Posted By: SteamyTeaAs you have an airtight house would you not just fit an MVHR unit and get the benefit or warmed clean air?
Posted By: Paul in Montreal you need to know that actual air change rate in litres/second and compare that with recommended values based on the occupancy level.
Paul in Montreal.
Posted By: Paul in MontrealYou need less than 3ACH@50Pa before an MHRV shows any benefit. Above that, and you're just adding to the ventilation losses (even with the heat recovery), plus there's the running cost of the fans.
Posted By: jms452Do you have a reference for the 3ACH figure? I see it quoted a lot but have never seen the original quantitative justification - surely this depends on lots of factors SFP, efficiency etc...
Posted By: JontiSo how do you calculate it if the level of occupancy changes from two to four or visa versa?
Posted By: Paul in MontrealYou need less than 3ACH@50Pa before an MHRV shows any benefit.
Posted By: RobinBSounds like we're saying between 3 and 5 ACH is a nomansland. Too tight to ventilate itself and too high for cost-effective MVHR. Also perhaps a bit late to route MVHR ducting?