Home  5  Books  5  GBEzine  5  News  5  HelpDesk  5  Register  5  GreenBuilding.co.uk
Not signed in (Sign In)

Categories



Green Building Bible, Fourth Edition
Green Building Bible, fourth edition (both books)
These two books are the perfect starting place to help you get to grips with one of the most vitally important aspects of our society - our homes and living environment.

PLEASE NOTE: A download link for Volume 1 will be sent to you by email and Volume 2 will be sent to you by post as a book.

Buy individually or both books together. Delivery is free!


powered by Surfing Waves




Vanilla 1.0.3 is a product of Lussumo. More Information: Documentation, Community Support.

Welcome to new Forum Visitors
Join the forum now and benefit from discussions with thousands of other green building fans and discounts on Green Building Press publications: Apply now.




    • CommentAuthorjohnnyh
    • CommentTimeNov 27th 2015
     
    Hi to all, i've been reading this forum for ages whilst getting round to installing my log burner and store. Finally it's in and working pretty well but i'm not really getting more than a day's worth of heating per charge and i had hoped for maybe two days when the weather is mild. I have ordered a tech 431 'steering' to control the CH mixer valve and in the meantime i have adjusted it right down which gives us a fairly low temp on the rads, not hot enough for a cold day. If i adjust the mixing valve back up, the tank destratifies. One solution i think would be some ufh circuits to cool the radiator return temperature but they would have to be fed from the radiator return to have this effect.
    The question is simply: Will this work?
  1.  
    how about oversizing the rads instead?
    • CommentAuthorjohnnyh
    • CommentTimeNov 27th 2015
     
    The thing is the rads are already installed as i have changed over from an oil fired system. I am going to add one or two more rads where i have space but the upstairs floors are not finished yet and i've seen these aluminium reflectors that can be installed across the joists to allow UFH. I was hoping i could then get more low level heat, at least upstairs, and help keep the tank stratified on colder days when i need to turn the flow up a bit, which at the moment destroys the statifiction.
    It's seems like a win-win situation as long as there are no reasons why the CH return cannot be used as UFH flow. Please feel free to correct or enlighten me!
    • CommentAuthorCWatters
    • CommentTimeNov 27th 2015
     
    What temperature is the rad return?
    • CommentAuthorjohnnyh
    • CommentTimeNov 27th 2015
     
    That's a good question! All i can assume is that it's too hot when the mixer is more than just barely open. The tank then drops from 85 at the top to 70 and beyond quite quickly.
  2.  
    Feel the temperature of the return, if it feels to hot to hold comfortably then its probably too hot, or get a pipe thermometer - they are quite cheap. As you have probably worked out already if the return is too hot or to fast then you will mess up the stratification.
    can you turn the flow rate down on the pump either by turning down the wick on the pump or by partially closing the valve that should be adjacent to the pump to facilitate changing the pump.
    By the way how big is the TS
  3.  
    Posted By: johnnyhI have ordered a tech 431 'steering' to control the CH mixer valve and in the meantime i have adjusted it right down which gives us a fairly low temp on the rads, not hot enough for a cold day. If i adjust the mixing valve back up, the tank destratifies.
    A 4 port mixer valve can help to minimise destratification by maximising the return temperature to the tank, but it may require you to use different take offs.

    Posted By: johnnyhOne solution i think would be some ufh circuits to cool the radiator return temperature but they would have to be fed from the radiator return to have this effect.
    The question is simply: Will this work?
    It depends. The flow rates, flow temperatures and thermal time constants are very different for radiators and UFH. If you're looking to dump huge amounts of heat into a building that is unlikely to over-heat then it will work. If you're looking for precise control of room temperatures in a well insulated building then it doesn't sound like the right way forward.

    David
    • CommentAuthorjohnnyh
    • CommentTimeNov 27th 2015
     
    Hi Peter in Hungary, it's a 2000 litre store, and the CH return is not too hot to hold when i feel it but when it seems to really destratisfy is the morning after the evening when i fire up and i'm not able to check it those mornings when the CH pump starts at 6am (too lazy,you see).

