Green Building Forum - Kitchen with only MHRV extract duct Tue, 19 Dec 2023 08:24:08 +0000 http://www.greenbuildingforum.co.uk/newforum/ Lussumo Vanilla 1.0.3 Kitchen with only MHRV extract duct http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=17180&Focus=291435#Comment_291435 http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=17180&Focus=291435#Comment_291435 Fri, 03 Sep 2021 21:49:55 +0100 wholaa Is it commonplace to have an MRHV system without any input duct? Just an extract duct? The house in particular has a small enough kitchen with low occupancy but it is in a three-story house and its MRHV is not beautiful so I wonder about pressure drop.]]> Kitchen with only MHRV extract duct http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=17180&Focus=291436#Comment_291436 http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=17180&Focus=291436#Comment_291436 Fri, 03 Sep 2021 23:56:19 +0100 Mike1 Kitchen with only MHRV extract duct http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=17180&Focus=291439#Comment_291439 http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=17180&Focus=291439#Comment_291439 Sat, 04 Sep 2021 08:09:44 +0100 Jonti Kitchen with only MHRV extract duct http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=17180&Focus=291440#Comment_291440 http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=17180&Focus=291440#Comment_291440 Sat, 04 Sep 2021 09:34:39 +0100 Ed Davies input supply ducts in other rooms (living room, bedrooms ?)?

Having only extract ducts in “wet” rooms (kitchens, bathrooms, shower rooms, WCs) and supply ducts in other rooms is the usual MHRV arrangement. A tiny amount of care is needed to ensure that there's enough airflow between the rooms even when the doors are shut - e.g., leaving a gap under the door clear of the carpet.

Alternatively you could have a house with only extract ducts feeding a heat pump which heats hot water, either for space heating or for DHW (washing, etc). Called an EASHP (extract air source heat pump).

Edit: change “input” to “supply”; had a mental block on the right word earlier.]]>
Kitchen with only MHRV extract duct http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=17180&Focus=291441#Comment_291441 http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=17180&Focus=291441#Comment_291441 Sat, 04 Sep 2021 10:58:49 +0100 djh :devil:]]> Kitchen with only MHRV extract duct http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=17180&Focus=291442#Comment_291442 http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=17180&Focus=291442#Comment_291442 Sat, 04 Sep 2021 12:09:05 +0100 Ed Davies Kitchen with only MHRV extract duct http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=17180&Focus=291445#Comment_291445 http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=17180&Focus=291445#Comment_291445 Sat, 04 Sep 2021 13:09:00 +0100 djh Kitchen with only MHRV extract duct http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=17180&Focus=291446#Comment_291446 http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=17180&Focus=291446#Comment_291446 Sat, 04 Sep 2021 13:55:31 +0100 wholaa
Thanks for the feedback, pardon the typo. Yes it is a MVHR system, Vent axia. The house has various positive outlets, such as the living room on the same floor. I have heard people suggesting that kitchens really should have a positive and a negative supply but I am just wondering is it is important. The ducting isn't great. It has a fair few sharp bends and flat channels so with the MVHR unit in the attic, I was worried if collectively these issues are combining to make a subpar installation that is over ventilating upstairs and under ventilating downstairs. So far the house is fine to live in but at the moment is is under-occupied.]]>
Kitchen with only MHRV extract duct http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=17180&Focus=291447#Comment_291447 http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=17180&Focus=291447#Comment_291447 Sat, 04 Sep 2021 15:43:37 +0100 djh Posted By: wholaaThanks for the feedback, pardon the typo. Yes it is a MVHR system, Vent axia. The house has various positive outlets, such as the living room on the same floor. I have heard people suggesting that kitchens really should have a positive and a negative supply but I am just wondering is it is important. The ducting isn't great. It has a fair few sharp bends and flat channels so with the MVHR unit in the attic, I was worried if collectively these issues are combining to make a subpar installation that is over ventilating upstairs and under ventilating downstairs. So far the house is fine to live in but at the moment is is under-occupied.
It's perfectly normal to just have an extract in the kitchen and a supply in a nearby room - dining room or living room for example. That's what we have. Sometimes there's also a supply in a different area of a kitchen, but only if the shape is unusual or the supply needs balancing for some reason.

Whoever designed the system should have calculated the flow resistance of all the ducts, taking into account such things as bends etc, to make sure the flowrates will be sensible. When the system is installed it should be balanced so that the actual flowrates match the design rates for each terminal. There's supposed to be a check list that shows the measured flow rates. It's easy enough to do the balancing - we did ours ourselves. The exact details depend on what type of duct system you have.]]>
Kitchen with only MHRV extract duct http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=17180&Focus=291602#Comment_291602 http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=17180&Focus=291602#Comment_291602 Sat, 11 Sep 2021 14:17:04 +0100 wholaa
I must get your thought on this duct (extraction) joint. Is airtightness normally ok to do joints?
https://i.ibb.co/94sHjSs/original-d2d45f7b-5bfd-4f05-894c-614609863109-20210307-223219.jpg]]>
Kitchen with only MHRV extract duct http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=17180&Focus=291608#Comment_291608 http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=17180&Focus=291608#Comment_291608 Sat, 11 Sep 2021 20:22:56 +0100 djh
But it looks like what I'm looking at is the duct above an extraction terminal that is then connecting to some type of horizontal duct and the junction is covered in some kind of sticky tape. What do I think? I don't think junctions in ventilation ducts normally need to be wrapped in sticky tape. But if there was a problem with the airtightness of a particular junction then it might be possible to seal it with an appropriate sticky tape. But whether there was a problem that couldn't be resolved in a better way and whether that is a suitable type of sticky tape I cannot say, I'm afraid.

It looks most like the points where my main intake and exhaust ducts pass through my airtightness barrier. There's a multitude of short lengths of Siga Rissan tape that seal each of the ducts to the airtightness barrier (lime plaster). And there's similar, although less impressive, around each of the main service penetrations - water, electricity and communications. So the technique can be useful, but I don't know whether this is a sensible use case.]]>
Kitchen with only MHRV extract duct http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=17180&Focus=291629#Comment_291629 http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=17180&Focus=291629#Comment_291629 Sun, 12 Sep 2021 17:35:51 +0100 wholaa Kitchen with only MHRV extract duct http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=17180&Focus=291633#Comment_291633 http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=17180&Focus=291633#Comment_291633 Sun, 12 Sep 2021 19:55:41 +0100 djh Posted By: wholaais assembling a joint like that with airtightness tape ok
As I said, I don't know what I'm looking at so I don't know what type of joint it is, let alone whether it's OK!

The tape work looks really messy to me
Tape tends to look messy. That's not the issue. Should tape have been used is the question?

It is an extract on a flat channel duct on my ground floor to the unit in the attic.
Ah we're narrowing it down, but still. What does the joint look like without the tape? Is it a proprietary system or something generic? Where can I see examples of the duct parts?

As a whole, the system is rather noisy so I am wondering is there is poor detailing causing pressure loss and a noisy system.
Something's definitely wrong then. What's the design flowrate in each of the ducts? Excessive flowrate is one common cause of noise. Another would be restrictions in the flow path, and poorly designed changes of direction.

You'll either need to get some indpendent expert take a look, or post lots and lots of detail here including specs, design drawings and photos of the reality if we're to help.]]>