Home  5  Books  5  GBEzine  5  News  5  HelpDesk  5  Register  5  GreenBuilding.co.uk
Not signed in (Sign In)

Categories



Green Building Bible, Fourth Edition
Green Building Bible, fourth edition (both books)
These two books are the perfect starting place to help you get to grips with one of the most vitally important aspects of our society - our homes and living environment.

PLEASE NOTE: A download link for Volume 1 will be sent to you by email and Volume 2 will be sent to you by post as a book.

Buy individually or both books together. Delivery is free!


powered by Surfing Waves




Vanilla 1.0.3 is a product of Lussumo. More Information: Documentation, Community Support.

Welcome to new Forum Visitors
Join the forum now and benefit from discussions with thousands of other green building fans and discounts on Green Building Press publications: Apply now.




    • CommentAuthorGarethC
    • CommentTimeFeb 28th 2016
     
    Apologies if covered elsewhere and/or stupid, but can anyone tell me:

    1. How good are high performing thermal stores/cylinders these days in terms of heat loss?

    2. What are the absolute best performing ones in this regard, and how well do they do?

    4. I may be wrong here, but am I right that you can't insulate around where the heating element enters, presumably since it's a fire hazard? Surely that hazard can be designed out...

    3. Why are cylinders, well, cylindrical? Box shaped would be more space efficient and easier to install. Is it just due to ease of manufacture, or is it due to in-use performance considerations?

    Thank you!
    •  
      CommentAuthorSteamyTea
    • CommentTimeFeb 28th 2016 edited
     
    They don't perform as well as expected/documented. More to do with the testing regime though.
    You can work out the performance pretty well from first principles. Just treat it as a wall with a known U-Value.
    They are cylindrical for 3 main reasons.
    Low surface area to volume ratio.
    They take pressure better (hoop stresses).
    They are cheaper to make.
  1.  
    Ref 4 - assuming you mean electric element, then there is a limitation on the current carrying cable but you can insulate as much as you want aside from, say, a toilet roll dia gap where the element/cable with losses from this hole being microscopic as a % of the whole. I put double insulation over top half, rather than same thickness insulation over whole cylinder.
    • CommentAuthorGarethC
    • CommentTimeFeb 29th 2016
     
    Thanks both. I'll do some working. I'm finding it strangely difficult to find good stats on DHW cylinders. E.g. what's the average amount and quality of insulation a new one arrives with.

    They appear to be obvious weak points in the efficiency of home heating systems. I know that you can retrofit extra insulation easily, but it feels like (I may be wrong) the standard of insulation of new 'off the shelf' cylinders isn't that great. Strange, because adding an extra 50-100mm of PUR shouldn't be expensive, and would make a real difference.

    As I say, I may be completely wrong. Struggling to find good statistics on 'average' performance. And I'd love to know what the best performing ones manage, but can't find much on that either.
    • CommentAuthorDarylP
    • CommentTimeFeb 29th 2016
     
    Look for standing heat losses - kW(h) / 24h ratings are applied to all 'new' HWCs.
    1.67 is about average for 250litres .
    Cheers :smile:
    • CommentAuthorEd Davies
    • CommentTimeFeb 29th 2016
     
    Posted By: GarethCStrange, because adding an extra 50-100mm of PUR shouldn't be expensive,
    I wonder how much that's is down to practicality of transport, fitting through doors, etc, rather than cost of materials and application.
    • CommentAuthorringi
    • CommentTimeFeb 29th 2016
     
    Just having pipework pre-installed that goes from the top of the tank, to exit the insulator lower down, could help cut heat lose.
    •  
      CommentAuthordjh
    • CommentTimeFeb 29th 2016
     
    Posted By: ringiJust having pipework pre-installed that goes from the top of the tank, to exit the insulator lower down, could help cut heat lose.

