Home  5  Books  5  GBEzine  5  News  5  HelpDesk  5  Register  5  GreenBuilding.co.uk
Not signed in (Sign In)

Categories



Green Building Bible, Fourth Edition
Green Building Bible, fourth edition (both books)
These two books are the perfect starting place to help you get to grips with one of the most vitally important aspects of our society - our homes and living environment.

PLEASE NOTE: A download link for Volume 1 will be sent to you by email and Volume 2 will be sent to you by post as a book.

Buy individually or both books together. Delivery is free!


powered by Surfing Waves




Vanilla 1.0.3 is a product of Lussumo. More Information: Documentation, Community Support.

Welcome to new Forum Visitors
Join the forum now and benefit from discussions with thousands of other green building fans and discounts on Green Building Press publications: Apply now.




  1.  
    Paul, just to clarify what you said above. Umbrella insulation saves more energy then under slab? That would mirror my findings with Tas
    • CommentAuthortony
    • CommentTimeNov 14th 2008
     
    For you my friends I have moved a temperature probe to outside 1m down, 1m away from house initial result 12.7 C.
    • CommentAuthorCWatters
    • CommentTimeNov 14th 2008
     
    Posted By:fostertom
    >I've not heard of a way to change the thermal conductivity of soil by heating it
    Didn't mean that - not sure how you got that from what I said?


    Power lost = Delta T/ Thermal Resistance

    Delta T between the room and deep soil is constant so If the thermal resistance is also constant the power lost must also be constant.

    You can "fill" something with heat but that doesn't generally change it's thermal resistance. The thermal resistance of water at 10C is pretty much the same as water at 20C even though it's been "filled" with a lot of heat. The exception might be if there was a phase change. eg the thermal resistance of ice and water may not be the same.

    The temperature of intermediate layers in the sandwich doesn't effect the heat flow once you reach steady state conditions.
    • CommentAuthorCWatters
    • CommentTimeNov 14th 2008 edited
     
    Perhaps we shouldn't get too hung up on this. Most of the heat loss is sideways around the perimeter. I guess there is a case for lining the sides of foundation trenches with insulation. Interestingly we have that although it was done to prevent heave on clay soil.
    • CommentAuthortony
    • CommentTimeNov 14th 2008 edited
     
    "Delta T between the room and deep soil is constant so If the thermal resistance is also constant the power lost must also be constant."

    Yes but the longer the heat path the lower this power loss will be
    •  
      CommentAuthorfostertom
    • CommentTimeNov 14th 2008
     
    CWatters, you've switched - originally
    Posted By: CWattersI've not heard of a way to change the thermal conductivity of soil by heating it
    now
    Posted By: CWattersYou can "fill" something with heat but that doesn't generally change it's thermal resistance
    Conductivity is different from resistance. Without changing the conductivity we can certainly change the effective resistance between inside and the primeval "equal to the annual average air temp" subsoil - by pushing further away the boundary where the 'primeval' subsoil meets our expanding bulb of warmed subsoil. That's what 'filling up' means - an expanding bulb of heat spreading from the injection point out through the subsoil, hottest at the injection point, tapering to "equal to the annual average air temp" at the advancing boundary. The temp gradient gets extended over an increasing distance or thickness of subsoil of unchanged conductivity. You can look at it either that an ever-increasing thickness of subsoil is being brought in as an insulant, or that the temp gradient is flattening. Either way, heat loss declines steadily quickly in the first, slower and slower in succeeding years, asymptotically never quite reaching a new steady-state.
    • CommentAuthorCWatters
    • CommentTimeNov 14th 2008
     
    Switching was an accident.
    Interesting explanation of the theory, thanks.
    • CommentAuthorCWatters
    • CommentTimeNov 14th 2008 edited
     
    Going back to what Mike7 posted, and hoping I have my units right...
    Silty loam, 10% water has a conductivity of 1.3 W/mC
    So if the stable layer is normally 1m down the U value is 1.3 W/m^2C
    To improve that to an equivalent of say 0.2 you would have to push the bubble down to 1.3/0.2 = 6.5 meters?
    •  
      CommentAuthorfostertom
    • CommentTimeNov 14th 2008
     
