Green Building Forum - warm flat roof joining rear dormer wall - achieving continuous layer of insulation? Tue, 19 Dec 2023 08:36:21 +0000 http://www.greenbuildingforum.co.uk/newforum/ Lussumo Vanilla 1.0.3 warm flat roof joining rear dormer wall - achieving continuous layer of insulation? http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=17775&Focus=300723#Comment_300723 http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=17775&Focus=300723#Comment_300723 Mon, 13 Mar 2023 21:01:23 +0000 number_thirty_three
In the attached photo (of my own handiwork), what I'm unclear about is:

how to make the insulation continuous between the warm flat roof construction and the vertical rear wall. In my drawing, there's a big gaping cold bridge between the fascia board and the inside.

I can see a couple of options, but is there a 'best practice' for this fairly common problem statement?

All the manufacturer's details show just one plane of detail - the warm flat roof, or a timber frame wall, there is a paucity of details showing the joins!

Options I've come up with:

1) Simple but probably won't work - Add a chunk of PIR at the end of the joists to make it wrap around - and hope that the fascia can be attached to that through to the joist end

2) Kinda complicated - add a modest depth of insulation to the end of the joists (say, 20mm) so that the fascia can be screwed through into the joist ends still; then place 150mm or more inbetween the joists where the joists overhang; then insulate the external side of the wall plate atop the stud wall.

(also, welcome any constructive criticism on any other elements of the detail)]]>
warm flat roof joining rear dormer wall - achieving continuous layer of insulation? http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=17775&Focus=300730#Comment_300730 http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=17775&Focus=300730#Comment_300730 Tue, 14 Mar 2023 11:11:25 +0000 djh
Anyway, the wall insulation needs to go up and meet the roof insulation. There are two main thermal bridges through its path. The wall plate and the joists. The wall plate could be made of some strong insulation material I suppose but that would likely be expensive. Which of the upright studs is the load-bearing one? Normally it's the inside one, so if we assume that then the wall plate could be moved inboard so it leaves a clear space for the insulation to pass upwards outboard of it. The joists passing through the rising insulation are probably a tolerable repeating thermal bridge; it all depends on exactly what number you're trying to achieve. You can make the wall insulation thicker within the joist area; full-fill out to the end of the joists maybe. Are the ends of the joists exposed or is there a soffit?]]>
warm flat roof joining rear dormer wall - achieving continuous layer of insulation? http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=17775&Focus=300735#Comment_300735 http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=17775&Focus=300735#Comment_300735 Tue, 14 Mar 2023 15:06:57 +0000 number_thirty_three Posted By: djhI'm not sure what the red line is? Nor whether the joists are exposed in the room or if there is some kind of ceiling?

red line is to show the a/t line; yes there'll be some kind of ceiling and wall lining.

Anyway, the wall insulation needs to go up and meet the roof insulation. There are two main thermal bridges through its path. The wall plate and the joists... The joists passing through the rising insulation are probably a tolerable repeating thermal bridge; it all depends on exactly what number you're trying to achieve.


Yes, exactly. I'm aiming for AECB standard, not quite Enerphit.

The wall plate could be made of some strong insulation material I suppose but that would likely be expensive.


Do you mean something like foamglas or perinsul?

Which of the upright studs is the load-bearing one? Normally it's the inside one, so if we assume that then the wall plate could be moved inboard so it leaves a clear space for the insulation to pass upwards outboard of it.

yes, makes sense.

You can make the wall insulation thicker within the joist area; full-fill out to the end of the joists maybe. Are the ends of the joists exposed or is there a soffit?


The ends will not be exposed - there'll be a soffit. Had considered placing insulation on end of and underside of joist - the challenge is just about ensuring the fascia and guttering can still be secured through to the joists...]]>
warm flat roof joining rear dormer wall - achieving continuous layer of insulation? http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=17775&Focus=300737#Comment_300737 http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=17775&Focus=300737#Comment_300737 Tue, 14 Mar 2023 15:40:48 +0000 GreenPaddy
Ceiling Joists don't have to run through. Insert end trimmer in timber to make a robust sandwich, into which the facia can be fixed. That's outside the insulation envelope.
Insert insulation between the ceiling joists directly above the wall head.
Add a cover layer of insulation over the joist tails and the wall head binder, with a batten fixed over that to give you a soffit fixing.

