Green Building Forum - Need help! Still got condensation after all my efforts!! Tue, 19 Dec 2023 08:22:50 +0000 http://www.greenbuildingforum.co.uk/newforum/ Lussumo Vanilla 1.0.3 Need help! Still got condensation after all my efforts!! http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=16853&Focus=285701#Comment_285701 http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=16853&Focus=285701#Comment_285701 Thu, 24 Dec 2020 13:10:04 +0000 deniance Last year I posted here about insulating my attic!
I was getting lots of condensation on the felt which was dripping down into the insulation!

Well.... I thought I’d fixed it, sealed all holes and penetrations and was thinking it was good!

Just been up there this morning and it’s exactly the same!! Just as bad as before!!

Any ideas what else I can do or even some method of monitoring where it’s coming from?

Only 3 rooms upstairs, one is a bathroom, so, I’ve ...

Made an insulated hatch with a sealed lid
Sealed all cable penetrations
Checked the bathroom fan connection
Sealed all wall plates of internal walls
Foamed up gaps
Sealed any gaps in coving below

All of the above were massive sources of air from the house getting into the attic, used a fan to find all the leaks, I also bought a box of 50 lap vents that you slide in the felt, you can see daylight through some of them and there is very good airflow , you can feel it and see the cobwebs blowing about!! But there is still enough air condensing to overpower this! Just can’t figure out where!

I thought all the work I did would make it less but it’s just as bad as before! Like someone’s gone up there with a hosepipe and misted it all!!

All I can think of is, the chimney wall as it passes through the roof does get a bit soaked when it’s raining, not dripping wet but just soaks up the moisture and the bricks turn dark, I wonder if the log burner flue dries it off and this then evaporates and floats across the attic and condenses again? Only had the burner on for two days so I’m doubting this theory!
Or maybe because it’s a terraced house, I wonder if it’s floating over the top of his attic and making it into my side??

Gotta try and sort it out, everything is going mouldy!!
Any ideas folks? Cheers]]>
Need help! Still got condensation after all my efforts!! http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=16853&Focus=285702#Comment_285702 http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=16853&Focus=285702#Comment_285702 Thu, 24 Dec 2020 13:30:05 +0000 bxman
or get out at the ridge?

how about a link to last years post

happy Christmas everyone]]>
Need help! Still got condensation after all my efforts!! http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=16853&Focus=285703#Comment_285703 http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=16853&Focus=285703#Comment_285703 Thu, 24 Dec 2020 13:51:47 +0000 deniance
There is a digital aerial just hanging in the loft and it is covered in drips of water so I know it’s condensation from the house!! Just can’t figure out from what! It’s gotta be quite severe to overcome the ventilation, the bathroom fan extracts through the wall and is right over the other side of the house so it’s not coming back into the roof

I’m just clutching at straws but it’s either, a massive hole I’ve missed, the rain dampened chimney wall drying out and recondensing or next doors humid air making its way over the top of the roof wall into my side?

I’ll see if I can snap a few pictures later]]>
Need help! Still got condensation after all my efforts!! http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=16853&Focus=285705#Comment_285705 http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=16853&Focus=285705#Comment_285705 Thu, 24 Dec 2020 14:09:06 +0000 philedge
If theres damp penetrating below the chimney flashing through porous brickwork then that will be adding to the humidity in the attic space as it dries out. To eliminate that as a source you could wrap the stack in plastic sheet and tape it all up for a couple of weeks to see if the attic dried up.]]>
Need help! Still got condensation after all my efforts!! http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=16853&Focus=285707#Comment_285707 http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=16853&Focus=285707#Comment_285707 Thu, 24 Dec 2020 14:23:28 +0000 deniance I’m thinking it’s the wall drying out adding to the humidity but when you see how much condensation there is makes you wonder if it is that? But I guess it’s gotta be one of these, so so process of elimination !
I’ll take some pictures soon! Thanks]]>
Need help! Still got condensation after all my efforts!! http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=16853&Focus=285708#Comment_285708 http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=16853&Focus=285708#Comment_285708 Thu, 24 Dec 2020 14:43:43 +0000 jms452
Where are you in the country?]]>
Need help! Still got condensation after all my efforts!! http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=16853&Focus=285709#Comment_285709 http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=16853&Focus=285709#Comment_285709 Thu, 24 Dec 2020 14:51:09 +0000 tony
Desperate measures would be to fit a fan to suck air out of your loft , this would be replaced by drier air from outside, clearing any damp, possibly only needed during cold weather]]>
Need help! Still got condensation after all my efforts!! http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=16853&Focus=285710#Comment_285710 http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=16853&Focus=285710#Comment_285710 Thu, 24 Dec 2020 15:02:02 +0000 deniance
Where are you in the country?</blockquote>

