Green Building Forum - Filling under floor void with EPS beads Tue, 19 Dec 2023 08:33:52 +0000 http://www.greenbuildingforum.co.uk/newforum/ Lussumo Vanilla 1.0.3 Filling under floor void with EPS beads http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=16574&Focus=280791#Comment_280791 http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=16574&Focus=280791#Comment_280791 Mon, 25 May 2020 19:58:16 +0100 Kenny_M Hope you are all keeping well. One advantage of lockdown has been the amount of work I have been getting done on the house, with my extension now finished and moving into the old part of the house.

I am about to fit a new floor in a downstairs bathroom and have been thinking about filling the underfloor void with EPS beads before I close it up, as a few threads on here have suggested. House is ~150-200 years old. Its difficult to find supplier of the beads, but found one supplier custompac who will deliver a pallet of 2265 litres for £164.88. Not sure if this is about right because I can’t find any alternatives. They don’t mention a thermal conductivity value so presume its not the graphite type, but as it will be between 300 to 500mm deep its maybe not critical.

I can see a lot of benefits from this, and the reduction in draughts probably as much of a benefit as the floor insulation, but can anyone suggest any issues/risks I should consider?

If I go ahead I presume all I need to do is protect any electrical cables, fill any large gaps where air could come in or beads go out with expanding foam, then pour the beads in.

I know that in walls this is normally mixed with a bonding agent, and have seen a suggestion of a weak pva mix on one thread. As I am pouring in from the top, would this still be necessary? I would be able to leave floor open for a while to give it a chance to settle then top up.

Any comments pro or against, much appreciated as always.]]>
Filling under floor void with EPS beads http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=16574&Focus=280793#Comment_280793 http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=16574&Focus=280793#Comment_280793 Mon, 25 May 2020 20:40:31 +0100 tony
You could consider spraying the beads in layers as they go in with weal pva say 10 to 1 every 100mm approx

The beads won’t settle much so long as no voids, stir with garden fork to help them settle

Send pics, report back after 6 months - price sounds fine did you calculate quantity needed. Shame about the lockdown or I would be there to help

👍]]>
Filling under floor void with EPS beads http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=16574&Focus=280804#Comment_280804 http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=16574&Focus=280804#Comment_280804 Tue, 26 May 2020 08:18:48 +0100 Kenny_M
When you say fill to the top, is a fill to the bottom of the joists ok? I am not sure if I could get higher than this given the limited locations I can get into to fill.

When you say report back after 6 months, what should I be looking for? If there is something I need to monitor for it might be difficult as the flooring I am not going to have non destructive access after the flooring goes down.]]>
Filling under floor void with EPS beads http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=16574&Focus=280806#Comment_280806 http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=16574&Focus=280806#Comment_280806 Tue, 26 May 2020 10:11:28 +0100 Victorianeco
I got all my beads free from a cavity wall installation company who had removed all their beads from older properties when upgrading them. Worth a look?]]>
Filling under floor void with EPS beads http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=16574&Focus=280807#Comment_280807 http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=16574&Focus=280807#Comment_280807 Tue, 26 May 2020 10:17:50 +0100 goodevans Filling under floor void with EPS beads http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=16574&Focus=280808#Comment_280808 http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=16574&Focus=280808#Comment_280808 Tue, 26 May 2020 11:30:52 +0100 tony Filling under floor void with EPS beads http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=16574&Focus=280812#Comment_280812 http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=16574&Focus=280812#Comment_280812 Tue, 26 May 2020 13:03:41 +0100 djh Posted By: Kenny_MWhen you say fill to the top, is a fill to the bottom of the joists ok? I am not sure if I could get higher than this given the limited locations I can get into to fill.
You could try blowing them into place with a leaf blower or a 'shop' vacuum on blow.]]>
Filling under floor void with EPS beads http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=16574&Focus=280814#Comment_280814 http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=16574&Focus=280814#Comment_280814 Tue, 26 May 2020 14:00:50 +0100 Mike1 Posted By: Kenny_MIts difficult to find supplier of the beads
Maybe try a local cavity wall insulation company?]]>
Filling under floor void with EPS beads http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=16574&Focus=280815#Comment_280815 http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=16574&Focus=280815#Comment_280815 Tue, 26 May 2020 14:16:48 +0100 Ian1961
You asked about risk/issues you should consider.

The main risk is that by blocking the underfloor void you increase the risk of dry rot in the floor timbers. Houses of the age of yours generally have just bare earth under the floor void which can mean humidity levels in the underfloor void that lend themselves to rot growing in timber. The cross ventilation designed into the floor void is there to prevent rot taking hold.

