Home  5  Books  5  GBEzine  5  News  5  HelpDesk  5  Register  5  GreenBuilding.co.uk
Not signed in (Sign In)

Categories



Green Building Bible, Fourth Edition
Green Building Bible, fourth edition (both books)
These two books are the perfect starting place to help you get to grips with one of the most vitally important aspects of our society - our homes and living environment.

PLEASE NOTE: A download link for Volume 1 will be sent to you by email and Volume 2 will be sent to you by post as a book.

Buy individually or both books together. Delivery is free!


powered by Surfing Waves




Vanilla 1.0.3 is a product of Lussumo. More Information: Documentation, Community Support.

Welcome to new Forum Visitors
Join the forum now and benefit from discussions with thousands of other green building fans and discounts on Green Building Press publications: Apply now.




    • CommentAuthorGotanewlife
    • CommentTimeDec 17th 2013 edited
     
    Well I thought all MVHR units had condensate drains; are such units normal? Mine says: "The paper heat exchanger operates as a moisture balancer in case of too low outdoor humidity or as a air dryer in case of high outdoor air humidity. Due to high hygroscopic features of the heat exchanger materials the unit does not need condensate drain."

    Elsewhere the 'paper' exchanger is described as: "Cross-flow polymerized cellulose enthalpy heat exchanger with heat recovery efficiency from 64% up to 72%"

    But also described as: "Thermal energy recuperating efficiency: upto 68%. Moisture recuperating efficiency: Up to 65%."

    The unit is a Vents VEU 100 P Mini; however, the Vents VUT 100 P Mini has a aluminium heat exchanger and a condensate drain but is not sold in the UK as far as I can see. Whilst I can see the logic it is hard to believe this system will remove as much moisture from the apartment as a unit with a condensate drain. There is also a bit where it says the VUT transfers 'sensible (sic) heat energy' from the extract air to fresh air in, whereas the VUE transfers both 'sensible energy' and 'latent moisture energy' to the fresh air in.

    Anyway I have bought the damn thing now and I am irritated - especially as the various translations from Ukrainian don't all say the same thing or even add up and because the UK sellers don't highlight the issue (are they even aware of it I wonder). With uninsulated solid walls I wanted something to reduce help humidity/risk of mould in the winter. I don't suppose anyone here can tell me that my issue with this unit it is not such a big deal.............please :sad:
    • CommentAuthorEd Davies
    • CommentTimeDec 17th 2013
     
    “Sensible heat energy” is a perfectly good term. Personally, I'd hyphenate it as “sensible-heat energy” but that's being hyper-picky.

    Sensible heat is heat you can sense, i.e., feel: heat which increases the temperature of something. The other type of heat is latent heat which changes the phase (solid, liquid, gas) of a material without increasing its temperature by melting or vaporizing it.

    I surmise that the paper exchanger:

    1) removes sensible heat from the exhaust air and

    2) removes some latent heat from the exhaust air by condensing water vapour when the exhaust air is cooled enough that the relative humidity reaches about 100% but

    3) re-evaporates that condensate into the inlet air reabsorbing the latent heat.

    It'll still be removing water vapour from the house. However, it'll be quite a bit less than one without the liquid water path through the paper when the outdoor relative humidity is high. I wonder if it's not something that would work well in the dry cold of a Ukrainian winter but less so in the damp cool of an Italian one. Also, I wonder how they stop mould growing on the damp paper.
  1.  
    Why don't bad smells propagate across to the inlet air flow along with the water vapour?

    David
    • CommentAuthorEd Davies
    • CommentTimeDec 17th 2013 edited
     
    And COâ‚‚. They probably do a tiny bit but the easy path for gasses is through the normal exhaust vent. It'll not be primarily water vapour going through the paper but liquid water.
    • CommentAuthorGotanewlife
    • CommentTimeDec 17th 2013 edited
     
    Posted By: davidfreeboroughWhy don't bad smells propagate across to the inlet air flow along with the water vapour?

    I can't say why not, but they do state: "Extract stale air transfers its moisture to the heat exchanger plates where the water vapour is condensed and absorbed. The recovered heat and moisture are transferred to intake air and germs and smells are left behind."
    Posted By: Ed DaviesI wonder how they stop mould growing on the damp paper.

