Home  5  Books  5  GBEzine  5  News  5  HelpDesk  5  Register  5  GreenBuilding.co.uk
Not signed in (Sign In)

Categories



Green Building Bible, Fourth Edition
Green Building Bible, fourth edition (both books)
These two books are the perfect starting place to help you get to grips with one of the most vitally important aspects of our society - our homes and living environment.

PLEASE NOTE: A download link for Volume 1 will be sent to you by email and Volume 2 will be sent to you by post as a book.

Buy individually or both books together. Delivery is free!


powered by Surfing Waves




Vanilla 1.0.3 is a product of Lussumo. More Information: Documentation, Community Support.

Welcome to new Forum Visitors
Join the forum now and benefit from discussions with thousands of other green building fans and discounts on Green Building Press publications: Apply now.




  1.  
    Debate open to all-comers to see what happens ... observations, experiences and thread links welcome.
    Issues: Ecology, Cost, heat store behaviour, compatability with wet & dry UFH, behaviour at installation etc etc ...
    Thanks,
    Mike.
  2.  
    A client of mine was all for a Limecrete slab till he compared the real world costs and used the £1000 he saved to buy another solar panel...

    J
    • CommentAuthorMike George
    • CommentTimeJul 3rd 2010 edited
     
  3.  
    Thank you both :smile:
  4.  
    Having read the protracted pimg-pong match referred to above (http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=1554&page=1)
    I'm still undecided from a CO2/emissions etc point of view, but in the mean time would like to pick out one technical point which may make my decision for me in the end ...

    "The main advantage of cement [used on its own] over lime is its 'setting time' It gains most of its strength very quickly - Partial set within 6hrs, quite hard within 24hrs Very hard within 30 days. Lime however can take a very long time to gain even partial strength, meaning the job often needs to be spread over a much longer period of time."

    My original question was about "OPC" vs Lime in relatively large floor slabs as opposed to as a mortar.
    I had heard that Limecrete "makes a better heat store" but was not clear in what way this could be the case.
    I had also heard that the setting &/or curing properties of limecrete make cracking more likely in a thick slab, but also make cracking less likely in a thin-film situation like layers of mortared bricks.

    My ground heat store is beginning to look like it will have sections made in different ways as a test bed for comparing methods, as there doesn't seem to be any other way of "proving" comparative efficiency.

    One section will be constructed with reclaimed bricks from on-site interleaved with insulation in such a way as to force a long path for heat to reach the top of the floor slab, thereby creating a time lag sufficient to set up an interseasonal store ...
    The heat for this section will be delivered by fluid in copper pipe, and the pipe will be run in the mortared planes between the layers of brick that make up the storing strata (as opposed to the insulation/diversion strata).

    My intuitive take on this is that a lime based medium would be better suited to running the pipes as it seems less likely than OPC to develop cracking in this thin-film situation (as opposed to being more likely in a thick slab) ... and if limecrete is indeed a better heat store maybe it would be a better conductor of heat from the pipes to the bricks?

    As ever any observations welcome .....
    • CommentAuthorchuckey
    • CommentTimeJul 4th 2010
     
    I would be very wary of using copper pipe to "bury" in lime or OPC. The reason is that any moisture in the lime/opc and any metallic compound anywhere will result in electrolysis and the possibility of the copper being corroded. I would use a plastic pipe because even the PVC sheathed copper pipes might have nicks through the plastic leading to corrosion.
    Frank
  5.  
    Ta!
    • CommentAuthorgb22
    • CommentTimeMar 10th 2016
     
    To re-open this thread as its exactly the question I'm trying to answer as referbing old stone farmhouse. Was originally planning to lay 50m2 of limcrete floor with UFH to keep the floor breathable and control moisture. However have now dug out the original concrete floor and found only a small bit of moisture under it, with the clay subsoil being rock hard and bone dry. My house has very good drainage around it and decent foundations, so am now questioning the extra expense, time and labour needed for Limecrete compared to standard materials in my situation.

    I am now seriously considering just putting in a DPM, pouring a thin concrete slab, 100mm of kingspan then UFH and either free flowing screed or standard 75mm cement/sand mix. Advantages are materials are over £1000 cheaper, and delivered ready mixed so will save a huge amount on labour compared to hand mixing the limecrete on site. Much faster curing times, much faster to lay. Better insulation as the solid board is cheaper than foamed glass so can afford to lay it thicker. Plus I can use the money saved to improve the insulation elsewhere in the house so in the long run will offset the higher carbon footprint by reduced heating needs.

    Am I missing something obvious or does this seem sensible?
    • CommentAuthortony
    • CommentTimeMar 10th 2016
     
    Has the house been live in?

    The thing that you could be missing is that heat or warmth drives away moisture, most houses are bone dry under the floors, I have taken loads up and understand why this is.

