Green Building Forum - DIY MVHR design and calculations Tue, 19 Dec 2023 08:26:25 +0000 http://www.greenbuildingforum.co.uk/newforum/ Lussumo Vanilla 1.0.3 DIY MVHR design and calculations http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=14912&Focus=254330#Comment_254330 http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=14912&Focus=254330#Comment_254330 Wed, 15 Feb 2017 08:54:23 +0000 MarkyP
So to get started with the first questions. I've read the part F tables with both minimum rates and boost rates for wet rooms.The total internal floor area is 258.5m2 which gives me a background (based on 0.3l/s) rate of 77l/s. This I know is considered high and advice is to after signoff experiment with lower system speeds but will work to this to size the system. My first question is how to use this overall requirement to work out air flow through a given duct. How do you divvy up the 77 l/s across my 5 extracts and 7 supplies?

next question is do I need to look for a unit which can cater for background 77l/s plus boost extract rates from wet rooms which is another 45l/s? I know I will also need to allow for pressure loss but, as a starting point, is worst case ventilation rate the system will need to deliver 125l/s? (77 + 45l/s)

I will be working on calculations spredsheet which can be viewed by anyone and which I will update as I go.

https://docs.google.com/spreadsheets/d/1NkEv0bN9S3EUHkfL0H3XfZp7HWId4t69-8Ynhz4xFmw/edit#gid=724798357]]>
DIY MVHR design and calculations http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=14912&Focus=254334#Comment_254334 http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=14912&Focus=254334#Comment_254334 Wed, 15 Feb 2017 09:39:26 +0000 gravelld DIY MVHR design and calculations http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=14912&Focus=254338#Comment_254338 http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=14912&Focus=254338#Comment_254338 Wed, 15 Feb 2017 11:24:51 +0000 DarylP DIY MVHR design and calculations http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=14912&Focus=254341#Comment_254341 http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=14912&Focus=254341#Comment_254341 Wed, 15 Feb 2017 12:01:20 +0000 djh
Then tweak all the figures so they are practical for whatever ducting system you are using and check all the flow rates are low enough to be quiet. Make sure the areas without vents (e.g. halls) are on a transit path for air and if not add vents and redistribute the flows.

You've only listed four extract rooms but I see five in your overall list of rooms. I also don't see a plant room anywhere listed - do you have one?]]>
DIY MVHR design and calculations http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=14912&Focus=254342#Comment_254342 http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=14912&Focus=254342#Comment_254342 Wed, 15 Feb 2017 12:01:57 +0000 Ed Davies
Isn't the flow required the greater of the sum of the supply rooms and of the extract rooms, rather than the total of both?

Edit to add: page 2 of this thread: http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=13405 though the whole thread's worth a skim.]]>
DIY MVHR design and calculations http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=14912&Focus=254344#Comment_254344 http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=14912&Focus=254344#Comment_254344 Wed, 15 Feb 2017 12:42:36 +0000 MarkyP
Ed- yes, I have a copy of Wookey's sheet. And thanks for the discussion reference. More questions will no doubt follow!

thanks both.]]>
DIY MVHR design and calculations http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=14912&Focus=254346#Comment_254346 http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=14912&Focus=254346#Comment_254346 Wed, 15 Feb 2017 13:02:02 +0000 djh Posted By: Ed DaviesIsn't the flow required the greater of the sum of the supply rooms and of the extract rooms, rather than the total of both?
Doesn't quite work like that . See Table 5.1a and 5.1b of Part F, especially the footnotes, and then 5.2d. The minimum whole dwelling supply ventilation rate is based on the total area, not just the supply area. I have no idea why.

