Green Building Forum - Whole House Air Filtration System Tue, 19 Dec 2023 08:38:57 +0000 http://www.greenbuildingforum.co.uk/newforum/ Lussumo Vanilla 1.0.3 Whole House Air Filtration System http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=17723&Focus=299977#Comment_299977 http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=17723&Focus=299977#Comment_299977 Mon, 30 Jan 2023 07:49:39 +0000 Victorianeco Whole House Air Filtration System http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=17723&Focus=300015#Comment_300015 http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=17723&Focus=300015#Comment_300015 Tue, 31 Jan 2023 13:10:24 +0000 Mike1 Whole House Air Filtration System http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=17723&Focus=300020#Comment_300020 http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=17723&Focus=300020#Comment_300020 Tue, 31 Jan 2023 16:19:55 +0000 tony Whole House Air Filtration System http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=17723&Focus=300024#Comment_300024 http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=17723&Focus=300024#Comment_300024 Tue, 31 Jan 2023 17:40:08 +0000 djh Posted By: Mike1This may be one time where buying the cheapest undersized MVHR unit you can find is actually worth it?Not quite sure how you would use this? Why undersized - I'd have thought that was a recipe for a rapid failure and a lot of noise meanwhile?]]> Whole House Air Filtration System http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=17723&Focus=300032#Comment_300032 http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=17723&Focus=300032#Comment_300032 Tue, 31 Jan 2023 21:54:43 +0000 Mike1 Posted By: djhWhy undersized - I'd have thought that was a recipe for a rapid failure and a lot of noise meanwhile?If filtration is the only concern (as it appears to be), rather than providing a particular air change rate, a cheap unit permanently running on a low setting _may_ be adequate. It would probably depend on the level of filtration required, and what is giving rise to the need for filtration. Hence my question mark above.

If it needs to provide whole-house ventilation too, a more robust solution would be required. Ideally MVHR...]]>
Whole House Air Filtration System http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=17723&Focus=300037#Comment_300037 http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=17723&Focus=300037#Comment_300037 Tue, 31 Jan 2023 22:39:42 +0000 Victorianeco
I intended fitting MVHR years ago but decided the house is probably too leaky (Victorian mid-terrace) to warrant MVHR. We still have open chimneys wedged with pillows in bags for instance]]>
Whole House Air Filtration System http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=17723&Focus=300038#Comment_300038 http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=17723&Focus=300038#Comment_300038 Wed, 01 Feb 2023 08:08:02 +0000 cjard Whole House Air Filtration System http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=17723&Focus=300048#Comment_300048 http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=17723&Focus=300048#Comment_300048 Wed, 01 Feb 2023 12:57:56 +0000 sgt_woulds
Ventive used to have filtration I believe, but they no longer have a PSV system suitable for domestic properties, (and they never answer enquiries so I've crossed them off my list)

Glidevale iPSV has no filtration.

We have the double whammy of a neighbour with a highly polluting wood stove and light sleepers who are sensitive to MV noise - I've never come across a truly silent mechanical vent in real life.]]>
Whole House Air Filtration System http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=17723&Focus=300123#Comment_300123 http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=17723&Focus=300123#Comment_300123 Sun, 05 Feb 2023 08:41:14 +0000 Dominic Cooney
[Vent-Axia Sentinel Kinetic]]]>
Whole House Air Filtration System http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=17723&Focus=300128#Comment_300128 http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=17723&Focus=300128#Comment_300128 Sun, 05 Feb 2023 17:33:40 +0000 borpin Posted By: Dominic CooneyOur MVHR is set to quiet mode overnightAbout a year ago, I started measuring CO² in the house and on the MVHR extract. I was surprised that the ventilation rate needed to keep the CO² stable and the difference one person made to that.

Humidity is pretty stable even after showers (well never to the problem levels) and the house is generally too dry and I need a Humidifier. So ventilation levels are basically set for CO² level control. For the 2 of us, that is on minimal setting all the time.

Side note, I started measuring the Home Office CO² with just me. Horrified at how high it got with the door closed (it has supply but no extract). I now leave the door ajar (and yes it has the gaps under the door) which maintains the level nicely.

