Home  5  Books  5  GBEzine  5  News  5  HelpDesk  5  Register  5  GreenBuilding.co.uk
Not signed in (Sign In)

Categories



Green Building Bible, Fourth Edition
Green Building Bible, fourth edition (both books)
These two books are the perfect starting place to help you get to grips with one of the most vitally important aspects of our society - our homes and living environment.

PLEASE NOTE: A download link for Volume 1 will be sent to you by email and Volume 2 will be sent to you by post as a book.

Buy individually or both books together. Delivery is free!


powered by Surfing Waves




Vanilla 1.0.3 is a product of Lussumo. More Information: Documentation, Community Support.

Welcome to new Forum Visitors
Join the forum now and benefit from discussions with thousands of other green building fans and discounts on Green Building Press publications: Apply now.




    • CommentAuthorborpin
    • CommentTimeMar 9th 2022 edited
     
    Following on from the replacement of my MHRV unit (http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=17402) I am beginning to wonder if I have been vastly over ventilating the house.

    With far more data available to me from the new unit and the addition of more CO² and Humidity sensors, the pattern I see suggests that I can turn the unit right down. The house is 570 m³

    Firstly Humidity - I have discovered the air in the house is really dry; down to 30% humidity. I've bought a humidifier, but even in my relatively small study it is only very slowly bringing the RH up (and running 100%). To me this indicates the fabric of the house is very dry. To be fair, the outside humidity is only 41% today!

    Secondly CO² - again this stays low during the day (as long as I leave the study door ajar - see other thread) and even in the evening, with 2 of us here, the large open plan room does not rise above 700ppm.

    I also have an IKEA air quality sensor (2.5 PM) although I have not been collecting data long enough to examine what it might be telling me or whether I believe it!

    The question really is, is the purpose of home ventilation largely to control humidity and CO² (and smells to some extent)? If so, I'm reducing my ventilation rates!

    As an aside, I felt part of the issue with the old unit was that it basically ran at the same rate all the time. I am going to put in an automation that runs it at higher speeds for short periods each day just to exercise the fans.

    Thoughts?

    “If you can't measure it, you can't manage it.”
  1.  
    That's right. Previous threads have discussed that the rate of ventilation required, is very much dependent on the dryness of the outdoors air.

    Cold outside -> less absolute humidity outside -> less ventilation needed.
    Mild outside -> more absolute humidity outside -> more ventilation needed
    Warm outside -> turn off electric fan and open windows.

    Any ventilator that runs at a constant flow rate (in m³/h or ACH or l/m²/h) is over ventilating for most of the time. You just need enough ventilation to get down to the desired humidity and CO2 on that day.

    Your MHRV will recover much of the sensible heat from over ventilating, so you are only paying for the fan power, but it will not recover the latent heat from evaporating moisture from (say) damp shower cubicles or wet washing. This might/not be enough to matter to you.

    If you desire it to be 40%RH indoors then you have to ventilate more than if you desire 60%. Your 30% means spending too much on ventilation, especially if you also spend on a humidifier.

    The CIBSE guide suggests that if the humidity is well managed then the CO2 will automatically be ok, but humidity is buffered so it might not spike up/down as fast as CO2 does.


    ISTR that DJH measured his air change rate of around 0.2-0.3 ACH at which he had fairly low humidity.

    If you are not using particular rooms, no need to ventilate them.
    • CommentAuthortony
    • CommentTimeMar 9th 2022
     
    CO2 at 700 indicates to me very under ventilated.
  2.  
    Whats the feeling , knowledge on a good CO2 level to aim for.