MarkyP, step 2 of 5.2d. Add up the individual room rates for ‘minimum high rate’ from Table 5.1a. Then just multiply each individual rate by whatever factor is required to make the total equal the rate determined in step 1. They will all get changed again by the practicalities of ducting. You just need to make sure you exceed the minimums in the regs.]]>
DIY MVHR design and calculations http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=14912&Focus=254350#Comment_254350 http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=14912&Focus=254350#Comment_254350 Wed, 15 Feb 2017 13:46:09 +0000 MarkyP
the supply room volumes - bit of a fiddle as many are room in roof with odd shapes. Any reason to not just proportion out the supply based on supply room floor area?]]>
DIY MVHR design and calculations http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=14912&Focus=254351#Comment_254351 http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=14912&Focus=254351#Comment_254351 Wed, 15 Feb 2017 13:59:37 +0000 ringi Posted By: djhMake sure the areas without vents (e.g. halls) are on a transit path for air

In most cases this is not important, as gases do defuse about and mostly sort themselves out.

Posted By: MarkyPah, got it. So my minimum high extract rates sum to 45 l/s, I'll just scale those up by an adjustment factor until they match the 77 l/s supply.


Do don't need to sale them up, you can just increase any one or more of them so as to get them to match the required supply. This can be done so as to make best use of duct sizes and/or based on your wishes, e.g. if you are going to dry lots of washing in the utility you may give it a higher extract, but leave a shower rooms that will get little use with the part F minimal requirement.

I think to much fess is made about getting all the airflows correct between rooms etc, and provided they are reasonable the building will just sort itself out. (Assuming you don’t have close fitting auto closing doors on your rooms!)]]>
DIY MVHR design and calculations http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=14912&Focus=254353#Comment_254353 http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=14912&Focus=254353#Comment_254353 Wed, 15 Feb 2017 14:27:13 +0000 RobL The MVHR boosts if CO2 is high, and controls the humidity to 50%. With 4 people + washing + cooking, it's easy to keep humidity to 50%, but CO2 can still get to 1000ppm. So I think the extra humidity is handy with MVHR - it allows higher fan speeds (so keeping CO2 down) without drying out the house excessively, which isn't great for the skin. We live in Cambridge, if relevent.]]> DIY MVHR design and calculations http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=14912&Focus=254357#Comment_254357 http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=14912&Focus=254357#Comment_254357 Wed, 15 Feb 2017 17:28:26 +0000 ringi Posted By: RobLI originally had an MVHR extract in our drying room, and found it took days to dry stuff.

Was your drying room cooler then the rest of the home?]]>
DIY MVHR design and calculations http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=14912&Focus=254359#Comment_254359 http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=14912&Focus=254359#Comment_254359 Wed, 15 Feb 2017 18:04:04 +0000 barney
By any metric that's still representative of good air quality in an occupied space

Regards

Barney]]>
DIY MVHR design and calculations http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=14912&Focus=254360#Comment_254360 http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=14912&Focus=254360#Comment_254360 Wed, 15 Feb 2017 18:13:53 +0000 joe90
I find this surprising, others have said drying clothes in a room with extract works well, I wonder what is different or have I missed something?]]>
DIY MVHR design and calculations http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=14912&Focus=254362#Comment_254362 http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=14912&Focus=254362#Comment_254362 Wed, 15 Feb 2017 19:51:19 +0000 Peter_in_Hungary Posted By: ringiI think to much fess is made about getting all the airflows correct between rooms etc, and provided they are reasonable the building will just sort itself out. (Assuming you don’t have close fitting auto closing doors on your rooms!)
Isn't that the basis for which the freshR is supposed to work - just on an even cruder basis, one input and one extract.]]>
DIY MVHR design and calculations http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=14912&Focus=254364#Comment_254364 http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=14912&Focus=254364#Comment_254364 Wed, 15 Feb 2017 20:03:23 +0000 Ed Davies Posted By: joe90I find this surprising, others have said drying clothes in a room with extract works well, I wonder what is different or have I missed something?I don't think it's surprising, the RH will be lower in a room with a supply. That's likely more significant than a slightly lower temperature.]]> DIY MVHR design and calculations http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=14912&Focus=254365#Comment_254365 http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=14912&Focus=254365#Comment_254365 Wed, 15 Feb 2017 20:04:44 +0000 MarkyP Posted By: Peter_in_Hungary
Posted By: ringiI think to much fess is made about getting all the airflows correct between rooms etc, and provided they are reasonable the building will just sort itself out. (Assuming you don’t have close fitting auto closing doors on your rooms!)