    Problem is where it goes after that. Since every installation is different, wherever you choose to bring the outlet is likely to be wrong, plus you somehow have to arrange to remove air from the loop and be able to drain it, So I suspect that putting the outlet in its natural place and then taking care with the external plumbing and insulation design is a better strategy. Plus open-vented tanks need it to go upwards anyway.
    • CommentAuthorgravelld
    • CommentTimeFeb 29th 2016 edited
     
    Posted By: DarylPLook for standing heat losses - kW(h) / 24h ratings are applied to all 'new' HWCs.
    1.67 is about average for 250litres .
    Cheershttp:///newforum/extensions/Vanillacons/smilies/standard/smile.gif" alt=":smile:" title=":smile:" >
    It's the average measurement. Doesn't mean it's how much you'll lose, because the measuring approaching is distinctly unrepresentative (AIUI, very little pipework allowed for, and one heating period before left for 24 hours).

    OP, have you looked at PCM stores? Their smaller size makes higher performance insulation possible. For example vacuum panels. Reading about it seems it cuts the heat loss by as much as a quarter but this really is an area where YMMV.
    • CommentAuthorEd Davies
    • CommentTimeFeb 29th 2016 edited
     
    What do the loss ratings for cylinders assume for the pipework? Ignore it? Assume copper lagged to the same thickness as the cylinder? … ?

    Using stainless for the first 300 mm or so would help a lot, I think. About 20 times less thermally conductive than copper.

    [ Cross-posted with gravelld: another advantage of PCMs is they can store more heat at a lower (fixed) temperature. ]
    • CommentAuthorringi
    • CommentTimeFeb 29th 2016
     
    Posted By: djh
    Posted By: ringiJust having pipework pre-installed that goes from the top of the tank, to exit the insulator lower down, could help cut heat lose.

    Problem is where it goes after that. Since every installation is different, wherever you choose to bring the outlet is likely to be wrong, plus you somehow have to arrange to remove air from the loop and be able to drain it, So I suspect that putting the outlet in its natural place and then taking care with the external plumbing and insulation design is a better strategy. Plus open-vented tanks need it to go upwards anyway.


    The benefit is that there is a LOT of heat lose from the top of a tank where the pipes connect as it is hard to insulation and hot water rises, then cools in the pipe and flows back into the tank.

    I agree that removing air is an issue if the tank is not mains pressure.
    •  
      CommentAuthordjh
    • CommentTimeFeb 29th 2016
     
    Posted By: ringithere is a LOT of heat lose from the top of a tank where the pipes connect as it is hard to insulation

    Yes, what I mean is that I think producing some better technique or products for doing this type of insulation would be more beneficial. It's obviously possible to use expanding foam in place once the plumbing's done but that can easily be or look messy. Something better might make a significant difference.
    •  
      CommentAuthorSteamyTea
    • CommentTimeFeb 29th 2016 edited
     
    Over at the 'other place' we discussed heat losses from HW cylinders quite a bit. There is a testing regime (not that I have looked at it in detail), but I think it involves heating the water up, taking it out fairly quickly and then looking at the total heat loss over 24 hours i.e. at a lower mean temperature. Not really how they are used in real life.
    My losses where around 4 kWh/day, but with some tinkering with recharge timing, more insulation, lower temperatures, I have this down to about 1.5-2 kWh/day.
    •  
      CommentAuthordjh
    • CommentTimeFeb 29th 2016
     
    Posted By: SteamyTealower temperatures

    That depends on heat source. With a PV-powered tank, it makes sense to try to get it as hot as possible, regardless of losses, because that maximises the length of dull period you can outlast. Of course, that kind of strategy also means you need to determine a long term average to get any meaningful numbers.
    •  
      CommentAuthorSteamyTea
    • CommentTimeFeb 29th 2016
     
    Also depends on what else you could have used the PV for. Maybe charging a car, or cooking some food.

    PV does not work very well on averages, unless your exporting it to a semi-infinite demand (like the grid).
    Why being off grid is so hard.
    • CommentAuthorgyrogear
    • CommentTimeFeb 29th 2016 edited
     
    Posted By: GarethCthe standard of insulation of new 'off the shelf' cylinders isn't that great.


    I agree - my one seems to be heating the basement cellar in which it is installed...

    My electrician says that this is not a problem, "as it is in any event warming the house".
    In effect, since our fresh air intake is in this room, I suppose that the water tank is preheating our inside air also.

    I have made some attempts at calculating the heat-loss:
    The tank is 250 liters and 3000 watts. Generally runs on off-peak hours only (= 8 hrs/day, of which six overnight and two at mid-day).

