Green Building Forum - Major article about Thermal bypass Tue, 19 Dec 2023 05:53:58 +0000 http://www.greenbuildingforum.co.uk/newforum/ Lussumo Vanilla 1.0.3 Major article about Thermal bypass http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=4191&Focus=56544#Comment_56544 http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=4191&Focus=56544#Comment_56544 Wed, 24 Jun 2009 23:55:22 +0100 tony
I have long suspected that small gaps and cracks in insulation have a disproportionate effect on heat losses.

Your reporting the 158% reduction in performance was found when there was a 3 mm crack must put an end to partial fill with sheet insulation

I recon it puts an end to sheet insulation unless inspected and controlled on an hourly basis.

lots of good points made

hopefully it will stop the nonsensical way we build party walls (you didn't mention the thermal bridging into the attic through the structure).

I am unconvinced that any ammount of training will make any difference to grass roots practice, at least not for at least 25 years.

tony]]>
Major article about Thermal bypass http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=4191&Focus=56570#Comment_56570 http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=4191&Focus=56570#Comment_56570 Thu, 25 Jun 2009 08:56:35 +0100 chuckey Frank]]> Major article about Thermal bypass http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=4191&Focus=56583#Comment_56583 http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=4191&Focus=56583#Comment_56583 Thu, 25 Jun 2009 12:19:56 +0100 Paul in Montreal Posted By: chuckeyIf sheet insulation material was smaller ( say 2' X 4') in size and had proper moulded "click?" or tongue and groove edgesThat's exactly what we have over here - except it's a shiplap edge rather than tongue and groove and the sheets are 2'x8' - makes it easier to carry them home in the car too! The sheets also have wooden battens moulded in to allow drywall or furring strips to be screwed to the sheets. Typically, this kind of insulation is used on the inside of the concrete walls of basements. Easy to install and easy to install a finished wall afterward.

Paul in Montreal]]>
Major article about Thermal bypass http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=4191&Focus=56585#Comment_56585 http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=4191&Focus=56585#Comment_56585 Thu, 25 Jun 2009 12:36:12 +0100 Saint Major article about Thermal bypass http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=4191&Focus=56591#Comment_56591 http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=4191&Focus=56591#Comment_56591 Thu, 25 Jun 2009 13:43:47 +0100 tony Major article about Thermal bypass http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=4191&Focus=56606#Comment_56606 http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=4191&Focus=56606#Comment_56606 Thu, 25 Jun 2009 18:03:43 +0100 Saint Major article about Thermal bypass http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=4191&Focus=56607#Comment_56607 http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=4191&Focus=56607#Comment_56607 Thu, 25 Jun 2009 18:59:01 +0100 tony ]]> Major article about Thermal bypass http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=4191&Focus=56634#Comment_56634 http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=4191&Focus=56634#Comment_56634 Thu, 25 Jun 2009 23:07:29 +0100 Saint Major article about Thermal bypass http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=4191&Focus=56656#Comment_56656 http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=4191&Focus=56656#Comment_56656 Fri, 26 Jun 2009 11:35:45 +0100 James Norton
J]]>
Major article about Thermal bypass http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=4191&Focus=56673#Comment_56673 http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=4191&Focus=56673#Comment_56673 Fri, 26 Jun 2009 13:38:17 +0100 Saint Major article about Thermal bypass http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=4191&Focus=56705#Comment_56705 http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=4191&Focus=56705#Comment_56705 Fri, 26 Jun 2009 20:54:06 +0100 Mark Siddall Thanks for your positive comments.

Saint,
Perhaps the condition that you mention was such that air movement behind the insulation was not possible. If this is the case then I agree that a 3mm gap would pose little threat (as the air is still), however, if there is air gap behind the insulation (warm side), then thermal bypass (in this case convective air movement behind the insulation and then through the gap) can occur resulting in a significant degradation in thermal performance.

Mark

P.S. You can find the article in GBM: http://www.greenbuildingmagazine.co.uk/summer09/]]>
Major article about Thermal bypass http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=4191&Focus=56708#Comment_56708 http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=4191&Focus=56708#Comment_56708 Fri, 26 Jun 2009 21:51:18 +0100 brig001 Major article about Thermal bypass http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=4191&Focus=56737#Comment_56737 http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=4191&Focus=56737#Comment_56737 Sat, 27 Jun 2009 22:37:13 +0100 tony
there again any of could do that on any site in the country using boards

Here is a challenge "can anyone post a photo of partial fill with boards with less than a 3mm gap between the boards and the blocks?" :boogie:]]>
Major article about Thermal bypass http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=4191&Focus=57282#Comment_57282 http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=4191&Focus=57282#Comment_57282 Fri, 03 Jul 2009 19:05:04 +0100 tony Major article about Thermal bypass http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=4191&Focus=57298#Comment_57298 http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=4191&Focus=57298#Comment_57298 Fri, 03 Jul 2009 20:39:47 +0100 Johan Posted By: SaintRecognising this problem years ago XPS boards have been available with shiplapped edges for use in partial fill cavities since the 80s and the XPS roofing boards with that edge profile even further back

