Home  5  Books  5  GBEzine  5  News  5  HelpDesk  5  Register  5  GreenBuilding.co.uk
Not signed in (Sign In)

Categories



Green Building Bible, Fourth Edition
Green Building Bible, fourth edition (both books)
These two books are the perfect starting place to help you get to grips with one of the most vitally important aspects of our society - our homes and living environment.

PLEASE NOTE: A download link for Volume 1 will be sent to you by email and Volume 2 will be sent to you by post as a book.

Buy individually or both books together. Delivery is free!


powered by Surfing Waves




Vanilla 1.0.3 is a product of Lussumo. More Information: Documentation, Community Support.

Welcome to new Forum Visitors
Join the forum now and benefit from discussions with thousands of other green building fans and discounts on Green Building Press publications: Apply now.




    • CommentAuthorballen
    • CommentTimeNov 3rd 2022 edited
     
    Hi all,

    Having joined the forum a couple of years ago while waiting for the purchase of our house to go through, I have definitely learnt alot and we are now ready to crack on with things.

    I do tend to be a bit of a perfectionist, however, as much as I would love a passive house, I realise that given a 130 year old building and a fairly limited budget, there is going to be a fair bit of compromise.

    The ideal solution would have probably been EWI all round with some sort of reclaimed brick slip finish - far too costly obviously, we didn't really want to loose the brick and are in a conservation area so would probably have had little choice with the front at least. As such, we've decided to split the work into two main phases - with one part of the building being primarily IWI, which will be happening first, allowing us to redecorate most of the house at the same time and the other EWI, coming at a later stage, when funds allow.

    The 'phase 1' plan is:
    Walls (blue on plan) - 80mm Woodfibre w/ lime render IWI giving 0.39ish u-value (possibly eps instead in ensuite)
    Suspended floor (green)- 200mm mineral wool breather membrane 'hammock' for support and VCL over the top, existing pitch pine boards to finish giving approx 0.19 u-value
    Attic rooms - 40mm celotex between rafters (leaving 50mm ventilation gap, felt lap vents to be fitted), 100mm celotex over top, boards taped with aluminium tape and an airtight tape to the walls, possibly battens to form 25mm service void then 12.5mm plasterboard giving a u-value of 0.16
    Windows - these are currently badly fitted UPVC casement windows, looking to change these to new UPVC sliding sash's - appreciate that this could be a little controversial but given the budget we have, these seemed a good compromise between making some improvement and the overall cost.

    Phase 2 would be converting the remaining 'back' roofs to warm roofs, whilst extending overhang for 150mm EPS EWI (red on plan), down to footing. New windows/doors fitted outbound in insulation layer.

    A few questions:
    - BCO suggested 100mm celotex be reduced to 75mm due to risk of interstitial condensation - he wasn't too bothered either way but given a decent VCL I'd have thought 100mm would pose no additional risk?

    - Woodfibre boards - any recommendations for a 'system'? Looking at ecomerchant's steico/breathaplasta as it seems fairly simple compared to some others and competitively priced.

    - How to people handle heavy fixings in woodfibre e.g. curtain poles, radiators where these can't be moved to an internal wall.

    - Internal Partition wall returns - I was looking at doing these in something like 30mm boards, coming in 500mm or so and tapering to avoid any steps. Not too sure how I'd achieve this other than a fair bit of time with a rasp?

    - Trickle vents - BCO wants these fitted, I'm not too keen on the idea of spending time taping and parging to improve the air tightness, just to spend a load of money on new windows with a big hole in, undoing all my hard work. I guess the only other option is MVHR though - is this ever going to be worth fitting given that even with my best efforts this is still likely to be a fairly leaky building - I have half a plan involving ductwork down chimney's but given the extra costs and possibly limited usefulness, perhaps trickle vents are the easier options

    Sorry for the long first post and thanks in advance, would welcome any other comments/thoughts on the above too!
      11446_0057_HRT005709288_IMG_41_0000.jpg
      floorplan.png
    •  
      CommentAuthordjh
    • CommentTimeNov 4th 2022
     
    Hello, and welcome.

