Green Building Forum - Plasterboard + 1/2" EPS Tent Tue, 19 Dec 2023 08:41:40 +0000 http://www.greenbuildingforum.co.uk/newforum/ Lussumo Vanilla 1.0.3 Plasterboard + 1/2" EPS Tent http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=17634&Focus=298684#Comment_298684 http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=17634&Focus=298684#Comment_298684 Tue, 08 Nov 2022 12:53:47 +0000 Dominic Cooney I suppose at least there was something, there was nothing in the stud walls that partitioned off the eaves storage space. Also nothing to stop the external air from the eaves blowing all the way across the room, under the floor boards, between the floor joists to the other side. Lets just say it is well ventilated!]]> Plasterboard + 1/2" EPS Tent http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=17634&Focus=298686#Comment_298686 http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=17634&Focus=298686#Comment_298686 Tue, 08 Nov 2022 13:31:58 +0000 Nick Parsons
Yes, the floor/ceiling cooling system is alive and well and active in many many thousands of Victorian attics and modern dormer bungalows.

Maybe we should compile a list of likely 'failures' in rooms-in-the-roof. I'll start with a loft conversion done in the last few years, signed off by BC. The designer/builders seem to have paid no heed to the fact that the adjoining lofts had not been converted. Party wall finish was simply dot-and-dab plasterboard...

Even where a terrace-full of attics adjoin, people often do not seem to note that step-gables are external walls!]]>
Plasterboard + 1/2" EPS Tent http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=17634&Focus=298687#Comment_298687 http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=17634&Focus=298687#Comment_298687 Tue, 08 Nov 2022 14:28:33 +0000 fostertom Plasterboard + 1/2" EPS Tent http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=17634&Focus=298708#Comment_298708 http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=17634&Focus=298708#Comment_298708 Thu, 10 Nov 2022 11:17:43 +0000 Dominic Cooney
I was going to put 100mm PIR underneath & tape the joins, fixed with 25x38 battens (because I have a load spare) then plasterboard & skim.
This would be a massive improvement over what is there now.

Is there any point putting anything in between? If I have to leave a 50mm air gap below the felt then that only leaves 20mm usable space.

At some point in the future I may redo the roof, at that point I can fully fill between the rafters and fix 100mm PIR over the top to make it a warm roof (with counterbattens, breather membrane, & tile battens).

Or at this stage should I try and put say 25mm PIR inbetween (easy to get hold of), or even 30 or 40mm? (internet only order I expect) then next common size - 50mm - may be too risky. In case I don't get round to redoing the roof for 10 years or more.

Any thoughts?]]>
Plasterboard + 1/2" EPS Tent http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=17634&Focus=298710#Comment_298710 http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=17634&Focus=298710#Comment_298710 Thu, 10 Nov 2022 12:10:10 +0000 Dominic Cooney Plasterboard + 1/2" EPS Tent http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=17634&Focus=298713#Comment_298713 http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=17634&Focus=298713#Comment_298713 Thu, 10 Nov 2022 12:24:56 +0000 Dominic Cooney Plasterboard + 1/2" EPS Tent http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=17634&Focus=298718#Comment_298718 http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=17634&Focus=298718#Comment_298718 Thu, 10 Nov 2022 14:28:48 +0000 WillInAberdeen
My childhood 1970s dormer bungalow had the dwarf walls of the dormer bedroom 'insulated' with some 1970s orange carpet, which someone had crawled into the triangle void to tack over the outside of the dwarf wall studs. Was as effective as you would expect. Many years later we bought an old farmhouse where the same thing had been done with fertilizer sacks.]]>
Plasterboard + 1/2" EPS Tent http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=17634&Focus=298729#Comment_298729 http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=17634&Focus=298729#Comment_298729 Thu, 10 Nov 2022 17:25:52 +0000 Dominic Cooney
That works out at U = 0.18