    Insulating the floor will make it slightly cooler under there and that in itself could make it damper, just something to beware of.

    I would spend on insulation, I always preferred to lay insulation under the concrete, then all the thermal inertia material is inside the thermal envelope which gives additional comfort.

    Will the walls be insulated? And how will the insulation join the floor insulation.
    •  
      CommentAuthorSteamyTea
    • CommentTimeMar 10th 2016 edited
     
    Not going to re-read this, but if Mike went for lime, has it set yet :wink:
    • CommentAuthorgb22
    • CommentTimeMar 10th 2016
     
    House has not been lived in for nearly 18 month now, and when it was I rarely had the heating on as was too expensive to run! Had a lot of rain this winter so was pleasantly surprised how dry it was under the concrete which was laid directly on top of clay with a lot of voids for moisture to potentially collect in.

    I've just spoken to a good local concrete firm we have used for farm work and they also suggested I can prob get away without a concrete slab foundation and just level off the clay with some sand to protect the DPM then put the solid insulation directly on this with the UFH and 75mm screed on top. Benefit of this means less digging and a thicker layer of insulation possible.

    As recommended on some other threads http://www.secondsandco.co.uk/ have some 130mm thick PIR board. It doesn't have any foil backing but works out cheaper than EPS so I'm considering using this with either 25mm or 50mm layer of foil backed PIR on top as will hopefully work out cheaper than buying all new board and be more effective. Any thoughts on this or experience of what quality the second hand boards from this company are like??

    Current plan is to plaster the walls level with lime then insulate internally with cork boarding from Ty Mawr. The boards will go down the edges of the UFH slab to meet the underfloor insulation. I'm hoping because the lime and cork is breathable what little moisture there is under the floor will wick up the walls and escape either through the cork boards or into the cavity of the stone wall. Cannot do EWI as in a conservation area.

    The lime will take forever to dry and cork boards are more expensive than dry lining with PIR but I don't think I can take the risk of trapping moisture in the walls as the wooden window and door lintels will all rot. However I might cheat a bit and dry line some of the walls which don't have timber in them and are at lower risk of rain penetration, depends how much money I have left in a few months time I guess!
    • CommentAuthorgb22
    • CommentTimeMar 10th 2016
     
    Just read another thread on here pointing out the foil coating has no insulating benefit without an air gap, so will go ahead with the cheaper solid insulation without foil and save myself £££. This forum is a goldmine :)
    • CommentAuthortony
    • CommentTimeMar 10th 2016
     
    I would want to see 100 structure so minimum without regs would be 100 concerted power floated with pipes and grid
    •  
      CommentAuthordjh
    • CommentTimeMar 10th 2016
     
    Posted By: gb22Just read another thread on here pointing out the foil coating has no insulating benefit without an air gap, so will go ahead with the cheaper solid insulation without foil and save myself £££. This forum is a goldmine :)

    The foil does two separate things:

    (1) if there's an air gap, it serves as a radiant barrier to reduce losses through radiation of heat. All radiant barriers need a small amount of free space next to them, I think.

    (2) it serves as a vapour barrier to stop gas escaping from certain types of insulation. Not relevant for EPS but it is for PUR, phenolic etc. The result of missing foil will be a smallish reduction in insulation over the years, as I understand it, and also makes the insulation more liable to collect water if any is present. I never researched it in any detail but I think it's probably a minor concern in your situation.
    • CommentAuthorgb22
    • CommentTimeMar 10th 2016
     
    Thanks for that Tony, a thicker screed makes sense to me. However by grid do you mean the screed should have steel mesh reinforcing which the UFH is attached to, I was just going to staple the UFH pipe direct to the insulation? The screed I'm thinking of using is not self leveling but a readymixed mortar with fibre in it, which from memory I think should replicate the strength of A142 steel mesh.

    I wasn't too concerned about the structural strength of having a slab considering what I have just dug up was done by my grandparents in the 1960's and was between 30mm - 100mm. They just poured it against the skirting boards which have long since rotten away thus providing no structural support. On the plus side it was nice and easy to dig up!
    • CommentAuthorgb22
    • CommentTimeMar 10th 2016
     
    Thanks djh, I have been looking into this more and found I can prob get 200mm EPS at a similar price than the second quality PIR. Going to ring for some quotes tomorrow. I am concerned the seconds will be damaged and uneven so harder to lay, and probably the reason they don't have foil is because they were rejected in the factory before they got to that stage, so will almost certainly not have the insulation properties of new boards. Also read somewhere that EPS is better suited for going under slabs as it is more resistant to moisture penetration than PIR. The downside is I will have to dig down a little further but would rather put the work in now so don't store up problems for the future.
    • CommentAuthortony
    • CommentTimeMar 10th 2016
     
    I would use a reinforcing or anti cracking mesh, do you need
    to pass building regs?
  6.  
    We laid a limecrete slab in a building conected to our house. It was comprised of a LECA bottom layer, a leca and pumice stone mix in the middle layer with UFH pipes and then a lime screed and stone slab covering. The middle layer of lime was hard enough to walk on the next day. We left it a month to harden before laying the UFH pipes, but I dobt that we really needed to be so cautious.

