Posted By: HerodotusThe obvious simple solution in a UK property would be a vented DHW cylinder with two coils, one from a wood boiler and one from the solar (with the option to add a buffer for UFH later). The problem with this is that, living in a single storey building with a flat roof, the venting/expansion requirement is tricky to do. I don't want to have to have a pump just to get adequate DHW pressure. Is there a way round this that I'm missing?
That leaves me with some sort of thermal store option - dumping the heat from boiler + solar + electric into a big tank of water and then extracting it into DHW via an internal coil/internal tank/external PHX. In the future we could potentially use the store water to run UFH as well. On paper this looks like the most suitable option for us, but it's also going to be expensive + I'm worried that for the quantity of DHW we need it's pretty wasteful heating a big thermal store. I'm also lost on the whole internal coil vs external PHX thing - I'm obviously keen to maintain as much stratification as possible so that we can get sensible temp DHW with a minimum size store, but I can't work out which system is better for that. PHXs can return cool water to the bottom of the tank, but only if the hot water demand is enough to coil the primary circuit water significantly; coils give you a certain amount of stored hot water + they're simpler + their impact on the cylinder water isn't dependent on speed of DHW demand, but I'm guessing that even the best designed coil is going to destratify the cylinder more than a PHX system operating in ideal conditions...
We're at 1200m altitude and it does freeze here occasionally - solar collector probably needs to be indirect with glycol I guess
Posted By: djh…if not then PV is a lot simpler and I believe is cost competitive.From my doodling on the subject:
Posted By: djhOr a drainback system, or a freeze-proof silicone-tubed system.Or cycle a bit of water through the collectors to warm them during cold nights. It's what I'm planning to do, combined with an emergency drainback which needs to be reset and refilled manually.
Posted By: Chris P BaconDidn't the Spanish government apply some mad tax so that you effectively had to pay the same amount for electricity whether you produced it yourself or got it from the grid? Or has that been reversed?
Posted By: Herodotusdjh - I'm not sure exactly what you mean about your PHX - are you saying that it keeps the secondary water inside the PHX pre-heated to 30? And that this is causing the primary circuit to run more than it needs to? This is exactly the sort of reason why I want to build me own control logic!
We recycle grey water + have very short pipe runs so warm-up times aren't a huge issue for us. If your PHX is returning water that is overly warm to the bottom of the store, that would suggest that the PHX is incorrectly sized for the application, no? Obviously it's not going to be as cold as mains input (and you probably wouldn't want it to be) - but it should be extracting enough heat to get you down to around 30C, shouldn't it?
I'd love to be convinced that a well-designed coil was the answer here, because it means I don't need an extra pump and a flow switch (not to mention the PHX itself) - but I'm still nervous about pumping mains-temperature water (which can be bloody cold here in winter) through the middle of the store - it seems like the internal cooling effect is much more likely to destratify things than a properly configured return from a PHX - but then I guess the key is in that "properly configured" bit! Can anyone with a modern TS with a full-height coil share their experiences in this regard?
Posted By: djhJust remembered, another option is a tank-in-tank design. They're common in Denmark I believe. I don't know what the pros and cons are though.
Posted By: ringiThey do not help unless you are willing to use a "sealed" DWH system, or have a location high up for the header tank.
Posted By: djhPosted By: ringiThey do not help unless you are willing to use a "sealed" DWH system, or have a location high up for the header tank.
I don't understand why the requirements would be any different to a thermal store with a coil or PHE?
Posted By: ringiThe coil in a thermal store and a PHE contains very little water, therefore there is very little risk of a large explosion when this water expands. The "inner tank" in a "tank in tank" often contains at least 100l of water, making it no different to a normal 100l DWH tank as far as the risk of it exploding etc.
Posted By: HerodotusFrom a safety perspective, I'm pretty uncomfortable about a sealed system with a solid fuel boiler. Even with pressure relief valves and maybe a heat-dump towel rail or somesuch, the prospect of having a potential bomb that could flatten my house if I overstoke the boiler makes me twitchy.
Posted By: ringiHence it seems best to separate the DWH tank from the thermal store.