Home  5  Books  5  GBEzine  5  News  5  HelpDesk  5  Register  5  GreenBuilding.co.uk
Not signed in (Sign In)

Categories



Green Building Bible, Fourth Edition
Green Building Bible, fourth edition (both books)
These two books are the perfect starting place to help you get to grips with one of the most vitally important aspects of our society - our homes and living environment.

PLEASE NOTE: A download link for Volume 1 will be sent to you by email and Volume 2 will be sent to you by post as a book.

Buy individually or both books together. Delivery is free!


powered by Surfing Waves




Vanilla 1.0.3 is a product of Lussumo. More Information: Documentation, Community Support.

Welcome to new Forum Visitors
Join the forum now and benefit from discussions with thousands of other green building fans and discounts on Green Building Press publications: Apply now.




    • CommentAuthortony
    • CommentTimeNov 24th 2015
     
    I read this recently,"Domestic buildings that have standard detailing for the SIPs roof and wall system can forego the requirement of a vapour barrier if a mechanically assisted ventilation and extraction system is installed such as an MVHR system (mechanical ventilation with heat recovery). Non-domestic buildings will almost certainly require a vapour barrier and should be assessed in accordance with BS 5250 depending on their use.

    I strongly disagree with this advice which would be laughed about in disbelief in Scandanavia and Canada.


    What is there to say that the MVHR will be used? What stops moisture migrating into the structure and condensing on the outside of the timber structure?


    I reckon this advice will be removed as it leaves the advisers open to litigation.
  1.  
    My understanding is that SIPS are already vapour-tight so no further barrier is needed (as it wouldn't do anything). Same thing for ICF construction, too.

    I could be wrong, though.

    Paul in Montreal.
    • CommentAuthortony
    • CommentTimeNov 25th 2015
     
    The main part of the panels may well be (closed cell insulation) but there is an AWFUL lot of wood, 125 plate posts 150 and 75 wide that would allow vapour to pass slowly through and these go through the structure, most are covered by osb inside and out but not all.
    • CommentAuthorDarylP
    • CommentTimeNov 25th 2015
     
    yes, the SIPs 'wall' is not 100% PU (or other insulant) but bridged by timber and OSB spigots and joints.

    I think the orig. comment is largely "marketing-speak", and not approved detail?
    Tony, where did it come from?:bigsmile:
    •  
      CommentAuthorfostertom
    • CommentTimeNov 25th 2015
     
    Agreed, internal ventilation is irrelevant, whether MHRV, conventional mechanical, or opening windows. Any kind of ventilation simply accellerates the exchange and equalisation of inside and outside air, importing all the water vapour content of the current outside air. Except for gross momentary internal peaks - cooking, bathing, tumble drying - ventilation does nothing to lower internal RH - that's a popular but outdated fallacy.

    Once indoor air is identical with outside air (by means of ventilation exchange), the only difference being the temp that each is currently at, then it's that temp difference that causes interstitial condensation when it's at its diurnal/seasonal largest difference - depending on the configuration of the wall sandwich.
    •  
      CommentAuthordjh
    • CommentTimeNov 25th 2015
     
    Posted By: fostertom Except for gross momentary internal peaks - cooking, bathing, tumble drying - ventilation does nothing to lower internal RH - that's a popular but outdated fallacy.

    So all the threads on all the forums where people have high humidity in their houses, often after insulating and draughtproofing old houses, and where ventilation, often just opening the windows more, improves the situation are lies? And humidity-controlled ventilation systems must be so obviously wrong that they'll never catch on. Methinks there's more going on than you recognize here.

    Once indoor air is identical with outside air (by means of ventilation exchange), the only difference being the temp that each is currently at, then it's that temp difference that causes interstitial condensation

    And how does this happen exactly? Temperature does not affect water vapour movement.

    http://www.conservationphysics.org/vap/hansen-moisture-transport-NSB14.pdf

    It's been said before, but there's a lot of good stuff on that site.
    • CommentAuthorEd Davies
    • CommentTimeNov 25th 2015 edited
     
    Umm, Tom, backing up DJH, what about this post from only 17 hours ago:

    Posted By: Simon StillThanks djh.