Ian]]>
Filling under floor void with EPS beads http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=16574&Focus=280817#Comment_280817 http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=16574&Focus=280817#Comment_280817 Tue, 26 May 2020 14:30:07 +0100 tony
Providing the house is warmer than the ground under it, true for all buildings in the uk apart from cold stores. And no flooding or plumbing leaks. Then an interesting bit of science comes into play - the partial vapour pressure of the moisture in the air in the house will be higher than the partial vapour pressure of the moisture in the air in the ground. So a downhill like process acts and moisture moves from in the house to the ground, if there is a vapour impermeable layer on the floor the joists will be drier than they have been for the last hundred years, even the wall plates will tend to dry out]]>
Filling under floor void with EPS beads http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=16574&Focus=280818#Comment_280818 http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=16574&Focus=280818#Comment_280818 Tue, 26 May 2020 14:32:51 +0100 gyrogear Posted By: Ian1961The cross-ventilation designed into the floor void is there to prevent rot taking hold.


OP does not specify what the joists are made of...

FWIW, there were vents in our crawlspace, when the entire floor-above, joists included, is concrete !

I would postulate that designer (1983) did not understand why he was doing it !
All the vents did was ''comply with the regulations" (!), cool the crawlspace, and drag heat downward out of our radiant floor !

So I blocked them up over 10 yrs ago, and had the electric radiant de-activated, and the crawlspace is now a solar hypocaust !

gg]]>
Filling under floor void with EPS beads http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=16574&Focus=280819#Comment_280819 http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=16574&Focus=280819#Comment_280819 Tue, 26 May 2020 15:04:24 +0100 Ian1961 Posted By: gyrogearI would postulate that designer (1983) did not understand why he was doing it !


Attached below is an extract of the current Part C of the Building Regs. I would imagine that they were the same or very similar back in 1983 so your designer and Local Authority BCO (no private inspectors back then!) were merely complying with the regs.]]>
Filling under floor void with EPS beads http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=16574&Focus=280820#Comment_280820 http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=16574&Focus=280820#Comment_280820 Tue, 26 May 2020 15:07:47 +0100 gyrogear
we crossed in the post, I had just added "meet the regulations (!).

However, the regulations do not explain WHY such ventilation is needed!

gg]]>
Filling under floor void with EPS beads http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=16574&Focus=280821#Comment_280821 http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=16574&Focus=280821#Comment_280821 Tue, 26 May 2020 15:33:34 +0100 Ian1961 Posted By: gyrogearHowever, the regulations do not explain WHY such ventilation is needed!

With good reason, the Building Regs Approved Docs tend to take a very cautious and risk averse approach. Most buildings in the UK are built in muddy fields by often semi-skilled labour. Part C of the regs also covers the risks from contaminated ground and volatile gases. Mitigation of ground contamination is not always what it should be and I imagine that's part of the reason for requiring ventilation of sub-floor voids - even when they are concrete and there's nothing that can rot.]]>
Filling under floor void with EPS beads http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=16574&Focus=280824#Comment_280824 http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=16574&Focus=280824#Comment_280824 Tue, 26 May 2020 18:26:25 +0100 Nick Parsons Filling under floor void with EPS beads http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=16574&Focus=280825#Comment_280825 http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=16574&Focus=280825#Comment_280825 Tue, 26 May 2020 20:10:08 +0100 Kenny_M

Posted By: Victorianeco
I got all my beads free from a cavity wall installation company who had removed all their beads from older properties when upgrading them. Worth a look?


Good call, although not sure if any are open at the moment with the lockdown.

Posted By: goodevansregular construction grade slab EPS costs in the region of £50 to £60 per cubic meter (+ vat) - and I'm sure that''ll be denser than loose beads.

I was thinking about looking into the price of EPS slab as a comparison so thanks for that. I suppose I could chuck some offcuts of EPS slab in the bottom to bulk it out a bit. In fact i'd imagine at the bottom layer small offcuts of any kind of insulation wouldn't do any harm, except for stuff that would compress or take up water of course.

Posted By: tonyI would worry about draughts getting in above the beads and making the floor cold if you don’t fill right up.

Thanks. I don't think draughts would be a problem in this case. One side is on to a solid hallway and the only external side doesn't have a vent and is a solid wall. The ventilation comes through from under the next room which is at a lower level so joist level is above floor level with respect to that room. The 4th side is on to a 1980's extension, the floor of which is not ventilated. The soil pipe goes under there but again at a lower level than the joists and this can be foamed shut. I'll try get it as high as possible but I wont be able to get access to every joist run to be sure that its fully filled everywhere.


Posted By: djhYou could try blowing them into place with a leaf blower or a 'shop' vacuum on blow.

Good call, but I don't have either! May need to improvise.


Regarding the discussions on ventilation. To clarify, its a standard period house arrangement, the joists are timber into solid stone walls, with ~1inch think floor boards. I am planning on fitting engineered wood floor on top of that now that I have removed the tiles (I'm aware that eng wood not recommended for bathroom but my wife wants it and as the bath in that room is never used its not likely to be an issue).

