Green Building Forum - Deep but uninsulated flooring slab?? What is this called?? Tue, 19 Dec 2023 06:45:53 +0000 http://www.greenbuildingforum.co.uk/newforum/ Lussumo Vanilla 1.0.3 Deep but uninsulated flooring slab?? What is this called?? http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=16791&Focus=284522#Comment_284522 http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=16791&Focus=284522#Comment_284522 Wed, 11 Nov 2020 16:46:23 +0000 converse Deep but uninsulated flooring slab?? What is this called?? http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=16791&Focus=284523#Comment_284523 http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=16791&Focus=284523#Comment_284523 Wed, 11 Nov 2020 17:00:43 +0000 Ed Davies
Not sure it'd be my first choice of a new build, though.]]>
Deep but uninsulated flooring slab?? What is this called?? http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=16791&Focus=284524#Comment_284524 http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=16791&Focus=284524#Comment_284524 Wed, 11 Nov 2020 17:45:06 +0000 converse Deep but uninsulated flooring slab?? What is this called?? http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=16791&Focus=284525#Comment_284525 http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=16791&Focus=284525#Comment_284525 Wed, 11 Nov 2020 17:48:36 +0000 fostertom Deep but uninsulated flooring slab?? What is this called?? http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=16791&Focus=284526#Comment_284526 http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=16791&Focus=284526#Comment_284526 Wed, 11 Nov 2020 21:42:58 +0000 djh Deep but uninsulated flooring slab?? What is this called?? http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=16791&Focus=284989#Comment_284989 http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=16791&Focus=284989#Comment_284989 Mon, 30 Nov 2020 20:46:10 +0000 jms452 Posted By: converseneed to build the levels up significantly.

300+mm of polystyrene plus a concerete slab will help build up your levels - you normally have to go down to get a good level of floor insulation.

Crushed concrete might be able to be reused as a bottom layer of sub base for your drive...]]>
Deep but uninsulated flooring slab?? What is this called?? http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=16791&Focus=284990#Comment_284990 http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=16791&Focus=284990#Comment_284990 Tue, 01 Dec 2020 10:53:24 +0000 bxman Heat loss is directly proportional to the Delta and heat losses through the floor are insignificant apart from at the perimeter when the exterior walls are not insulated on their exterior.

To my mind that insulation would be better used elsewhere. if you can incorporate EWI you will get some thermal mass which will stand you in good stead.]]>
Deep but uninsulated flooring slab?? What is this called?? http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=16791&Focus=284993#Comment_284993 http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=16791&Focus=284993#Comment_284993 Tue, 01 Dec 2020 13:31:26 +0000 dereke
I'm thinking of ripping all the floors out (they are not fixed to the walls, like piers in the middle holding it all up) laying down insulation on the ground and walls then infilling with hardcore and putting a screed and underfloor heating in. I think the thermal mass would be useful for getting the most out of my heating system and also switching to an agile tariff (turning off the heating for a few hours at peak time should not have a big impact).

Hell of an upheaval though. Please don't mention it to my wife!]]>
Deep but uninsulated flooring slab?? What is this called?? http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=16791&Focus=286739#Comment_286739 http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=16791&Focus=286739#Comment_286739 Mon, 25 Jan 2021 11:58:04 +0000 converse Heat loss is directly proportional to the Delta and heat losses through the floor are insignificant apart from at the perimeter when the exterior walls are not insulated on their exterior.

To my mind that insulation would be better used elsewhere.</blockquote>
Yes, agreed. Crucial point is from DJH above - I have no idea what Building Control would think. Ground water levels are also going to be an issue, though there is a handy ditch running the length of the plot that can take groundwater away. Has anyone used Geocell in this sort of application?? - looks like it could provide drainage and insulation at the same time.]]>
Deep but uninsulated flooring slab?? What is this called?? http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=16791&Focus=286744#Comment_286744 http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=16791&Focus=286744#Comment_286744 Mon, 25 Jan 2021 12:34:49 +0000 djh Posted By: converseHas anyone used Geocell in this sort of application?? - looks like it could provide drainage and insulation at the same time.
Yes, it will provide drainage and a capillary break. I'm not quite clear as to its relevance for your scenario?