    Hi Davidfreeborough, i've got a 3 way mixing valve installed which works ok as long as i keep it very much closed, i.e. quite low rad temps, and i've now ordered a motorisation and thermomatic control system (the tech 431) so would a 4 way mixer be better? my house is quite well insulated but due to it's construction, certainly not averse to having a bit of heat dumped into it and i don't think we'll ever overheat!
  4.  
    If it de-stratifies in the mornings then if you have TRV everywhere and they are open (to get the temp up to daytime temp. then perhaps at that time you have a high flow around the system which will be shoving a lot of return water into the TS and so causing turbulance - just a thought.
    I had a concern about my TS (also 2000lts) about disturbing the stratification either from the CH or the DHW that is a separate tank along side the TS. To avoid the possibility I put a return manifold on the outside of the TS to allow the return water to enter at its own temperature - tests after installation showed it works, but it would be difficult to retrofit. see here http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=13082&page=1#Item_8
    • CommentAuthorJonG
    • CommentTimeNov 28th 2015
     
    I have an UFH circuit plumbed off the return, but this is from a gas boiler. The ramp down to lowest modulation is still too high for the house heat loss, so effectively the UFH circuit acts as a crude buffer, by the time the rads have dumped their heat the flow temp is roughly OK for the UFH but i have never tested it and in reality there should be a 20 degree delta on the rads and 7 on the UFH.

    It works in so far that the house and room on UFH (pug screed under chip and laminate) gets to temp fine, but the boiler still cycles a bit in warmer temps.
    • CommentAuthorringi
    • CommentTimeNov 28th 2015
     
    Rather then controlling the mixer based on the flow temperature to the redactors, what about controlling it based on the return temperature?

    When the building is colder, the return temperature will be lower, so more heat will then be given to the building.

    You may also do better letting the heating run all night, so it does not need lots of water to heat up in the morning.
    • CommentAuthorjohnnyh
    • CommentTimeNov 29th 2015
     
    So it can be done Jon. Thanks for that info, i will definitely try and get some UFH installed. I am also going to have a proper look at your manifold Peter although i don't quite understand how it works exactly.
    When my new valve controller arrives i will look into the possibility of it controlling the return temp but then i also want to be able to crank up the heat through the rads without going ouside to the boiler shed and manually changing the mixer valve setting. The controller seems to be multifunctional so maybe it will be able to do both in some way. I'll post some info when it arrives and i've got to grips with it.

    Thnks for all the good ideas!

    John.
    • CommentAuthorbxman
    • CommentTimeNov 29th 2015
     
    Posted By: johnnyhThe thing is the rads are already installed as i have changed over from an oil fired system. I am going to add one or two more rads where i have space but the upstairs floors are not finished yet and i've seen these aluminium reflectors that can be installed across the joists to allow UFH. I was hoping i could then get more low level heat, at least upstairs, and help keep the tank stratified on colder days when i need to turn the flow up a bit, which at the moment destroys the statifiction.
    It's seems like a win-win situation as long as there are no reasons why the CH return cannot be used as UFH flow. Please feel free to correct or enlighten me!


    Is it new or a refurb ?

    No expert but AIUI
    UFH upstairs is not normally necessary if you have the ground floor cosy.
    Can you try for 1 winter as see how it works out ?
    • CommentAuthorgyrogear
    • CommentTimeNov 29th 2015
     
    "I was hoping i could then get more low level heat, at least upstairs"

    Have you considered a radiant wall, instead of a radiant floor ?

    gg
    • CommentAuthorjohnnyh
    • CommentTimeNov 29th 2015
     
    Its a refurb, a long, slow refurb...

    It's an old stone building with no south-facing windows, (but no north-facing either) and high ceilings. It's not an easy task to heat this place. The ground floor is not that cosy and if the UFH upstairs might mean i could turn off one or two rads upstairs then that may also help the stratifcation in the store.

    Radiant wall? The same set up as the floor? ( but in the wall of course).

    I could wait til after the winter for the UFH and it might well happen that way anyway. What i'm searching for really is a way to make the store last 2 days in the milder weather.
  5.  
    Posted By: johnnyhI am also going to have a proper look at your manifold Peter although i don't quite understand how it works exactly.

    It works on the same principal as the stratification within the TS. When you push 60 deg. water into a TS which is 40 deg at the bottom then the 60 deg. water will rise up until it reaches an equal temperature but there will be some mixing as it does so. The faster you shove the return water in the more mixing there will be. Putting a manifold on the outside allows return water to rise up the outside of the TS and enter at its own temperature level which eliminates the mixing inside the TS.