    Sort of ... and mike7, we've done some basic calcs and it seems that heat loss (after near-equilibrium is reached, after a year or three) drops rapidly as the notional 'bubble' gets bigger, but after a point the the further reduction in loss gets negligible, with increasing 'bubble'. In particular, a 6m cube (single house size) 'bubble' suffers equilibrium loss about twice that of a near-infinite size 'bubble'. That, I think, we can all live with, and proceed to discuss single-house size schemes, knowing that even expanding the 'bubble' to multi-house estate scale doesn't hugely improve matters. Anyone comment on that?
    • CommentAuthormike7
    • CommentTimeNov 14th 2008
     
    <blockquote><cite>Posted By: tony</cite>For you my friends I have moved a temperature probe to outside 1m down, 1m away from house initial result 12.7 C.</blockquote>

    That compares quite well with my guesstimate sketch which gives 12.2 or thereabouts. Got any figures for the floor nearer the outside wall? Is the soil noticably damper 1m down outside than in?

    <blockquote><cite>Posted By: CWatters</cite>Going back to what Mike7 posted, and hoping I have my units right...
    Silty loam, 10% water has a conductivity of 1.3 W/mC
    So if the stable layer is normally 1m down the U value is 1.3 W/m^2C</blockquote>

    That's right, but it is a U value for a bit of floor which is only exposed to a deltaT of 1.2C from Tony's figures. To get the equivalent Uvalue for exposure to the full 10C deltaT, multiply 1.3 by 1.2/10 to get 0.156 W/m2C...... or 0.072 W/m2C using Tony's estimate of conductivity. We're getting warmer.
    • CommentAuthortony
    • CommentTimeNov 14th 2008
     
    Soil very dry everywhere inside and outside. Near outside wall 750mm down inside house = 16.1 C
  2.  
    Tony,

    can you give us a few more details of the construction of your floor slab and associated perimeter insulation. How are you digging a hole in the middle of your floor to get the temperature probe in? What sort of probe are you using and how are you doing the probing? Just interested!

    Paul in Montreal.
    • CommentAuthortony
    • CommentTimeNov 14th 2008
     
    Floor slab was built 1920's wood block 30mm on tar on 40mm screed on 100 concrete on spasmodic rubble on nice subsoil which is a bit stony.

    I am drilling a hole 10mm or 16mm and very carefully feeding in a type k thermocouple probe linked to a recorder. Checked the temp first and they are OK.

    The hole warms up as I drill it but cools to steady state within 3 hours.

    I should have better perimeter insulation but only have cavity wall insulation down to ground level = 300 below ffl
    •  
      CommentAuthorfostertom
    • CommentTimeNov 14th 2008 edited
     
    A very useful test case then. What's the length x width ratio that makes up your 80m2, tony? Has it been steadily maintained at 20oC av for years, so well equilibriated? (that's a gd word!)
    • CommentAuthortony
    • CommentTimeNov 14th 2008
     
    Basic house is 6x11 with a small front projection in the middle of the long wall 1m x3m , There is a rear addition 5m x6m , the first 1.5m is solid floor then it changes to insulated suspended wood floor.

    Heating regime is 19 - 7am to 9 an then 16.5 to 5pm then 21 to 10 30 pm then 16.5 to 7 am house never gets below 18 at present

    I dont agree with P/A approximations before the computer age they may have been acceptable but not any more.
    • CommentAuthormike7
    • CommentTimeNov 14th 2008 edited
     
    <blockquote><cite>Posted By: fostertom</cite>Sort of ... and mike7, we've done some basic calcs and it seems that heat loss (after near-equilibrium is reached, after a year or three) drops rapidly as the notional 'bubble' gets bigger, but after a point the the further reduction in loss gets negligible, with increasing 'bubble'. In particular, a 6m cube (single house size) 'bubble' suffers equilibrium loss about twice that of a near-infinite size 'bubble'. That, I think, we can all live with, and proceed to discuss single-house size schemes, knowing that even expanding the 'bubble' to multi-house estate scale doesn't hugely improve matters. Anyone comment on that?</blockquote>

    How do your calcs compare with the figures/formulae djh and I came up with? Any chance of a look? Our original conclusion was that there would be a real annual maintenance charge of heat required to maintain the bubble ( or thermal bund wall as I've come to think of it), and that it could be a significant proportion of the heat stored. That leads to the question: "What proportion of the heat delivered to the store needs to be recoverable for the store to be considered viable?"

