regular pressure this is 0.075ACH. 1.5ACH@50Pa is the R2000 maximum allowed air leakage for certification. Doesn't the current UK Part L suggest something like 5ACH@50?
Paul in Montreal.
Posted By: Mike George10m3/m2/yr @50PaAre you sure there's a per year term in there?
Posted By: Mike GeorgeIn Cananda you use a different measure again.We do? I thought we used ACH@50Pa and this can be nominally converted to normal pressure by dividing by 20. The m3/m2 stuff I find very confusing since it is dependent on the size of the building whereas ACH is easier to visualize.
Posted By: Paul in Montreal
[...]ACH@50Pa and this can be nominally converted to normal pressure by dividing by 20. The m3/m2 stuff I find very confusing since it is dependent on the size of the building whereas ACH is easier to visualize.
Paul in Montreal.
Posted By: Paul in MontrealPosted By: Mike George10m3/m2/yr @50PaAre you sure there's a per year term in there? Paul in Montreal.