    The return pipe has an elbow at the base so that the return flow is heading up the manifold before getting to the first entry point (the alternative would have been to tee off the return up into to the manifold but this would/could have allowed the return to 'inject' into the TS and perhaps nullify the manifold).

    Reading about TSs before I put together mine I noticed that there were several varieties of built in baffle plates, spreaders and alike along with various discussions about the importance of stratification and I had never thought stuffing 60+ deg water into the base of a TS at 40 deg would help stratification. So I took a punt and ordered the TS to be made. The plumber who did the installation work had never seen anything like it and doubted it would make any difference and was surprised when I showed him the figures. (I was also surprised and relieved that it works as well as the figures show)

    BTW if its an old stone building can you put on EWI. it will help LOTS
    • CommentAuthorringi
    • CommentTimeNov 29th 2015
     
    Have a look at "fan convectors" e.g. http://www.myson.co.uk/products/ivector.asp I think it will be easy to replace your radiators with them without doing much plumbing and they will run with lower water temperatures that will let you get more heat out of your store.
    • CommentAuthorringi
    • CommentTimeNov 29th 2015
     
    One or two fun converters, something like http://www.myson.co.uk/products/fan_convectors.asp will let you get more heat out of your system without having to change your mixer valve setting. Just turn them on when your normal radiators are not giving enough heat. (Maybe even run them on the return water from your normal radiators.)
    • CommentAuthorgyrogear
    • CommentTimeNov 30th 2015 edited
     
    Hi again...

    Posted By: johnnyhi'm not really getting more than a day's worth of heating per charge and i had hoped for maybe two days when the weather is mild


    Couple of questions:
    what is the heating requirement (at the moment, not when you're finally finished...)
    what is the power rating of the wood stove ?
    what is the power when the TS is fully charged ?
    how many days' HR can fit in the TS ?
    ======
    Posted By: johnnyhIt's an old stone building with no south-facing windows, (but no north-facing either) and high ceilings. It's not an easy task to heat this place.


    Great ! sounds like the perfect place for a RW...

    You might find THIS interesting...
    https://www.aecb.net/forum/index.php?topic=5138.0

    gg
  6.  
    Posted By: johnnyhHi Davidfreeborough, i've got a 3 way mixing valve installed which works ok as long as i keep it very much closed, i.e. quite low rad temps, and i've now ordered a motorisation and thermomatic control system (the tech 431) so would a 4 way mixer be better?
    It depends upon the flow rates & how the system is connected. If you have the radiators with TRVs connected in parallel with multiple zone UFH then it can help to maintain a more constant flow rate from the thermal store. As the TRVs close then more of the flow will go via the 4 port valve's "bypass" route back to the thermal store. The return from the UFH is mixed with this "bypass" bringing it closer to the thermal store flow temperature. However, you need to position the take-offs, manifolds, etc to make sure this higher flow rate doesn't cause destratification. A 3 port mixing valve doesn't lift the UFH return temperature up towards the thermal store flow temperature, but it minimises the flow from the thermal store which will help to reduce destratification. Which approach is best will depend upon the thermal store, the take-offs chosen, the flow rates, the flow temperatures, the manifold arrangement, etc.

    David
    • CommentAuthorringi
    • CommentTimeNov 30th 2015
     
    Are there not two types of 4 port values?

    I think one type mixes the return, mid taping of thermal store and top taping of thermal store to get the flow. So the top of the store is only is used if the mid of the store is too cold.

    I think the other type keeps a constant flow rate in a boiler, while deciding how much of that flow goes into the UFH, so that the bypass does not operate on the boiler.
  7.  
    The 4 port mixing valve I thinking of behaves as follows:

    https://www.underfloorheatingsystems.co.uk/2013/04/how-does-underfloor-heating-cope-with-high-boiler-flow-temperatures/

    Sounds like its the second of the two types you describe.

    David
    • CommentAuthorjohnnyh
    • CommentTimeDec 1st 2015
     
    I don't actually know my heating requirements. The radiators (mostly cast iron) will keep us warm as long as they are on and they are not really that big, perhaps 700mm x 1000mm or 700 x 1200mm as an average size and of the 4 column variety.
    The store is 2000 litres and boiler is 40kw.