    Ive seen suggestion <800 is good but theres very little out there backing it up.
    I think advice (pre covid) for schools , office etc is < 1500
    • CommentAuthortony
    • CommentTimeMar 9th 2022
     
    With ventilation below 500 is good, above 600 poor above 800 dire

    Depends on how many people/animals are in the house.
  3.  
    outside is 400-450

    what are the negatives of higher CO2 , say at 800
  4.  
    CIBSE say that 1000ppmv is well ventilated, and more is OK but indicates the room might smell sweaty.

    https://www.cibsejournal.com/cpd/modules/2011-04/

    Tony the lower numbers we've heard recently are from where people are trying to hyper-ventilate public spaces to control Covid, and are using CO2 as a proxy measure, then opening windows in January, IE the downside of low CO2 is just you need more ventilation hence more heat losses. Might not be an issue for Mr&Mrs Borpin.

    HSE say that above 1500ppm indicates that more ventilation is needed to disperse Covid, eg in a workplace where different households meet.
    https://www.hse.gov.uk/coronavirus/equipment-and-machinery/air-conditioning-and-ventilation/identifying-poorly-ventilated-areas.htm
    • CommentAuthorjamesingram
    • CommentTimeMar 9th 2022 edited
     
    Will, thats the info I've been working with the last decade or so.

    Im interested in why some people suggest lower.
    other than the basic fresh airs good for you, which is certainly intuitive.

    the US HVAC trade body have always suggested lower but Ive never really found anything substantial to back it up.

    my home (120m2 5 occupants, MHRV but not that air tight probably, 3G, super insulated , close to zero heating)
    sits at 500-1000 depending on occupants, if its goes over 1200ish I ventilate by opening windows.
    10 people round and it'll quickly pop up to 2000 in an hour
  5.  
    I do remember a Mark Brinkley article years ago suggesting ventilation was over rated , again it was just looking at some basic numbers rather than coming from some trong building science research
    •  
      CommentAuthordjh
    • CommentTimeMar 9th 2022
     
    Posted By: borpinFirstly Humidity - I have discovered the air in the house is really dry; down to 30% humidity. I've bought a humidifier, but even in my relatively small study it is only very slowly bringing the RH up (and running 100%). To me this indicates the fabric of the house is very dry. To be fair, the outside humidity is only 41% today!
    Something is definitely odd there. I've only ever seen humidity as low as 30% once, at work with a new MVHR system that hadn't been setup properly :( Itchy eyes and all the rest. But I very rarely see the external humidity below 70%. Internally it mostly sits between 40% and 50% these days. The first five years were completely different. How much buffering is there in your house?

    I thought your MVHR was an enthalpy-recovery type, so the air shouldn't be getting dry?

    You could try turning it off and see what happens (you won't die instantly!).
    • CommentAuthorEd Davies
    • CommentTimeMar 9th 2022
     
    Posted By: borpin sometime near the middle of the afternoon of 2022-03-09: “To be fair, the outside humidity is only 41% today!”

    Where's that and how was it measured? Scanning around

    https://www.ventusky.com/?p=52.83;-1.66;6&l=humidity

    for 15:00 this afternoon finds humidities down to 50% or so in largish parts of the NE of England (around Leeds to Newcastle) with everywhere else being 60% or higher.

    (PS, went to look on your website for location clues but it wasn't responding and eventually gave some sort of database error.)
  6.  
    Very localised temperature differences can have large effects on the Relative humidity, an extra couple of degrees in a sunny spot can swing the RH by 10 %. (Outdoors or indoors)


    But it's the Absolute humidity in g/m³ that matters here:

    the net water removed from the house = the m³h of ventilation x ((the g/m³ humidity in the outgoing house air) - (the g/m³ humidity in the incoming atmospheric air)
    • CommentAuthorborpin
    • CommentTimeMar 10th 2022
     
    Posted By: Ed DaviesPosted By: borpin sometime near the middle of the afternoon of 2022-03-09: “To be fair, the outside humidity is only 41% today!”
    My weather station (although to be fair I was looking at the wrong dial). Livingston Scotland (graph last 24Hrs).

    Posted By: djhThe first five years were completely different. How much buffering is there in your house?
    Been built 9 years now so the building has settled down. However, I think it has got overly dry because it has been over ventilated.

