Posted By: IanCDThe store is stratified, as you describe, with DHW at the top and CH lower: heating feed is about 3/5 of the height of the store, with DHW feed above that. Heating return is about 1/4 of the way up and the solar coil connections are below that. CH flow (out) doesn't have an additional mixer valve.
Posted By: Pile-o-StoneJust a point on Plate Heat Exchangers. We have one attached to our 350l heatbank for the DHW and I haven't found any problems with it ruining stratification.
Posted By: goodevansNot necessarily Peter, - the water being heated will have come from the outside mains - perhaps 11 to 20 centigrade - If the heat exchanger is efficient the top of the tank water should be cooled to nearer say 25 centigrade after it has passed through the heat exchanger then placed into the bottom of the tank.
Posted By: Peter_in_HungaryPosted By: goodevansNot necessarily Peter, - the water being heated will have come from the outside mains - perhaps 11 to 20 centigrade - If the heat exchanger is efficient the top of the tank water should be cooled to nearer say 25 centigrade after it has passed through the heat exchanger then placed into the bottom of the tank.
Except that most PHX are designed to have a 15 -20 deg drop from input to output otherwise you can't get the rated output.
Posted By: Pile-o-StoneI tried to google the temperature drop across a heat exchanger, but couldn't find anything. Do you have a link with details of the 15C to 20C drop you're quoting? If that temperature drop is accurate, then I guess the water pump attached to the heat exchanger is pumping HW through the HX more than twice as fast as the mains water is coming in. We have pretty fierce mains water pressure, but the pump is on the lowest of the three speed settings.
Posted By: Pile-o-StoneIs it not the case that to raise mains water temperature by 48 degrees, it would reduce the temperature of the feed by at least 48 degrees (with a little extra for inefficiencies)? So to use your initial example, 80C from the top of the tank would be reduced to 32 degrees when it is fed to the bottom of the tank, which would cool the 40C water that was stored there.
Posted By: Peter_in_HungaryThe temperature coming from the PHX is nothing like as cool as the mains water going in, if it was there would be very little heat transfer towards the end of the PHX. which is why the primary flow has a designed temp. of 80/60.
Posted By: Peter_in_HungaryIf in the summer when the top of the store is 80 and the bottom not heated then putting 50 deg water (assumed same 30 deg drop)
Posted By: djhThe temperature of the water being returned into the bottom of the tank is just under 30°CWell this is good news - it means that the boiler supply will always allow full condensing.
Posted By: goodevansOther than disadvantage 1 above, is there really a problem of the bottom of the tank being warm providing it is cool enough to allow the boiler to reach full condensing mode. Not perfect stratification but good enough.
Posted By: djhI don't know. My system is fully electric and I try to get the whole tank as hot as possible when the energy is free.
Posted By: goodevans
With a stores with eternal plate exchangers like the Gledhill I see the following disadvantages.
1) The bottom of the store may not be the coolest - therefore some extra, useless, heat loss from the tank in the summer months (but cost of that loss vastly reduced if solar pv used).
2) a complicated system means more parts to fail. But the tank itself is therefore very simple and all the other bits sit outside the tank and can be replaced.