Home  5  Books  5  GBEzine  5  News  5  HelpDesk  5  Register  5  GreenBuilding.co.uk
Not signed in (Sign In)

Categories



Green Building Bible, Fourth Edition
Green Building Bible, fourth edition (both books)
These two books are the perfect starting place to help you get to grips with one of the most vitally important aspects of our society - our homes and living environment.

PLEASE NOTE: A download link for Volume 1 will be sent to you by email and Volume 2 will be sent to you by post as a book.

Buy individually or both books together. Delivery is free!


powered by Surfing Waves




Vanilla 1.0.3 is a product of Lussumo. More Information: Documentation, Community Support.

Welcome to new Forum Visitors
Join the forum now and benefit from discussions with thousands of other green building fans and discounts on Green Building Press publications: Apply now.




    • CommentAuthoreastong
    • CommentTimeFeb 2nd 2009
     
    Our loft is Scottish construction, slates, sarking boards and 4 inch rafters. I've seen other comments on insulation but I want to check the need for vapour barrier on the inside of the insulation and whether a vapour barrier is needed between the sarking/rafters and outside of the insulation. Also what do people think the best insulation is? I realise that we will need to batten the rafters on the inside to create extra depth for insulation.
    •  
      CommentAuthorbetterroof
    • CommentTimeFeb 2nd 2009 edited
     
    Are you stripping right back to the rafters and then insulating in the cavities from inside? or is some of this going on with the roof off? There are a number of options you can use tbh
    • CommentAuthortony
    • CommentTimeFeb 2nd 2009
     
    Inside the insulation -- on the warm side.
    • CommentAuthoreastong
    • CommentTimeFeb 2nd 2009
     
    I would like to leave the slates on, so we would be adding insulation from the inside between the rafters. Tony's comment is suggesting vapour barrier on the warm side in the room then insulation against the sarking boards.
    • CommentAuthorMike George
    • CommentTimeFeb 2nd 2009 edited
     
    Hi eastong, lots on the site about this. Use the search function for 'roof insulation' This may cover it though http://www.greenbuildingforum.co.uk/forum114/comments.php?DiscussionID=266&page=1
    • CommentAuthorCWatters
    • CommentTimeFeb 3rd 2009 edited
     
    I believe you should only fill the cavity between the rafters if you have breathable sarking/membrane which I don't think you have. I think you would need to build a ventilated roof and would expect the finished construction to be something like..

    1) slates
    2) sarking boards
    3) 50mm ventilated cavity (vents at eaves and ridge)
    4) 50mm Celotex between rafters
    5) 100mm Celotex below rafters
    6) Vapour barrier
    7) Plasterboard.

    The depth of 3+4 choosen to fill the 100mm rafters.
    Second layer below rafters installed at 90 degrees.
    The vapour barrier could be formed by taping the joints on the celotex or fixing up plastic sheet.
    Total thickness of Celotex 150mm gives U-Value around 0.16.

    The Celotex U-Value calculator recommends "25 x 50mm fixing batten under rafterline (recomended where insulation below rafters in excess of 50mm thick)" but I've omitted that from the above.

    http://www.celotex.co.uk/
    • CommentAuthorpmcc
    • CommentTimeFeb 3rd 2009
     
    Would a reasonable option be to replace item 4 (rigid insulation between rafters) with some kind of breathable membrane filled with cellulose? I have a similar project to eastong, with 70s non-insulated timber frame house and lots of complicated spaces to fill. Ruled out a warm roof due to cost of taking down and putting back the the roof (~350m2).

    I've been thinking about how to pour cellulose from the top attic to fill the space above the sloping ceilings (coombes?) to a sufficient depth which still allows ventilation. One idea is to fix a membrane of some kind at the right height between each set of rafters at both ends (upper loft and lower void above eaves), stretch it tight, fix to rafters, then pour in the insulation. One the insulation is in place then the tautness of the membrane would no longer be critically important.

    Benefits are ease of fitting (important for me because I'll do it with my sons and I'm not a builder), elimination of air gaps and good thermal resistance.

    Roof leaks might be an issue, but presumably membranes are somewhat waterproof...