    Posted By: ballenI do tend to be a bit of a perfectionist, however, as much as I would love a passive house, I realise that given a 130 year old building and a fairly limited budget, there is going to be a fair bit of compromise.
    I started out with an early 1970s house and as I learned more, I chose instead to take the time to find a plot and build a passivhaus. My point is that your choice to take a Victorian house and in a conservation area too is a strong indication of different priorities. It's important to sort those out and articulate them, IMHO. For one thing it would perhaps let you pick one of the many retrofit standards and decide to meet it, and that can be a very powerful motivating factor.

    I'm not a retrofit expert so I'll leave most of it to others but a few comments:

    * I wouldn't go for UPVC windows but if you need to go for UPVC windows then why sliding sash, given you're concerned about airtightness? At least go for a good brand like Rehau.

    * Plan to buy a good quality MVHR unit and plan now for the ducting. It will be a revalation.

    * Heavy fixings in walls - either put specific timber noggins etc in the required places, or spread the load with multiple fixings and/or epoxy injection, or put a 'false' wall in front to take the load e.g. a sheet of OSB.

    * I don't understand the roof insulation. It sounds like insulation between the rafters, then an air gap then more insulation. Which doesn't make sense. When you say 'over the top' do you mean 'underneath'? Also, are you confident aluminium tape will remain airtight for the long term?
  1.  
    Its difficult to see from the picture - is it solid wall everywhere or is there cavity in places?

    For windows I'm with djh, why sash windows? I would go for good upvc casement tilt and turn windows.
    And they look tall enough to have tilt and turn on the lower half with fixed lights above but make sure the frames top and bottom are the same width because fixed lights can be standard frames without opening light s inset which gives a wider glass area but lould look silly.

    Bay windows can be particularly nasty in terms of cold ingress. These deserve particular attention especially the flat roof part both insulation and its water tightness. What plans?

    Radiators - You can get legs for radiators which transfer the weight to the floor. If you use these and then fix the usual brackets screwed through the IWI this should be OK.
    • CommentAuthortony
    • CommentTimeNov 4th 2022
     
    EWI to flank side and rear walls . IWI to front wall . Roof target U-value 0.1 , add floor insulation
  2.  
    A few scatter-gun comments.

    Is the drive to the R of the RHS rendered wall yours? If not can you negotiate to buy a bit of your neighbour's land? A client of mine did this.

    Assuming the 50mm ventilation gap really is ventilated (I often see lovely gaps and very poor 'ins' and 'outs') then 75, 100, 150 (looooong screws!) is going to make little difference. The beauty of properly-ventilated roofs is that the WV does not get to hang around long enough before being blown away.

    Wood-fibre. I have used Pavatex for years, with Baumit plasters. The latter very 'friendly' to use.

    Re rasp, don't get out your surform, as I used to. Buy an EWI rasp, which is like a cross between a cheese grater and a large plastering trowel. Made for EPS AFAIK but does the business on WF.

    Agree avoid sliding sash if really going for A/T.

    If you are not going for HRV then you need to prove to BCO that you have 'enough holes' somewhere. If you go for HRV in the long term trickle vents can be removed and blocked.
    • CommentAuthordb8000
    • CommentTimeNov 5th 2022
     
    Posted By: tonyEWI to flank side and rear walls . IWI to front wall . Roof target U-value 0.1 , add floor insulation

    I have been thinking about this for my Edwardian detached solid wall home. I’m glad to hear that it’s not (in concept) a bad idea.
    Like Ballen’s it has a pretty front and side aspect that could only ever suit iwi. And two undressed stone aspects that could do Ewi.
    When it comes to the corner, would one continue the iwi along the wall that has ewi to help minimise the thermal bridge? Thinner iwi or a short amount using one of those tapered insulation boards you can get?
    @ballen that’s a lovely house you have!
    Ta
    Dave
  3.  
    @db8000, I am just racing the weather doing what you propose. In fact we finished the render yesterday on about 120-ish m2 of Victorian cavity brick wall with (on one elev) 120mm and (on the other) 160mm wood-fibre. Went to and fro between WF and (much cheaper and lighter) EPS, particularly in the light of a bad back and boards weighing about 23kg, but heart said WF. Ours is detached, and 2 elevs built to 'show off'. It's not that pretty, but all the fancy detailing (stone plinths, keystones, rubbed brick arches, ornamental brickwork round windows, bay windows, faces the road. The other 2 walls are 'ar$e-end-of-a-terrace' architecture - fine enough to no letters home.