    The pipework and rads have been installed for a few years now so i am willing to 'tap in' to the system where it's easy to do so but a full redesign a different story.
    • CommentAuthorjohnnyh
    • CommentTimeDec 1st 2015
     
    The boiler is only a metre from the store and the pipes are all lagged. I don't have a laddomat sensor, it's switched on and off by the boiler controller (the ekoster).

    if the the idea of the batch burning/laddomat/thermal store combo was to burn hot and fast to get every last bit of energy then the pump should be switched on and off to achieve this and the fan should run all the time unless there is nowhere left for the heat to go (store full) or there is a problem and the boiler needs to shut down. This doesn't seem very complicated to me but it is too complicated for the ekoster. Maybe it's just a question of pump switching hysteresis.

    i will try a few more different settings and methods and see what that does but maybe i do need some data logging as i'm getting a bit buried under bits of paper with temperatures and times scribbled on!
  8.  
    Posted By: johnnyhif the the idea of the batch burning/laddomat/thermal store combo was to burn hot and fast to get every last bit of energy then the pump should be switched on and off to achieve this and the fan should run all the time unless there is nowhere left for the heat to go (store full) or there is a problem and the boiler needs to shut down. This doesn't seem very complicated to me but it is too complicated for the ekoster. Maybe it's just a question of pump switching hysteresis.

    The job of the Laddomat is to keep the boiler at a high enough temperature so that proper combustion can take place. It does this by recirculating the water within the boiler until there is sufficient heat to pass to the thermal store whilst maintaining the boiler temperature. The Laddomat pump must run all the time and should stay on until the boiler has run out of fuel otherwise the recirculation can not happen.

    If you do stop the pump on the Laddomat the construction is such that a valve will open and allow gravity circulation to the detriment of boiler temperature. If the boiler /TS pipework does not facilitate gravity circulation then the boiler will overheat triggering what ever mechanism the boiler has to manage over heating.

    The fan driving the combustion however can switch on and off and the fan will run until a pre-set maximum temp. is reached when it should switch off until the temp. falls whereupon it should start up again. The other event that should switch off the fan is 'out of fuel'. This should also switch off the Laddomat pump. The out of fuel signal is often generated by a flue thermostat although on my boiler this is sensed by the boiler dropping below a pre-set level (70deg in my case) and this low temp. signal is overridden during the start phase.
    • CommentAuthorjohnnyh
    • CommentTimeDec 2nd 2015 edited
     
    Every time the fan stops i assume there are combustible gases escaping through the chimney without igniting. I know the laddomat is there to protect the boiler against undertemperature but it also inadvertently controls it's maximum temp as well so it is the most efficient way to control the temp. of the boiler, i.e. keep it in the 85-90 degree zone.
    Thinking about it, perhaps the reason my temperature swings so much if i set the 'pump on' to 86 or 87 is because the laddomat thermostat, i'm assuing it's a wax type thing, takes a minute or two to open and close. So when the boiler control turns the pump on there is a delay in which time the boiler hits 91 (fan stops) and then once the incoming cooler water has cooled the boiler a bit, there is another delay while the laddomat closes again and the temp drops to 79 and outside the 'zone'. Could i have a slow thermostat cartridge?
    • CommentAuthorgyrogear
    • CommentTimeDec 2nd 2015 edited
     
    "I don't actually know my heating requirements. "

    You are not alone (I suspect that many people install (expensive) heating systems without giving it a single thought...).
    ================
    You could do a rule-of-thumb HR calculation by estimating (or counting...) what installed power you actually have - is it enough to keep the place warm, Y or N... etc.
    or , "what would you put on a dream-list ?" (such as 10 x 1-kW radiators, one in each room etc. etc.).

    Otherwise, some smart & easy-to-use calculators online...
    such as...
    https://www.chromalox.com/resources-and-support/calculators/comfort-heater.aspx

    ======
    Otherwise, concerning your thermal store, a few details would be useful:
    what dimensions, actually?

    (to my mind, it does not sound like it is stratifying very much at all)
    for optimal stratification, it needs to be T-A-L-L... and "not flat"...

    gg
    • CommentAuthorjohnnyh
    • CommentTimeDec 2nd 2015
     
    I did a quick calc on the chromalox site for my worst room, it has an external door, two windows and two internal doors. It came up with 1283w/h which doesn't sound that much but i suppose if i added it all up it would be quite a bit. For a 2-minute fag-packet-style calc i would multiply that by maybe 2.5 to cover the downstairs and the same floor space upstairs but perhaps better conditions so times 2 for that. So that makes 1283 x 4.5 = 5774w/h heating required. So i suppose that's too much for a 2000 litre store then at the worst time of the year.