FWIW, I believe tomorrow's Grand Designs will be about an earth-sheltered house with an uninsulated floor and lots of underground perimeter insulation. Should be interesting.]]>
Deep but uninsulated flooring slab?? What is this called?? http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=16791&Focus=286752#Comment_286752 http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=16791&Focus=286752#Comment_286752 Mon, 25 Jan 2021 12:59:08 +0000 converse Deep but uninsulated flooring slab?? What is this called?? http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=16791&Focus=286754#Comment_286754 http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=16791&Focus=286754#Comment_286754 Mon, 25 Jan 2021 13:20:49 +0000 converse https://www-dreieck-co-uk.dualstackcdn.com/images/TECHNOPOR-design-guide-ground-floor-commercial1.17MB-1.jpg

Like this]]>
Deep but uninsulated flooring slab?? What is this called?? http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=16791&Focus=286768#Comment_286768 http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=16791&Focus=286768#Comment_286768 Mon, 25 Jan 2021 16:20:54 +0000 djh
That looks a lot like a diagram of a passive slab.

There's a PDF about the system we used at
https://www.glavloc.com/downloads/KORE-Passive-Slab-Design-Guide.pdf
We had to dig a big hole and part-fill it with loads of hardcore (recycled from some industrial process), then the EPS 'bucket' and then the concrete slab. French drain around the outside. I got one firm of groundworks contractors to do everything.

You can obviously extend the insulation out further from the edge of the raft. EPS is what they use but geocell should work as well. It's not normal/necessary to bond the sheets of EPS together AFAIK. Maybe to allow drainage?

There's an article that discusses both systems at https://passivehouseplus.ie/magazine/guides/the-ph-guide-to-insulating-foundations]]>
Deep but uninsulated flooring slab?? What is this called?? http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=16791&Focus=286977#Comment_286977 http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=16791&Focus=286977#Comment_286977 Fri, 29 Jan 2021 11:48:09 +0000 converse Deep but uninsulated flooring slab?? What is this called?? http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=16791&Focus=286981#Comment_286981 http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=16791&Focus=286981#Comment_286981 Fri, 29 Jan 2021 13:04:58 +0000 djh Posted By: converseI appreciate there might be arguments with the Building inspector and probably wouldn't pass building regs in UK as I read them
I think you're mostly right, but the GD episode had no insulation under the floor AIUI so it's possible to get around the regs (or at least the Approved Documents) if you know what you're doing.

They like most people used EPS for the insulation they do have rather then Geocell. I'm not sure why we're spending so much time discussing Geocell? Do you have some particular reason to want to use it?]]>
Deep but uninsulated flooring slab?? What is this called?? http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=16791&Focus=286984#Comment_286984 http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=16791&Focus=286984#Comment_286984 Fri, 29 Jan 2021 13:43:09 +0000 converse Deep but uninsulated flooring slab?? What is this called?? http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=16791&Focus=286987#Comment_286987 http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=16791&Focus=286987#Comment_286987 Fri, 29 Jan 2021 14:49:23 +0000 djh Posted By: converseI also have reservations about its longevity. It's not as if it could be easily replaced if it's underneath a building
Indeed. There's 400 mm underneath our building so I hope it lasts! There have been some tests of longevity and I think there are links somewhere on this forum. But the thing that made me relax about the question was when I realised that railway embankments and some motorways are held up by EPS 'hardcore'.

I don't like its environmental credentials, but it is a very useful material at a reasonable price with a lot of track history so I'm happy to live with it as I live with my concrete slab.]]>
Deep but uninsulated flooring slab?? What is this called?? http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=16791&Focus=287026#Comment_287026 http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=16791&Focus=287026#Comment_287026 Sat, 30 Jan 2021 20:27:16 +0000 Petlyn Deep but uninsulated flooring slab?? What is this called?? http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=16791&Focus=287166#Comment_287166 http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=16791&Focus=287166#Comment_287166 Fri, 05 Feb 2021 11:26:58 +0000 fostertom There is a good case for using petroleum oil to make insulations, when their use saves many times their oil content, in energy that doesn't have to be burnt subsequently for space heating.
There's that aspect of eco credentials, in which EPS is about on a par with the other plastic insulations; AFAIK it's in the other kinds of chemical pollution, which is IMO more insidious and long-reaching, that EPS shines compared with the others.