You can get PUR boards with tongue and groove in UK, Recticel do them. Called Eurosarking SL, http://www.recticelinsulation.com/UK/EN/Product/Eurosarking+SL/]]>
Major article about Thermal bypass http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=4191&Focus=57307#Comment_57307 http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=4191&Focus=57307#Comment_57307 Fri, 03 Jul 2009 22:28:15 +0100 tony Major article about Thermal bypass http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=4191&Focus=57312#Comment_57312 http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=4191&Focus=57312#Comment_57312 Fri, 03 Jul 2009 23:21:05 +0100 Mike George Posted By: tonyno takers then?

Done plenty, but no photos. Next extension I will photograph as I go.]]>
Major article about Thermal bypass http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=4191&Focus=57392#Comment_57392 http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=4191&Focus=57392#Comment_57392 Sun, 05 Jul 2009 13:11:31 +0100 James Norton Posted By: tonyIsn't the gap we are talking about between the blocks and the sheets? t & g etc do not effect this gap


That was my understanding, but also coupled with an inevitable gap elsewhere, which allows the cold air into the gap behind the boards, a la dot and dab...

...but to be honest I should probably re-read the article to do it justice.

J]]>
Major article about Thermal bypass http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=4191&Focus=57503#Comment_57503 http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=4191&Focus=57503#Comment_57503 Mon, 06 Jul 2009 23:31:06 +0100 Mark Siddall
I hope this clarifies things.

Mark]]>
Major article about Thermal bypass http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=4191&Focus=57558#Comment_57558 http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=4191&Focus=57558#Comment_57558 Tue, 07 Jul 2009 15:19:21 +0100 Johan Posted By: tonyIsn't the gap we are talking about between the blocks and the sheets? t & g etc do not effect this gap.Sorry, I read Pauls post and took it as meaning the 'crack' between the edges of the sheets. From Mark S. reply I take this is what we're talking about.

I would've though any air leakage between sheets degrades the thermal performance more then the 'gap' between the sheets and the inner leaf?]]>
Major article about Thermal bypass http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=4191&Focus=57559#Comment_57559 http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=4191&Focus=57559#Comment_57559 Tue, 07 Jul 2009 15:25:38 +0100 GBP-Keith http://www.greenbuildingmagazine.co.uk/summer09/]]> Major article about Thermal bypass http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=4191&Focus=57565#Comment_57565 http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=4191&Focus=57565#Comment_57565 Tue, 07 Jul 2009 17:07:36 +0100 beelbeebub

I'm interested in this as it impacts a little on my thoughts for wall construction.

I was/am thinking of
solid blockwork inner leaf
100-150mm PU boards
Cavity
Rainscreen (possibly brickwork)

effectively an externally insulated wall.

This problem of gaps between the insulation slabs and between the insulation slabs and the blockwork seems a bit of a problem.

Here's a thought.

If, rather than using a single 100mm thickness of slab, I used 2x50mm slabs that could be laid in a broken jointed fashion so the edges don't line up through the thickness would I reduce the gaps through the insulation?

Secondly, would it be possible to use something like bathroom tiling grout to spread (using one of those combs) on the outside of the blockwork to stick (just like giant bathroom tiles) the first layer of PU insulation on. Once "stuck" up the edges could be taped. The grout behind the PU would act to help fill any gaps between the plaster and the blockwork and the taping would then prevent any air infiltration through the insulation. The second layer of PU slabs could then be laid, possibly using an adhesive to stick it to the first.

Finally cavity ties designed for thin block work would be "nailed" through the insualtion into the blockwork. Insulation clips would then fit over to ties to hold the PU slabs in place permanently (the tile grout only being a tempory bond and a cavity filler).

Then the outer leaf could be built up as per normal.

I would end up with a partial fill cavity BUT as the outer leaf was built after the insulation has been installed I can pay extra attention to getting a good seal and fit.

The tile grout would act as a tempory fix to hold the insulation in place and as a filler/flow disruptor to reduce the convection between the blocks and the PU.]]>
Major article about Thermal bypass http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=4191&Focus=57568#Comment_57568 http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=4191&Focus=57568#Comment_57568 Tue, 07 Jul 2009 17:30:39 +0100 tony
I recon we are heading back towards retro filling the cavities.]]>
Major article about Thermal bypass http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=4191&Focus=57576#Comment_57576 http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=4191&Focus=57576#Comment_57576 Tue, 07 Jul 2009 19:04:13 +0100 beelbeebub
see: http://www.ancon.co.uk/main.asp?pageID=159

I admit i'm not too sure about the idea as it seems a bit odd, but they are an approved product. They seem to have some type of high pitch thread on them (like an impact driver) so maybe as you bang them in they cut their own thread.

