Home  5  Books  5  GBEzine  5  News  5  HelpDesk  5  Register  5  GreenBuilding.co.uk
Not signed in (Sign In)

Categories



Green Building Bible, Fourth Edition
Green Building Bible, fourth edition (both books)
These two books are the perfect starting place to help you get to grips with one of the most vitally important aspects of our society - our homes and living environment.

PLEASE NOTE: A download link for Volume 1 will be sent to you by email and Volume 2 will be sent to you by post as a book.

Buy individually or both books together. Delivery is free!


powered by Surfing Waves




Vanilla 1.0.3 is a product of Lussumo. More Information: Documentation, Community Support.

Welcome to new Forum Visitors
Join the forum now and benefit from discussions with thousands of other green building fans and discounts on Green Building Press publications: Apply now.




  1.  
    I have a roof that needs the insulation upgrading. The roof make-up in to out is
    T&G 12mm planking
    VCL
    100mm x 100mm rafters with mineral wool between
    20mm sarking boards
    battens and slates (concrete/asbestos)

    The plan is to remove the battens and slates and add
    50mm x 150mm (fixed vertically) with mineral wool between
    Breather membrane
    battens and new slates.

    Using Ubakus.de shows no problems - however if the internal VCL is removed then serious problems occur on the inside of the sarking boards if the internal RH goes above 50% and the external temp goes below +6.

    Up until now the place has been used as a holiday home with minimal to no winter usage but now the plan is to use it year around so interstitial winter condensation could be an issue. If the VCL was put up with the same work quality as the rest of the works then there will be holes and bad joins within the VCL

    I would rather not take down the T@G or remove the sarking boards due to the work and expense involved

    You read here about electricians and plumbers making holes in the VCL with gay abandon but how much damage (or poor installation) can be tolerated in a VCL before there is a danger of interstitial condensation?
    • CommentAuthorEd Davies
    • CommentTimeJun 13th 2020
     
    It seems odd to me that your additional layers would make the situation of your existing sarking boards worse as they should now be much warmer. OK, the breather membrane won't be as vapour open as the original build up but still …
  2.  
    Sounds like the sarking layer has inadvertently been treated as being low permeability in the calculation (or possibly the breather or slates have been) - or the batten gap has inadvertently been treated as not ventilated.

    Those 1D condensation calculations are a bit hit-and-miss, especially for roofs where the outside gets heated by the sun.

    Thought experiment: if there were no sarking layer and instead the rafters were solid and 250deep, everything else the same as proposed, would there be condensation somewhere in the middle of the rafters?

    Would there be a problem in that case, if the VCL were missing?

    Hope not, as my roof is like that!
  3.  
    Ed - the additional layers didn't make thinks worse. As original with the VCL there is condensation on the inside at the point of the rafters (= mould) and without the VCL the sarking boards get condensation up to 48% moisture content ( all at 65% RH internally)
    With the additional layers and with the VCL there is no condensation anywhere. Without the VCL there is condensation on the sarking boards when the internal RH is 65% giving a 12.9% moisture content. Taking out the breather membrane lowers the moisture content of the sarking from 12.9% to 11.9%

    Will - If there is no sarking layer and no VCL then condensation starts under the breather membrane above 50% RH internally. If the breather membrane is removed then there no condensation anywhere up to 85% RH internally.

    So - With a VCL there are no problems (no surprise there!)
    without a VCL there are problems at the sarking layer above 65% RH internally.

    The breather membrane can make things worse in marginal situations (but not IMO enough to warrant leaving it out)

    With a VCL there are no problems, without a VCL there are always problems at the sarking layer but less with the additional layers.
    The question is what level of damage would be acceptable to the VCL before interstitial condensation problems occur at the sarking (What level of damage or poor workmanship to people accept to the VCL in the ordinary course of building?)
    • CommentAuthorEd Davies
    • CommentTimeJun 13th 2020
     
    Is there mould on your sarking boards now, do you know?
    •  
      CommentAuthordjh
    • CommentTimeJun 13th 2020 edited
     
    FWIW http://www.dpcalc.org/ gives estimates of mould risk and other problems.
  4.  
    >>>ubakus.de

    I think that's a good tool for u-values, but wasn't convinced about doing condensation stuff with it. Previous thread:

    http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=16112
  5.  
    Posted By: Ed DaviesIs there mould on your sarking boards now, do you know?

    I can't see the sarking boards now - or ever unless I trash the roof as any mould will appear on the inside of the boards which are not accessible, however as the building has not been occupied in the winter months since the loft conversion I would not expect to see any problems.


    Posted By: WillInAberdeenI think that's a good tool for u-values, but wasn't convinced about doing condensation stuff with it. Previous thread:

    http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=16112" rel="nofollow" >http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=16112

    IMO a good tool but I view such tools as an indicator to be used with caution, i.e. if it says there is no problem - then there may not be, if it says there is a problem then there probably is.!
    Do any of the predictive software modeling tools (free or otherwise) come with a guarantee?