    I'm anxious only to point out that the single house notion is somewhere on a dangerously steep slope between viable and not, so it is vital to know just where "to avoid disappointment". The recent 'Massive Thermal Store' topic by Jon touched on this, and there it seemed to me that you only needed to double the linear scale for the numbers to look quite promising.

    I don't want to hijack Tony's interesting thread here - should we continue on the original ....John Holt (shouldn't that be Hait?) thread?

    Edit: PS What's a P/A approximation?
    • CommentAuthortony
    • CommentTimeNov 14th 2008
     
    Perimeter over Area approximation often used to try to help with floor problems
    • CommentAuthorEd Davies
    • CommentTimeNov 14th 2008
     
    Tony, any idea how far down your water table is? Or, for that matter, how far down it'll likely to be at the end of January if we have a wet winter? It seems to me that the moment the "bubble" touches ground with any water flowing through it the losses will shoot up enormously.
    • CommentAuthortony
    • CommentTimeNov 14th 2008
     
    Fortunately 200m away from where I live there is a 15mdeep cutting and I am on chalk so water table is way down.
    • CommentAuthorhowdytom
    • CommentTimeNov 14th 2008
     
    Tony could you get some longer drill bits or an extension ? just wondering what the temp is internally near outside wall @ 2meters depth, what an excellent thread.
    tom
    • CommentAuthortony
    • CommentTimeNov 14th 2008
     
    Its tough getting down to 1 m but I intend to try for deeper. outside I bashed in a rod but afraid of getting it stuck half way down indoors.

    You offering to pay for the drill bit?
    • CommentAuthorhowdytom
    • CommentTimeNov 14th 2008 edited
     
    after all the help I've gained form this forum, I'll gladly make you an extension for an SDS ?
    tom
    P.S. whisper your postal address, you'll have it next week !
    • CommentAuthorhowdytom
    • CommentTimeNov 17th 2008
     
    OK
    good luck
    I'd still happly make it F.O.C. I really would like your floor heat data, at 2m !.
    • CommentAuthormike7
    • CommentTimeNov 18th 2008 edited
     
    Fostertom, while Tony is otherwise engaged toasting sandwiches:-

    <blockquote><cite>Posted By: mike7</cite><blockquote><cite>Posted By: fostertom</cite>Sort of ... and mike7, we've done some basic calcs and it seems that heat loss (after near-equilibrium is reached, after a year or three) drops rapidly as the notional 'bubble' gets bigger, but after a point the the further reduction in loss gets negligible, with increasing 'bubble'.</blockquote>

    How do your calcs compare with the figures/formulae djh and I came up with? Any chance of a look? </blockquote>

    Specifically, are your calculations for three dimensions?

    Also, djh's/my results seem bomb-proof to me - bring on your bomb!:shocked:

    ...Aaaand another thing: You say above 'the further reduction in loss gets negligible' - you mean the absolute level of loss is approaching a constant non-zero value? If so, I agree, and that's the figure we're after.
    • CommentAuthortony
    • CommentTimeNov 19th 2008
     
    Under hall floor at one meter down = 18 C constantly. Will go deeper tomorrow.
    • CommentAuthortony
    • CommentTimeNov 19th 2008
     
    At 0.5m 18.5
    • CommentAuthormike7
    • CommentTimeNov 20th 2008
     
    <blockquote><cite>Posted By: tony</cite>Under hall floor at one meter down = 18 C constantly. Will go deeper tomorrow.</blockquote>

    <blockquote><cite>Posted By: tony</cite>At 0.5m 18.5</blockquote>

    Good-oh. How far are these from the nearest outside wall?
    • CommentAuthortony
    • CommentTimeNov 20th 2008
     
    3.5m
    • CommentAuthortony
    • CommentTimeNov 20th 2008
     
    Cant drill deeper :sad: stuff keeps falling down the hole cant even get to 1m anymore with the probe.

    I think the isotherms under look a bit like this and there is not to scale floor plan too.
      john140.jpg
    • CommentAuthortony
    • CommentTimeNov 20th 2008
     
    Which got overlaid
      john139.jpg
   