    It's made a big difference after 2 days. Towels drying quickly is a sure sign
    in this thread:

    http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=13829
    • CommentAuthorringi
    • CommentTimeNov 25th 2015
     
    Both of you are right!, It comes down to where you measure the RH. Measure the RH on the inside of the insulation then ventilation does reduce it in winter, but measure it on the air that exit though a gap in the insulation then it does not.
    •  
      CommentAuthorfostertom
    • CommentTimeNov 25th 2015 edited
     
    Posted By: djhwhere people have high humidity in their houses, often after insulating and draughtproofing old houses, and where ventilation, often just opening the windows more, improves the situation
    Yes, if after draughtproofing there's no ventilation, so internal vapour generation peaks don't get away, then adding some ventilation allows the inside air to be exchanged for outside air of lower abs water vapour content. I'm not saying that a fairly small sufficiency of ventilation/air exchange isn't necessary/effective, but once equilibriated with outside, adding more doesn't progressively lower internal RH.

    So is daft to say that any particular kind of ventilation can obviate need for vap barrier - though ironically that vap barrier won't be needed anyway if designed to be safely 'breatheable.

    Posted By: djhTemperature does not affect water vapour movement
    With approx equal abs water vapour concentration inside and out, thanks to ventilation exchange (it's same air inside and out), the only difference between the two is air temp, hence different RH. For any given wall sandwich, both that temp difference, and the abs outdoor temp, will determine both the rate of water vapour diffusion from inside to out, and whether it condenses intersitially or not.

    What other variables are there?

    Or are you disagreeing that internal abs water vapour concentration is closely locked to outside ditto, given 'some' ventilation exchange, and admitting that short-lived internal water vapour production spikes may temporarily disturb that equality?
    •  
      CommentAuthorfostertom
    • CommentTimeNov 25th 2015 edited
     
    Posted By: Ed Daviesif the air inside the house is drier than it would be with less ventilation
    Does 'drier' mean RH, or abs concentration?

    Posted By: Ed Daviesadditional ventilation will bring it progressively closer
    'closer' becomes 'equalised' as a result of only a modest amount of bulk ventilation exchange, so it's a red herring to imply a progressive lowering of internal RH by adding more and more ventilation.
    •  
      CommentAuthordjh
    • CommentTimeNov 25th 2015
     
    The point is that what causes mould in buildings usually IS lack of ventilation and some heating. It's nonsense to say that apart from some spikes ventilation doesn't help. Ventilation limits the humidity and is what keeps it at a sensible level instead of climbing to unhealthily high values. So depending on the wall design, it may very well change WUFI results from fail to pass. But I agree it does depend on specifics and on the ventilation actually being run.

    Posted By: fostertomWith approx equal abs water vapour concentration inside and out, thanks to ventilation exchange (it's same air inside and out), the only difference between the two is air temp, hence different RH. For any given wall sandwich, both that temp difference, and the abs outdoor temp, will determine both the rate of water vapour diffusion from inside to out, and whether it condenses intersitially or not.

    I take exception to two points in that paragraph.

    Firstly, the ventilation doesn't equalize the humidities because you're ignoring buffering. Even in brick houses, the contents have a significant effect.

    But the second point is more important and is that no, the temperature does not influence the rate of diffusion. If the abs water vapour concentration inside and out were indeed equal then there would be no diffusion. Or so says that reference I linked:

    "The conclusion of Janssen's review was that the papers stating an occurrence of thermal diffusion are flawed, and therefore there is no support for the claim that temperature has an effect on moisture transport."
    •  
      CommentAuthorfostertom
    • CommentTimeNov 25th 2015
     
    I won't answer blow-for-blow, but re-state hopefully clearer.

    Modest ventilation is essential, to effectively equalise inside with outside air - it can't possibly do more than that. Ventilation should be just enough to achieve that, no more. As outside air becomes inside air, it's the same air, just raised to higher temp, and that lowers its RH below what it was while outside, even tho abs water vapour concentration remains same.

    Then intermittent water vapour is added - cooking, bathing, tumble drier - but it only takes 1 or 1.5max airchanges to re-equalise inside with outside. The 'bit extra' of ventilation rate needed to cope with those spikes is in fact lower as a result of casual (furnishings) or deliberate (Warmcel or other organic insulation) hygroscopic buffering - the in-the-air concentration peak is lower and is spread over longer time.