    The base question remains
    How much damage or bad workmanship to a VCL is acceptable before replacement or remedial action is needed?
    •  
      CommentAuthordjh
    • CommentTimeJun 14th 2020 edited
     
    Posted By: Peter_in_HungaryI can't see the sarking boards now - or ever unless I trash the roof as any mould will appear on the inside of the boards which are not accessible

    Endoscope camera and a small drilled hole? I'm not sure it would be worth it though, as you say.

    How much damage or bad workmanship to a VCL is acceptable before replacement or remedial action is needed?

    I don't think there's a single answer to that question. It depends entirely on the whole construction, not just the VCL. Basically, is the flow of vapour through the VCL sufficient to cause condensation and does that condensation stay in place long enough to cause mould or rot or whatever. i.e. a serious condensation analysis is required to answer the question for any particular situation.
  6.  
    In the previous thread I linked to, we discussed an oversimplification in the BS EN method, that indicates condensation, where in fact there cannot be.

    If you think about the existing sarking after you have added the proposed insulation, in winter the existing sarking will be considerably warmer than the proposed breather membrane. Now imagine that the sarking is wet. The proposed breather membrane acts like a cold 'dehumidifier' element and attracts water vapour from the sarking, drying it out. So long as the membrane layer is more breathable than the combined (T&G, VCL and sarking) layers, more vapour will escape the construction than can enter it.

    You want the biggest vapour resistance to be on the inside.

    When the T&G was fitted, with 1000s of nails, presumably the VCL became well holed..? If you worry that will let more vapour through than can escape through the sarking, then you could drill some 1" holes in the sarking before fitting the new insulation.

    If you examine the existing sarking now (midday in mid June) you'll probably find it is too hot to touch! and hence bone dry.

    Do you think the existing wool still fills the cavity below the sarking, or will it have slumped, based on the workmanship you see?
    •  
      CommentAuthordjh
    • CommentTimeJun 14th 2020
     
    Posted By: WillInAberdeenYou want the biggest vapour resistance to be on the inside.

    As long as you're in a cool climate.
    • CommentAuthorgyrogear
    • CommentTimeJun 14th 2020 edited
     
    Posted By: WillInAberdeenWhen the T&G was fitted, with 1000s of nails


    but presumably (= theoretically...) the T&G should be airtight - the primary point of interest

    therefore moisture from inside the room should not be able to escape into the roof structure becos no air to carry it.

    So IMO, the fist point of interest should be the quaility of the ceiling (and not the hypothetical issue of the quality of the vapour barrier and/or sarking layer above it...).

    The second point of interest - which then becomes primary - should be the quality of installation of the to-be-installed rainscreen, to prevent external moisture (precipitation...) (via the slates etc.) pooling on the barrier, then getting firstly onto the new insulation and secondarily into the roof structure.

    So yes, PiH - obviously go for a state-of-the art installation of the new rainscreen - no deliberate rips, holes, sagging, bagging etc. ! and a proper roofing job.

    gg
    •  
      CommentAuthordjh
    • CommentTimeJun 14th 2020
     
    Posted By: gyrogearbut presumably (= theoretically...) the T&G should be airtight - the primary point of interest

    Why would T&G be airtight? (unless it is glued with an appropriate adhesive and there are no shakes in the timber)
    • CommentAuthorIan1961
    • CommentTimeJun 15th 2020
     
    Posted By: Peter_in_HungaryI would rather not take down the T@G or remove the sarking boards due to the work and expense involved


    The practical solution to this potential issue would be to use battens and cross-battens under your slates with a
    vented eaves & ridge detail to create a min 25mm clear air path. The normal advice however is that ventilation is only needed if you use a close-fitting roof finish such as interlocking roof tiles.
    • CommentAuthorEd Davies
    • CommentTimeJun 15th 2020
     
    Posted By: Peter_in_HungaryUsing Ubakus.de shows no problems - however if the internal VCL is removed then serious problems occur on the inside of the sarking boards if the internal RH goes above 50% and the external temp goes below +6.
    Going back to the original question, how does Ubakus model the sarking boards? I.e., how does it take into account the gaps between the boards whose effect must be very dependent on the characteristics of the insulation inboard of them and really ought to be modelled in at least 2D.

    Does it just use an area-weighted average of the permeability of the boards and the gaps? Is there any possibility that the apparent problem is due to it not modelling the gaps at all?
    •  
      CommentAuthorfostertom
    • CommentTimeJun 15th 2020 edited
     
    My understandings in this are based on multi cases I ran when I had 8wks free access to WUFI - but using fairly mild English (Atlantic climate) weather data sets. It may be different in Atlantic but harsher Scotland, and much more so in Continental Hungary.

    WUFI told me that

    1) the 'biggest vapour resistance to be on the inside' old conventional wisdom/rule of thumb had no effect, whether I made that 'resistance' or 'resistivity' (a big difference, never clarified in the old wisdom).

    2) with constructions fully 'breatheable' (water-vapour-open) right through, even if only moderately permeable, like EPS and OSB, 1) applied;
    and interstitial condensation only happened in the outermost zone,
    but was OK because it soon enough dried out with a bit of sun on an approx weekly scale, or failing that, certainly come summer - it never built up year by year to become permanently wet, and mould/rot dies in the dry period, if it even gets started.