    Yes, return the IWI to cloak the thermal bridge - in full depth if you can. I find the Nick Parsons dual-depth purpose-made bookcase concept works here.
    • CommentAuthorballen
    • CommentTimeNov 7th 2022
     
    Thanks for the comments guys.

    Re. priorities - I think this is fair, the house is basically my wife's dream house - she loves 'old stuff' and the period features are a key thing for her. It took a lot of convincing that internal insulating and losing the original cornice was acceptable (we plan to replace with matching). The house suits us for now, as a (fairly) young and growing family - 2 kids, 3rd due in April, 2 dogs - decent garden for these. It's more about making it somewhat more affordable in winter but most importantly more comfortable and also reducing our carbon footprint.

    This is the main reason for wanting sliding sash - but I see this reasoning along with plastic windows doesn't make sense. I'm trying to find a supplied for Vrogum Solborg windows which use some compression seals and have better airtightness figures. I assume the main reason against sliding sash is the brush seals - is this just because they are not very good full stop or that they degrade quickly?

    Rafter insulation - yes between and under the rafters. Sounds like aluminium tape won't be good enough - am considering installing a separate VCL rather than taping all joints with an expensive airtight tape. Nick - Good point about the ventilation here - I'm not convinced it is great. I was planning on fitting felt lap vents to improve and probably eave ventilators when the soffits and gutters are replaced.

    Driveway is ours - wall is sand/cement rendered so had plans to remove this before EWIing with EPS, extending roof overhangs to suit. A lot of services to move though.

    Woodfibre - I looked at Pavadry which appealed (I am not a plasterer) but the idea of putting plasterboard over woodfibre seemed a bit counter intuitive. I'd been looking at using Baumit MP69 as a parge coat. What are you using on the woodfibre boards RK70?

    One potential issue that I hadn't thought about is that the Front/Side aspects have previously been repointed - in cement. Long term I would like to repoint properly in lime but is this likely to cause any issues in the meantime? I noticed some of the woodfibre IWI systems recommended it was lime.

    Chimneys - All of ours are external and in need of repointing above the roof line. I was considering blocking these up and filling with something like vermiculite - possibly using the space to run MVHR ducting to the ground floor living room and dining room. I've seen alot mentioned on doing this with internal chimneys but get the impression external chimneys could be riskier. Any thoughts on this?

    Thanks!
    •  
      CommentAuthordjh
    • CommentTimeNov 7th 2022
     
    Posted By: ballenChimneys - All of ours are external and in need of repointing above the roof line. I was considering blocking these up and filling with something like vermiculite - possibly using the space to run MVHR ducting to the ground floor living room and dining room. I've seen alot mentioned on doing this with internal chimneys but get the impression external chimneys could be riskier. Any thoughts on this?
    Usually, MVHR ducts are run in the internal (warm) spaces, because they're carrying air at near room temperature. If they're installed somewhere outside the thermal envelope, then they need insulating quite well to avoid defeating the purpose of an MVHR. Internal chimneys are automatically insulated as long as they're closed at the top, but external chimneys would obviously need to be insulated. Depending on your plans this might be something you do anyway.

    PS The (short) duct runs to the fresh air from the MVHR unit need to be insulated because they are carrying air at outside temperature. Hence mounting the MVHR somewhere near an outside wall is usually a good idea.
  4.  
    IWI on street-facing elevations and EWI on rear or side elevations is a fairly common strategy.

    I’m someone who thinks appearance matters and therefore generally am in favour of some compromise on attractive brick or stone built street elevations, balanced out by some fairly substantial external insulation elsewhere.