    Posted By: tonyCO2 at 700 indicates to me very under ventilated.
    From all I have read, 700ppm is perfectly acceptable level for comfort. My study CO² meter triggers me to open the door at 750ppm.

    Posted By: WillInAberdeenAny ventilator that runs at a constant flow rate (in m³/h or ACH or l/m²/h) is over ventilating for most of the time. You just need enough ventilation to get down to the desired humidity and CO2 on that day.
    Ok, good to know. I can now automate this quite easily.

    Posted By: Ed Davies(PS, went to look on your website for location clues but it wasn't responding and eventually gave some sort of database error.)
    Ah, thanks. Not done much recently and it needs a good sort out and update of the backend. Another job for the list!
      Screenshot 2022-03-10 074615.png
    • CommentAuthorRobL
    • CommentTimeMar 10th 2022
     
    We had low RH a few weeks after turning on the mvhr, the default settings were a bit aggressive. Itchy skin, the works, people were getting desperate. I turned it right down, and then added a CO2 sensor and turned it down some more. Now it's usually set to 2%, increasing from there based on RH and humidity. Have some lovely data, thought I'd add in temp & RH in & out here (Cambridge).
      RH and Temp in an out.JPG
    • CommentAuthorEd Davies
    • CommentTimeMar 10th 2022
     
    Just checked the weather at Edinburgh airport for yesterday afternoon. From 12:50 to 15:20 the temperature was 11°C and dewpoint 3°C from which I get a relative humidity of 57%. That's quite low but I'm still a bit sceptical about Borpin's readings of not a lot more than half that. It could be a matter of sensor calibration or, as WiA suggests, local effects which maybe don't reflect the actual absolute humidity.
    •  
      CommentAuthordjh
    • CommentTimeMar 10th 2022
     
    Posted By: RobLNow it's usually set to 2%
    That sounds like a Reg unit. What's that in m³/hr (or l/s if you must :devil:)
    • CommentAuthorRobL
    • CommentTimeMar 10th 2022
     
    2% of full :-)
    From the datasheet that'll be around 7m^3/hr.

    For interest, attached a pic of dewpoint indoor and outdoor. There's all sorts of ways of calculating dewpoint... I chose the simplest, it's good enough, I'm an engineer, not a scientist :-)

    Tdp = T - (100-RH)/5
      Dewpoint.JPG
    •  
      CommentAuthordjh
    • CommentTimeMar 10th 2022
     
    Posted By: RobL2% of full :-)
    From the datasheet that'll be around 7m^3/hr.
    Thanks. That sounds like a ridiculously low ventilation rate, but if it works for you :)

    I don't understand the manufacturer's logic in labelling the MVHR with a meaningless value like 2%. It presumably knows the actual rate, assuming it's a constant volume system, so why wouldn't it tell you that?

    BTW, a couple of weeks ago we discovered that insulated blinds really do work. We have honeycomb blackout blinds in our bedroom (honeycombs lined internally with silver foil/paint/whatever). We noticed some dark grey spots on the bottom edge seal of one window that has a blind mounted on the outside of the frame. (i.e. the blind covers the whole of the window reveal). We believe they were spots of mould on the surface of the seal. I used an infrared thermometer to check the temperature in that corner and sure enough it was just below the dewpoint. When the blind is open it's well above the dewpoint (PH design famously guarantees this temperature). So now whilst it's cold outside we don't close the blind the last couple of inches so there's more air movement there. The other windows in the room don't suffer from the problem, perhaps because the blinds are mounted inside the frame, right next to the glass. So the bottom rail of the blind, which is made of metal, acts as a thermal bridge between the seal at the glass face and the internal air in the room.
    • CommentAuthorborpin
    • CommentTimeMar 11th 2022
     
    Posted By: Ed DaviesJust checked the weather at Edinburgh airport for yesterday afternoon. From 12:50 to 15:20 the temperature was 11°C and dewpoint 3°C from which I get a relative humidity of 57%. That's quite low but I'm still a bit sceptical about Borpin's readings of not a lot more than half that
    Which is quite a way away, out in the open, 200M lower and close to the sea but YMMV.