After reading a paper on the effects of gaps in the insulation it would seem pretty vital to either seal the insulation layer totally or fill the gaps behind the insulation layer.

As sealing the insulation layer is likely to be impossible that leaves filling the gap behind.

I could move to a fully filled cavity of rockwool but I need 200mm of rock wool to get the same effect as 120mm of PU.

Maybe 100mm of PU backed by 50mm of rockwool, still built up in the same way

If the tile grout used for "tacking" the first layer of PU slabs onto the blockwork can act to effectively seal the back cavity I could be onto a winner!

here's the paper on the effects of gaps behind insulation etc

http://www.viking-house.ie/downloads/Lecompte%20paper_partial%20fill%20cavity%20walling.pdf]]>
Major article about Thermal bypass http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=4191&Focus=57579#Comment_57579 http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=4191&Focus=57579#Comment_57579 Tue, 07 Jul 2009 23:15:32 +0100 tony
I could move to a fully filled cavity of rockwool but I need 200mm of rock wool to get the same effect as 120mm of PU.

this is not true as 1 the 120 of PU will have little gaps reducing its performance possibly to below that of a similar thickness of batts!]]>
Major article about Thermal bypass http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=4191&Focus=57591#Comment_57591 http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=4191&Focus=57591#Comment_57591 Wed, 08 Jul 2009 11:33:50 +0100 MarkBennett Posted By: beelbeebubI could move to a fully filled cavity of rockwool but I need 200mm of rock wool to get the same effect as 120mm of PU.

Don't forget that PU needs a 50mm air gap, so 120mm of PU needs a 170mm cavity. Rockwool can fully fill the cavity, so 200mm of rockwool only needs a 200mm cavity. Shrinks the wall thickness difference to just 30mm. (Not to mention any argument about gaps around the PU etc.)]]>
Major article about Thermal bypass http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=4191&Focus=57594#Comment_57594 http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=4191&Focus=57594#Comment_57594 Wed, 08 Jul 2009 12:05:09 +0100 tony glad I chose full fill batts now]]> Major article about Thermal bypass http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=4191&Focus=57598#Comment_57598 http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=4191&Focus=57598#Comment_57598 Wed, 08 Jul 2009 12:52:17 +0100 bot de paille
Don't forget that PU needs a 50mm air gap, so 120mm of PU needs a 170mm cavity. Rockwool can fully fill the cavity, so 200mm of rockwool only needs a 200mm cavity. Shrinks the wall thickness difference to just 30mm. (Not to mention any argument about gaps around the PU etc.)</blockquote>

Why does PU need an airgap and rockwool doesnt?]]>
Major article about Thermal bypass http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=4191&Focus=57600#Comment_57600 http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=4191&Focus=57600#Comment_57600 Wed, 08 Jul 2009 13:08:30 +0100 MarkBennett Posted By: MarkBennett
Posted By: beelbeebubI could move to a fully filled cavity of rockwool but I need 200mm of rock wool to get the same effect as 120mm of PU.


Don't forget that PU needs a 50mm air gap, so 120mm of PU needs a 170mm cavity. Rockwool can fully fill the cavity, so 200mm of rockwool only needs a 200mm cavity. Shrinks the wall thickness difference to just 30mm. (Not to mention any argument about gaps around the PU etc.)

Sorry, that should be 25mm air gap, not 50mm. Hence 120mm of PU needs a 145mm cavity, compared to a 200mm cavity for Rockwool.]]>
Major article about Thermal bypass http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=4191&Focus=57601#Comment_57601 http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=4191&Focus=57601#Comment_57601 Wed, 08 Jul 2009 13:14:44 +0100 MarkBennett Posted By: bot de paille
Posted By: MarkBennett
Posted By: beelbeebubI could move to a fully filled cavity of rockwool but I need 200mm of rock wool to get the same effect as 120mm of PU.


Don't forget that PU needs a 50mm air gap, so 120mm of PU needs a 170mm cavity. Rockwool can fully fill the cavity, so 200mm of rockwool only needs a 200mm cavity. Shrinks the wall thickness difference to just 30mm. (Not to mention any argument about gaps around the PU etc.)


Why does PU need an airgap and rockwool doesnt?

I believe that for PU the gap is needed to stop water that has penetrated the outer leaf from coming into contact with the insulation. The gap ensures it runs down the inside skin of the outer leaf.

Not sure why rockwool doesn't need this and can therefore be full filled. I can only guess that it is more tolerant to water ingress. Tony?]]>