    I would support your plan to use sliding sash on the street elevations but agree you should consider tilt/turn in other locations. Just be sure to think through whether the room layout can accommodate an inwards opening window, if you are looking at that type.

    Agree with other comments that bay window should be given particularly careful thought.

    I’m also a bit confused by the roof insulation. Are you planning for between & under the rafters on the main house portion, and between & over for the rear /outrigger portion. Seems to make sense because although over-rafters is always preferable if possible, it does have aesthetic implications for eaves and so on.

    Remember you have potential cold bridges at any transition between an externally-insulated wall and internally-insulated pitched roof (or vice versa) and you might want to consider the same strategy of returning insulation down walls as described for the junctions of EWI and IWI.

    Also for the roof … remember there is always the option (only if you take the tiles off) of replacing roofing felt with a breather membrane and then fully filling between rafters, so you get an extra 50mm of insulation without any loss of internal height. Just the extra depth of a 25mm counterbatten added externally which is often small enough that it can be disguised. Arguably this is only worth doing if you are taking tiles off anyway, and/or want to replace old and deteriorating roof felt.

    I’m interested why you are considering woodfibre boards for the walls but seem happy with celotex for the roof? Is it worries about “breathability”? No-one really seems to agree about this yet but my impression is it doesn’t matter too much unless maybe you are somewhere with high rainfall and porous brickwork.

    For MHVR getting ducting to work is a right pain in an old building especially if space is already a bit tight. I have long been interested in the approach of using a few strategically placed in-wall units instead - but haven’t looked at the options for a few years so am a bit out of date.
  5.  
    Ballen said: ''What are you using on the woodfibre boards RK70?''

    Sorry for late reply. Yes, I use RK70 and the 'Kalkin glatt' final finish, which is OK to use but very different to 'pink plaster'.

    Remember if you have existing lime plaster and it is not all clogged up with gloss or vinyl silk you can use that as the parge coat and simply augment where required. I always 'butter' the boards with a 10mm toothed-trowel coat of RK70 so that if my parge coat is not perfect the 'buttering' will fill any hollows.

    My house has sand/cement re-pointing and some spalling brickwork, but it had spalling before we did any IWI. The 'rate of attrition' seems no worse.
    • CommentAuthorballen
    • CommentTimeNov 9th 2022
     
    Yes, primarily interested in woodfibre for breathability - does seem to be a slightly contentious topic although I did think that the general consensus was that it was a good thing.

    Roof - yes between and under in main house, between and over for the rear. Don't have the budget to replace the main roof currently, doing this internally seemed like an acceptable compromise and could be made to tie into IWI easily. The rear roof's are more in my capability, would need overhangs extended for EWI anyway (I don't like the idea of siliconing on plastic trims) and would tie into the EWI nicely. There'd still be a few IWI/EWI junctions that would need thinking about but I think doing it this way would reduce the potential cold bridges.

    Retrofit MVHR - this does look like its going to be the biggest challenge - I'd ideally like to avoid having boxed in ducting everywhere. Chimneys seemed to provide a built in duct but agree that insulating ducting in these would be a challenge. I'd thought about using insulated ducting and the back filling the chimney with a loose fill insulation.

    Perhaps a slightly easier option would be to run the ducting alongside a chimney breast and box these in making it look as one. The chimney breasts are very shallow internally but there should be just enough room to do this with 75mm semi-rigid ducting.

    The other option would be to use a single room MVHR for the ground floor rooms and run a whole house MVHR for the second/3rd floor - bit easier to do this as the eaves provide a hidden route for ducting (will insulate rafters right down to the wall plate, rather than to the dwarf wall and down)

    WIth either of these options I'm still going to struggle running ducting down to the kitchen/utility - my thoughts on this were to build an external service void when EWI - such that the unit would be located in the loft above the bathroom/rear bedroom, with a box running externally down the wall to the attic above the 'breakfast room' (plans to knock this through into the kitchen creating a kitchen/diner). This box could have 100mm eps EWI installed either side of it and an additional 150/200mm over the top - quite a thickness of EWI in places but a well enough insulated service void for ducting?
  6.  
    I am working on retrofitting 3 separate "small" mhrv units to our 19thC stone house, each extracting from one room and feeding into an adjacent room*. Reasons:

    - easier and much cheaper than trying to run ducts to a big manifold in a central location with no existing routes
    - compatible with slow bit-at-a-time renovation
    - several small mhrvs much cheaper than a single house-sized one
    - allows ventilation at the right time - eg boost the kitchen one when cooking, and the guest bedroom one when there are guests, instead of having to boost the whole house
    - allows different temperatures at different times in different rooms without losing efficiency.