I’m in South Wales, Cardiff ish]]>
Need help! Still got condensation after all my efforts!! http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=16853&Focus=285711#Comment_285711 http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=16853&Focus=285711#Comment_285711 Thu, 24 Dec 2020 15:05:28 +0000 deniance Need help! Still got condensation after all my efforts!! http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=16853&Focus=285712#Comment_285712 http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=16853&Focus=285712#Comment_285712 Thu, 24 Dec 2020 15:06:12 +0000 deniance Need help! Still got condensation after all my efforts!! http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=16853&Focus=285713#Comment_285713 http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=16853&Focus=285713#Comment_285713 Thu, 24 Dec 2020 15:07:07 +0000 deniance Need help! Still got condensation after all my efforts!! http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=16853&Focus=285714#Comment_285714 http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=16853&Focus=285714#Comment_285714 Thu, 24 Dec 2020 15:08:30 +0000 deniance Need help! Still got condensation after all my efforts!! http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=16853&Focus=285715#Comment_285715 http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=16853&Focus=285715#Comment_285715 Thu, 24 Dec 2020 15:09:18 +0000 deniance Need help! Still got condensation after all my efforts!! http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=16853&Focus=285716#Comment_285716 http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=16853&Focus=285716#Comment_285716 Thu, 24 Dec 2020 15:11:38 +0000 deniance Need help! Still got condensation after all my efforts!! http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=16853&Focus=285717#Comment_285717 http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=16853&Focus=285717#Comment_285717 Thu, 24 Dec 2020 15:16:45 +0000 deniance
Desperate measures would be to fit a fan to suck air out of your loft , this would be replaced by drier air from outside, clearing any damp, possibly only needed during cold weather</blockquote>


I know , I thought I had it cracked, I found a cable penetrating the plasterboard of the bedroom , only a 10mm hole but all the surrounding insulation was soaking from it and a little water up the wall right next to it, so I knew it was just a case of sealing the attic up and venting it , I found dozens of leaks, foamed up, caulked up, tubes and tubes of the stuff! It hasn’t made a blind bit of difference ! So annoying!!! But I won’t let it beat me! Thermal camera is currently on charge ! I’ll investigate soon!]]>
Need help! Still got condensation after all my efforts!! http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=16853&Focus=285721#Comment_285721 http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=16853&Focus=285721#Comment_285721 Thu, 24 Dec 2020 16:33:57 +0000 revor Prior to the extra insulation the loft was warm enough so that the air did not get to the dew point.]]> Need help! Still got condensation after all my efforts!! http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=16853&Focus=285723#Comment_285723 http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=16853&Focus=285723#Comment_285723 Thu, 24 Dec 2020 16:56:45 +0000 deniance Posted By: revorWhat are your ceilings made from would they be lath and plaster?. I once had a Victorian house and replaced some of the lath and plaster ceilings with duplex board (foil backed plaster board) particularly the bathroom. Just with living in a house causes a phenomenal amount of moisture which will find way through ceilings if porous including plasterboard. It can often happen that when you insulate a loft area it becomes that cold that the high humidity air getting in there condenses out and the ventilation in the loft area may not be sufficient to move it. What is the ventilation in the living areas?. A work colleague never had trouble with condensation in his loft until he put extra insulation in there. He found out about it when water started dripping through the ceiling fitting in the bedroom. The vapour was not just going up through the light fitting in the bedroom but through all of the ceiling.
Prior to the extra insulation the loft was warm enough so that the air did not get to the dew point.

