Green Building Forum - Fire escape from a mediaeval cellar Tue, 19 Dec 2023 04:41:48 +0000 http://www.greenbuildingforum.co.uk/newforum/ Lussumo Vanilla 1.0.3 Fire escape from a mediaeval cellar http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=15744&Focus=268608#Comment_268608 http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=15744&Focus=268608#Comment_268608 Thu, 24 May 2018 20:46:36 +0100 jemhayward
Are there any rights of appeal, or ways around this or are we just completely stuffed!

If we proceed without getting building regs done, what would happen to us?]]>
Fire escape from a mediaeval cellar http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=15744&Focus=268611#Comment_268611 http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=15744&Focus=268611#Comment_268611 Fri, 25 May 2018 00:33:35 +0100 goodevans Posted By: jemhaywardIf we proceed without getting building regs done, what would happen to us? As a minimum selling would be difficult the house would not be mortgageable.

Is the cellar going to be a habitable room i.e. a kitchen /study / living room etc - if not (i.e. being used as a store room / cellar / workroom / utility) then fire regs may not apply (no heating in the cellar may help define this). I am putting a storeroom above my garage - it will have a staircase - the garage is detached and will need building regs (2 floors) but no fire escape is required because it will be for occasional use - in effect it will be used as a detached loft with a permanent staircase.

As usual a quick plan of the proposed 3 floors would help.]]>
Fire escape from a mediaeval cellar http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=15744&Focus=268640#Comment_268640 http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=15744&Focus=268640#Comment_268640 Fri, 25 May 2018 16:02:59 +0100 jemhayward
I'll try to post some plans here over the weekend.]]>
Fire escape from a mediaeval cellar http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=15744&Focus=268649#Comment_268649 http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=15744&Focus=268649#Comment_268649 Fri, 25 May 2018 21:46:43 +0100 mark_s
Lots of people do work without getting building regs sign off. The usual thing when selling is that you have to buy an indemnity policy (£150 or so?). They key thing is not to make the council/building regs people aware of things (cant get insurance for it if you've alerted the authorities).


I can't see how the house would be unmortgageable. Our house was bought with various stuff uncertified but the seller paid for an insurance policy.
Interestingly (or not, you decide) I later found behind a plasterboard wall a plan for building work showing a fire escape from the loft conversion. Perhaps the fact that it would have passed through a chimney and emerged in mid air was why it never happened.]]>
Fire escape from a mediaeval cellar http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=15744&Focus=268650#Comment_268650 http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=15744&Focus=268650#Comment_268650 Sat, 26 May 2018 00:00:57 +0100 djh Posted By: mark_sLots of people do work without getting building regs sign off. The usual thing when selling is that you have to buy an indemnity policy (£150 or so?). They key thing is not to make the council/building regs people aware of things (cant get insurance for it if you've alerted the authorities).
I would hope that the law will change fairly shortly so that ignoring safety issues gets you put in prison, irrespective of what building regs says.

Jem, I would find a local surveyor who specializes in building regs and talk to them. I don't think your situation is straightforward.]]>
Fire escape from a mediaeval cellar http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=15744&Focus=268678#Comment_268678 http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=15744&Focus=268678#Comment_268678 Sun, 27 May 2018 11:17:03 +0100 goodevans
For Part B, Bathrooms, cellars and utility rooms, lofts are not habitable, however studies, living rooms bedrooms and kitchens are.

It is clear that the conversion of a cellar into a study for example means that the full fire escape rules apply - so presumably a cellar with a single internal staircase is permissible. What do you intend to use the cellar for?]]>
Fire escape from a mediaeval cellar http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=15744&Focus=268680#Comment_268680 http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=15744&Focus=268680#Comment_268680 Sun, 27 May 2018 11:35:16 +0100 goodevans Fire escape from a mediaeval cellar http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=15744&Focus=268686#Comment_268686 http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=15744&Focus=268686#Comment_268686 Sun, 27 May 2018 12:29:50 +0100 Simon Still
There was no issue with the back basement rooms in our new build (a store and utility, that are accessed through each other). There's nothing to stop someone sticking a desk or even a bed in the store room and using it for another purpose but there were no issues with planning or building regs as designed/built.

if it's not a habitable room you would just need to make that clear when you come to sell. It's quite common with basic boarded out attic rooms.]]>
Fire escape from a mediaeval cellar http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=15744&Focus=268687#Comment_268687 http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=15744&Focus=268687#Comment_268687 Sun, 27 May 2018 13:54:03 +0100 mark_s I would hope that the law will change fairly shortly so that ignoring safety issues gets you put in prison, irrespective of what building regs says.

</blockquote>

You're being rather dogmatic. Nobody is ignoring safety here.

I think it is clear from the OP's posts that this isn't going to be anything more than storage and in a rather special property which isn't going to be compliant with building regs in all sorts of ways.

Am I incorrect in thinking that building regs are only guidance anyway. The legislation sets out requirements and the building regs documents set out some approved methods of complying with the legislation. It is always open to a householder to fulfil the rules in a manner outside the building regs.