    If this looks like it might work I'll read up about membranes (links v welcome)!
    •  
      CommentAuthorali.gill
    • CommentTimeFeb 3rd 2009
     
    i believe sarking in scotland is just standard timber with no bitumen but welcome correction on this. (An idea of build date to check relevant b.con spec would be useful)
    50mm vent void in rafters, spec'd by b.con is 25mm void and 25mm to allow for sagging of the felt. In the o.p's case sarking is rigid so you may be able to go 3)25mm 4)75mm or maybe safer 3)40mm and 4)60mm.
    Then i'd counterbatten 50mm x 50mm and insulate between using pir cavity batts to gauge spacing and save cutting. If screwing through rigid foil-faced insulation to rafters use 50x50 of duck tape at screw location to prevent penetration of screw head and retain vcl quality as best as can be hoped.
    Then over that fix a laminated osb/pir hybrid board onto the 50x50 c'batten. Mark (hi-vis) fixing lines on the osb to suit the plasterboard sheet size - place a clear polythene vcl and staple up (only on the fixing line) - apply a silicone mastic over staple holes (full length of fixing line) and fix directly over the mastic a 2x1 or 3x1(d.i.y) batten for fixing plasterboard and to provide a service cavity.

    Counterbattening 50 x 50 reduces thermal bridging compared to battening directly over rafter but also gives body for mechanical fixing of what comes after. Spec further up the thread assumes fixing p'bd directly onto vcl and through 100mm insltn then into a seasoned rafter.
    fostertom has a spec that includes multifoil in the mix so thats also worth considering.
    •  
      CommentAuthorali.gill
    • CommentTimeFeb 3rd 2009
     
    pmcc - whats on the rafters now, under the roof covering?
  1.  
    Hi,
    Couple of points from a non roofer.
    In Scotland its generally its 25mm gap below the sarking planks (not OSB board unless its a new build) and these are covered with the breatable membrane, but on older properties you will find the black bitumous felt. When the breather is used a 2-3mm gap is left between each plank ie the width of a nail, but on older property the planks are butted up tight. Not entierly sure about the ridge. So a 25mm sq batten can be fixed up under the sarking to push the insulation slab up against.
    Cheers
    Mike up North
    • CommentAuthorCWatters
    • CommentTimeFeb 3rd 2009 edited
     
    Posted By: pmccWould a reasonable option be to replace item 4 (rigid insulation between rafters) with some kind of breathable membrane filled with cellulose?


    That would work if you can be sure of maintaining the ventilated gap 3).
    • CommentAuthorpmcc
    • CommentTimeFeb 4th 2009
     
    Posted By: ali.gilli believe sarking in scotland is just standard timber with no bitumen but welcome correction on this. (An idea of build date to check relevant b.con spec would be useful)


    Ali, build date 1974 (evidence suggests that the builder was in a rush to get to the pub).

    Sarking is timber. Between sarking and the rafters (attached to wooden pieces going across the roof above the rafters) there is some stuff which looks like a membrane. Apologies for non-technical description. It's multi-layered, black, looks tearable, with coarse cross-hatching and polythene bag type of edging sticking out of the middle layer. Stuck underneath facing into the attic voids is a 1cm layer of stuff which looks like glass wool insulation, although I cannot imagine its function.

    Just to be clear, the sarking board appears to be placed on top of battens (?) across the roof. So there is a small gap between the 'membrane' and the sarking board.

    50mm vent void in rafters, spec'd by b.con is 25mm void and 25mm to allow for sagging of the felt. In the o.p's case sarking is rigid so you may be able to go 3)25mm 4)75mm or maybe safer 3)40mm and 4)60mm.


    Rafters are 150mm, so I could put in 100mm of insulation above the existing plasterboard and leave a 50mm ventilation gap.

    Then i'd counterbatten 50mm x 50mm and insulate between using pir cavity batts to gauge spacing and save cutting. If screwing through rigid foil-faced insulation to rafters use 50x50 of duck tape at screw location to prevent penetration of screw head and retain vcl quality as best as can be hoped.
    Then over that fix a laminated osb/pir hybrid board onto the 50x50 c'batten. Mark (hi-vis) fixing lines on the osb to suit the plasterboard sheet size - place a clear polythene vcl and staple up (only on the fixing line) - apply a silicone mastic over staple holes (full length of fixing line) and fix directly over the mastic a 2x1 or 3x1(d.i.y) batten for fixing plasterboard and to provide a service cavity.

    Counterbattening 50 x 50 reduces thermal bridging compared to battening directly over rafter but also gives body for mechanical fixing of what comes after. Spec further up the thread assumes fixing p'bd directly onto vcl and through 100mm insltn then into a seasoned rafter.


    Thanks for the detailed info! Looks highly relevant for the side attic voids. Decision will probably be based on whether I can afford to lose the extra 50mm. Probably yes, although the big side attic is used for storage and the void on the other side may become inaccessible if too much space lost.

    For the coombe ceilings I was really hoping not to remove the existing ceiling plasterboard. The Warmcel idea was to find an easy way of installing and still get effective thermal insulation. The problem with PIR type of boards seems to be that rafters with irregular gaps will be very hard to completely fill. I can't easily get into the coombe gap to apply foam, without removing the plasterboard from the existing ceiling.