Isn't that the basis for which the freshR is supposed to work - just on an even cruder basis, one input and one extract.

possibly for a small dwelling. for my house they proposed 3 fresh-r units and I think 5 room to room fans to achieve adequate airflow which made the product very expensive compared to ducted MVHR systems.]]>
DIY MVHR design and calculations http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=14912&Focus=254368#Comment_254368 http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=14912&Focus=254368#Comment_254368 Wed, 15 Feb 2017 21:28:49 +0000 djh Posted By: ringi
Posted By: djhMake sure the areas without vents (e.g. halls) are on a transit path for air


In most cases this is not important, as gases do defuse about and mostly sort themselves out.
I don't want to get into an argument so I suggest anybody reading this thread reads the research for themselves and forms their own opinion.]]>
DIY MVHR design and calculations http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=14912&Focus=254377#Comment_254377 http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=14912&Focus=254377#Comment_254377 Wed, 15 Feb 2017 22:46:30 +0000 RobL
Was your drying room cooler then the rest of the home?</blockquote>

No - the whole house is a similar 16-20degC, depending on the sex of who you ask :-)

I think it's just low RH air dries stuff faster than 50% RH air.]]>
DIY MVHR design and calculations http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=14912&Focus=254388#Comment_254388 http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=14912&Focus=254388#Comment_254388 Thu, 16 Feb 2017 02:56:52 +0000 wookey Posted By: gravelldGreat idea to work on an openly visible sheet!

Mine has been openly visible for a year, of course :-)

http://wookware.org/files/MVHR.ods
http://wookware.org/files/MVHR.xlsx

And has the exciting feature of working offline. Bit quaint in this day and age, I know, but I actually think that's an advantage. But if Marky wants to make a google sheet rather than improve mine, that's cool too.

What you _really_ want for this is a visual design tool where you draw the layout and indicate segment sizes/types/connections, then a sheet does all the sums. It'd be a lot easier to drive than filling in lots of error-prone bits of sheet that bake in the layout. Not sure what the easiest way to do that is, so I didn't :-)]]>
DIY MVHR design and calculations http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=14912&Focus=254392#Comment_254392 http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=14912&Focus=254392#Comment_254392 Thu, 16 Feb 2017 08:20:15 +0000 MarkyP Posted By: wookey
Mine has been openly visible for a year, of course :-)

http://wookware.org/files/MVHR.ods
http://wookware.org/files/MVHR.xlsx

And has the exciting feature of working offline. Bit quaint in this day and age, I know, but I actually think that's an advantage. But if Marky wants to make a google sheet rather than improve mine, that's cool too.

What you _really_ want for this is a visual design tool where you draw the layout and indicate segment sizes/types/connections, then a sheet does all the sums. It'd be a lot easier to drive than filling in lots of error-prone bits of sheet that bake in the layout. Not sure what the easiest way to do that is, so I didn't :-)

your sheet has been a great help. I've already lifted some of the basic ideas and conversion calcs into mine. Rather than try to make a new version of yours, I'm finding it easier from a thought process point of view to build my own. And I had no easy way to share an Excel, where it's a doddle with google. Also I use google for a couple of reasons - anyone with a modern browser can view it, no need to download a sheet and open in bloated MS software. Another feature (admittedly not helpful here) is you could see me editing it in real time if you were viewing at the same time as I were working on the sheet, this is a powerful feature of google's Docs suite. In fact, if I changed the permissions to allow it, we could all be editing the sheet in real time. This can be really powerful in a buisness setting. Also it's worth adding that Google sheets is available offline, you just sync your google drive locally and work in a browser as normal.]]>
DIY MVHR design and calculations http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=14912&Focus=254393#Comment_254393 http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=14912&Focus=254393#Comment_254393 Thu, 16 Feb 2017 08:20:59 +0000 SteamyTea Posted By: wookeyWhat you _really_ want for this is a visual design tool where you draw the layout and indicate segment sizes/types/connections, then a sheet does all the sums.There is this to help with the drawing:

http://sketchup.engineeringtoolbox.com/hvac-components-to_16.html

And stuff of interest on this page:

http://www.engineeringtoolbox.com/ventilation-systems-t_37.html]]>
DIY MVHR design and calculations http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=14912&Focus=254397#Comment_254397 http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=14912&Focus=254397#Comment_254397 Thu, 16 Feb 2017 09:24:07 +0000 Ed Davies
No need for bloated MS software. Bloated open-source software (LibreOffice) will do the job equally badly. I doubt Wookey used anything from MS to create these sheets and I didn't need any to read and play with them.