The U value of the existing roof works out at 1.936 and there is no attempt at insulation behind the dwarf walls!
There doesn't seem to be an option for carpet or Hessian Sacks in that U-value calculator, so we can't compare!]]>
Plasterboard + 1/2" EPS Tent http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=17634&Focus=298733#Comment_298733 http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=17634&Focus=298733#Comment_298733 Thu, 10 Nov 2022 18:37:34 +0000 Peter_in_Hungary
In the first example you quote 12.5 plaster board, in the second you use 9 mm PB. Over here we don't use 9 mm PB much because it has a tendency to sag especially if it is not vertical. Was the change intentional or a typo? Also no one here skims PB its all tape and fill, much cheaper and quicker.]]>
Plasterboard + 1/2" EPS Tent http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=17634&Focus=298735#Comment_298735 http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=17634&Focus=298735#Comment_298735 Thu, 10 Nov 2022 19:47:50 +0000 Dominic Cooney
The existing plasterboard is 9mm, I have been playing around with that U-value calculator and realised there are options for both thicknesses. Tape and fill would be preferable, I would have to space the battens to suit the size of tapered edge plasterboard exactly, which would probably mean running the battens horizontally (due to the odd spacing of the existing rafters)]]>
Plasterboard + 1/2" EPS Tent http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=17634&Focus=298743#Comment_298743 http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=17634&Focus=298743#Comment_298743 Thu, 10 Nov 2022 21:46:20 +0000 wookey Plasterboard + 1/2" EPS Tent http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=17634&Focus=298745#Comment_298745 http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=17634&Focus=298745#Comment_298745 Thu, 10 Nov 2022 22:36:30 +0000 Dominic Cooney Plasterboard + 1/2" EPS Tent http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=17634&Focus=298748#Comment_298748 http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=17634&Focus=298748#Comment_298748 Fri, 11 Nov 2022 10:11:05 +0000 WillInAberdeen
Ive been gluing pb onto PIR but only for vertical wall - not tried on ceilings yet! I used instant grab polymer adhesive, got through quite a few tubes trying to run continuous beads round each board edge and criss cross across the middle.

Dominic, the 1200x900 plasterboards suit me better for working on ceilings alone. The 9mm stuff doesn't seem to be sold so much round here, maybe there are some fire or noise regs or something. The 1970s plasterboard ceiling has sagged a little round each fixing, but not really noticeable because of the swirly artex and the woodchip wallpaper..]]>
Plasterboard + 1/2" EPS Tent http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=17634&Focus=298755#Comment_298755 http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=17634&Focus=298755#Comment_298755 Fri, 11 Nov 2022 15:46:07 +0000 djh Plasterboard + 1/2" EPS Tent http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=17634&Focus=299082#Comment_299082 http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=17634&Focus=299082#Comment_299082 Thu, 01 Dec 2022 17:11:23 +0000 Davycrocket
I'm thinking of doing this unless someboy has experienced a failure of such a scheme ?]]>
Plasterboard + 1/2" EPS Tent http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=17634&Focus=299083#Comment_299083 http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=17634&Focus=299083#Comment_299083 Thu, 01 Dec 2022 17:47:04 +0000 tony Plasterboard + 1/2" EPS Tent http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=17634&Focus=299085#Comment_299085 http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=17634&Focus=299085#Comment_299085 Thu, 01 Dec 2022 17:58:05 +0000 Jeff B Posted By: DavycrocketCould you not have boarded over the orginal PB with PIR and stuck that and the new PB on with a suitable adhesive ?

I'm thinking of doing this unless someboy has experienced a failure of such a scheme ?

I put PIR insulation boards directly onto the existing plasterboards on my dwarf walls/skeilings. However I would not trust adhesives so I used 25 x 50mm battens to secure the first layer of 50mm PIR (screwed through) and then put 25mm boards between the battens (friction fit with Alu tape over the joins) and then screwed the new PB to the battens. Worked very well, no problems AFAIK.

Note: I am aware that purists would be horrified at the thought of all the thermal bridges caused by the screws!]]>
Plasterboard + 1/2" EPS Tent http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=17634&Focus=299101#Comment_299101 http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=17634&Focus=299101#Comment_299101 Thu, 01 Dec 2022 20:16:43 +0000 Davycrocket Plasterboard + 1/2" EPS Tent http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=17634&Focus=299102#Comment_299102 http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=17634&Focus=299102#Comment_299102 Thu, 01 Dec 2022 20:19:08 +0000 Davycrocket
Hi Tony did you read my reply re loaning of the cavity wall gun mate ?]]>
Plasterboard + 1/2" EPS Tent http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=17634&Focus=299107#Comment_299107 http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=17634&Focus=299107#Comment_299107 Thu, 01 Dec 2022 22:24:33 +0000 Jeff B Posted By: DavycrocketWhat wouldn't you trust about the adhesive mate ?

Probably because I am a 75 years of age old codger who life's experience has shown that the chances of two items that are screwed together have a far greater chance of staying together than two that have been stuck together with adhesive! :wink:

Also it would have been quite problematic using adhesives when attaching 12mm foil backed PB onto sloping ceilings!]]>
Plasterboard + 1/2" EPS Tent http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=17634&Focus=299108#Comment_299108 http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=17634&Focus=299108#Comment_299108 Fri, 02 Dec 2022 07:45:11 +0000 Dominic Cooney Posted By: DavycrocketCould you not have boarded over the orginal PB with PIR and stuck that and the new PB on with a suitable adhesive ?

In this particular case I removed all the old plasterboard because I have also removed the dwarf wall on each side of the room, as well as the flat ceiling in the middle. So the original skeiling part was less than one third of the plasterboarded area of this room.
This has gained us 800mm each side of the room, so 1600mm in total, less 100 each side when I put the PIR on the block walls plus the plasterboard so more like 1.37 metres total extra on this room dimension. It will look and feel bigger and more spacious, it will bring the previously cold ventilated-to-outdoors eaves storage inside the warm envelope. The whole job will prevnt cold outdoor air from blowing all across the room underneath the floorbards (Kitchen is below).