    * Though one of them is a through-the-wall

    We are looking at hr100r "two room" units which are basic but fit for our purpose. However they seem to be getting towards the end of their products life, and the replacement model is much better and hence too expensive.
    •  
      CommentAuthordjh
    • CommentTimeNov 9th 2022
     
    Posted By: ballenChimneys seemed to provide a built in duct but agree that insulating ducting in these would be a challenge. I'd thought about using insulated ducting and the back filling the chimney with a loose fill insulation.
    FWIW, Ubbink do insulated ducting that is fairly effective (each length is all one piece of insulation and there are preformed curves etc). Filling the chimney with EPS beads afterwards would be good insulation and easy to do.

    Posted By: WillInAberdeenI am working on retrofitting 3 separate "small" mhrv units to our 19thC stone house, each extracting from one room and feeding into an adjacent room*.
    The thing I still don't understand about multiple units is the multiple penetrations issue. That is, with conventional MVHR you're told to have the intake and exhaust terminals fairly close together on the same wall, or the same slope of the roof. And the reason given is that if they're too far apart, and more so if they're on different faces, then they experience different pressures and you get through drafts that you don't want, unbalancing the MVHR. I still don't understand how multiple single room units get around this issue. If there are any good explanations out there, I'd love to read them.
  7.  
    Many 19thC houses didn't originally have indoor bathrooms/ wet rooms etc, so it is common to find an early-20th-C extension out the back with a kitchen and utility or shower room downstairs and a bedroom and bathroom upstairs - IE with all the 'wet' rooms grouped around a single drain downpipe. Our last 4 houses were like that, as it seems is Ballen's.

    This makes it relatively easy to have all the intakes/exhausts on the same wall.
  8.  
    Posted By: WillInAberdeeneach extracting from one room and feeding into an adjacent room*.


    I don't quite understand what you mean by this ... any chance of a diagram showing how you have got it set up?
  9.  
    For example on Ballen's floorplan:

    Mhrv unit #1 could extract directly from the kitchen, and supply into the dining room through a short duct with no manifolds. Unit located in a kitchen cabinet, intake/exhaust straight thru the kitchen external wall.

    Mhrv unit #2 could extract directly from the laundry room and supply through the wall into the breakfast room. Located in the laundry room, in a cabinet on the partition wall between those two rooms.

    Mhrv unit #3 could extract from the upstairs bathroom and supply into the adjacent bedroom. Located above the bathroom ceiling.

    And so on.... Ballen has five wet rooms (we have fewer) so they might want up to 5 mini mhrvs, depending how many bathrooms are in use often enough. 5 off HR100R @ Ă‚ÂŁ270 each, no manifolds, minimal ducts = Ă‚ÂŁ1600. Costs more to have better units.
    • CommentAuthorMike1
    • CommentTimeNov 10th 2022 edited
     
    Posted By: ballenRetrofit MVHR - this does look like its going to be the biggest challenge - I'd ideally like to avoid having boxed in ducting everywhere
    Although circular ducting is normally used, it's possible to use low-profile rigid rectangular ducting (e.g. Polyvent 234 x 29mm, Manrose 225 x 25mm, Helios 218 x 55mm) or semi-flexible oval ducting (e.g. Alnor 132 x 52mm) and convert between them. That may give you some more flexibility, though you should still minimise bends and turns where possible.
    •  
      CommentAuthordjh
    • CommentTimeNov 10th 2022
     