I too worry that spreadsheets are too difficult to read and audit for anything which is not very simple. A visual ventilation design tool would be great, particularly if it could extract the geometry from a more comprehensive building design system, but often a simple program can make these sort of calculations quite readable:

https://edavies.me.uk/2014/04/heatloss/

(Readable enough that, on a quick look just now, I noticed that the window U values seem to be swapped: the bedroom windows will be 2G as they're escape windows (top hinged) whereas the remaining windows (in the warmer parts of the house) will be 3G centre hinged. You can get 3G top hinged but they're very expensive. Still, that overestimates the heat loss very slightly so it's a “safe” error.)]]>
DIY MVHR design and calculations http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=14912&Focus=254442#Comment_254442 http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=14912&Focus=254442#Comment_254442 Thu, 16 Feb 2017 16:50:31 +0000 MarkyP
I'm thinking of using the ubbink radial ducts, the semi cricular AE55SC looks good in terms of air speed for a given volume so using that to generate some more numbers. I've worked out the number of ducts and their lengths and and now looking at the air speed figures for each duct. I looked at the manufacturer data sheet, the air speed relationship to the volume of airflow is linear and works out at 1m/s per 19.6m3/h. So am I on the right track to use this to work out the air speed in each duct? I have the m3/h value for each duct and I've divided by 19.6 to get the airspeed. Unless I've missed something, the numbers look good - even with the system at full chat the worst duct is just over 3m/s. Only doubt is my crude calc doesnt allow for duct length which I have a nagging feeling I should have factored somehow, or is this just a case of balancing using restrictor rings to balance the flow across each duct at commissioning? Main goal at this point is to know the duct air speeds will be low from a noise point of view. next step is to work out the pressure side of things and then I can size the MVHR unit]]>
DIY MVHR design and calculations http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=14912&Focus=254444#Comment_254444 http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=14912&Focus=254444#Comment_254444 Thu, 16 Feb 2017 17:36:26 +0000 ringi DIY MVHR design and calculations http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=14912&Focus=254459#Comment_254459 http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=14912&Focus=254459#Comment_254459 Thu, 16 Feb 2017 20:17:33 +0000 djh Posted By: MarkyPI'm thinking of using the ubbink radial ducts, the semi cricular AE55SC looks good in terms of air speed for a given volume so using that to generate some more numbers.
My system uses the AE35 ducts and we only had to double up for the kitchen (with hindsight I probably would have put two extract vents in the kitchen instead of doubling up). My design meets the passivhaus design criteria, which are stricter than Part F when it comes to speed and noise, so I'm surprised that you need to go to AE55. Do you have enough vents?

Duct length, and the number of bends, is critical. With the Ubbink system, you don't balance anything at commissioning time, it is all done at design time. Which is just as well because changing a restrictor ring after everything is installed could well be extremely difficult. Ubbink have a spreadsheet that calculates everything.

Note that whilst the semi-rigid ducts provide a lot of flexibility in routing the ducts, you do need to consider the congestion at the distribution boxes and how you will route each duct out of that area. I was able to cross one duct over another in the space between the metal webs of my joists, which was essential.]]>
DIY MVHR design and calculations http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=14912&Focus=254486#Comment_254486 http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=14912&Focus=254486#Comment_254486 Thu, 16 Feb 2017 22:35:34 +0000 MarkyP Posted By: djh
Posted By: MarkyPI'm thinking of using the ubbink radial ducts, the semi cricular AE55SC looks good in terms of air speed for a given volume so using that to generate some more numbers.