We will likely still use the eaves area for storage but in furniture (blanket boxes etc.) and also form a rearranged airing cupboard that will now be properly insulated!]]>
Plasterboard + 1/2" EPS Tent http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=17634&Focus=299109#Comment_299109 http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=17634&Focus=299109#Comment_299109 Fri, 02 Dec 2022 07:46:33 +0000 Dominic Cooney Plasterboard + 1/2" EPS Tent http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=17634&Focus=299110#Comment_299110 http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=17634&Focus=299110#Comment_299110 Fri, 02 Dec 2022 07:54:35 +0000 Dominic Cooney I cut both sides of the board with a sharp knife and snapped the board, so almost no dust created.

I still have the top bit to do above the chords & purlins, but helpfully this is approx 800mm long so my pieces cut 400 x 2400 will then get cut into 3 lengths of 800 x 400

The 100mm layer will go over these held in place with 25mm battens.

The radiator under the window will probably go somewhere else, as it will need moving inwards anyway to make room for 100mm PIR on the end wall.]]>
Plasterboard + 1/2" EPS Tent http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=17634&Focus=299111#Comment_299111 http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=17634&Focus=299111#Comment_299111 Fri, 02 Dec 2022 08:00:05 +0000 Dominic Cooney
My parents would have been celebrating the birth of their new baby boy a few days earlier. (although disappointed that I wasn't a girl, after my 3 older brothers!)]]>
Plasterboard + 1/2" EPS Tent http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=17634&Focus=299112#Comment_299112 http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=17634&Focus=299112#Comment_299112 Fri, 02 Dec 2022 08:15:54 +0000 Dominic Cooney It is almost impossible to remove without wrecking either the PIR or the P/B or both. I did manage to carefully peel a 25mm sheet of misplaced PIR off of a very dusty stone wall so that I could re-do it (it was sticking out proud of the one next to it - I was just using it as gap filler in this location on an internal wall).
We used it on the walls of the barn conversion we did recently, but we also fixed the PIR mechanically with plastic insulation fixings, then pink foam glued the P/B to the surface.
I can see the appeal in using it for skeilings, but it would need to be held in place while it goes off, for which screws are an easy solution anyway. You could use just a few screws and take them out again after, but this would seem a bit pointless.
My concern with adhesive-only on existing skeilings or ceilings is that any paint layer could act as a release agent?
Also longevity, although it stuck very very well when we used it last year, would this still be the case in 10, 20 or even 47 years time?]]>
Plasterboard + 1/2" EPS Tent http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=17634&Focus=299114#Comment_299114 http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=17634&Focus=299114#Comment_299114 Fri, 02 Dec 2022 10:27:04 +0000 Davycrocket
Probably because I am a 75 years of age old codger who life's experience has shown that the chances of two items that are screwed together have a far greater chance of staying together than two that have been stuck together with adhesive!<img src="/newforum/extensions/Vanillacons/smilies/standard/wink.gif" alt=":wink:" title=":wink:"></img>

Also it would have been quite problematic using adhesives when attaching 12mm foil backed PB onto sloping ceilings!</blockquote>

Fair do's Jeff :bigsmile:]]>
Plasterboard + 1/2" EPS Tent http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=17634&Focus=299115#Comment_299115 http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=17634&Focus=299115#Comment_299115 Fri, 02 Dec 2022 10:35:02 +0000 Davycrocket Plasterboard + 1/2" EPS Tent http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=17634&Focus=299212#Comment_299212 http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=17634&Focus=299212#Comment_299212 Mon, 12 Dec 2022 09:41:19 +0000 Dominic Cooney I have managed to push it away from the roof felt a bit and squeeze 25mm of PIR behind it.]]> Plasterboard + 1/2" EPS Tent http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=17634&Focus=299213#Comment_299213 http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=17634&Focus=299213#Comment_299213 Mon, 12 Dec 2022 09:49:09 +0000 Dominic Cooney I have managed to pull it away a small amount and squeeze 12mm of Aerogel board behind it.
The location of these pipes are the reason that during the "Beast from the East" in 2018 we had no hot water.
(this part of the roof is on the east side)]]>
Plasterboard + 1/2" EPS Tent http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=17634&Focus=299584#Comment_299584 http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=17634&Focus=299584#Comment_299584 Tue, 10 Jan 2023 15:08:12 +0000 Davycrocket
Whilst trying to find the culprit I discovered that the fibreglass was wet presumably caused by warm air escaping from below ?

The insulation is touching the felt in the eaves.

If I pulled the said insulation out could it be replaced with eps beads between the joists ?

I think ive stopped the air escape from below by changing the downlights to fire rated alternatives.]]>