Green Building Forum - UFH and insulation on uninsulated slab Tue, 19 Dec 2023 07:07:41 +0000 http://www.greenbuildingforum.co.uk/newforum/ Lussumo Vanilla 1.0.3 UFH and insulation on uninsulated slab http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=17850&Focus=301718#Comment_301718 http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=17850&Focus=301718#Comment_301718 Fri, 26 May 2023 23:51:04 +0100 wookey http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=13875 for that.

This job (floor insulation) has now reached the top of the pile so its design time.

I am trying to quantify the pros/cons of various flooring retrofits and whether to put in UFH despite limited height and thus insulation. Sums are much harder for floors than for other building elements because simple area calcs are just wrong. Has anyone come across any tools other than PHPP to help with this?
Someone must have worked out a way to do some FEM analysis with a FreeCAD model by now?

So what I have is a rectangular 1960s detached house which is all close to enerPHit grade now apart from my original concrete slab floor. I also have perimeter insulation (100mm XPS) on 3 sides down about 700mm below ground to the top of the foundation. The 4th side has a modern (2014) PH-grade extension with 170mm XPS below 150mm slab with UFH-in 50mm screed on top. Some more details at http://wookware.org/house/retrofit/

The combination of very low heat-load due to good airtightness and 3G plus U=0.15 walls all round, and perimeter insulation is one reason why I think it might still make sense to put wet UFH in the floor despite the fact that there will only be 30-50mm insulation under the pipe which various rules of thumb say is 'not enough'.
What I need is some quantification of how this all works in practice.

It seems to me that if the flooring is designed with high conductivity so most of the heat does up not down, and low flow temps so losses are minimised, this might be reasonably efficient. But maybe, in fact, it will still be worse/no better than than radiators? How to do the sums is my question.

Current flooring is 20mm parquet on 2mm bitumen. And there is ~20mm screed which comes up fairly easily in the one place I have checked so far (but one can presume that that may be quite variable across the whole ground floor. I have 60mm above the parquet to the back door threshold and 70mm above to the front door. So means we have 80mm to play with comfortably - maybe 90-100 if the screed removal works out well.

The current plan is something like:
5mm LVT (0.4 W/mK)
18mm cellecta hideck gypsum cement board (0.45 W/mK)
ali spreaders
50mm XPS or PIR containing 16mm pipe. (0.033 W/mK)

I can't find anyone selling pre-routed PUR or PIR sheets. They are all EPS or XPS. Seems to me they would be useful for the 'limited height' retrofit case.

There are plenty of suppliers that will sell you a 20mm EPS/XPS sheet along with 16 or 12mm UFH pipe to retrofit a concrete floor, but that's obviously pretty crummy (4-8mm of actual insulation below pipe - i.e. bugger-all, and thinner pipe adds to pumping loses). We can clearly do much better than that.

There are thinner floor-coverings that can work. I used 12mm multipro (calcium silicate, 0.26W/mK)) in my workshop (over XPS) and it's fine, but it's not T&G so you have add joint-pieces to stop differential movement. T&G floors are a lot less faff.

PHPP says my current overall heating demand is 52kWh/m2.a, and with the floor done as above it reduces to 35kWh/m2a, so 33% improvement. Digging up the whole floor to put 170mm XPS underneath would get it down to 28 - a 46% improvement.

But PHPP isn't allowing for the large thermal bridge of the central chimney or other internal walls on the slab which won't get insulated (maybe it has an approximation for that)? Nor that the perimeter insulation is different on one side, so those numbers are somewhat approximate.

It does show that this is the difference between enerPHit or not. (in previous iterations I did get the heat loss down to 28kWh/m2.a without the floor-digging, but I think there were mistakes. All my refinements since have made the headline number slightly worse so I'm not as close to enerPHit as I thought I was).

Hmm, I'm sidetracking myself here! What I was hoping to get feedback on was best floor-buildup options given 80mm on top of slab, how to evaluate this UFH vs radiators only (vs both), and any other useful analysis tools for how much heat goes up and how much down, and how sensitive this is to detailed material choice/thickness.]]>
UFH and insulation on uninsulated slab http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=17850&Focus=301720#Comment_301720 http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=17850&Focus=301720#Comment_301720 Sat, 27 May 2023 09:47:53 +0100 WillInAberdeen
I think a major weakness of PHPP and SAP are they fixate you onto minimal energy usage, as a surrogate for carbon emissions, while completely ignoring the extra embodied carbon from manufacturing the new cement and plastic.

In our current house I am thinking about some kind of floating timber deck over insulation over the existing slab, optimising for comfort rather than for extreme minimum heat loss. In our case it is somewhere down the list as it will mean replacing the kitchen units, but I eyed up the same products as you.

The calculation methods all seem a bit hazy, because there is a huge unknown about the conductivity of the soil and the water table in each different site.

Obviously heat resistance depends on (distance/area).It's a 3D radial heat transfer where the further/deeper the distance the heat flows (r), the greater the perpendicular area it has available to flow through (1/r²), favouring longer/wider /deeper flow paths, with wide areas compensating for long path length. However all the Therm models etc seem to be in 2D in which perpendicular area is (1/r), so they focus onto shorter length paths around the perimeter of the slab, recommending wing insulation etc.

So I am treating the numbers as indicative at best and focusing on 'what is possible' rather than 'what will it achieve'...!