    Townwater temperature = 10.5°C
    No thermostat on the tank, just a mixing valve (set for “HOT”): HW temp = 50°+ (guessing at 52°C)
    Therefore TD = (52)-(10) = 42K
    fully charged tank holds:
    250 x 42 = 10,500 kcal
    x 1.163 = 12,211 watts

    I only fully charge the HWC fully for 3 days at the weekend – in the week, I charge it in mid-day off-peak only = 2 hours. So it generally consumes 6 kWh per day, in the week, as verified by meter reading.

    Our (estimated) HW usage is 2 showers per day + various washing/rinsing – total estimated usage = (2 x 50) + (5x5) = total 125 litres. = one-half of the tank.

    Estimated electrical consumption for warming one-half of the tank = 6100 watts, which tallies more or less with the meter reading… Q.E.D.

    (I did the estimates without any fiddling of the numbers – honest…):bigsmile:

    So contrary to expectations and on the face of it, if the numbers are right, we do not appear to be losing much heat out of the tank at all…

    However, we must be losing *SOME* heat, because the rest of the basement is between 16.1°C and 17.3°C, whereas the cellar where the tank is, is at 18.6°C.

    Some of this heat might be due to lighting = 4 ft fluorescent tube (? 30 W), which is generally left ON.
    (not a good idea, I know…).
    =====================
    I tried running online calculator at http://www.chromalox.com/resource-center/calculators/comfort-heater.aspx to determine the cellar heat-loss: it came up with 680 watts which sounds like A LOT to me (our bedroom gave 560 watts, and it is twice the size) plus has a 1 sq.m window…). (we do not have any heating in the bedroom) (just ourselves :cool:).

    The cellar is totally buried, 9 ft square x 7.5 ft high = 600 cft; no windows, bare cement floor; outside wall lined with insulated gypsum board. Backwall (= blockwork) insulated idem; other two walls = 3-inch hollow brick. Ceiling uninsulated.

    Given that the air is changed continually due to the fresh-air intake, the numbers -- contrary to expectations again -- might in fact be right: because of the cold air draught, the cellar requires 680 watts of heat: the fluo tube probably delivers about 10 watts of useful heat (?), meaning that 660 watts are being delivered by the hot-water cylinder - seems like a lot: it means a loss-rate of 660 watts, out of an average daily input of 6 kW.

    OK, the top half of the HWC will be generally HOT and account for 6 kW, and the bottom half will be "generally cool" so account for ? 500 watts ?

    all enlightenment welcome

    gg

    (contrary to appearances, this is an attempt to contribute to the debate...) :shamed:

    er...Added factor, just realized: in the simulator, I set the design temps as "12°C external, 20°C internal" TD = 8°C.

    So the 680 watts heat requirement is to get the cellar to 20°C, and we are NOT at 20°C, only at 18.6.
    Can't decide (at such a late hour...) what this means !! eek
    • CommentAuthorEd Davies
    • CommentTimeFeb 29th 2016 edited
     
    Posted By: gyrogear250 x 42 = 10,500 kcal
    x 1.163 = 12,211 watts
    watt·hours.

    Estimated electrical consumption for warming one-half of the tank = 6100 watts
    I think you mean 6100 watt·hours/day (which would be just over 254 W) but I'm not sure.

    …it means a loss-rate of 660 watts, out of an average daily input of 6 kW.
    6 kWh daily (= 250 W) vs 660 W continuous. Not really comparable.

    All very confusing.
    • CommentAuthorgyrogear
    • CommentTimeFeb 29th 2016
     
    Posted By: Ed DaviesAll very confusing.


    hmm - feared it might be !

    gg
    •  
      CommentAuthordjh
    • CommentTimeMar 1st 2016
     
    Posted By: SteamyTeaAlso depends on what else you could have used the PV for.

    Don't think so. Limiting the available PV will necessarily change the achievable temperatures, but it doesn't change the strategy for heating the tank from PV, I think. Get it as hot as possible, regardless of losses.
    • CommentAuthorringi
    • CommentTimeMar 1st 2016
     
    Ideally you want to heat the DWH tank top to bottom up to about 50c, then heat the complete tank as hot as possible. That way you get usable DWH even if you can't heat the complete tank.
    •  
      CommentAuthordjh
    • CommentTimeMar 1st 2016
     
    Posted By: ringiIdeally you want to heat the DWH tank top to bottom up to about 50c, then heat the complete tank as hot as possible. That way you get usable DWH even if you can't heat the complete tank.