    The building had a damp issue that has been solved by a combination of limecrete slab, french drain and sheepswool/lime IWI. Its a lovely, warm space in there and a model that the main house is being based on (except I'm using woodfibre batts rather than sheeps wool for IWI).
    • CommentAuthorSilky
    • CommentTimeMar 11th 2016 edited
     
    I'm in a similar situation and only have around 30 cm depth to play with. I also have the added complication of potential lateral water penetration due to being in a flood zone. The base is a heavy, firm clay. My plan is simply to fill with glass foam aggregate, 20 cm, and compact this with a wacker plate, then 10 cm limecrete screed finish on top. Geo textile membrane under the foam glass to keep it clean and under the limecrete. No DPM's. I wrote on here before because I was curious about why there cannot be a pourable limecrete, i.e. adding a plasticizer to the mix to make it flow, which could be done at the cement works? And/or simply making a runny mix, lower compressive strength, but surely enough for a domestic floor and more water in mix = increased permeability, which is the raison d'etre for using limecrete? Additionally I'm curious about using crushed limestone aggregate in the mix, Seems crushed limestone will increase the insulation of the limecrete ( see "liquid limestone" in Australia ), any one have experience with this?

    I'm nearly there now.. so in a few weeks I will go to the cement works here in Germany and ask them what they can do, if not then I have the same dilema, either mixing limecrete by hand, extra time, expense, effort. Or copping out and going for a concrete slab. p.s. There is an architect here in Germany, specifying just compacted foam glass with clay tiles on top... as a breathable, insulated and flood proof floor. But I still like the idea of having a floor slab/screed of some sort..
  7.  
    Another option would be to have a hybrid system where kingspan insulation is fitted in the centre of the room to within a few feet of the surrounding walls, with the wall area filled with LECA or foamglass. The whole lot then covered with limecrete.

    This will give better u-values for the majority of the floor area but allow the edges to be breathable, preventing any water from being forced into the walls.

    If I had my time again with the outbuilding, I think I'd use the hybrid approach.
    • CommentAuthorjfb
    • CommentTimeMar 11th 2016
     
    i put 200mm graphite eps under 100mm reinforced concrete slab in an old farmhouse where I was initially considering a breathable build up. No problems after 2 years around the external walls. I have wood fibre insulation on the inside of all external walls and MVHR and pretty airtight as well which all helps.

    I'm happy I did - certainly cheaper than the limecrete method.
    •  
      CommentAuthordjh
    • CommentTimeMar 11th 2016
     
    Posted By: Pile-o-StoneAnother option would be to have a hybrid system where kingspan insulation is fitted in the centre of the room to within a few feet of the surrounding walls, with the wall area filled with LECA or foamglass. The whole lot then covered with limecrete.

    This will give better u-values for the majority of the floor area but allow the edges to be breathable, preventing any water from being forced into the walls.

    It may not matter but this approach would probably lead to the floor near the wall being colder. The perimeter already tends to be colder because of edge effects and this scheme would increase that tendency. It may make no difference but perhaps it may increase any condensation on the floor near the walls. Obviously exactly what happens will depend on a whole lot of factors.
    • CommentAuthorgb22
    • CommentTimeMar 11th 2016
     
    I have no doubt a limecrete slab and the glass pumice insulation are the best option for a house with damp problems and no DPM membranes in the walls. However they are far more expensive in terms of both materials and labour to hand mix than bog standard EPS and ready mixed screed. In my case I have decided to go for the cheaper option whilst also increasing the insulation thickness under the slab to reduce running costs long term. Limecrete both needs to dry out, which only takes a few days as you point out Pile, however just like OPC but slower it also needs to cure which is a chemical reaction with air, a process that never stops so ideally needs to be left exposed for as long as possible before laying floor coverings etc.

    Silky - there are companies who can deliver ready mixed limecrete or mix the amount you need on site but when I got quotes they were way out of my league. I highly doubt you can get a free flowing limecrete, I would guess any plasticizer would seriously compromise the breathability and so there would be no benefit over using much cheaper OPC products. Adding excess water to make it flow would also make the limecrete so weak your floor covering would likely fail, or cracking could damage the UFH pipework?