I'm aware that the normal arrangement is for the uf to be ventilated to ensure the timber remains dry, and have read the counter argument in other threads that as long as the joists are kept warm by the insulation below they should remain dry.

In terms of evaluating risk, what's the worst thing that could happen? I am presuming the answer to that is that water or water vapour builds up somewhere within the void. If it builds up below or in the middle of the insulation it should drain away through the soil. It could make the base of the walls a little damp, but I don't know of any reason why that would be a problem.

If it caused the joists to rot then I could end up having to lift the floor and replace the joists which is expensive and disruptive and would outweigh the benefit, but the question is, how likely is that? I suspect it is not very likely, but the biggest problem is that I won't be able to access under the floor to check this.

I have thought before about fitting sensors. If I could get inexpensive component type humidity sensors that I could screw to a few joists and run the wires to an access plate then that would be a quick job. However, I am not sure where to begin with that or whether such sensors could be read with an ohmmeter or would need a power supply or an interface etc.

Edit: re humidity sensors, I just thought that I could just hammer a few nails into the underside of the joists and solder wires on to them, then run the wires to an access point in the wall. Measure immediately after filling and check periodically for any reduction in resistance over time.]]>
Filling under floor void with EPS beads http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=16574&Focus=280827#Comment_280827 http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=16574&Focus=280827#Comment_280827 Tue, 26 May 2020 21:52:05 +0100 gyrogear Posted By: Nick ParsonsGG, are you not outwith the remit of the UK bldg. regs anyway? As to why u/fl ventilation might be required, radon is a possibility.

Nick, Yes, indeed I am, but French regulations are just about the same !

gg]]>
Filling under floor void with EPS beads http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=16574&Focus=280829#Comment_280829 http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=16574&Focus=280829#Comment_280829 Tue, 26 May 2020 23:02:33 +0100 tony Filling under floor void with EPS beads http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=16574&Focus=280840#Comment_280840 http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=16574&Focus=280840#Comment_280840 Wed, 27 May 2020 15:00:37 +0100 fostertom Posted By: tonythe partial vapour pressure of the moisture in the air in the house will be higher than the partial vapour pressure of the moisture in the air in the ground. So a downhill like process acts and moisture moves from in the house to the ground, if there is a vapour impermeable layer on the floor the joists will be drier than they have been for the last hundred years, even the wall plates will tend to dry outYep - think of the lowest soil surface (and lower parts of perimeter foundation walls) as a dehumidifier - a relatively cold condensing surface that will draw water vapour molecules to it from throughout the house, not requiring any air movement to carry it.

Relative humidity will increase in a gradient from the house interior down to that condensing surface, in proportion to the reducing temperature along that gradient; the floor joists will be pretty much at the lower RH end (higher temp end) of that gradient; will in fact become part of the house's interior environment.

The beads will greatly reduce convection and mixing of the air in the void, allowing that gradient to establish itself. Before the beads, the higher RH/lower temp would indeed have convected themselves throughout the void, affecting the joists.]]>
Filling under floor void with EPS beads http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=16574&Focus=280844#Comment_280844 http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=16574&Focus=280844#Comment_280844 Wed, 27 May 2020 15:45:53 +0100 Kenny_M
While the middle 80% of the joist will be warm, the ends will be in a very cold outside wall, probably even colder than normal due to the insulation keeping the heat in the room.

If condensation will migrate towards the coldest part, is there a risk that it will collect there?]]>
Filling under floor void with EPS beads http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=16574&Focus=280846#Comment_280846 http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=16574&Focus=280846#Comment_280846 Wed, 27 May 2020 17:19:47 +0100 fostertom Posted By: Kenny_Mthe ends will be in a very cold outside wall, probably even colder than normal due to the insulation keeping the heat in the roomThe joist ends and the wall will be just as cold without filled void, plus the draught of outside ventilation air. Can't blame the fill for that - EWI would fix it, or not having joists bearing into uninsulated wall.]]> Filling under floor void with EPS beads http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=16574&Focus=280853#Comment_280853 http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=16574&Focus=280853#Comment_280853 Wed, 27 May 2020 18:13:25 +0100 Kenny_M
Unfortunately, EWI is not possible for more than one reason, and removing and repositioning joists would be too disruptive and costly to be worthwhile. As it stands I was only supposed to be replacing the tiles with eng wood, and I just thought of the EPS fill as a relatively quick win while the boards were accessible.

Unless I am misinterpreting, it sounds like you are saying that joist ends could be the weak link here. While they might not be colder, they could be as cold, and they would be part of a thermal bridge between the wooden floor and the external wall.

