Home  5  Books  5  GBEzine  5  News  5  HelpDesk  5  Register  5  GreenBuilding.co.uk
Not signed in (Sign In)

Categories



Green Building Bible, Fourth Edition
Green Building Bible, fourth edition (both books)
These two books are the perfect starting place to help you get to grips with one of the most vitally important aspects of our society - our homes and living environment.

PLEASE NOTE: A download link for Volume 1 will be sent to you by email and Volume 2 will be sent to you by post as a book.

Buy individually or both books together. Delivery is free!


powered by Surfing Waves




Vanilla 1.0.3 is a product of Lussumo. More Information: Documentation, Community Support.

Welcome to new Forum Visitors
Join the forum now and benefit from discussions with thousands of other green building fans and discounts on Green Building Press publications: Apply now.




    • CommentAuthorMarkyP
    • CommentTimeJan 17th 2017
     
    Vent Axia declined to give me a design, referring me to a couple of resellers (I was told they only give direct design help to developments with multiple dwellings). From what I've read on other threads, several here have designed their own. Can anyone outline the approach to sizing the unit? My house is 285m2, the unit will be located in a central position and I'm erring towards a radial system with ducts run between the intermediate floor level joists and along the eaves (loft conversion). I have 5 extracts serving 3 bathrooms, a kitchen and utility. I have 7 supplies serving 4 bedrooms and three regularly occupied ground floor rooms.
    • CommentAuthorgravelld
    • CommentTimeJan 17th 2017
     
    I'm still waiting on an outline design for the Fresh-R, how long does it take?

    Also, what's a Fresh Forward device?

    At least Vaventis have answered their email though, more than Ventive have done....
    • CommentAuthorMarkyP
    • CommentTimeJan 17th 2017 edited
     
    I got a reply fairly quickly, within a week or so I think.I did send a nudge after a week and got a reply and got a design on my drawings the following day.

    fresh forward are the in wall fans which carry air from room to room.
    • CommentAuthorgravelld
    • CommentTimeJan 17th 2017
     
    Thanks. It's almost a week now. I'll give them a day or two.
    •  
      CommentAuthordjh
    • CommentTimeJan 17th 2017
     
    Posted By: MarkyPCan anyone outline the approach to sizing the unit?

    Calculate the required flow rates for Part F - they will typically be greater than needed most of the time. Then pick a unit or multiple units that is/are big enough to produce that rate and still have some spare capacity. Then do the duct design, thinking about flow speeds (for noise) as well as the volume rates required (hint: you'll probably want two ducts into the kitchen). Work out the pressures involved and check that the MVHR unit is still comfortable.

    Personally, I'd get the supplier to design the system and check it carefully myself.
    • CommentAuthorGreenfish
    • CommentTimeJan 17th 2017
     
    "Personally, I'd get the supplier to design the system and check it carefully myself. " - good advice from DJH.

    I also found that suppliers took months to come back, and often were not very informative about what they were providing. Maybe it is better now? Seemed crazy to me that people that did nothing else but MVHR systems were unable/unwilling to give out quotes within days not months. Ensure you leave time and ask lots of questions.

    I wish had had done more checking before we ended up with the system I have. It works, but more by luck than good design, and it was "designed" by a supplier.

    The diagram from GreenPaddy (no relative) on this thread http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=6681, was useful for own calculations (do them to check the supplier). Unfortuneately it no longer appears (since forum changes), can we get it back?
    • CommentAuthorwookey
    • CommentTimeJan 27th 2017 edited
     
    You've had good advice from various people, but here's my (fairly recent) experience.

    I fitted MVHR DIY last year. In a 1st-floor cupboard using rigid ducting. Mostly spiral steel, but one section in rectangular plastic (because it fits well between joists). I did my own design sums, and the spreadsheet is here: http://wookware.org/openbuilding/MVHR/MVHR.xlsx

    It's quite comprehensive, calculating quite thoroughly from 1st principles, and caters for a whole range of square and round piping in various materials (but only rigid ducting). You'll have to change it to deal with your structure (ie. which pipe segments branch into other pipe segments, then fill in pipe materials and sizes and lengths, and list bends etc). It also confusingly has several ways of calculating flow-rates, because there is partF, and 'sensible' and per-room-divvying-up. I tried various to see how they reconciled. You can use it to ensure that a given unit will supply enough air down runs and that the velocity in the pipe is not too high. And see how well-balanced things are. It makes no allowance for fabric loss, assuming than in+out match, but that's easy to change. It may well still have bugs, but my setup-works and is quiet, so it did its job.

    PartF is _way_ more ventilation than any sane person needs IMHO. But if you design it so that that doesn't make excessive noise, then the thing will be almost silent in real use. Like RobL I made the pipes large, and the net result is that you can't hear the unit anywhere on normal (low) setting except the bathroom (because that pipe is ~1m long). You can just about hear it on boost (medium) setting because my house is a quiet place.