Moral of the story, measure your CO².]]>
Whole House Air Filtration System http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=17723&Focus=300133#Comment_300133 http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=17723&Focus=300133#Comment_300133 Sun, 05 Feb 2023 20:09:50 +0000 djh Posted By: borpinHumidity is pretty stable even after showers (well never to the problem levels) and the house is generally too dry and I need a Humidifier. So ventilation levels are basically set for CO² level control. For the 2 of us, that is on minimal setting all the time.Our MVHR has a 'trickle' setting of 50 m³/hr (approx 14 l/s) and we typically run on that up to 17 hours a day and 125 m³/hr for the other seven (or longer) whilst the heater might be running. I'm curious about your humidity. What is 'too dry' as an RH number?]]> Whole House Air Filtration System http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=17723&Focus=300139#Comment_300139 http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=17723&Focus=300139#Comment_300139 Sun, 05 Feb 2023 23:29:00 +0000 RobL Posted By: borpinAbout a year ago, I started measuring CO² in the house and on the MVHR extract. I was surprised that the ventilation rate needed to keep the CO² stable and the difference one person made to that.

Side note, I started measuring the Home Office CO² with just me. Horrified at how high it got with the door closed (it has supply but no extract). I now leave the door ajar (and yes it has the gaps under the door) which maintains the level nicely.

Moral of the story, measure your CO².

We cook, dry clothes indoors, aim for 50% RH indoors. Our VH sentinel+B natively has RH, aftermarket added CO2 feedback(recommend). It can get 50% RH, but we’d need to target lower than that to appreciably drop CO2 lower (maybe 800ppm typical). The unit can easily strip all the moisture out of the air if it tries! Many offices in my experience get lower CO2 than that, but are very low RH in winter - ok for a bit, but people eventually get itchy skin, and pick up infections.

Measuring RH and CO2 is a first step for anyone interested in air quality - very few people recognise either issue.]]>
Whole House Air Filtration System http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=17723&Focus=300151#Comment_300151 http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=17723&Focus=300151#Comment_300151 Mon, 06 Feb 2023 17:50:57 +0000 Simon Still Posted By: Mike1
Posted By: djhWhy undersized - I'd have thought that was a recipe for a rapid failure and a lot of noise meanwhile?
If filtration is the only concern (as it appears to be), rather than providing a particular air change rate, a cheap unit permanently running on a low setting _may_ be adequate. It would probably depend on the level of filtration required, and what is giving rise to the need for filtration. Hence my question mark above.


How much money are you really going to save? You still need all the ducting and supply/extract hardware. You still need high quality fans. So the only saving would be the lack of a heat exchanger. But even in a leaky house you'd expect the heat exchanger to add some value to offset the cost of running the fans (vs running the fans without any heat exchange)]]>
Whole House Air Filtration System http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=17723&Focus=300315#Comment_300315 http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=17723&Focus=300315#Comment_300315 Thu, 16 Feb 2023 17:44:48 +0000 minisaurus
Moral of the story, measure your CO².</blockquote>

What is your definition of high?

Submarines use 3000 ppm I think]]>
Whole House Air Filtration System http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=17723&Focus=300317#Comment_300317 http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=17723&Focus=300317#Comment_300317 Thu, 16 Feb 2023 18:00:38 +0000 djh https://www.kane.co.uk/knowledge-centre/what-are-safe-levels-of-co-and-co2-in-rooms

What are safe levels of CO2 in rooms?

250-400ppm Normal background concentration in outdoor ambient air

400-1,000ppm Concentrations typical of occupied indoor spaces with good air exchange

1,000-2,000ppm Complaints of drowsiness and poor air.

2,000-5,000 ppm Headaches, sleepiness and stagnant, stale, stuffy air. Poor concentration, loss of attention, increased heart rate and slight nausea may also be present.

5,000 Workplace exposure limit (as 8-hour TWA) in most jurisdictions.

>40,000 ppm Exposure may lead to serious oxygen deprivation resulting in permanent brain damage, coma, even death.]]>