*Well not me personally - I went on holiday while someone else got messy! Will you be able to move out while you lay new floors, does it need to be a 'fast drying' system?]]>
UFH and insulation on uninsulated slab http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=17850&Focus=301721#Comment_301721 http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=17850&Focus=301721#Comment_301721 Sat, 27 May 2023 10:07:22 +0100 djh
What's the central chimney used for? i.e. does it still need to be there? I remember that you put a course of insulation in your external walls; presumably you could do the same in your internal ones if you were keen?

What's the screed made from? Presumably it can be made to come up everywhere by a suitable application of violence. Worst case you might need to make good the slab underneath in some places.

I make the sums add up a little differently.
Available height: 60 mm free door height + 20 mm parquet + 2mm bitumen + 20 mm screed = 102 mm
So you could add a little more insulation, I think.

As regards UFH, I think you're pretty much committed to the idea that the earth under the house will stabilise at a somewhat warmer temperature and so limit heat loss a bit. It sounds like your heat load is well within the capabilities of a UFH system so I wouldn't bother with radiators (you could plumb in some spare pipes just in case maybe). The system should work regardless of how much analysis you do or don't do :devil:

Sorry I haven't answered most of your questions.]]>
UFH and insulation on uninsulated slab http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=17850&Focus=301724#Comment_301724 http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=17850&Focus=301724#Comment_301724 Sun, 28 May 2023 12:08:44 +0100 GreenPaddy
Or do it a bit more traditionally, with a screed depth just to cover the pipes (clipped to the rigid insul board below), and adhere the cement board to that thin screed surface. Prob betterheat transfer from the pipes as opposed to the formed crummy insul board.]]>
UFH and insulation on uninsulated slab http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=17850&Focus=301725#Comment_301725 http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=17850&Focus=301725#Comment_301725 Sun, 28 May 2023 17:31:32 +0100 WillInAberdeen Posted By: wookeyfloor-buildup optionsUsing conductive and high-heat-capacity materials (screedboard) immediately under the surface is good for conducting UFH heat during the winter hours while UFH is running. But feels cold underfoot during hours when the UFH is turned off, if you like to walk round without shoes. For your house, the UFH might not be on for many hours of the year? Even a few mm of timber (eg ply or fibreboard) makes vinyl warm underfoot, though can be disastrously absorbent if there is a slow water leak (we found!). Just a balancing act...

Posted By: wookeyhow to evaluate UFH vs radiators
The table on pg9 of "MCS-021 Heat Emitter Guide" is useful for this
https://mcscertified.com/wp-content/uploads/2021/10/MCS-021-.pdf

Posted By: wookeyhow much heat goes up and how much down
This is harder than meets the eye. Are you hoping to heat the block of soil inside your floor perimeter insulation to a) room temperature or b) UFH temperature?

If a), the UFH heat will flow down into the cooler soil and up into the equally-cooler room, in proportion to the R values upward from the pipe (surface+LVT+screed) vs downward from the pipe (insulation), about 10:1.

If b) the soil, once heated to UFH temperature, will not absorb any more UFH heat, which will all rise into the room. Once the UFH is turned off, some of the heat stored in the soil will slowly return back to the room, the rest will eventually find its way to the outside air or the subsoil, in proportion to the U values of the floor vs the soil (about 1:1).

If the UFH only runs relatively few hours per year, the soil will end up closer to room temperature (a) than to UFH temperature (b), and v.v. if the UFH runs continuously as it might with a heatpump.]]>
UFH and insulation on uninsulated slab http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=17850&Focus=301726#Comment_301726 http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=17850&Focus=301726#Comment_301726 Sun, 28 May 2023 17:57:13 +0100 djh
If there's enough depth for timber, I'd always consider either cork or bamboo instead of vinyl, depending on total depth. Both don't mind water and are better ecologically.

BTW, I think you meant to refer to the older MCS 021 heat emitter guide which can be found at
https://www.grantuk.com/media/1386/mcs-021-heat-emitter-guide-for-domestic-heat-pumps-issue-21.pdf
for the particular diagram you referred to, rather than the newer Heat Pump Guide you linked to.]]>
UFH and insulation on uninsulated slab http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=17850&Focus=301727#Comment_301727 http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=17850&Focus=301727#Comment_301727 Sun, 28 May 2023 20:51:50 +0100 WillInAberdeen UFH and insulation on uninsulated slab http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=17850&Focus=301728#Comment_301728 http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=17850&Focus=301728#Comment_301728 Mon, 29 May 2023 09:25:13 +0100 jms452
https://www.forbo.com/flooring/en-gl/products/linoleum/cmlack

Particularly good in kitchens and bathrooms although that's more personal preference]]>
UFH and insulation on uninsulated slab http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=17850&Focus=302715#Comment_302715 http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=17850&Focus=302715#Comment_302715 Thu, 03 Aug 2023 03:58:51 +0100 wookey
Do people recommend anything in particular? I reckon there is probably 15mm variation in slab top c.f. 'level' over the whole area, which feels quite thick for self-levelling? I can spend time cutting down the high spots to get it more consistent but it's tedious. It's important that the base is solid, flat and well-stuck down so as to avoid noisy and flappy floors.

(I found the original iron internal gas pipe in the process (it's in a slight channel in the slab and stuck up somewhat into the screed. I'll be getting rid of that before insulating as it no longer connects to anything and we will be disconnecting the supply in the next year or so.)]]>