Cat number one skinned. More cats for skinning no doubt :bigsmile:]]>
warm flat roof joining rear dormer wall - achieving continuous layer of insulation? http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=17775&Focus=300740#Comment_300740 http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=17775&Focus=300740#Comment_300740 Tue, 14 Mar 2023 16:57:02 +0000 number_thirty_three Posted By: GreenPaddyMaybe something like this?

Ceiling Joists don't have to run through. Insert end trimmer in timber to make a robust sandwich, into which the facia can be fixed. That's outside the insulation envelope.
Insert insulation between the ceiling joists directly above the wall head.
Add a cover layer of insulation over the joist tails and the wall head binder, with a batten fixed over that to give you a soffit fixing.

thanks GreenPaddy, that's really helpful]]>
warm flat roof joining rear dormer wall - achieving continuous layer of insulation? http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=17775&Focus=300744#Comment_300744 http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=17775&Focus=300744#Comment_300744 Tue, 14 Mar 2023 20:02:58 +0000 djh Posted By: number_thirty_threeDo you mean something like foamglas or perinsul?
No, Compacfoam or another of the more dense EPS products.

Posted By: number_thirty_threered line is to show the a/t line
Why isn't the airtight line also the VCL?

Posted By: GreenPaddyCeiling Joists don't have to run through.
That's probably true as long as the overhang isn't too much. My structural engineer insisted on sprockets underneath a 600 mm overhang. But if they don't and if the wall plate is moved inboard then the whole thing simplifies to the existing wall insulation being carried straight up to meet the roof insulation. No extra faffing required.]]>
warm flat roof joining rear dormer wall - achieving continuous layer of insulation? http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=17775&Focus=300747#Comment_300747 http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=17775&Focus=300747#Comment_300747 Tue, 14 Mar 2023 20:56:02 +0000 number_thirty_three Posted By: number_thirty_threered line is to show the a/t lineWhy isn't the airtight line also the VCL?

Because in all warm roof construction details I have seen, there's a VCL on the top of the structural deck under the insulation. And I couldn't see how on earth it would be possible to tie that into the internal a/t layer on the walls (not just that rear wall but all the internal adjoining walls... so then thought perhaps better to have an internal a/t layer that is fully continuous as well.]]>
warm flat roof joining rear dormer wall - achieving continuous layer of insulation? http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=17775&Focus=300755#Comment_300755 http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=17775&Focus=300755#Comment_300755 Wed, 15 Mar 2023 12:56:55 +0000 GreenPaddy
Why do manuf details show it immed under the roof deck??? They don't know what your detailing will be, so show it to make sure you know it is BELOW the insulation layer. You can move it further inboard if you wish, if it suits your detail. I've seen arch's with the VCL above joists, and then they wrap the VCL over the joist ends and back in again, putting the VCL at the joist ends outside the insulation - wrong.]]>
warm flat roof joining rear dormer wall - achieving continuous layer of insulation? http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=17775&Focus=300763#Comment_300763 http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=17775&Focus=300763#Comment_300763 Thu, 16 Mar 2023 09:33:25 +0000 number_thirty_three Posted By: GreenPaddyYour VCL needs to be continuous, I would argue, to meet the wall VCL. No need for two layers. The VCL at your red line is the correct place. There's no moisture being generated above that red line for any other layer to control. The VCL should pretty much always be as far in to the building (warm side) as poss, though usually outboard of service battens, so services don't penetrate it.

Why do manuf details show it immed under the roof deck??? They don't know what your detailing will be, so show it to make sure you know it is BELOW the insulation layer. You can move it further inboard if you wish, if it suits your detail. I've seen arch's with the VCL above joists, and then they wrap the VCL over the joist ends and back in again, putting the VCL at the joist ends outside the insulation - wrong.

That's really helpful GreenPaddy - thanks. ISWYM about being able to move it inboard - makes perfect sense. It's one of those situations where I've grasped some of the principles of this stuff - continuous layer of insulation and vcl but not quite got the confidence to ignore a manufacturer's detail!]]>