    Perhaps 'polymerized cellulose' isn't paper as we know it.....

    Thanks Ed. It is as I guessed, it works but it doesn't work as well as I would have thought and I imagine I wouldn't have bought it if I had realized.....not that there is much (if any) choice out there at this performance price point. On the plus side I have found that the frost protection is via a user controllable dial graduated from -30 deg (wince!) to +30 deg - when it gets to the set point it turns off the supply fan (factory set to 3 deg) BUT this means I can use it as a summer by-pass so that when all the windows and doors are open during the summer nights with the air temp inside much higher than outside, I can set it to extract only. Win some lose some. Anyway: buyer beware!

    Thanks (again) Ed our posts crossed but at least I understand why now - still not convinced about the mould yet.....
    • CommentAuthorskyewright
    • CommentTimeDec 17th 2013
     
    Posted By: Gotanewlife
    Posted By: Ed DaviesI wonder how they stop mould growing on the damp paper.

    Perhaps 'polymerized cellulose' isn't paper as we know it.....

    Is the paper heat exchanger a permanent fixture or a removable, cleanable, replaceable (or even disposable) part of the device?
    •  
      CommentAuthorSteamyTea
    • CommentTimeDec 17th 2013
     
    Cold try making one with paper, that would be nice and cheap and a good use for the Daily Telegraph
  2.  
    Ahhh Steamy, I can always rely on you....

    Is there something wrong with the telegraph?

    Skyewright. There is only one supplier of this product in the UK (though they also sell on the internet at 66% of their 'proper' on line shop) - it is a new product and they have only just started stocking the filters. It appears that the exchanger is easily replaceable but I wouldn't think it would be possible to buy one any time soon, if ever.
    •  
      CommentAuthorSteamyTea
    • CommentTimeDec 17th 2013 edited
     
    Posted By: GotanewlifeIs there something wrong with the telegraph?
    No, has the best sports coverage (Matt does good cartoons too) and I tend to get a rather large pile of them in the back of the car. Being a broadsheet is helpful as it is easier to make an MVHR with a large surface area.
    When I was a kid I made a glider that had 'doped' paper wings, apart from liking the dope way to much, I liked the was that the tissue paper tightened up on the frame. Not sure how waterproof/vapour tight it is, but could be a cheap way of making a unit.
  3.  
    We get the weekly 'World Edition' of The Telegraph posted to us (heavy on expat stuff), but I suspect it makes a much better firestarter for my wood burner than a cross-flow filter.
    •  
      CommentAuthorSteamyTea
    • CommentTimeDec 17th 2013
     
    If you cut it into 5 by 5 inch squares you can use it as toilet paper too. Less CO2 emissions as well, though 'no comment' on particulate matter.:bigsmile:
  4.  
    ERVs are quite common over here - the "E" standing for Energy as they recover both sensible and latent heat by transferring moisture. They're actually recommended in a cold dry climate as ventilation in winter will tend to reduce the internal humidity too much.

    See http://www.dpoint.ca/blog/item/181 for a good article about this.

    Paul in Montreal.
    • CommentAuthorGotanewlife
    • CommentTimeDec 21st 2013 edited
     
    Thanks for confirming that Paul, I have noticed you mention that you have very low humidity in the winter before. It is quite simple; Vents sell 2 almost identical units, the Vents VUE-100 P Mini and the Vents VUT-100 P Mini, the only difference is that the VUE-100 P Mini is optimized for cold dry climates and the Vents VUT-100 P Mini is optimized for cold damp climates. It is not a surprise that I couldn't find a single other HR fan for sale in the UK that operates in this fashion! One the one hand I am irritated with myself for missing it on the other hand it would be a bit like checking that a car had 4 wheels.

    Anyway it is too late for me, I have not even bothered asking Fantronix for anything, but I have written to them and advised them of the situation in the hope that they will do the right thing and withdraw the product from sale. I also wrote a review but it gets moderated.......

    Such a shame because at circa £300 and up to 100m^3/hr it UNIQUELY sits just above the biggest vented single room Heat Recovery units with the next nearest unit costing £900 and is therefore the only economical unit for sale in the UK for a small flat/apartment that will fit in a ceiling void. Even the nastiest MVHR units in the box shape format cost double this mainly because they have far greater capabilities than just for a small flat.