    As far as mould or interstitial condensation is concerned, intermittent RH peaks are irrelevant, except insofar as they slightly bias internal RH upward, long-term - but the ventilation should be sufficient (but modest) to make that bias almost negligible.

    Going back to the OP, I suppose if you're assuming worst-case hopeless tenants who prevent ventilation while generating lots of water vapour, then yes a VCL may be key to preventing interstitial condensdation (but irrelevant to surface mould). Then, installing tamper-proof MHRV (as distinct from more preventable forms of ventilation) may lessen or eliminate the necessity for VCL - but foolish to so generalise - calc it in WUFI. That can be the only half credible meaning of that OP.

    Posted By: djhthe temperature does not influence the rate of diffusion
    Do you mean temp, or temp difference?
    Posted By: djhIf the abs water vapour concentration inside and out were indeed equal then there would be no diffusion
    Now you're giving me hope of clarification - surely on GBF I've been put right, in terms that 'vapour drive' is always from warm side to cold side, and only extreme (and rare) low abs vapour concentration on the warm side, relative to high abs concentration on the cold side, could reverse that. That also seems to figure in basic theory diagrams in the excellent-textbook WUFI Help. I could never make sense of that tem-driven 'vapour drive', but admit I've parroted it here.
    •  
      CommentAuthordjh
    • CommentTimeNov 26th 2015
     
    Tom, do you measure humidity in your own home? And does it match what you are saying?

    At my house this morning, it was 3 °C outside, so dewpoint was either that or below. Inside my house was 21 °C and ventilation was 150 m³/hr, so according to you, the relative humidity should be 31% or less. It was actually 47%, which is close to the lowest it's ever been.
    •  
      CommentAuthorfostertom
    • CommentTimeNov 26th 2015 edited
     
    So, trying to understand what's happening ...

    You're saying that:
    Typical modest rates of ventilation do not near-enough replace inside air with outside;
    Inside air is not equal to current outside air, except warmed up and intermittent extra water vapour peaks added (cooking, bathing) until re-equalised;
    Typical ventilation is merely dilution of inside air, not near-enough complete replacement;
    Inside air permanently (or usually) has much higher abs water vapour concentration than the outside air it's being diluted with by ventilation.

    I want to know:
    Where does this perpetual addition of water vapour inside, come from? Is it just those intermittent peaks (cooking, bathing) plus perpetual occupants' respiration?
    Surely that is intermittent enough to be near-completely exchanged away in between the peaks, by typical modest ventilation?
    And, if outward-diffusion is driven entirely by difference of abs water vapour concentration, not by temp difference, then all the outward-diffusion must be due solely to that perpetual addition of water vapour inside.
    In other words, in a house that's heated and ventilated but unoccupied, so no addition of water vapour happening inside, outward-diffusion would stop eventually, as inside air would indeed eventually become equalised by the ventilation with outside air, except warmed up?
    •  
      CommentAuthordjh
    • CommentTimeNov 26th 2015
     
    Posted By: fostertomSo, trying to understand what's happening ...


    http://www.conservationphysics.org/

    It's been said before, but there's a lot of good stuff on that site.
    •  
      CommentAuthorfostertom
    • CommentTimeNov 26th 2015 edited
     
    Looks good Dave - apart from your mention a few posts above I wasn't aware of this - maybe a ready made alternative to seeking wisdom from GBF!
    Pity it doesn't go into u/ground heat and water flow.
    • CommentAuthorgyrogear
    • CommentTimeNov 26th 2015 edited
     
    great discussion - thanks a lot !

    Therefore, per http://www.conservationphysics.org/ppubs/humidity_buffering_building_interiors_nsb2011.pdf:

    "Well ventilated unfired perforated brick, 5 cm thick, has a buffer capacity of 27 m3 per square metre of surface for a daily RH cycle. One can regard the sum of the buffer values of the wall lining and the furnishing as a virtual (larger) volume of a room, into which water vapour from infiltration and internal generation has to disperse, with a consequently smaller RH variation".

    would I be right in thinking that creating a "DUMP" of perforated brick in my Crawlspace would provide for a lower RH level... (because running a halogen lamp down there, 24/24, did nowt to the RH...).

    gg
    • CommentAuthortony
    • CommentTimeNov 26th 2015
     
    No
  2.  
    Posted By: gyrogearwould I be right in thinking that creating a "DUMP" of perforated brick in my Crawlspace would provide for a lower RH level.