    Posted By: RobL2% of full :-)
    I can see me getting to that. A note though, do exercise the fans at different speeds - I am sure the fact the old unit ran at a constant rate over an extended period contributed to the early failure.

    Posted By: djhI don't understand the manufacturer's logic in labelling the MVHR with a meaningless value like 2%. It presumably knows the actual rate, assuming it's a constant volume system, so why wouldn't it tell you that?
    I think because it depends on the static pressure of the system. I think that is related to the effort of pushing the air through and I am not sure how to measure that.
      Screenshot 2022-03-11 133541.png
    • CommentAuthorborpin
    • CommentTimeMar 11th 2022
     
    Posted By: Ed DaviesFrom 12:50 to 15:20 the temperature was 11°C
    The sun came out (it does that occasionally in Scotland)!
      Screenshot 2022-03-11 133907.png
    •  
      CommentAuthordjh
    • CommentTimeMar 11th 2022
     
    Posted By: borpin
    Posted By: djhI don't understand the manufacturer's logic in labelling the MVHR with a meaningless value like 2%. It presumably knows the actual rate, assuming it's a constant volume system, so why wouldn't it tell you that?
    I think because it depends on the static pressure of the system. I think that is related to the effort of pushing the air through and I am not sure how to measure that.
    I'm not quite sure what you mean by 'it'. The MVHR has to measure the flowrate in order to deliver it. The static pressure might determine how much energy it has to use to do that, as does the wind strength at any particular time, but the flowrate is the actual deliverable and is what is stated to be constant. My 'standard' setting is 125 m³/hr set according to regs, and I very rarely see the actual value less than 124 or more than 127.
  7.  
    I very much doubt that the airflow measurement on a domestic MHRV has an accuracy better than +-10%, because you need an expensive step up in technology to measure air flows more accurately than that, eg to measure down to 2% of range.

    I'd be less surprised if the motor speed is controlled by PWM and the "2% of full" refers to the pulse width, which is not quite the same as the fan speed being at 2% of maximum speed.

    As Borpin’s colourful graph shows, the air flow rate depends on fan speed and back pressure in quite a complicated way, so 2% of full fan speed could give you a lot more than 2% of full air flow rate.
    • CommentAuthorborpin
    • CommentTimeMar 11th 2022
     
    Posted By: WillInAberdeenI'd be less surprised if the motor speed is controlled by PWM and the "2% of full" refers to the pulse width, which is not quite the same as the fan speed being at 2% of maximum speed.
    Yes I agree, I think it is a % of maximum and the maximum depends on the static pressure.

    I've been investigating measuring the static pressure and it doesn't seem that tricky, just need to get a meter. It is also clear that too much static pressure can have a detrimental effect on the unit. So if your vents are too closed, you could easily end up with too much static pressure.
    •  
      CommentAuthordjh
    • CommentTimeMar 11th 2022
     
    Posted By: WillInAberdeenI very much doubt that the airflow measurement on a domestic MHRV has an accuracy better than +-10%, because you need an expensive step up in technology to measure air flows more accurately than that, eg to measure down to 2% of range.
    Dunno. Apparently it uses a vane anemometer. It would seem a bit strange indicating down to single m³/hr differences if they're only measuring 10 times that. My point is that the device is designed to deliver a specific airflow rate, and the duct resistance is simply a fact of life it has to deal with in each individual installation (obviously there are specs for the acceptable ranges of resistance). Within those limits it should deliver identical airflow performance. That's what the customer wants, expects and pays for. I've asked them to clarify. This is true for all constant flow MVHR units, is it not?