    Damn and blast it!!!:cry::angry:

    Anyone think I could adapt the thing if I could get hold of the right heat exchanger?
  5.  
    Posted By: GotanewlifeAnyone think I could adapt the thing if I could get hold of the right heat exchanger?
    Yes!! The HRV/ERV units over here can be converted from one to the other by simply changing the core.

    Paul in Montreal.
  6.  
    Posted By: Paul in Montrealby simply changing the core

    No! It will not be that simple!! as I'll have to make a condensate trap under the exchanger, removing the insulation I shouldn't wonder and find a way of attaching a 32mm pipe in a water tight way. Still very encouraging thanks P-i-M and I have E Mail'd Fantronix the only supplier of the units in the UK to see if they will help.
    • CommentAuthorGotanewlife
    • CommentTimeDec 21st 2013 edited
     
    oops posted in error
    • CommentAuthorbxman
    • CommentTimeDec 21st 2013 edited
     
    Gotanewlife you say to Paul

    I have noticed you mention that you have very low humidity in the winter before.

    I think you will find that once the air temperature gets below freezing the relative humidity drops to 0% as any water vapor has attached it'self to structures or vegetation.

    So the majority of the time in Ukrainian winter the air source will be bloody cold and equally dry.

    If I was you ; I would try it and see you may well find it does not present any great problem there will not be static air in the unit when it is running surely it is damp static air that encourages condensation and molds etc .

    What does the filter itself look like is it a replaceable/exchangeable heat ex-changer type construction only made out of paper ?
  7.  
    Gotanewlife, you wrote:

    ''JT, not wanting to hijack your thread but you can probably give me a bit of quick advice anyone else finding this thread could use too. I am specing my external louvres now for a baby system (max 100m^3/hr), 125mm/204-60 ducting. I must put insect screens in. I want to minimize back pressure obviously and also save money....

    I have 600mm thick solid walls and I was thinking I could drill a 125+ hole and then chip out the wall for any shape size louvre I want. Do you think this will help much? What size/shape would be worth going up to (diminishing returns etc), can you suggest a type of louvre, given I have zero possibility of rain hitting the grill but that the grills are at the same height and likely to be too close together (not sure how close yet 1m maybe). Any advice gratefully received. By the by, I was toying with investing in a cheap airflow tester but worried about their effectiveness/ benefit for the to me considerable cost - guess I won't get one then:wink:''

    Is that with ref to this thread?

    http://www.greenbuildingforum.co.uk/forum114/comments.php?DiscussionID=11405&page=1#Item_6
  8.  
    Posted By: bxmanI think you will find that once the air temperature gets below freezing the relative humidity drops to 0% as any water vapor has attached it'self to structures or vegetation.


    No, that's not true. Water vapour can exist down to -40C

    This is what I see right now in Montreal:

    Temperature: -7.3°C
    Dewpoint: -8.8°C
    Humidity: 89%

    As for swapping cores for HRV/ERV, I was talking more for the machines here which do have condensate drains. If you find an HRV makes things too dry, it's easy to make it into an ERV.

    Paul in Montreal.
    • CommentAuthorEd Davies
    • CommentTimeDec 21st 2013 edited
     
    Posted By: bxmanI think you will find that once the air temperature gets below freezing the relative humidity drops to 0% as any water vapor has attached it'self to structures or vegetation.
    As PiM says, that's not right.

    Water can go directly from solid to gas and back. It's called sublimation when when a solid turns to a gas, e.g., ice turns to water vapour. The equilibrium, aka saturated, vapour pressure (corresponding to 100% RH) is a little bit lower over ice than it is over liquid water at the same temperature but not much. There's no big discontinuity as the temperature drops past 0 °C.
  9.  
    Posted By: Nick ParsonsIs that with ref to this thread?


    Yes it is - ooops:confused::shamed: Ta Nick.

    Bxman - I am a simple chap, so for me as my unit recuperates up to 68% of the condensate and all other units don't - it is not what I needed, expected or what is appropriate. I have not heard about removing static electricity from water vapour preventing mould before but that really isn't my point.
    • CommentAuthorbxman
    • CommentTimeDec 22nd 2013
     
    I know every time we breath out in sub zero temperature we put water vapor into the air but can that air hold sufficient moisture to have a high RH .