Posted By: djhYou can obviously extend the insulation out further from the edge of the raft. EPS is what they use but geocell should work as well
This is where I hesitate to use plastic insulations, as horizontal skirt outboard of the building perimeter. Here it really is a little or a lot or accidentally exposed to the elements, and to mechanical distruption due to imposed ground loads varying over time.
The idea of it lying what - 300mm? - below finished GL, covered with topsoil, paving or whatever sounds really poor.
If topsoil, roots will soon enough penetrate and disrupt, even with root barrier overlay. The thin topsoil layer, isolated from deeper massiveness, will scorch is summer, freeze in winter and struggle to retain moisture stability.
Much better to use inert mineral Geocell, or my preference LECA, tho 2x or 3x thicker (for given insulation) and more expensive - but less so if you order LECA not in bags like garden bedding compost with fancy silicone coatings etc, but by the lorry load (or dumpy bagged or even blown-tanker load) in civil engineering grade.
Then it becomes just a mineral geological stratum compatible with topsoil and subsoil, tolerant of mechanical disruption or root penetration, and leaves the topsoil less liable to temperature swings.]]>
Deep but uninsulated flooring slab?? What is this called?? http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=16791&Focus=287180#Comment_287180 http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=16791&Focus=287180#Comment_287180 Fri, 05 Feb 2021 16:01:41 +0000 Dominic Cooney Posted By: fostertommy preference LECA

How far out from the building would you go with this? and how deep?
We have a plain rectangular building 14.5m x 10m
Perhaps extend it 1m out from the perimeter and 500mm deep?]]>
Deep but uninsulated flooring slab?? What is this called?? http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=16791&Focus=287183#Comment_287183 http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=16791&Focus=287183#Comment_287183 Fri, 05 Feb 2021 16:44:50 +0000 fostertom
This thread started as the latter but is tending to veer off into an insulated slab, perhaps supplemented with a perimeter horizontal 'wing'.

1m of downstand is worth 2m of 'wing', and the bulk of the loss through it is where it's closest to the building, so it needs to be thickest there, tapering off outward.

A horizontal 'wing' of perimeter insulation may only be necessary instead of a downstand 'coffer dam' of insulation, where depth can't be achieved because the foundation is shallow, maybe built off shallow bedrock, but even then some more or less vertical EPS against the wall or at say 45o against vestigal foundation, like attached. Make it up as you go along!

To calc, I postulated 21C at floor/inner wall surface, 0C exterior ground surface. Therefore 0C ground temp at the far tip of the 'wing'. Other ground temps at 0.5m intervals diminishing from 21C to 0C. At each interval, use the local delta-t and conventional U value to calc heat loss for that 0.5m strip. From that you can see where the 'wing' thickness needs to be thickened and where it can be allowed to diminish. Turns out, what's shown on the attached isn't really thick enough - but a lot better than nothing and prob works better than it should, as the floor is, as I say, heavily temp-stabilised by direct connection with subsoil - shattered rock/shale in this case. At any rate, the downward temp gradient of the floor is hugely flattened.

