Posted By: lineweightSomething I'm a bit unclear about: with cool air inside, and warm air outside, is an MVHR system able to operate in "reverse" such that the hot air is kept outside and the cool air inside?
Posted By: djhPosted By: lineweightSomething I'm a bit unclear about: with cool air inside, and warm air outside, is an MVHR system able to operate in "reverse" such that the hot air is kept outside and the cool air inside?
Yes. If the external temperature is greater than the internal temperature then the summer bypass closes (or stays closed). So the heat exchanger is in circuit and incoming warm air is cooled to (almost) the same temperature as that inside before being circulated. So the best behaviour is to close all the windows, and blinds if you have them, and wait for cooler air in the evening.
FWIW, our bypass opened again today.
Posted By: lineweight4. Uncomfortably cold inside / warmer outside -> open bypass
Can't think when no. 4 would ever happen though.
Posted By: djhPosted By: lineweight4. Uncomfortably cold inside / warmer outside -> open bypass
Can't think when no. 4 would ever happen though.
Number 4 isn't a condition that opens the bypass on my MVHR, nor on most others I suspect. As you surmise, it's not a condiition that's ever occurred, AFAIK. Opening windows would be the obvious thing to do, much as in the reverse situation to get greater cooling.
edit: Actually, the condition for #3 is simpler. Whatever the temperature inside is, if it's warmer outside then keep the heat exchanger in circuit.
Posted By: lineweightHave got it now, I guess there are 4 possible scenarios
1. Comfortable temp inside / colder outside -> heat exchanger works to keep heat in
2. Uncomfortably warm inside / colder outside -> open bypass
3. Comfortable temp inside / warmer outside -> heat exchanger works to keep heat out
4. Uncomfortably cold inside / warmer outside -> open bypass
Can't think when no. 4 would ever happen though.
Posted By: Peter_in_HungaryPosted By: lineweightHave got it now, I guess there are 4 possible scenarios
1. Comfortable temp inside / colder outside -> heat exchanger works to keep heat in
2. Uncomfortably warm inside / colder outside -> open bypass
3. Comfortable temp inside / warmer outside -> heat exchanger works to keep heat out
4. Uncomfortably cold inside / warmer outside -> open bypass
Can't think when no. 4 would ever happen though.
No. 4 happens to our house, we have 50cm stone walls and EWI, quite often this time of year e.g. yesterday ! it was 17deg inside and 24 deg outside. (Daytime temp). So we open the windows. The heating has been off for sometime now!
Posted By: djhI was musing earlier - there's a range of external conditions (and probably sequences of conditions) over which my house is comfortable without active heating or cooling. I expect the same is true for all (most?) houses but that the external temperatures for which it is true varies from house to house. It occurred to me that maybe the range is an interesting number, i.e. the difference between the upper and lower external temperatures for which the house is comfortable (or to spec or something). Is the range a figure of merit for the design, perhaps?
As to where the comfortable range is within the full range of external temperatures, I suppose that as long as the house gets a bit cool at the lower end of the range and a bit warm at the upper end of the range, it doesn't matter too much?
Sorry if this is OT for the thread.
Posted By: lineweightPosted By: Peter_in_HungaryPosted By: lineweightHave got it now, I guess there are 4 possible scenarios
1. Comfortable temp inside / colder outside -> heat exchanger works to keep heat in
2. Uncomfortably warm inside / colder outside -> open bypass
3. Comfortable temp inside / warmer outside -> heat exchanger works to keep heat out
4. Uncomfortably cold inside / warmer outside -> open bypass
Can't think when no. 4 would ever happen though.
No. 4 happens to our house, we have 50cm stone walls and EWI, quite often this time of year e.g. yesterday ! it was 17deg inside and 24 deg outside. (Daytime temp). So we open the windows. The heating has been off for sometime now!
How long into summer does your "coolth" store last?
There must be a bit of a judgement call about whether you want to start throwing it away now, because presumably that means that the effect will not last as long into the "uncomfortably hot outside" portion of summer as it would otherwise.
Posted By: richardelliotDoes the Vent Axia know to shut the bypass when it is cooler inside than outside?