    Could I have said close to 0%RH ? Are you in fog at the moment Paul ?
    or does fog have a RH of 100%?

    They say you learn something every day although when you get old and stupid like me you are inclined to forget

    more than what you learn .
    With regard to the Ukrainian equipment .
    With the fresh air flowing into the MVHR even if it was fully saturated it would be warmed as it passed through so any problem that might occur would come from saturated air from the house being cooled and condensing on the paper which would presumably absorb the moisture and evaporate it off into the incoming air flow on the other side .

    I think it would work OK.
    who knows ? try it and see
    • CommentAuthorbxman
    • CommentTimeDec 22nd 2013
     
    hi
    If you had a impermeable heat ex-changer any condensation would build up and need to be drained away .
    As I understood it this system the cold surface as far as the exhaust flow was concerned is the paper element with the incoming air on it's other face . is that correct ?
    • CommentAuthorGotanewlife
    • CommentTimeDec 22nd 2013 edited
     
    Bxman. Cool air can hold less humidity than warm air. Inside air invariably has more water vapour in it than external air. Choosing my terms carefully). Warm humid air usually drops (condensate) that excess water into a drain when it is cooled warming up the incoming air but in my system the excess water is transferred to the incoming stream - I don't need to try it to know it will work and there is no problem other than it not working hard to lower the internal humidity like all other MVHRs sold in the UK. I can't put it any simpler than that bxman and I can't see where you are coming from. However, this thread has given me the info I needed or confirmed what I thought. Thanks all.
  10.  
    Posted By: bxmanCould I have said close to 0%RH ? Are you in fog at the moment Paul ?


    Not at all!

    Current temperature is -6.9C, dewpoint is -8.6C and the RH is 88%

    Coldest day this year (Jan 23rd) had these stats:

    Temperature: -26.9C
    Dewpoint: -32.1C
    RH 61%

    Still a long way from 0% RH! It was very cold and very clear, not a trace of fog. Of course, that 61%RH air at -27C would have a RH of only 1% when heated to 21C - this is why we have a problem with dryness in winter.

    Paul in Montreal
    • CommentAuthorEd Davies
    • CommentTimeDec 22nd 2013
     
    Posted By: bxmanI know every time we breath out in sub zero temperature we put water vapor into the air but can that air hold sufficient moisture to have a high RH .
    Lot of confusion in this sentence but it's not uncommon. Maybe we need a FAQ.

    Firstly, air doesn't “hold” moisture. Water vapour is a gas like any other and exists in the mixture with oxygen, nitrogen, CO₂, argon, etc. The other molecules don't care (much) how much WV there is. Air is not like a sponge which can hold a certain amount of water.

    What limits the amount of WV is that there's a continuous process of condensation and evaporation going on on flat surfaces of water and on any dust or salt particles in the air (condensation nuclei). The amount of condensation happening is basically a function of how much WV there is in the air (directly proportional, I think) whereas the amount of evaporation depends on the temperature.

    If you have a flat surface of clean water (as a liquid or as ice) and still air over it it'll reach an equilibrium amount of WV in the air where the rates of evaporation and condensation balance. The pressure of the water vapour in this condition is called the equilibrium (or, rather confusingly, the saturated) vapour pressure.

    Note that this vapour pressure does not depend (much) on the amount of air present. Even in a vacuum the EVP is about the same - about 0.5% different, IIRC, can't remember if it's higher or lower though I'd guess higher.

    The EVP does depend, strongly, on the temperature because the rate of evaporation is strongly affected. Rough rule of thumb is that the EVP doubles for every 10 °C increase in temperature and halves for every 10 °C decrease.

    As the temperature increases the EVP increases and so does the absolute humidity (number of grams of water vapour in a kilogram or cubic metre of air). These are not quite in lock-step as the density of the air decreases with increasing temperature (at constant pressure) but over the ranges of temperature we're talking about that's a minor difference.

    Anyway, getting back to the point: by definition 100% RH is the maximum amount of water vapour the air can “hold” under common conditions so, yes, at sub-zero temperatures the air can “hold” sufficient water vapour to reach 100% RH.

