Posted By: djhWhat I would like to see is a fi-wi heat exchanger used to improve the efficiency of a conventional system.And the FreshR control systems as well.
Posted By: djhI noticed that the brochure was clearly labelled for 'retrofit' as well. They don't seem to be targeting new build at all, most likely for the reasons you state. It's a useful option to consider against all the other possibilities. What I would like to see is a fi-wi heat exchanger used to improve the efficiency of a conventional system.We use FreshR's mostly in new builds, this PassivHaus competition was for retrofits.
Posted By: Viking HouseDucted MVHR is always on using 40% of the electricity costs in a Passive HouseWhy couldn't it be controlled-modulated/intermitent like the FreshR, if equiped with sophisticated sensing like the FreshR is?
Posted By: Viking HousePosted By: djhI noticed that the brochure was clearly labelled for 'retrofit' as well. They don't seem to be targeting new build at all, most likely for the reasons you state. It's a useful option to consider against all the other possibilities. What I would like to see is a fi-wi heat exchanger used to improve the efficiency of a conventional system.We use FreshR's mostly in new builds, this PassivHaus competition was for retrofits.
If you put the FiWi heat exchanger into a conventional MVHR ducted system then you lose the benefits of FreshR over ducted MVHR like:
Ducted MVHR is always on using 40% of the electricity costs in a Passive House, leading to a 50 year return on investment. 2 FreshR units use £5 worth of electricity per annum.
The heat-loss from a Passive House is equal to the heat-loss from ventilation
FreshR only ventilates occupied areas and slows to 10% when nobody's home, the downstairs unit snoozes when everyone is upstairs and vica-versa. The average occupancy levels in 10 Low Energy Houses tested in Holland last Winter with FreshR's fitted was 35%. The FreshR HRVs reduced the average ventilation rate from 0.3ACH to 0.12ACH while maintaining air quality, this reduced the heating demand by 50%, so FreshR HRV has the capacity to reduce the heating demand of a Passive House from 15kWh/m2.annum to 7kWh/m2.annum. We've agreed a 15% lower ventilation rate with the PassivHaus Institute but Peter Warm has conservatively calculated it at a 25% lower ventilation rate but its still being negotiated.
After balancing a ducted MVHR in a Passive House in 2008, (150m3 in, 150m3 out) I noticed that if an internal door is left open the balance went off by 10%, (ie it switched to 135m3 in, 165m3 out), with 0 degree external, 20 degree internal air temperature the return air temperature would drop from 17 degrees to 14 degrees when an internal door is opened. In the winter of 2007/2008 I visited 8 clients we'd built Passive Houses for and 3 had the Ducted MVHR switched off, soon after I met Jon Kristinsson who showed me the solution which was a self balancing unit fitted into the external wall or window.
I've an interest in this product so my opinions are biased!
Posted By: djhI just measured my MVHR. It's using 26 W, which I calculate to be 0.625 kWh/day or 228 kWh per year. My electricity consumption at the moment appears to be about 5 kWh/day, which is net of the PV's contribution i.e. lower than actual. I make that 12.5%. If we were also to include my winter consumption at the PH-allowed heating allowance of 15 kWh/m²/year or a bit over 2000 kWh/year that would bring it down to under 6% of consumption. So I'd be very interested to learn where your alleged 40% figure comes from?I measured a number using between 50W and 120W, (none as low as 26W, was this at a medium setting?) so 85W x 24 hours x 365 days = 745kWh/annum, with an average Passive House using 2,000kWh per annum, that's 37%.
Posted By: djhIn a PHPP if you look at the Monthly Method page in a 200m2 Passive House you'll see the heat loss from the floor, NSEW walls, roof, NSEW windows and ventilation. You'll also see the heat gains from windows, and appliances. The overall heatloss is 15kWh x 200m2 = 3,000kWh and the heat loss from ventilation is usually also 3,000kWh's, check it out its neither incorrect nor outrageous! Ducted MVHR has long been the weakest link in a Passive House!The heat-loss from a Passive House is equal to the heat-loss from ventilationThat simply isn't true, of course. The heat loss is the loss through the fabric (U-values etc), plus the infiltration loss, plus the ventilation loss. I can't be bothered doing the sums, because it's such an outrageously incorrect claim.
Posted By: djhMy MVHR is self-balancing and I wouldn't dream of turning it off, so I'm not entirely sure what the above rambling is trying to say. Some MVHR units are worse than others? Some MVHR units are installed wrongly? Some MVHR users do not have the system properly explained to them?Ramblings Explained:
Posted By: Viking HouseThe heat-loss from a Passive House is equal to the heat-loss from ventilation,
Posted By: djhThat simply isn't true, of course.