    Buffering doesn't lower RH, it just evens out the peaks and troughs; ie, the avg RH stays the same BUT buffering may stop the peak RH getting above dew point, which is really what we are interested in.
    • CommentAuthorgyrogear
    • CommentTimeNov 26th 2015 edited
     
    Not sure I understand that !

    I thought that the dew point was a *temperature*, namely, that at which the humidity in the air will condense out, into "wet water..."

    (I obviously understand the need to prevent that happening !)
    So to prevent the air temp getting that cold, I thought I would warm the CS, with incandescent lamps...
    But I find that as the temperature increases, so does the RH !

    (I am in the process of concreting the CS floor (it is just earth...)).

    I suppose that until the floor is finished, the humidity will just keep coming up, from the ground (not to say, out of my concrete...).

    I don't really like the idea of a wet crawlspace...
    ===========
    So I found this chart:

    The CS currently is at 17.8°C and the RH is 85%
    (The house is at 19.5°C and 62% RH)
    The CS dewpoint is 15°C

    Per the chart, the RH should be the orange line = 40%
    Therefore I deduce that my CS RH is far too high
    However, since the CS temp is 2°C above the dewpoint, "I should be OK, as condensation will not occur"

    My local weather is: temp 11°C, 83% RH, increasing to 97% tomorrow...

    Thanks to anybody for telling me if I am still on the rails here !

    gg
    •  
      CommentAuthorfostertom
    • CommentTimeNov 27th 2015
     
    What a treasure house is http://www.conservationphysics.org

    I can also offer the WUFI Pro Help file, which is an excellent text book, as well as application-specific. Click on my name above to email me, and I'll send it. I hope they wouldn't mind - I think it comes with the WUFI Free version anyway - if it encourages people to use WUFI.
    •  
      CommentAuthordjh
    • CommentTimeNov 27th 2015 edited
     
    Posted By: gyrogearI thought that the dew point was a *temperature*, namely, that at which the humidity in the air will condense out, into "wet water..."

    You're kind of right, but so was Gotanewlife. He meant the point at which the RH reaches 100%. For a given mix of steam and air there's a corresponding temperature, but you can also just reduce the amount of steam.

    (I obviously understand the need to prevent that happening !)
    So to prevent the air temp getting that cold, I thought I would warm the CS, with incandescent lamps...
    But I find that as the temperature increases, so does the RH !

    (I am in the process of concreting the CS floor (it is just earth...)).

    What you're seeing is 'buffering'. Earth, specifically clay, is one of the best humidity buffer materials. BTW, notice that those perforated bricks need to be UNFIRED. i.e. clay, not pottery.

    I suppose that until the floor is finished, the humidity will just keep coming up, from the ground (not to say, out of my concrete...).

    Exactly, so I hope there's a good DPM under the concrete.

    I don't really like the idea of a wet crawlspace...
    ===========
    So I found this chart:

    The CS currently is at 17.8°C and the RH is 85%
    (The house is at 19.5°C and 62% RH)
    The CS dewpoint is 15°C

    Per the chart, the RH should be the orange line = 40%
    Therefore I deduce that my CS RH is far too high
    However, since the CS temp is 2°C above the dewpoint, "I should be OK, as condensation will not occur"

    My local weather is: temp 11°C, 83% RH, increasing to 97% tomorrow...

    Thanks to anybody for telling me if I am still on the rails here !

    I think you're probably on the rails, but I don't understand the chart. What is the vertical axis showing and what material(s?) is it for. Psychrometric charts are normally pretty curves, sometimes with hysteresis loops.

    Condensation in the crawlspace doesn't really matter, unless it's on wood - typically the joists. That's why insulating between and under the joists is often used.

    edit: corrected Psychrometric.
    • CommentAuthortorrent99
    • CommentTimeNov 27th 2015
     
    Basically if you take a shower the buffer will absorb it and let it out slowly. To do that it needs to have a period of otherwise low RH so it can release the moisture its trapped. If you've got a damp floor constantly pumping moisture into the air the buffer will initially slow the rise in RH, until it gets full, and then you are back to square 1.