    The rate of evaporation (sublimation) from ice is a bit lower than from liquid water so the EVP over ice is a tad lower than over liquid water at the same temperature (e.g., supercooled water which is below 0 °C but has not yet frozen). Still, the differences at the sort of temperatures were likely to reach in the UK are quite small.

    More information following the links from here:

    https://en.wikipedia.org/wiki/Goff%E2%80%93Gratch_equation
    https://en.wikipedia.org/wiki/Arden_Buck_equation

    I've got some Python code I did a while ago to do Arden Buck equations, somewhere.
    • CommentAuthorbxman
    • CommentTimeDec 22nd 2013
     
    Good Morning Getanewlife

    So what you were hoping to do was to lower your indoor RH as well as recovering heat from this unit .

    It seems the unit has been designed with the intention of alleviating the problem Paul has where he ideally needs to add moisture to his incoming air.

    You have no price or dimensions for the one the same manufacturer makes with the aluminium heat exchanger would it be wise to see if you can get those first .

    http://www.ventilation-system.com/cat/508/

    look like a bargain if they are as efficient as they say and both appear the same size

    http://www.ventronix.co.uk/acatalog/Heat_Recovery_Unit_-_VUT-200V_mini_EC.html talking of £840 here maybe that is why your supplier does not stock the aluminium version .

    cheers Paul and I am concerned about what it costs to keep warm !!
    • CommentAuthorGotanewlife
    • CommentTimeDec 22nd 2013 edited
     
    Posted By: bxmanSo what you were hoping to do was to lower your indoor RH as well as recovering heat from this unit .
    I am glad that you have finally grasped the nub of the issue.
    Posted By: bxmanYou have no price or dimensions for the one the same manufacturer makes with the aluminium heat exchanger would it be wise to see if you can get those first
    There is no price because no retailer in the western world sells one! I have no idea why you think I have no dimensions for the VUT model, as I have said they are virtually identical. I have the full specs for both versions: the external dimensions are identical, the fans are identical, all the controls/electrics are identical and almost all the spec is identical, and there is only 1 instruction manual for both variants with just a little section about the difference between 2 types. Given the structure of the inside I would bet my best friend's right arm that the exchangers are interchangeable see good pic here of insides:
    http://www.ebay.com/itm/Heat-Recovery-Ventilation-Unit-Whole-House-Extraction-Ventilation-System-/130591379982

    You have made a mistake with your second link; it is for the much bigger 200 model - though you might have noted that all their models are all the VUT version except for the 100. Also note that Fantronix, Ventronix and the EBay shop 'The Ventilation Shop' are all the same company and that they are the sole distributor of Vents MVHR, as far I have seen. Thanks for your interest but I have done a lot of research on this.
  11.  
    Posted By: bxmancheers Paul and I am concerned about what it costs to keep warm !!


    It's not too bad - we use about 15000kWh a year for heating and general electrical usage and about 3600kWh in natural gas for cooking and hot water. Electricity here is around Can$0.06 per kWh so about 3.7p

    Paul in Montreal.
    • CommentAuthorbxman
    • CommentTimeDec 22nd 2013
     
    Good Gracious.

    That sounds very reasonable Paul mostly Hydro and Nuclear I imagine .

    Hi Gotanewlife

    after your admonishment I have now looked a bit more carefully and it seems they only do the breathable exchanger on the the 100 model .

    There must be some reason why a unit twice the capacity should be 4 times the price.

    I am so sorry I never understood your original post said that you wanted the unit to lower your RH. I had stupidly assumed you were wanting to recover the precious heat before you pumped out the air that had been used and degraded in your property.

    I agree the documentation is not that clear it talks of " polymerized cellulose" as the H/E material on the VUE model .

    But with the VUT model it in most places describes it as " Plastic" and yet in the one place as "Aluminium" .

    You might try and telephone Mr. Aleksandr Pavlenko . on 380- 44-4063625
    He could possibly help you.

    May be you should cut down on the sources of high Humidity or run a de-humidifier when it gets above acceptable levels.

    The documentation for the VUE makes it abundantly clear that this model can alleviate the problems associated with to low a RH within a property.
   