    3) adding a VCL made matters far worse!

    The 'ideal' construction that this leads to is, from inside to out:
    plasterboard and skim;
    on 95 or 145 studs or rafters;
    11mm OSB3 sheathing ootside the studs/rafters;
    blown-in cellulose fibre full-filling the inter-stud/rafter space;
    150 or 100 EPS fixed EWI-style over the sheathing;
    down-slope battens fixed together in pairs over the ridge, to prevent sliding down the slope;
    relective breather underslating felt draped over the battens, shiny side down;
    battens and slates/tiles/shingles;
    or instead of the downslope battens etc, acrylic render on the EPS.

    Note, no timber in the sandwich, outboard of the sheathing, where interstitial condensation can occur;
    the OSB, gapfilling glued and screwed and all joins nogged, is the airtight layer; even if not a super air barrier, in tandem with the blown-in cellulose, make a overall adequate, and robust, airtight buildup.

    Peter's proposed builup looks like this, except that he's putting thermal-bridging rafters in the outer 150mm - no need, I'd say. Tho WUFI might give a different answer for Hungary.
  7.  
    Posted By: Ed DaviesGoing back to the original question, how does Ubakus model the sarking boards? I.e., how does it take into account the gaps between the boards whose effect must be very dependent on the characteristics of the insulation inboard of them and really ought to be modelled in at least 2D.

    The sarking boards are entered as 20mm timber, pine with 5mm spacing so the gap should be accounted.

    Posted By: fostertom2) with constructions fully 'breatheable' (water-vapour-open) right through, even if only moderately permeable, like EPS and OSB, 1) applied;
    and interstitial condensation only happened in the outermost zone,
    but was OK because it soon enough dried out with a bit of sun on an approx weekly scale, or failing that, certainly come summer - it never built up year by year to become permanently wet, and mould/rot dies in the dry period, if it even gets started.

    3) adding a VCL made matters far worse!

    With a fully breathable lay-up I could imagine that any condensation has a chance to dry out in either direction, I can see that adding a VCL could make things worse if there is a low permeability layer in the somewhere middle because any condensation that got past the VCL would be trapped until it got though the low permeability layer (20mm sarking boards in my case).
    I am reminded of a picture of a blown double glazed unit with several inches of water sitting in it because condensation got in through the failure but could not get out again.

    I found it interesting that adding a breathable membrane on the outer edge created a condensation point on the inside of the breathable membrane when the internal RH went high enough (according to Ubakus) - but then I presume anything that slows down the movement of vapour will generate a condensation risk (hence my concern about the sarking layer)

    Given the VCL will have some damage and having kicked it around here a bit I a coming to the conclusion that the safe thing to do is to remove the sarking layer (as being less disruptive than removing the T&G replacing the VCL and then remaking the skeiling ceiling)
  8.  
    Peter, hope your project goes well, if the sarking has 5mm gaps between boards then it is completely air- and vapour- permeable. (Air circulates round the boards and equalises the moisture both sides, that's what the gaps are there for). The 'problem' is something to do with a problem in the calculation, not in the construction. Good luck however you proceed!
    • CommentAuthorEd Davies
    • CommentTimeJun 17th 2020
     
    Posted By: WillInAberdeenPeter, hope your project goes well, if the sarking has 5mm gaps between boards then it is completely air- and vapour- permeable. (Air circulates round the boards and equalises the moisture both sides, that's what the gaps are there for).
    Doesn't that depend a bit on the materials each side hence my comments about needing a 2D model. Still, with mineral wool underneath it should be pretty close.

    Posted By: WillInAberdeenThe 'problem' is something to do with a problem in the calculation, not in the construction.
    I think that, too. A resistance/resistivity muddle or something like that, perhaps?
  9.  
    Posted By: Ed Davies
    Posted By: WillInAberdeenThe 'problem' is something to do with a problem in the calculation, not in the construction.
    I think that, too. A resistance/resistivity muddle or something like that, perhaps?

    But I don't know enough about the subject to sensibly differentiate between calculation and construction so the tendency would be to err on the safe side.
    However if a 5mm gap makes the sarking boards effectively vapour open (which surprises me that 5mm is enough) then perhaps a re-think
    • CommentAuthorwookey
    • CommentTimeSep 24th 2022
     
    "The question is what level of damage would be acceptable to the VCL before interstitial condensation problems occur at the sarking".

    The answer to this depends entirely on how airtight the contruction is. A 2mm gap can let in very large amounts of water if enough air is going through it. But if the construction is reasonably airtight and air is just diffusing or moving gently then small gaps like that are not a problem.

    So you can tolerate quite a lot of VCL damage if the construction is reasonably airtight, _much_ less if it's really leaky.
    https://www.greenbuildingstore.co.uk/information-hub/moisture-in-buildings/
    (that says '800g of water through a 1mm wide 1m long gap @20kPa (-10C outside) but doesn't say over what period. Hour? day? month? year?)