    Biggest problem I see is putting in a vcl above the plasterboard on the coombe ceilings. Can't think how to do it except to take off the plasterboard.

    fostertom has a spec that includes multifoil in the mix so thats also worth considering.


    I find the physics of multifoils interesting, but doubt whether they are particularly suitable for my situation. Scotland does tend towards the damp and gloomy - strangely enough excess heat has never been a problem in the 13 years I've lived in the house ;). Anyway, I'm looking into summer solar heat capture and inter-seasonal storage so attic heat will hopefully be syphoned away.
    • CommentAuthorralphd
    • CommentTimeFeb 4th 2009
     
    With a vented roof there is no need for a vapor barrier (assuming drywall, primer, & paint on the warm side).
    Bulk movement (i.e. air leaks) is the main source of vapor movement so you do need a good air barrier. Drywall is better than poly as an air barrier so you still don't need poly.
    "The plywood exterior sheathing was the principal air barrier, followed by the gypsum board, polyethylene and cellulose."
    http://www.cmhc.gc.ca/publications/en/rh-pr/tech/90-240.pdf
    • CommentAuthortony
    • CommentTimeFeb 4th 2009 edited
     
    It is still a good idea to have a vb even with a vented roof.
    • CommentAuthorMike George
    • CommentTimeFeb 4th 2009 edited
     
    ralph, I'm confusd about what you're saying. The reference details a rate of around 1.5ach@50Pa, which is not very good at all.
  2.  
    Posted By: Mike GeorgeThe reference details a rate of around 1.5ach@50Pa, which is not very good at all.
    What do you mean it's not very good? None of the Stamford Brook properties achieved this level of air tightness. Maybe you're not seeing the @50Pa - at regular pressure this is 0.075ACH. 1.5ACH@50Pa is the R2000 maximum allowed air leakage for certification. Doesn't the current UK Part L suggest something like 5ACH@50?

    Paul in Montreal.
    • CommentAuthortony
    • CommentTimeFeb 4th 2009
     
    10 !! and if you cant get there try again if that still fails then give up.

    Vaguely reminiscent of colanders.
    • CommentAuthorralphd
    • CommentTimeFeb 4th 2009
     
    Posted By: tonyIt is still a good idea to have a vb even with a vented roof.


    I agree it's not a bad idea, but that doesn't make it a good idea.
    • CommentAuthorMike George
    • CommentTimeFeb 5th 2009 edited
     
    Posted By: Paul in Montreal
    Posted By: Mike GeorgeThe reference details a rate of around 1.5ach@50Pa, which is not very good at all.
    What do you mean it's not very good? None of the Stamford Brook properties achieved this level of air tightness. Maybe you're not seeing the@50Pa- at regular pressure this is 0.075ACH. 1.5ACH@50Pa is the R2000 maximum allowed air leakage for certification. Doesn't the current UK Part L suggest something like 5ACH@50?

    Paul in Montreal.


    Yes, my mistake, I mixed the units up. Its all these different ways of measuring the same bloody thing! .UK regs for example is 10m3/m2/hr @50Pa, whereas the software I am familiar with is ach @ normal pressure. In Cananda you use a different measure again.

    I am confused about being even more confused than I thought I was:cry:
  3.  
    Posted By: Mike George10m3/m2/yr @50Pa
    Are you sure there's a per year term in there?

    Posted By: Mike GeorgeIn Cananda you use a different measure again.
    We do? I thought we used ACH@50Pa and this can be nominally converted to normal pressure by dividing by 20. The m3/m2 stuff I find very confusing since it is dependent on the size of the building whereas ACH is easier to visualize.

    Paul in Montreal.
    • CommentAuthorralphd
    • CommentTimeFeb 5th 2009 edited
     
    Posted By: Paul in Montreal
    [...]ACH@50Pa and this can be nominally converted to normal pressure by dividing by 20. The m3/m2 stuff I find very confusing since it is dependent on the size of the building whereas ACH is easier to visualize.

    Paul in Montreal.


    The divide by 20 method is an oversimplification that is so inaccurate it is not scientific (it frequently results in estimates of natural air infiltration rates that are less than half of the measured rates).

    Details in my previous post:
    http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=3485
    • CommentAuthorMike George
    • CommentTimeFeb 5th 2009 edited
     
    Posted By: Paul in Montreal
    Posted By: Mike George10m3/m2/yr @50Pa
    Are you sure there's a per year term in there? Paul in Montreal.


    No its m3/m2/hr. A typo, probably too much caffiene, good job someone's awake:wink:

    We don't use ach@50Pa at least not for compliance with Part L.