Posted By: fostertomOn a morning like this when not a leaf is stirring outside, there won't be any 'natural' ventilation
Posted By: fostertomAny ideas whether MVHR would actually helpfully upset the weak process of stack effect?
Posted By: WillInAberdeenEdit to add but maybe it's obvious: if the house is so leaky that it is already adequately ventilated just by the leaks, then just bolting on a MHRV will just increase airflow
Posted By: an02ewintermittent extraction working as required (probably less than every use of the room) would be more benificial.
Posted By: an02ewI get plenty of work installing and commissioning MVHR required by labc following self builders deciding to have trickle vents removed from their windows. I can’t be financially as the vents are only a few £ vs £1000s for MVHR. it’s a baby step toward a better ATs?It's a significant step towards airtightness. But more than that, particularly if you live in an urban area, it also provides much improved sound insulation.
Posted By: WillInAberdeenI want to ventilate my bathroom, kitchen, spare bedroom all at different times of day depending on usage. I want different temperatures in different rooms at different times.Your use case is quite different to mainstream MVHR usage, methinks. In the big scheme of things, the individual extract rates aren't that great or that important. The largest rate is the kitchen (it's the only room that requires a double duct in our house). The extract rates at all times have to match the supply rate and that is set by IAQ requirements. As you've said, that can be optimised somewhat by e.g. humidity control. But then you use the artificially high constant 0.5 ACH as a strawman. ISTR the building regs figure is 8 l/s (30 m³/hr) per person for excellent IAQ and 4 l/s per person minimum with a backstop of 0.3 l/s/m². Intermittent extractors are required to operate at much greater rates than continuous ventilation - double or so. And of course they usually present a severe airtightness challenge.
Posted By: djhartificially high constant 0.5 ACH as a strawman. ISTR the building regs ... backstop of 0.3 l/s/m²
Posted By: djhHmm I think your numbers are right but your conclusion is wrong.
Posted By: WillInAberdeen60 l/s = 216m³/h. The minimum continuous rate is 13 l/s = 50m³/h. As DJH mentioned, that much should be enough for a whole house, nevermind just the kitchen.
Posted By: Mike1It's a significant step towards airtightness
Posted By: an02ewBut these are intermittent at best, some being never used or isolated, my auntie tapes up all extraction for fear of spiders getting inside, and doesn’t have an issue with damp or mould.In our airtight house we don't really get spiders inside, and my wife tends to keep an odd one to catch the occasional fly/mosquito.
Posted By: tonyNo minimum it is always worthwhile+1
Posted By: WillInAberdeen0.3l/s/m² = 0.5ach, for the usual height room. No strawmen there!Perhaps you'd like to show your working, to demonstrate the lack of strawmen?
Posted By: djhthe building regs figure is 8 l/s (30 m³/hr) per person for excellent IAQ and 4 l/s per person minimumWhere's that from? AD F requires minimum 25,31,37 l/s for 2,3,4 bedrooms, or more depending on floor area. That's 133m³/h minimum for a 4-bed which is way more than we seem to need. Scottish standards require 18l/s = 65m³/h based on number of wet rooms.
Posted By: WillInAberdeenWhere's that from? AD F requires minimum 25,31,37 l/s for 2,3,4 bedrooms, or more depending on floor area. That's 133m³/h minimum for a 4-bed which is way more than we seem to need. Scottish standards require 18l/s = 65m³/h based on number of wet rooms.
Posted By: djh+1
Posted By: an02ewWhy are LABC insisting on continuous ventilation once trickle vents are removed?
Posted By: WillInAberdeenA) ventilation per unit floor area, AD F requires 0.3l/s/m² = 1.08m³/h/m²
B) room volume per unit floor area= 2.3m³/m² (for typical room say 2.3m high)
ventilation per unit volume A÷B = 0.5 per hour
I'd understood that ancient versions of CIBSE guide mentioned 0.5achNot that I'm aware of. I thought the magic number that got quoted was 0.44, which corresponds to the 8' ceiling height figure, but I can't find it now.
You mentioned running at 50m³/h - how many ACH is that? (Show working please )Yes, scarily low. Something like 0.135 (PHPP volume is 369 m³) But for seven hours overnight it's 0.339 or 0.447 depending whether it's run at 'normal' or 'boost' setting. (which affects the heating) So about 0.2 ACH on average.
Posted By: WillInAberdeenThe 4 l/s is the figure from Part F (2010-2013) and the 8 l/s is from memory but I haven't found the reference. It might be in one of the BRE documents or maybe the compliance guide; I haven't checked. Part F (2021) apparently changes the basis completely and now has 6 l/s per bedroom irrespective of how many people are in it. Presumably a compromise between one and two people and god forbid you have more than two in one room apparently. The whole thing is a bit of a mess IMHO. But I suppose they're trying to size the systems (ventilation holes or fan power) and how far you open the vents or how fast you run your fans is up to you.Posted By: djhthe building regs figure is 8 l/s (30 m³/hr) per person for excellent IAQ and 4 l/s per person minimumWhere's that from? AD F requires minimum 25,31,37 l/s for 2,3,4 bedrooms, or more depending on floor area. That's 133m³/h minimum for a 4-bed which is way more than we seem to need. Scottish standards require 18l/s = 65m³/h based on number of wet rooms.
Posted By: an02ewhowever to balance the system one should concider the minimums for extract too, ofter when added together these can be larger due to the trend of en-suites for every bedroomIndeed so. e.g. the numbers in our PHPP are supply air 127 m³/h with the nominal 4.2 people and 140 m³/h extract air. The numbers for our building regs compliance were 125 m³/h normal and 165 m³/h boost. In reality with just two of us most of the time we don't usually need that. I checked CO2 and humidity with calibrated instruments and they were good.
IMHO, yes. The air quality is so much better. But then I also believe houses should be built, and renovated, to be much more airtight than they currently are.Posted By: djh+1At any level of AT? evan at numbers higher than 4 or 5 AC/hr fabric leakage?
Why are LABC insisting on continuous ventilation once trickle vents are removed?Is that a question for me? I didn't use LABC so I don't really know, but I expect it's because it's required by Part F para 1.52 et seq?
Posted By: WillInAberdeenRICS consider anything above 1.5m ceiling height to be habitable, apparently.
Posted By: WillInAberdeenMHRV must comply with an obscure BRE guide from 1994, which suggests that (leakage+deliberate) ventilation should add up to 0.5-0.7ach, and that leakage will be 0.7ach for a typical house, or 0.2-0.35ach for a specially detailed house. So MHRV should be sized for 0.3ach or less, maybe 0, which is hardly prescriptive!