I suppose the joists being cold are only an issue if moisture can reach them. I am planning on fitting a few mm of XPS underlay, so that should minimise any vapour that can reach it from inside the house. Not sure of the risk of moisture heading up through the walls to the joists as there will not be a DPC

Just trying to make sure I have thought through and understand all the implications and risks here.]]>
Filling under floor void with EPS beads http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=16574&Focus=280858#Comment_280858 http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=16574&Focus=280858#Comment_280858 Wed, 27 May 2020 21:58:08 +0100 Kenny_M
I found the name of Sophie Pelsmakers on another thread, and then found her paper comparing EPS full fill with wood fibre between joists. No surprise that EPS was better, but other main takeaway was that measured u value of the improvement was about double the modelled value.

That took me to:

Pelsmakers, S., Elwell, C.A.,(2017), Heat loss reduction potential of suspended timber ground floor insulation interventions

A number of different flavours of insulated and uninsulated floors with RH measurements from the void over four seasons. Two of the floors had full fill of EPS beads, and both exceeded the set threshold of 80% RH for significant time periods. Figure 13 for anyone who is interested, shows the RH across different seasons and locations in the void. Bottom of the void is not surprisingly the worst, near 100% at times, but probably not a major concern.

However, the other consistently high RH measurement was near the top of the joists within the beads, which is a bit more concerning. All of the measurement locations (except for the bottom) are well below 80% at certain times of the year, but some sit very high for long periods

Floor 11 and 15 are the EPS fills, and table 4 and figure 13 where I am getting the above from, link below for anyone who is interested.

https://discovery.ucl.ac.uk/id/eprint/10056175/1/Mould%20paper_review_final_accepted%20version2.pdf]]>
Filling under floor void with EPS beads http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=16574&Focus=280859#Comment_280859 http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=16574&Focus=280859#Comment_280859 Wed, 27 May 2020 22:34:55 +0100 tony Filling under floor void with EPS beads http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=16574&Focus=280861#Comment_280861 http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=16574&Focus=280861#Comment_280861 Thu, 28 May 2020 00:55:25 +0100 gyrogear
gg]]>
Filling under floor void with EPS beads http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=16574&Focus=280866#Comment_280866 http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=16574&Focus=280866#Comment_280866 Thu, 28 May 2020 11:03:56 +0100 Ian1961 Posted By: Kenny_MBeing doing a bit of research on this tonight. Thought others might be interested.

Interesting link. Thanks Kenny.
I see that one of the conclusions from the report is: 'Most insulated floors in this sample meet or exceed the critical thresholds for mould growth for significant periods' which confirms my earlier comment about the risk of mould growth.]]>
Filling under floor void with EPS beads http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=16574&Focus=280870#Comment_280870 http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=16574&Focus=280870#Comment_280870 Thu, 28 May 2020 14:14:28 +0100 Kenny_M Posted By: Ian1961Interesting link. Thanks Kenny.
I see that one of the conclusions from the report is: 'Most insulated floors in this sample meet or exceed the critical thresholds for mould growth for significant periods' which confirms my earlier comment about the risk of mould growth.

True, but its also fair to say that some of the uninsulated floors also 'meet or exceed the critical thresholds for mould growth for significant periods'.

I also took a measurement last night of the void in the space that I was planning to fill and I got a reading of 85%. This void is not properly through ventilated at the moment, with ventilation only coming in from one side, via another void, so its not impossible that filling it might reduce rather than increase the RH, but who knows. The one thing the status quo has in its favour is that there is no evidence of rot in the joists at the moment, although there has occasionally been a smell in that room which smells like damp earth to me.]]>
Filling under floor void with EPS beads http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=16574&Focus=280876#Comment_280876 http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=16574&Focus=280876#Comment_280876 Thu, 28 May 2020 15:55:56 +0100 Mike1
A big influence in my caution was seeing a room filled - covering every surface, floor to ceiling - with rampant dry rot. It was actually a ground floor room in an old bank that had been sealed up without ventilation for several years, rather than a floor void, but a graphic illustration of some of the potential risks.]]>
Filling under floor void with EPS beads http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=16574&Focus=280885#Comment_280885 http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=16574&Focus=280885#Comment_280885 Thu, 28 May 2020 22:43:50 +0100 Ian1961 Posted By: Mike1A big influence in my caution was seeing a room filled - covering every surface, floor to ceiling - with rampant dry rot. It was actually a ground floor room in an old bank that had been sealed up without ventilation for several years, rather than a floor void, but a graphic illustration of some of the potential risks.

Same here. I’m currently working on the refurbishment of a large commercial building where dry rot is rampant across the walls and ceiling of the unventilated damp basement]]>
Filling under floor void with EPS beads http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=16574&Focus=280886#Comment_280886 http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=16574&Focus=280886#Comment_280886 Thu, 28 May 2020 23:56:55 +0100 tony
It has nothing to with filling floor voids with insulation.]]>