Familiarity with the principle should achieve convincing of an open minded Building Inspector, at least in an existing building.]]>
Deep but uninsulated flooring slab?? What is this called?? http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=16791&Focus=287188#Comment_287188 http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=16791&Focus=287188#Comment_287188 Fri, 05 Feb 2021 19:52:37 +0000 Dominic Cooney Posted By: fostertommore or less vertical EPS against the wall or at say 45o against vestigal foundation

Thanks that’s really helpful. I think it will be a case of making it up as we go along. There is some depth to foundations, but ground levels differ all the way around (it’s possible that the foundations are actually level all the way round) So can do some vertical then slope off at 45 degrees from the strip foundations (under the blockwork walls) and then there is also to deal with big square foundations for the steel uprights!]]>
Deep but uninsulated flooring slab?? What is this called?? http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=16791&Focus=287253#Comment_287253 http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=16791&Focus=287253#Comment_287253 Sun, 07 Feb 2021 19:57:37 +0000 Viking House Wing insulation increases the temperature of the ground beneath the insulation, I modeled this and found that increasing the temperature of the ground beneath 300mm of insulation by 10 degrees reduces the heat-loss of a 200m2 house by 30kWh/annum, about £5, so the return on investment could be about 100 years.
Last time I looked the Embodied energy of foamed glass on the ICE Database was 2-3 times higher than EPS.
Frost protected insulated footings were used as early as the 1930s by Frank Lloyd Wright in the Chicago area.
But since that time, the Europeans have taken the lead in applying this concept over the last 60 years.
There are now over 1 million homes in Norway, Sweden, and Finland with insulated shallow footings which are recognized in the building codes as a standard practice.]]>
Deep but uninsulated flooring slab?? What is this called?? http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=16791&Focus=287258#Comment_287258 http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=16791&Focus=287258#Comment_287258 Sun, 07 Feb 2021 21:54:17 +0000 Dominic Cooney Posted By: Viking Houseinsulated shallow footings

Hi VH
I can fully see the benefit of a passive slab on a new build, but
What would you recommend in our retrofit situation?
a plain rectangular building 14.5m x 10m
Hoping for EWI then continue down to foundations.]]>
Deep but uninsulated flooring slab?? What is this called?? http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=16791&Focus=287259#Comment_287259 http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=16791&Focus=287259#Comment_287259 Sun, 07 Feb 2021 21:57:26 +0000 Dominic Cooney Deep but uninsulated flooring slab?? What is this called?? http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=16791&Focus=287260#Comment_287260 http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=16791&Focus=287260#Comment_287260 Sun, 07 Feb 2021 22:04:13 +0000 Viking House http://www.viking-house.ie/passive-house-renovation.html#prettyPhoto Scroll down to see the skirting temperature improvement.]]> Deep but uninsulated flooring slab?? What is this called?? http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=16791&Focus=287262#Comment_287262 http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=16791&Focus=287262#Comment_287262 Sun, 07 Feb 2021 22:18:19 +0000 Viking House
I don't believe you'll achieve what you hope Dominic, I believe the ground will never heat up enough and will remain cold, any heat you put in will conduct away through the ground. The closest we got to no heating was this house http://www.viking-house.ie/solar-enhanced-passive-house.html
The 40m2 Solar Roof reduced the heating demand from 15kWh/m2/annum to 1kWh/m2/annum and the hot water demand from 20kWh/m2/annum to 1kWh/m2/annum. It has a 50m3 insulated gravel Thermal Store beneath the house and has an annual heating/hot water and electricity cost of €120.]]>
Deep but uninsulated flooring slab?? What is this called?? http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=16791&Focus=287264#Comment_287264 http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=16791&Focus=287264#Comment_287264 Mon, 08 Feb 2021 08:52:39 +0000 fostertom
I would add - why VH only go 500mm deep? The deeper the better, without going an inch deeper than the base of the found - or only by cutting outward at flatter-than-45o. In the pics I attached is was on bedrock, but still we came outward at 45o.

I'm sure there are really serious 'wing' designs that would achieve near-zero floor loss - that would look more like ground-coupled/earth-sheltered cave-like principle.]]>
Deep but uninsulated flooring slab?? What is this called?? http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=16791&Focus=287299#Comment_287299 http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=16791&Focus=287299#Comment_287299 Mon, 08 Feb 2021 17:25:39 +0000 Viking House Deep but uninsulated flooring slab?? What is this called?? http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=16791&Focus=287310#Comment_287310 http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=16791&Focus=287310#Comment_287310 Mon, 08 Feb 2021 18:12:37 +0000 fostertom