Home  5  Books  5  GBEzine  5  News  5  HelpDesk  5  Register  5  GreenBuilding.co.uk
Not signed in (Sign In)

Categories



Green Building Bible, Fourth Edition
Green Building Bible, fourth edition (both books)
These two books are the perfect starting place to help you get to grips with one of the most vitally important aspects of our society - our homes and living environment.

PLEASE NOTE: A download link for Volume 1 will be sent to you by email and Volume 2 will be sent to you by post as a book.

Buy individually or both books together. Delivery is free!


powered by Surfing Waves




Vanilla 1.0.3 is a product of Lussumo. More Information: Documentation, Community Support.

Welcome to new Forum Visitors
Join the forum now and benefit from discussions with thousands of other green building fans and discounts on Green Building Press publications: Apply now.




    • CommentAuthordebbiel
    • CommentTimeJan 12th 2016
     
    Hello,
    I'm building a timber frame house 140mm studwork braced externally by 9mm OSB board, breather membrane, battens and horizontal larch cladding.
    I'd welcome advice/opinions on insulation for the external walls.
    I'd like to use 140mm sheep wool in the studwork, which I have been told is good in timber frame because of being able to absorb moisture. However, I don't think this is enough to get through Building Regs so I'm considering adding to the inside to improve performance and eliminate thermal bridging, but keep getting different advice.
    Here's what I'm considering:
    a) 25mm kingspan type rigid insulation - seems to give good performance, but would adding a layer of this detract from the benefits of the sheepswool?
    b) 50mm more sheepswool with horizontal cross battens. We like the idea of sticking with sheepswool, but this loses the most space, and still would give an amount of thermal bridging where the battens cross the studwork.
    c) Steicotherm rigid boards. Seems to my limited knowledge to complement the properties of the sheepswool, but performance doesn't seem to be as good as Kingspan, so probably have to use 40mm instead of 20mm boards.
    Does anyone have any comments to help please?
    Also, I was going to do insulation, then polythene vcl, then plasterboard. Someone has suggested using sheepswool in the studwork, then vcl, then steicotherm then plasterboard, so that fixings (sockets etc) are less likely to puncture the vcl. Does that seem sensible? Also to improve the vpl by using a product called Intello, so moisture can be redirected.
    Thanks in advance for any help, I seem to be going round in circles with this one!
    • CommentAuthorcjard
    • CommentTimeJan 12th 2016
     
    A) no, but there shouldn't really be much in the way of moisture in the wall so you don't need its breathing properties
    B) don't worry about that level of thermal bridging; you don't seem to be building a passivhaus and wood is effective enough as an insulator
    C) few things are as good as kingspan in terms of bang for buck


    On mine, I did kingspan between studs, kingspan over studs, then osb internally, then a reflective vcl, then battens, then plasterboard. The reflective vcl needs a cavity to work. The osb gives something to screw battens to, or socket boxes etc..

    Consider warmcel in etween the studs.. You fit the over insulation, then they come and drill a hole in it and blow the pocket full of fluff.

    As noted earlier you're looking to construct a wall that has a vapour impermeable membrane on the inner, because human activity generates moisture and a breathable membrane on the outer so any moisture in the wall can make its way out. Intello is a vapour barrier but a little more sophisticated than polythene. It's resistance to the passing of vapour changes according to temperature which is intended to help walls dry out and stay that way. You don't install it in addition to any other vcl
    • CommentAuthorDarylP
    • CommentTimeJan 13th 2016 edited
     
    debbiel,

    Even tho' we are in Wales, and I would love to say to use sheep's wool, DON'T!

    As above, PIR is your best insulant in terms of cost/thickness/performance.
    Fill the studs with 140mm PIR, (snug fit/foamed in place) then consider minimum 50mm PIR on the o/s of the 9mm sheathing, vcl on the inside of the 140mm studs, and if you need it, battened service cavity.
    Part L sorted, good air-tightness will pay dividends in the future.

    Good luck:smile:
    • CommentAuthortony
    • CommentTimeJan 13th 2016
     
    I would insulate on the outside of the studs

    Beware of thinking that wood is a sufficiently good insulator, it is not. Worse case is condensation forming at the coldest places (on top of the dpc and soaking into the plate)

    I would go mineral insulation between studs, vapour barrier, 50 or 75 EPS on the outside with your battens over breather layer

    Pir is tricky to get perfect and expensive real wool is organic and probe to decay and mega expensive too.
    • CommentAuthorgravelld
    • CommentTimeJan 13th 2016
     
    Is thickness important? If not I would've thought EPS would give best bang for buck.
    • CommentAuthorcjard
    • CommentTimeJan 13th 2016
     
    grav, it is for sure, if you can afford the thickness. That said, most of my kingspan was seconds and around half the price of EPS so it was a no brainer for me
    •  
      CommentAuthordjh
    • CommentTimeJan 13th 2016
     
    Like Tony, I would suggest putting insulation on the outside of the frame rather than the inside. I would also suggest using a regular TF rather than a deep one. You could use rigid insulation on the outside of the timber frame and either rigid or cellulose between the studs. Either EPS or PIR depending whether you have the space for EPS. Or you could build a frame with Larsen trusses on the outside and fill the whole space with cellulose.

    If you have the insulation outside the timber frame, then the frame never gets cold enough for condensation or rot to occur, so the VCL is less important (some say not necessary).
    • CommentAuthorringi
    • CommentTimeJan 13th 2016
     
    Cutting EPS or PIR to fit between the studs will take a long longer then you think! Get the frame maker to fit it, or use something that is quicker to fit.

