Posted By: WillInAberdeenSeems odd, as quarter of a tonne of scalding water in an DHW cylinder above the stairs, would seem to be as hazardous as quarter of a tonne of scalding water in a thermal store, location and pressure being equal...?
Posted By: djhwhy would anybody have a pressurised thermal store?Aren't CH systems typically sealed and wouldn't you normally run the radiators directly off the water in the thermal store (without a heat exchanger)? So couldn't it become very pressurised in a failure situation?
Posted By: WillInAberdeenThere are requirements in building regs for vented DHW systems, such as : 19mm vent pipe, non- resettable thermal cutout, overflow, supports, accessibility, etc. But I can't see where the equivalent is written for a vented thermal store or CH system.
Posted By: Ed DaviesAren't CH systems typically sealed and wouldn't you normally run the radiators directly off the water in the thermal store (without a heat exchanger)? So couldn't it become very pressurised in a failure situation?
Posted By: WillInAberdeenNo, those requirements are specifically for "heated wholesome water" only, not central heating.
Posted By: djhPosted By: WillInAberdeenNo, those requirements are specifically for "heated wholesome water" only, not central heating.
"Hot water storage system means a vessel for storing:
"a. heated wholesome hot water or softened
wholesome hot water for subsequent use
"b. water that is used to heat other water
"together with any ancillary safety devices
described in paragraphs 3.10 and 3.11 of this
Approved Document and all other applicable
operating devices."
Posted By: WillInAberdeen
Building Stds/regs apply when constructing or modifying, so can't impose requirements for maintenance.
Posted By: CharentemanThese plates are very expensive - c £4.50/lm for two pipe section - am I being realistic in thinking this will work effectively?
Posted By: Charentemanif it were a DWH cylinder it would have to be pressurised (with expansion vessel) to deliver hot water to the upper floors (no loft space for header tank)
Posted By: Charenteman...and have an indirect solar coil?
Posted By: CharentemanIs there any consensus as to whether TS or DWH is better?
Posted By: CharentemanTS/DHW heated by Solar Thermal panels and/or immersion heaters and/or AHP when not called for heat as priority?
How to control the AHP (when not called for UFH) so that it is not competing against free solar?
Posted By: CharentemanI have to say that given the floor constraints, I am becoming very uncertain about the suitability of an AHP for our heating - capital and running costs and most importantly whether it will keep us comfortably warm in a sub zero French winter!