My system uses the AE35 ducts and we only had to double up for the kitchen (with hindsight I probably would have put two extract vents in the kitchen instead of doubling up). My design meets the passivhaus design criteria, which are stricter than Part F when it comes to speed and noise, so I'm surprised that you need to go to AE55. Do you have enough vents?

Duct length, and the number of bends, is critical. With the Ubbink system, you don't balance anything at commissioning time, it is all done at design time. Which is just as well because changing a restrictor ring after everything is installed could well be extremely difficult. Ubbink have a spreadsheet that calculates everything.

Note that whilst the semi-rigid ducts provide a lot of flexibility in routing the ducts, you do need to consider the congestion at the distribution boxes and how you will route each duct out of that area. I was able to cross one duct over another in the space between the metal webs of my joists, which was essential.

the AE55 ducts gave me a reasonable air speed of 3m/s of less, albeit at the max regs requirement of 279m3/h. I dont expect to need to run boost at that rate in practice but thought I should cater for the worst case. I will have a play with the numbers of the smaller duct and see. Not sure how adding more vents would help me, I have enough in terms of coverage for supplies and extracts, but would be adding duct runs to allow me to use a narrower ducts, think I'd prefer fewer bigger ducts over more smaller.

The distribution boxes are proving to be a bit of a headache. I think I can make it work by buying the 24 port boxes which mean I can take ducts into three sides of each box and avoid a spagetti situation.

How do you access the Ubbink calculator? sounds interesting..]]>
DIY MVHR design and calculations http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=14912&Focus=254520#Comment_254520 http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=14912&Focus=254520#Comment_254520 Fri, 17 Feb 2017 14:04:12 +0000 ringi Posted By: MarkyPThe distribution boxes are proving to be a bit of a headache. I think I can make it work by buying the 24 port boxes which mean I can take ducts into three sides of each box and avoid a spagetti situation.

There is no reason you can't use more then one distribution box and connect them back to your MVHR unit with large rigid ducts.]]>
DIY MVHR design and calculations http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=14912&Focus=254531#Comment_254531 http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=14912&Focus=254531#Comment_254531 Fri, 17 Feb 2017 17:44:33 +0000 djh Posted By: ringi
Posted By: MarkyPThe distribution boxes are proving to be a bit of a headache. I think I can make it work by buying the 24 port boxes which mean I can take ducts into three sides of each box and avoid a spagetti situation.

There is no reason you can't use more then one distribution box and connect them back to your MVHR unit with large rigid ducts.
Interesting; I hadn't seen those new distribution boxes before. Do get the noise reduction option. I see they call the calculator 'a commissioning tool'. I think it will be much easier to use a single 24-port box as you suggest if you can make a feasible layout. Using multiple boxes would mean getting back into the bad old days of balancing calculations etc, as well as taking yet more space and extra expense.]]>
DIY MVHR design and calculations http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=14912&Focus=254535#Comment_254535 http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=14912&Focus=254535#Comment_254535 Fri, 17 Feb 2017 17:54:08 +0000 wookey
Hmm, pretty sure I haven't got one of those, and also sounds a lot like being dependent on a very nosey corporation (which exists by selling my data) for my software. Not at all keen on that. But you are right that the option does improve the functionality.

And yes of course I don't have MS office - that was written with Libreoffice calc. (I normally use Gnumeric, but that sheet found a major bug in named cells exported then imported via ODF).

I quite understand about having to re-write these things to actually understand them. Spreadsheet is pretty-much a write-only language, that only very recently acquired named-variables. It's vile, but handy.]]>
DIY MVHR design and calculations http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=14912&Focus=254548#Comment_254548 http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=14912&Focus=254548#Comment_254548 Fri, 17 Feb 2017 21:47:31 +0000 ringi Posted By: djhUsing multiple boxes would mean getting back into the bad old days of balancing calculations

Not if the ducts to them where oversized so they had no real effect on air flow rates.

Posted By: djhas well as taking yet more space


That depends on the layout, I expect that for a lot of homes, having separate boxes on each floor may save space as some of the boxes will fit between floor joists.]]>