    Fiting PIR/EPS on the outside of a frame is a lot quicker, as there are few cuts to make.

    Personally I would not want PIR on the outside if EPS was an option due to beathablity.
    •  
      CommentAuthordjh
    • CommentTimeJan 13th 2016
     
    As long as you have enough insulation on the outside to keep all the structure above dewpoint, breathability isn't an issue. I would always prefer EPS personally, but if there isn't space then PIR may be a necessity although I would then think carefully about fire risk. I also personally prefer something conformal like cellulose or mineral wool or even sheeps wool in between studs, but others have said that fitting rigid insulation is practicable if done right.
    • CommentAuthorringi
    • CommentTimeJan 13th 2016
     
    Its not just the dewpoint, sooner or later all buildings get a leak....
    • CommentAuthorTriassic
    • CommentTimeJan 13th 2016 edited
     
    Having recently fitted PIR between stud work, I can confirm it takes an age to measure, cut and fit and is very messy stuff to cut, dust ever here! Any gaps then have to be filled with expanding foam.

    Next time I'm going for high density mineral wool or cellulose between the 140mm studs and PIR boards on the outside of the studs, so as to eliminate cold bridging. Just need to sort out which gives the best u value?
    • CommentAuthorPaulJ
    • CommentTimeJan 13th 2016
     
    Don't try to fit 140mm rigid insulation as it will be a pain to plasterboard. Simplest is 120mm Celotex FR5000 (fire resistant and good insulator) between studs with gaps filled with expanding foam, then 100mm foil tape to seal over studs and onto boards and 50mm over gaps gaps where boards meet.

    Nail or screw a 25mm x 50mm batten over the studs to make a service cavity / low e gap. Finish with Habito plasterboard for extra strength / fixing etc.

    U = 0.23, price and hassle = low, performance = good.
    • CommentAuthorPaulJ
    • CommentTimeJan 13th 2016
     
    Oh, and consider a passive slab for this build type.
    •  
      CommentAuthordjh
    • CommentTimeJan 13th 2016
     
    Posted By: ringiIts not just the dewpoint, sooner or later all buildings get a leak....

    It doesn't matter. Breathability is about water vapour not liquid water. And water vapour doesn't matter as long as the temperature is warm enough that RH is below 80% or so. Drainage is a separate matter.
    • CommentAuthordebbiel
    • CommentTimeJan 13th 2016
     
    Thanks for all your comments. Unfortunately I can't insulate on the outside of the frame as I've already done the cladding. Duh, the things you learn on your first build! So back to internal solutions. Must say I am surprised at the lack of enthusiasm for sheepswool - it's making me reconsider. My reasons for choosing it was because supporting British farmers (if you choose the right brand), the moisture absorbing properties, fire safety and the fact that it's supposed to create a healthy, non toxic environment. But maybe I've just been persuaded by the hype?!
    • CommentAuthorShft
    • CommentTimeJan 13th 2016 edited
     
    There are a few recommendations for a lesser amount of PIR sheathing externally than between, in this thread - I was told this was not allowable unless the external PIR depth was greater than the fill depth: which is correct?

    I (long time lurker who came to the forum after I started my self build - Scotland) have 12.5mm PB > 19mm SV > 50mm PIR sheathing > VCL > 150mm PIR kit fill, foamed (148mm PIR in 146mm kit, compressed by the 19mm battens over the 50mm PIR) > 9mm OSB > BM > Cavity > rendered concrete block.
    •  
      CommentAuthordjh
    • CommentTimeJan 14th 2016
     
    Posted By: debbielMust say I am surprised at the lack of enthusiasm for sheepswool - it's making me reconsider. My reasons for choosing it was because supporting British farmers (if you choose the right brand), the moisture absorbing properties, fire safety and the fact that it's supposed to create a healthy, non toxic environment.

    Your reasons are all valid but are very similar to the reasons for using cellulose (recycled newspapers), which to my mind is an equally virtuous but more predictable and less expensive alternative. There's a big difference between the price of raw fleeces and the price of wool insulation that makes me worry.

    The problem with internal insulation is that it pushes down the temperature of everything and especially the wooden structure outboard of it, meaning they're more likely to get into troublesome humidity regimes, so careful design is definitely needed. That said, my preference would definitely be for a hygroscopic insulation in such circumstances - wool, cellulose, wood fibre, straw etc.

    It might be worth talking to one or more of the firms who specialize in these types of insulation to get a recommended and warranted design.
    • CommentAuthorDarylP
    • CommentTimeJan 19th 2016
     
    debbiel,
    Sorry, Buckinghamshire is a bit far from us..... :cry:
    However if you need any email support, feel free to ask.

    Good luck, Daryl:smile:
    • CommentAuthorthe souter
    • CommentTimeJan 19th 2016
     
    Hi Debbiel,
    Is there not an architect involved who can run dew point calcs? Unclear why the buildup has emerged as a problem at this stage in the Warranted work? There is a lot of empirical knowledge on this site, a lot of wisdom. Be wary, though, of stepping in to building physics relying on hearsay...

    The steico (universal board) comes in at either 35mm or 50mm and would maintain breathability. We have had transportation damage with this product, so talk this through with your supplier beforehand- ie if tongues/ grooves are snapped or dinged you will not accept them. If in good nic, you can line out a room rapidly with it.
    djh speaks sense