    If the top of the tank is hotter than 50°C then it will be used more slowly so I'm not sure that heating the entire tank is necessary or even a good idea? Heating top down is definitely a good idea, though, and fortunately that tends to happen with most systems.
    • CommentAuthorringi
    • CommentTimeMar 1st 2016
     
    Heat lose increases with dT, so it may be better to have a lots of water stored at 60c, then less water stored at 85c.
    •  
      CommentAuthordjh
    • CommentTimeMar 1st 2016
     
    Posted By: ringiHeat lose increases with dT, so it may be better to have a lots of water stored at 60c, then less water stored at 85c.

    Heat loss also increases with area, so it may be better to have a smaller volume of hot water? I can't be bothered to work it out because (a) the heat tends to rise anyway and (b) I suspect the results are going to depend a lot more on how the water is discharged.

    My basic point is that with a PV-powered tank, it's better to keep on putting in as much energy as you can spare in order to allow you to 'survive' a longer dull period rather than worry about limiting the temperature to minimise standing losses. It's a different strategy to that appropriate with a reliable source like E7, for example.
    • CommentAuthorGarethC
    • CommentTimeMar 1st 2016 edited
     
    Are my maths wrong here?

    A 200l (0.2 cubic metre) volume rectangular tank of dimensions 0.36mx0.36mx1.5m has surface area of 2.48 square metres.

    Assume hot water at 45 degrees, and room temperature of 18 degrees, so 27 degree delta.

    Assume 100mm of foil faced PUR insulation giving a u-value of 0.235W/m2K (so ignore thermal resistance of tank walls, and don't account for 'piercings' yet).

    So heat loss is 0.235x2.48x27=16W

    So 24 hour heat loss is about 24x16=378Wh, 0.4kWh

    Too low surely, what am I doing wrong?
    •  
      CommentAuthordjh
    • CommentTimeMar 1st 2016
     
    Posted By: GarethCToo low surely, what am I doing wrong?

    Temperature is usually hotter than that, insulation is normally thinner than that and the associated plumbing accounts for a lot of the losses. Oh and you need to take the external dimensions of the insulation rather than the tank for calculation to get a conservative number.
    • CommentAuthorEd Davies
    • CommentTimeMar 1st 2016 edited
     
    45 °C is probably a bit low. The lowest usable is really around 38 °C (shower temperature). With a thermostatic mixer you'd need a few more degrees as they generally let a bit of cold through whatever. Then to store a useful amount of heat you need more degrees still.

    Also, “piercings” are, I understand, a significant part of the losses.

    [Huh, cross-posted with DJH. Perhaps using the middle of the insulation for the area calculation would be a good approximation.]
    • CommentAuthorgravelld
    • CommentTimeMar 1st 2016
     
    'Piercings'? You mean the pipes in/out?
    •  
      CommentAuthordjh
    • CommentTimeMar 1st 2016 edited
     
    Posted By: gravelld'Piercings'? You mean the pipes in/out?

    yes - and sensor ports etc.
    • CommentAuthorPaul_B
    • CommentTimeMar 2nd 2016
     
    I have a Akvaterm 750L Solar Plus thermal store. It has 100mm of insulation and a baffle plate to aid stratification. The manufacture states heat loss of 91W. I have temperature sensors at four levels feeding into a home automation system. The stratification works well and the top stays at a fairly constant between 60 and 52 degrees the bottom varies over a wider range going as low as 35 degrees. It can supply two showers simultaneously and a third straight after without any discernable temperature loss and water at mains pressure. The space heating needs a bit more work on the controls but this is on hold until the solar panels are commissioned.

    Paul
    •  
      CommentAuthordjh
    • CommentTimeMar 2nd 2016
     
    Posted By: Paul_BI have temperature sensors at four levels

    I'm trying to decide where to put my sensors. Are there any particular places on the tank you would recommend? Do you think four is the right number, or doesn't it matter?
   