Posted By: PeterWThe original build up had mineral wool in between the rafters and required an over eaves vent tray (although the spec also showed breathable membrane....) and this was designed in to stop the crown wool bunching over the eaves - this has now moved up the rafter to the ceiling height, so should the tray also move..? IS there a requirement to have 2 vent trays, or none at all given this is supposedly breather membrane...?The main purpose of the ventilation gap is to ventilate the cold loft above the flat ceiling. Using a breather membrane would allow you to avoid ventilating the rafter space in the sloping section &, if the breather membrane BBA certificate allows it, could potentially allow you to avoid ventilating the cold loft space too. The latter would likely require a continuous VCL or at least what is typically called a "well-sealed" ceiling. Doing this would increase the thickness of insulation that could be accommodated in the sloping ceiling & reduce wind washing of the mineral wool insulation in the loft.
Posted By: PeterWThe 50mm PUR under the rafters seems to add most, which goes in line with the view that its the first inch of insulation that does the most !This is because the 50mm PUR below the rafters is not bridged by timber.