    Rigid ducting is a pain to fit. I spent about £330 on ducting in total (so nearly as much as the unit - I got an ITHO HRU ECO-4 cheap for £400). I spent about 8 days cutting and fitting (and glueing and taping and insulating) pipe in a cupboard and loft - which was quite dull. If I was doing it again I'd seriously consider djh's posh semi-rigid pipe + plenum setup, just as it'd be easier to fit and purchase (not so many bits of pipe of different sizes). I bought most of my stuff from UK supplier ducting online, who make their own pipe and have a good range at very reasonable prices. http://www.ducting-online.co.uk/PBSCCatalog.asp?CatID=2285504
    They do plastic too, although you can get bits (slightly) cheaper elsewhere.

    You could be a tight-arse on ducting sizes, but as it's lots of fitting and not that much cost I don't think there is much point. I used a bit of 180 (for main in/out) as that's the machine spigot size, mostly 150 for major runs and quite a bit of 100 for individual bedrooms. Fittings matter for overall pipe resistance so try not to have more than you need. I missed out the downstairs bog as getting a pipe to it was too much of a pain. It could be done later if I really cared enough. No pipe is visible in the house - it's all in the cupboard, the loft, or the floor/ceiling. Loft piping is a compromise on building airtightness and especially pipe insulation. Insulate it carefully, but it'll still be colder than is ideal.

    I spent £30 on an anemometer for commissioning (which to be honest isn't finished - I measured everything, but haven't gone back to the sheet to see how the sums compare with reality, and try to do balancing, because it obviously 'basically works'). I've also bought a CO2/temp/humidy vthings sensor to see how rooms change when it's on/off, but haven't got round to plumbing that in yet either...

    I have a small (4.5kW) woodburner which is not room-sealed and used daily. The MVHR does not seem to have caused any change in the operation of this. Maybe there is marginally less draft when it's cold - hard to tell.
    • CommentAuthorwookey
    • CommentTimeJan 27th 2017
     
    There's a grease trap in the kitchen MVHR extract


    Where did you find one of these? I couldn't find one which just fits behind the extract vent. I did find some unfeasibly expensive thing, but surely a grease filter membrane in a pipe shouldn't be a very large or expensive item.
    • CommentAuthorringi
    • CommentTimeJan 27th 2017
     
    Posted By: wookeyI have a small (4.5kW) woodburner which is not room-sealed and used daily. The MVHR does not seem to have caused any change in the operation of this. Maybe there is marginally less draft when it's cold - hard to tell.


    Unless the MVHR is greatly out of balances and/or your home is very airtight it will not effect a woodburner. It is when a home is refitted to a good standard of airtight along with quality new builds that issues are seen with woodburner not getting a good draft.
  1.  
    Wookey - the kitchen extract vent which the Green Building Store has supplied for us has a square grid with a grease filter behind it. Ours is a replaceable fleece one, but according to the MVHR brochure on their website, they also do a wire one that can go in a dishwasher.
    • CommentAuthorMarkyP
    • CommentTimeJan 30th 2017
     
    wookey - thanks for the detailed post and sharing your calcs sheet.
    • CommentAuthorCoruh82
    • CommentTimeFeb 11th 2017
     
    There is no point in fitting a MVHR system unless your hose is less than 3 Air Changes per Hour (ACHs) If you fit an MVHR and your house isn't air tight then you will in effect be pumping heat out of the house in positive pressured rooms and sucking cold in on the negatively pressured rooms. Mind you you will have filtered air and far less dust in the house! Just to show how unsimple this calculation of whether to fit or not is: Building control requires mechanical ventilation if you are below 5 cumecs/hour/metre square @ 50 pascal differential. (Confusing as there are two different units being used here but are roughly similar in most houses) This is to prevent damp and condensation problems. More explanation here http://www.airtighthousetesting.co.uk/mvhr-fitting-service/what-is-mvhr/
    •  
      CommentAuthordjh
    • CommentTimeFeb 11th 2017
     
    Welcome to the forum, coruh82.

    That's not quite right. The building regs are based on a 3 m³/m²/hr as-built limit and suggest that you should base expectations on that if you design to less than 5 m³/m²/hr in terms of requirements for mechanical ventilation. The suggestion that it is not worth fitting MVHR if the building has above 3 m³/m²/hr leakage is based on whether or not the MVHR will cost more to run than it saves in heat recovered. But many people on this forum have first-hand experience of the improvement to indoor air quality that an MVHR brings regardless of airtightness. Humidity is an imprtant part of this, of course.

    BTW, have you read the guidance about commercial posting on this forum?