    Theoretically if a suitable buffer existed you could put it in your bathroom instead of a ventilation fan. (But others in the house might object to an unfired brick wall full of holes taking up a good chunk of your bathroom! ;-) )


    Dew point is a temperature at which a particular concentration of moisture in air will condense out. Basically hot air can hold more water. RH tells you how "full" the air is **at a particular temperature***. If you cool the air it can hold less water, the RH goes up because the air is more "full" of water (the water hasn't increase the carrying capacity has gone down ). The dew point is when the carrying capacity has got so low that the air has to release some of the water as condensation.

    Imagine a squeezy bottle with some water in it. Cooling the bottle is like squeezing it. The more you cool/squeeze the bottle the less space there is inside. Eventually as you keep squeezing (cooling) you reach a point when there isn't enough space inside to hold the water you put in and the water overflows. This is the dew point for that amount of water.
    • CommentAuthorgyrogear
    • CommentTimeNov 27th 2015
     
    Many thanks to djh and torrent99 for those explanations !
    ===================
    "What is the vertical axis showing and what material(s?) is it for ?"

    Apologies, I must have amputated the legends without noticing:
    the L/H side is temperature in °C, and RHS is in °F.
    I "suppose" (= "just assumed...") the chart is for AIR...??
    =========================
    "What you're seeing is 'buffering'. Earth, specifically clay, is one of the best humidity buffer materials. BTW, notice that those perforated bricks need to be UNFIRED. i.e. clay, not pottery."

    Good news to hear about the CLAY for buffering...
    I did a sort-of DIY proctor test on my mud floor, and it looks like half-cay, half-sand.
    Guess this is thus LOAM.
    I have been steadily digging it out and replacing it with limecrete, so there is NO vapour barrier underneath...

    So without abusing of your time and patience and good-will, to what extent could a limecrete slab (thick) ALSO provide buffering ?

    gg
    •  
      CommentAuthordjh
    • CommentTimeNov 27th 2015
     
    According to the conservationphysics papers that we've been mentioning elsewhere, lime doesn't provide much buffering itself but it is quite vapour open so it allows vapour to see the hopefully hygroscopic buffer behind it - i.e. the soil in your case.

    Here are some links to Psychrometric charts:

    http://www.powerknot.com/how-to-read-and-use-a-psychrometric-chart.html
    https://en.wikipedia.org/wiki/Psychrometrics

    I'm not clear what the purpose of your limecrete floor is? I don't think it will reduce the humidity much if at all.
    • CommentAuthorgyrogear
    • CommentTimeNov 28th 2015 edited
     
    Thank you for the links, djh, very pertinent, I will have a lot of reading to do over the weekend !

    In particular, the notion of "relative volume" is neat and will certainly help me get a better understanding of the subject...
    ==========
    The limecrete floor started off as a simple project to stabilize the CS mud floor (which was pretty awful), using lime, raked in to the surface.

    My motivation was simply to "sanitize" the crawlspace as I did not want such a horrible zone under my house (the CS had quite obviously at some time previous been used for storing firewood (!). Removing the rotted firewood was a horrendous experience, as you might imagine. Plus bare copper pipes had been condensing into the floor for years...

    Somewhere in the process I discovered that when the infloor electric radiant was running, the CS temperature increased by 2°C. I did not like the idea of this, so got sidetracked into insulating the CS walls (100 mm of XPS).

    From there things evolved towards "conditioned crawlspace".
    However, I did not like the idea of a floor membrane, so decided on a slab.

    Basically due to lack of access, and bad logistics (impossibility of ready-mix...) & to cut a long story short, I finally ended up going for an "ad-hoc" limecrete slab, using in-situ loam.

    So as you "encouragingly" suggest, I expect the slab to "breath water", in both directions.

    When I'm finished, the CS will be conditioned with house air, which will be ejected outside.

    So that is the current status: Works in Progress... I have 4 square meters of floor complete, and the remainder (44 sq.m) in various stages of completion. A single-handed CS dig in 32-inch free height is a pretty laborious project (-:

    If there is anybody out there building CS, just have a thought for the poor owner, a few years down the line...

    gg
  3.  
    Respect and sympathy in equal measures!!!
    • CommentAuthorgyrogear
    • CommentTimeNov 28th 2015
     
    thank you !

    I sure deserve it, LOL !!

    ha ha !