    Whilst I'm a big fan of semi-rigid ducting (it's what we have for all the internal ducting), I'd recommend choosing a product that has a smooth internal surface rather than exposing ribs internally. The difference is quite significant, I believe. I second the opinion about minimising bends and especially corners.
  10.  
    Some other options:

    Passivhaus decentralised MHRV
    https://www.paulheatrecovery.co.uk/cascade-mvhr/
    this one has a through-the-wall unit, and then separate fans located through internal walls around the house to circulate the fresh air as needed through all of the rooms, rather than using ducts


    Push-pull Mhrv: (other makes are available)
    https://www.partel.ie/product/lunos-e/
    https://www.ventilation-alnor.co.uk/index/news/industrial-news/hru-wall-rc.html
    This through-the-wall unit extracts stale air out of the house, while collecting the heat in a ceramic block. After a minute, it swaps over to bringing fresh air in, recovering the heat from the block. You have several units around the house, some makes will synchronise so that one unit extracts while the other imports, which helps distribute fresh air without ducts.
    •  
      CommentAuthordjh
    • CommentTimeNov 10th 2022
     
    I can see that if all the wetrooms are in a vertical stack obliged by a single soil pipe, then in that case single room MVHR units could work. But I don't think Ballen's place is like that. It has three wetrooms spread along the length and height of one wall, but then two more in the opposite corner. So I'm still left with the puzzle I mentioned.

    I like Blumartin's product, but I'm less convinced by the push-pull systems - maybe I'm just too sceptical. The push-pull units are quite low capacity, so you'd need quite a lot of them.
  11.  
    I can't speak for the layout of Ballen's house, but it does look like all their wetrooms are adjacent to the cream painted wall in the picture.

    TBH this may be more of an issue for new-builds - compared to the "as is" situation, or the Building regs default solution, this would be low down my list of concerns! But if someone felt strongly about it, then the more expensive single room units are self-balancing (possibly that Lunos one is).

    Push-pull units are available in different sizes, this one is 90m³/h, but indeed the whole point of dMHRV is to have several smaller units. https://www.partel.ie/product/lunos-nexxt-e/

    Did you have any specific unconviction about the push-pull units - any links to drawbacks?

    (Edit: for clarity, decentralised MHRV doesn't have to be 'single room' units - there are also "two room" units which are marketed at serving two adjacent rooms, such as a bedroom with adjacent bathroom, with short duct runs through the dividing wall.)
    • CommentAuthorlineweight
    • CommentTimeNov 10th 2022
     
    Posted By: WillInAberdeenFor example on Ballen's floorplan:

    Mhrv unit #1 could extract directly from the kitchen, and supply into the dining room through a short duct with no manifolds. Unit located in a kitchen cabinet, intake/exhaust straight thru the kitchen external wall.

    Mhrv unit #2 could extract directly from the laundry room and supply through the wall into the breakfast room. Located in the laundry room, in a cabinet on the partition wall between those two rooms.

    Mhrv unit #3 could extract from the upstairs bathroom and supply into the adjacent bedroom. Located above the bathroom ceiling.

    And so on.... Ballen has five wet rooms (we have fewer) so they might want up to 5 mini mhrvs, depending how many bathrooms are in use often enough. 5 off HR100R @ Ă‚ÂŁ270 each, no manifolds, minimal ducts = Ă‚ÂŁ1600. Costs more to have better units.


    Yes, I see. So you are kind of taking advantage of the partition wall between adjacent rooms as a way of putting some distance between extract and intake points.
  12.  
    That's right, the same idea as if those rooms had supply and extract terminals from a central Mhrv.
    •  
      CommentAuthordjh
    • CommentTimeNov 10th 2022
     
    Posted By: WillInAberdeenI can't speak for the layout of Ballen's house, but it does look like all their wetrooms are adjacent to the cream painted wall in the picture.
    Eh? The plan shows a laundry & WC, a kitchen, and a bathroom against that wall, and an ensuite and another WC against the front wall at the right-hand side.

    I'm curious what you or they mean by 'self-balancing and by how it works. The term doesn't appear in the Lunos catalogue so do you have a link to a description please?