THE APPROVED DOCUMENTS
This document is one of a series that has been
approved and issued by the Secretary of State
for the purpose of providing practical guidance
with respect to the requirements of Schedule 1
to and Regulation 7 of the Building Regulations
2010 (SI 2010/2214) for England and Wales.
At the back of this document is a list of
all the documents that have been approved
and issued by the Secretary of State for
this purpose.
The Approved Documents are intended to
provide guidance for some of the more common
building situations. However, there may well be
alternative ways of achieving compliance with
the requirements.
Thus there is no obligation to adopt any
particular solution contained in an Approved
Document if you prefer to meet the relevant
requirement in some other way.


legislation is :
http://www.legislation.gov.uk/uksi/2010/2214/images/uksi_20102214_en_001]]>
Fire escape from a mediaeval cellar http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=15744&Focus=268703#Comment_268703 http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=15744&Focus=268703#Comment_268703 Tue, 29 May 2018 14:38:55 +0100 jemhayward
If we could make the cellar habitable, we'd use it as a dining room, and spend money making it as habitable as possible, lowering the floor, adding heating, electrics and a glass cover over the lightwell. If it is destined to be 'just storage' if we cannot comply with the fire escape rules, then we can't justify blowing our life savings on it.

Ironically we've now managed to clear the soil/rubble from the window and it measures about 44cm wide, so almost compliant - though at least one current member of the household couldn't fit through a 45cm window anyway!]]>
Fire escape from a mediaeval cellar http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=15744&Focus=268704#Comment_268704 http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=15744&Focus=268704#Comment_268704 Tue, 29 May 2018 14:49:51 +0100 jemhayward http://www.legislation.gov.uk/uksi/2010/2214/images/uksi_20102214_en_001

Useful link, and the legislation is remarkably vague, but the fire regs don't apply to prisons, so I think we'll use it to incarcerate the teenager.]]>
Fire escape from a mediaeval cellar http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=15744&Focus=268706#Comment_268706 http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=15744&Focus=268706#Comment_268706 Tue, 29 May 2018 15:38:59 +0100 djh Posted By: mark_s
Posted By: djh
Posted By: mark_sLots of people do work without getting building regs sign off. The usual thing when selling is that you have to buy an indemnity policy (£150 or so?). They key thing is not to make the council/building regs people aware of things (cant get insurance for it if you've alerted the authorities).

I would hope that the law will change fairly shortly so that ignoring safety issues gets you put in prison, irrespective of what building regs says.


You're being rather dogmatic. Nobody is ignoring safety here.

I think it is clear from the OP's posts that this isn't going to be anything more than storage and in a rather special property which isn't going to be compliant with building regs in all sorts of ways.

Am I incorrect in thinking that building regs are only guidance anyway. The legislation sets out requirements and the building regs documents set out some approved methods of complying with the legislation.
Yes, you're incorrect. The legislation is the building regulations. As you say, the Approved Documents are simply approved ways to meet the regulations.

I would hope the house does meet the regulations, in that they explicitly deal with incorporating modifications to existing buildings that in turn meet the requirements when they were built, whatever they were.

Suggesting avoiding the building regs is not acceptable behaviour to my mind, it's exactly the kind of behaviour that leads to consequences down the road. Ignoring the building regulations is an offence. Buying an insurance policy under false pretences is also an offence. I don't think stating that is being dogmatic, just realistic, and hopefully viewed as constructive.]]>
Fire escape from a mediaeval cellar http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=15744&Focus=268708#Comment_268708 http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=15744&Focus=268708#Comment_268708 Tue, 29 May 2018 18:33:45 +0100 fostertom Posted By: jemhaywardat least one current member of the household couldn't fit through a 45cm window anyway!Try turning the dog lengthwise]]> Fire escape from a mediaeval cellar http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=15744&Focus=269359#Comment_269359 http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=15744&Focus=269359#Comment_269359 Sat, 14 Jul 2018 13:34:31 +0100 Sap202 ie if there is an existing staircase then the basement can be accepted as existing
Any other situation then the work would interpreted as "conversion" and the full gamut of regulations would apply not just means of escape]]>
Fire escape from a mediaeval cellar http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=15744&Focus=269360#Comment_269360 http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=15744&Focus=269360#Comment_269360 Sat, 14 Jul 2018 13:40:44 +0100 Sap202 Fire escape from a mediaeval cellar http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=15744&Focus=269717#Comment_269717 http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=15744&Focus=269717#Comment_269717 Fri, 03 Aug 2018 11:11:10 +0100 jemhayward Posted By: Sap202If the cellar is existing then their is no need to take fire regs into account provided that the work that you do carry out does not adversely affect the means of escape from the the "existing basement"
ie if there is an existing staircase then the basement can be accepted as existing
Any other situation then the work would interpreted as "conversion" and the full gamut of regulations would apply not just means of escape

We ran into this problem when we did our barn. One building inspector said that we were dealing with an 'existing room' so fire escape regs didn't apply, and the other one disagreed. We then applied for listed building consent to alter the window to allow it to comply, and were, of course, refused.

In the cellar we're basically fixing things, not altering things, though it looks like the floor level has actually been raised at one stage, so we may 'restore' it to the lower level when we unblock all the underfloor drainage.]]>
Fire escape from a mediaeval cellar http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=15744&Focus=270037#Comment_270037 http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=15744&Focus=270037#Comment_270037 Mon, 27 Aug 2018 15:49:40 +0100 vord
How did you stumble upon your cellar? I'm sure I have one but have drilled holes through floors before recovering and have only found earth so far.]]>
Fire escape from a mediaeval cellar http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=15744&Focus=270039#Comment_270039 http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=15744&Focus=270039#Comment_270039 Mon, 27 Aug 2018 17:16:09 +0100 gyrogear Posted By: vordI'm sure I have one but have drilled holes through floors before recovering and have only found earth so far.

It might be less bother to hire a geobiologist for the afternoon...

gg]]>