    Anything with air voids in it will insulate, crushed limestone as far as I know is a solid material so no insulating properties whatsoever? My house has 70cm thick solid stone walls, however from an insulation point of view they are useless!

    I think the foamed glass does compact down very hard but I wouldn't risk laying UFH without a decent solid screed which won't crack. Maybe a good idea if not laying UFH though.

    Tony - I am not being inspected for building regs but am trying to make sure I surpass them especially regards insulation. With the floor I know in theory I should put in a layer of hardcore and a strong slab to meet the regs. However we have laid hundreds of square metres of concrete in the farm buildings, only 15cm thick C30 slab with fibre, laid directly on the clay with no DPM or steel mesh in most of it. It gets hammered by 10 tonne plus tractors driving over it all day but as the clay is so hard we have had no problems with cracking or water coming through. However good drainage around the building is critical to make sure water doesn't get in and weaken the clay.

    As my house has lean to buildings on three sides and the ground level on the 4th side is below the new floor I am confident I can keep water out so no point digging deeper just to put in hardcore. Apparently its harder to staple UFH direct to EPS compaired to PIR so will prob cable tie it to A142 steel mesh where needed as we have some spare lying around anyway. Despite building regs it should be bomb proof by the time we are finished!

    Thanks for your thoughts everyone :)
    • CommentAuthorgb22
    • CommentTimeMar 11th 2016
     
    Thats exactly what I'm looking at jfb, what thickness wood fibre insulation did you use and are you happy with it?
    • CommentAuthorgb22
    • CommentTimeMar 11th 2016
     
    We are also fitting MVHR as convinced this will transform the air quality in the house and eliminate damp.
    • CommentAuthorjfb
    • CommentTimeMar 11th 2016
     
    i used mostly 60mm IWI, some 100mm and 20mm in reveals for windows.
    Went for the cheaper boards from Steico in the end (couldn't really justify the cost for the pavadendro that i was looking at originally) and all seems good so far. Good attention to gap filling needed for any boards that didn't meet up perfectly as the steico boards only butt joint.
    Also - consider how you are going to deal with the airtightness layer. For this sort of method the render behind the IWI is the airtight layer and so you need to pay attention to how it joins onto the roof airtightness layer .I also used tapes for around windows that have a fleecy bit that gets rendered into the render behind the IWI. All worth paying attention to if your are aiming for MVHR.
    Good luck.
    • CommentAuthorgb22
    • CommentTimeMar 11th 2016
     
    Thanks jfb thats a big help. I was thinking about using cork boards from Ty Mawr but may go down your route depending on what works out as the most cost effective method. I will make the house as air tight as possible within budget, its one of the benefits of doing the work myself.

    This is probably a rooky question but did you do your first fix wiring and plumbing before applying the render under the IWI or afterwards? My electrician suggested I should plaster the walls level first and then he will know where the finished wall surface will be so he can fit socket boxes etc before the IWI layer goes on. This would mean we would have to notch out the cable runs in the IWI, to me it makes more sense to bury the wiring in the base coat plaster so we have a flat surface to stick the IWI to and fit socket boxes after? Will obviously cut out holes for electrics in IWI before fitting, assuming the other half doesn't change her mind about where she wants them!
    • CommentAuthortorrent99
    • CommentTimeMar 11th 2016
     
    Posted By: gb22Thanks jfb thats a big help. I was thinking about using cork boards from Ty Mawr but may go down your route depending on what works out as the most cost effective method. I will make the house as air tight as possible within budget, its one of the benefits of doing the work myself.

    This is probably a rooky question but did you do your first fix wiring and plumbing before applying the render under the IWI or afterwards? My electrician suggested I should plaster the walls level first and then he will know where the finished wall surface will be so he can fit socket boxes etc before the IWI layer goes on. This would mean we would have to notch out the cable runs in the IWI, to me it makes more sense to bury the wiring in the base coat plaster so we have a flat surface to stick the IWI to and fit socket boxes after? Will obviously cut out holes for electrics in IWI before fitting, assuming the other half doesn't change her mind about where she wants them!


    Are you using thicker cable to take into account that it's going through Xmm of insulation on it's way to the socket box?
    •  
      CommentAuthordjh
    • CommentTimeMar 11th 2016
     
    Posted By: torrent99Are you using thicker cable to take into account that it's going through Xmm of insulation on it's way to the socket box?

    The part that is against (or in) the wall is on an uninsulated surface, so is fine. The part that goes through the depth of the insulation isn't long enough to have to be derated.
    • CommentAuthortorrent99
    • CommentTimeMar 11th 2016
     
    Really? Even with 50+mm of insulation?

    e.g.
    https://www.tlc-direct.co.uk/Book/4.3.6.htm

    (I know it's the old regs, but the principles still apply)

    I only ask because I'm struggling with this myself.
   