    My dislike of the push-pull units is just personal prejudice. I feel an instinctive distrust of systems that rely on passing exhaust air and fresh air over the same surfaces and rely on those surfaces staying sterile for many years. I know the manufacturers say it is all fine. :bigsmile:

    Yes, I understand the two-room units and also the Blumartin 'ducted exhaust but not supply' arrangement.

    One other issue to be aware of with two-room or other short ducted units is that it restricts the placement of the terminal in each room quite a lot. So it's worth checking that the resulting placements are sensible. Obviously the flow rates need to be compatible as well.
  13.  
    ?? The downpipe from the ensuite and WC, is clearly visible against the cream painted side wall, which also forms the side of the kitchen laundry etc ??

    The lunos.de website describes how their fans are controlled at a constant-volume-flow, compensating for variation in outside pressures from changes in the wind (they mention suitability for coastal and hilly areas). "The unit meets the new requirements for wind pressure stability according to EN 13141-8".

    So the same constant volume flow rate during the intake phase, as during the exhaust phase -> same volume of warm air is extracted during the cycle as cold air is drawn in -> unit always stays balanced.

    If it wasn't volume balanced, the ceramic heat recovery block would get hotter and hotter each cycle, so have more and more temperature driving force to transfer heat into the cold air, which would also be self-balancing that way.

    Ă‚ÂŁ500 each on Amazon, so you have to pay your money to take your choice... not currently on my shopping list!
    •  
      CommentAuthordjh
    • CommentTimeNov 11th 2022 edited
     
    The bathroom and the downstairs WC are definitely against the opposite wall. The kitchen I agree spans the two

    Unfortunately EN 13141-8 is one of those standards where you have to pay money to read it. So I haven't. But https://www.partel.co.uk/product/lunos-e60/ , which refers to the standard, says "An optional, intelligent control system ensures that the occurring back pressures are balanced up to 20 Pa" so apparently (a) it is optional and (b) the requirement is only up to the low end of a Beaufort Force 4 and considerably below the 50 Pa used for airtightness testing (and higher values are used in particularly windy countries, I believe). So it doesn't really answer my question I think.
  14.  
    The actual wind speed at street level in a housing area doesn't exceed F4 for many hours of the year, that's why domestic wind turbines have never caught on. You need a good fetch of open water or fields to get a wind speed close to the numbers in the forecasts. A sailing anemometer outside the kitchen door shows how many hours each year are actually windy there, not enough.

    Should they choose this option, Ballen's downstairs WC has a wall facing the same direction, and the upstairs bathroom ventilation could vent through the same roof face if it were
    Located above the bathroom ceiling
    This does seem like a bit of a non-issue to me TBH, a) for typical retrofits, b) with brief thought about where to put the vents, c) with well designed equipment, or d) at all.
    • CommentAuthorballen
    • CommentTimeNov 13th 2022 edited
     
    The single room units I'd been looking at were the push-pull, but it did seem like I would basically need a unit for each room - becomes quite expensive and their not that aesthetically pleasing. Likewise for something like Fresh-R which looked like it would require multiple units and again, soon add up in cost.

    I quite like the idea of multiple small units working between two rooms - not something I'd come across before and has certainly given me something to think about. I think what you've suggested would give me something like the attached - with red being extract and blue supply.

    The bedroom/en-suite unit would likely live in the cupboard next to the top floor WC - I'm thinking these could be combined although I might need a bigger unit? Perhaps I could then feed supply's to the remaining two bedrooms?

    This would then just leave the lounge without any sort of ventilation - is this acceptable or would I need an alternative e.g. push pull unit here?

    The biggest issue with this proposal is the dining room/kitchen arrangement given the slightly awkward ducting in the kitchen and across the hallway. This could probably be boxed in quite satisfactorily although I believe it still leaves the supply vent in a less than ideal position.

    I'm somewhat torn between this idea and a whole house unit - for which I think I have duct routes worked out for everything but the living room again. However, would be more difficult to install and require a fairly big (expensive) unit I believe.
      mvhr single room.png