    my store is the correct shape, it is approx 2.8m high and 1.1m diameter and it does stratify. In fact the very first firing when the water inside was 16 degrees, we were amazed that the top could be at 82 and the middle and bottom had not moved even 0.1 degrees. The problem of destratification comes as soon a i take heat at any kind of rate which will hopefully be helped by my motorised mixer control.
  9.  
    Posted By: johnnyhEvery time the fan stops i assume there are combustible gases escaping through the chimney without igniting. I know the laddomat is there to protect the boiler against undertemperature but it also inadvertently controls it's maximum temp as well so it is the most efficient way to control the temp. of the boiler, i.e. keep it in the 85-90 degree zone.
    Thinking about it, perhaps the reason my temperature swings so much if i set the 'pump on' to 86 or 87 is because the laddomat thermostat, i'm assuing it's a wax type thing, takes a minute or two to open and close. So when the boiler control turns the pump on there is a delay in which time the boiler hits 91 (fan stops) and then once the incoming cooler water has cooled the boiler a bit, there is another delay while the laddomat closes again and the temp drops to 79 and outside the 'zone'. Could i have a slow thermostat cartridge?


    The boiler fan will (should) only stop when the upper temperature is reached. Yes combustible gasses will go up the chimney but the only way to stop this is to keep the fan running regardless of temp., boiling or any other event in the boiler. Don’t forget that when the fan is not running the fire is not out and so most of the combustible gasses will burn, you just won’t have the efficiency of the gasification.
    For what its worth the fan on my boiler runs continually until the boiler reaches the high set temp. which is about 88deg. At this time most of the TS is at the same temp.

    The Laddomat has a ‘wax type thing’ as a thermostat and as such gives a proportional control. The Laddomat controls the temp. of the water going into the base of the boiler. The temp. of the boiler at the outflow will be higher.

    The Laddomat installation instructions say the the unit should be as close as possible to the boiler, mine is installed at the base of the boiler with only a maintenance stopcock between it and the boiler.

    If the Laddomat pump is running continually then the thermostat will proportionally control the input (return) temp. of the boiler without temp. swings on the input flow.

    The fan should run continuously until the top set temp is reached and it should then stop to avoid over heating the boiler. When the temp. drops the fan will start again (start point governed by the hysteresis of the thermostat switch) The output temp. will fluctuate once the top set temp. is reached due to the hysteresis of the thermostat switch

    So.....the Laddomat provides a stable return temp. for the boiler by variably mixing the return from the TS with recycled water from the boiler output. This can only happen if the Laddomat pump is running – therefore it should run continuously. The control temp. of the Laddomat is adjusted by changing the thermostat insert within the unit for one of a different value. (easy DIY job)

    The combustion fan should run continuously until the top set temp. is reached, it should then cycle under control of the boiler thermostat.

    In practice on my boiler the Laddomat runs continuously until the boiler runs out of fuel (low temp. thermostat)
    The fan runs continuously until top temp. is reached and then cycles. It is also switched off by the low temp. thermostat.
    The TS rises in temp. gradually with the boiler running at a higher temp. until the TS reaches the temp of the boiler (which is controlled by the Laddomat) then both rise together until there is no more fuel.
    If the boiler reaches the top temp. the fan stops but the Laddomat continues to run, removing any heat from the boiler

    With advantage my system would benefit from a flue thermostat to signal end of fuel which would avoid the Laddomat pumping whilst the boiler temp. is falling at end of fuel. This would save some loss of heat back through the boiler........its on the ‘to do’ list.
  10.  
    Posted By: johnnyhThe problem of destratification comes as soon a i take heat at any kind of rate which will hopefully be helped by my motorised mixer control.


    That will be because you are stuffing too much water at too high a temp. into the base of the TS and the turbulence created damages the stratification.

    Most systems (here) use a mechanical 3 way valve (adjustable temp.) to mix the CH return with the output from the TS to lower the feed temp. to the CH (and also to reduce the amount taken from and going back to the TS) The lower feed temp. to the CH will lower the return temp. and combined with the reduced flow back to the TS will aid stratification.

    This however all assumes that the radiators are sufficiently large to give the required heat at a lower flow and return temp. If your rads are sized so that you need 80deg. in with a 10-15deg. drop to get out sufficient heat then you will be stuffing 65 - 70deg back into the TS with almost no mixing and the stratification won't stand a chance.
   