It was lath and plaster but now it’s normal plasterboard with emulsion paint

It is house air condensing just can’t pinpoint it, thought I’d stopped the majority but something is still allowing a lot up there!]]>
Need help! Still got condensation after all my efforts!! http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=16853&Focus=285724#Comment_285724 http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=16853&Focus=285724#Comment_285724 Thu, 24 Dec 2020 17:22:14 +0000 djh
I suspect it was the epic at
http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=16335]]>
Need help! Still got condensation after all my efforts!! http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=16853&Focus=285725#Comment_285725 http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=16853&Focus=285725#Comment_285725 Thu, 24 Dec 2020 17:26:53 +0000 djh Posted By: tonyDesperate measures would be to fit a fan to suck air out of your loft , this would be replaced by drier air from outside
Not necessarily if the loft space is open to next door's as well.]]>
Need help! Still got condensation after all my efforts!! http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=16853&Focus=285726#Comment_285726 http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=16853&Focus=285726#Comment_285726 Thu, 24 Dec 2020 17:32:18 +0000 jms452 Posted By: denianceemulsion paint

Kitchen and bathroom paint is more of a vapour barrier than emulsion - and easier than foil backed plasterboard.


That said after the efforts you have put into stopping warm wet air from inside getting into the loft space my suspicion would shift to liquid water coming in from outside, warming up in the sun then condensing in the cold evenings.


Posted By: deniance I’m in South Wales, Cardiff ish


So wet and windy then...

...and in that first photo water is coming in from the roof.

have you got photos of the roof (particularly that area) from the outside?

Do the neighbours in the terrace have similar issues?]]>
Need help! Still got condensation after all my efforts!! http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=16853&Focus=285728#Comment_285728 http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=16853&Focus=285728#Comment_285728 Thu, 24 Dec 2020 17:43:07 +0000 deniance Posted By: djhbxman asked: "how about a link to last years post"

I suspect it was the epic at
http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=16335" rel="nofollow" >http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=16335

:tongue: that’s the one!]]>
Need help! Still got condensation after all my efforts!! http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=16853&Focus=285729#Comment_285729 http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=16853&Focus=285729#Comment_285729 Thu, 24 Dec 2020 18:13:36 +0000 tony Need help! Still got condensation after all my efforts!! http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=16853&Focus=285730#Comment_285730 http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=16853&Focus=285730#Comment_285730 Thu, 24 Dec 2020 19:20:31 +0000 deniance Posted By: tonyI don’t like the continual water/wet coming in via chimney, you are fighting a loosing battle with a source of wet , please can you post a pic showing the outside of the chimney please.
I’ll get one tomorrow]]>
Need help! Still got condensation after all my efforts!! http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=16853&Focus=285731#Comment_285731 http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=16853&Focus=285731#Comment_285731 Thu, 24 Dec 2020 19:22:51 +0000 deniance Need help! Still got condensation after all my efforts!! http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=16853&Focus=285732#Comment_285732 http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=16853&Focus=285732#Comment_285732 Thu, 24 Dec 2020 19:24:07 +0000 deniance Need help! Still got condensation after all my efforts!! http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=16853&Focus=285733#Comment_285733 http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=16853&Focus=285733#Comment_285733 Thu, 24 Dec 2020 19:25:10 +0000 deniance Need help! Still got condensation after all my efforts!! http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=16853&Focus=285734#Comment_285734 http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=16853&Focus=285734#Comment_285734 Thu, 24 Dec 2020 19:26:47 +0000 deniance Need help! Still got condensation after all my efforts!! http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=16853&Focus=285739#Comment_285739 http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=16853&Focus=285739#Comment_285739 Fri, 25 Dec 2020 17:25:47 +0000 bxman
Or put a sheet of plastic temporarily over the top of your insulation so that it can pool in the middle .

And then go up the following day and see if it has caught any rain that has been blown in .

It could be that .]]>
Need help! Still got condensation after all my efforts!! http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=16853&Focus=285740#Comment_285740 http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=16853&Focus=285740#Comment_285740 Fri, 25 Dec 2020 19:36:10 +0000 revor
https://www.british-gypsum.com/products/gyproc-drywall-sealer?tab0=0]]>
Need help! Still got condensation after all my efforts!! http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=16853&Focus=285741#Comment_285741 http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=16853&Focus=285741#Comment_285741 Fri, 25 Dec 2020 19:49:26 +0000 tony