Home  5  Books  5  GBEzine  5  News  5  HelpDesk  5  Register  5  GreenBuilding.co.uk
Not signed in (Sign In)

Categories



Green Building Bible, Fourth Edition
Green Building Bible, fourth edition (both books)
These two books are the perfect starting place to help you get to grips with one of the most vitally important aspects of our society - our homes and living environment.

PLEASE NOTE: A download link for Volume 1 will be sent to you by email and Volume 2 will be sent to you by post as a book.

Buy individually or both books together. Delivery is free!


powered by Surfing Waves




Vanilla 1.0.3 is a product of Lussumo. More Information: Documentation, Community Support.

Welcome to new Forum Visitors
Join the forum now and benefit from discussions with thousands of other green building fans and discounts on Green Building Press publications: Apply now.




  1.  
    I remember reading somewhere [can't remember where] that using steady state calculations; the maximum heat loss through a ground bearing slab is predicted to be around 10% of the total for a building. Obviously this varies with the introduction of insulation. Is the 10% figure correct? If so how much of a saving is made by the introduction of insulation and how quickly does the saving diminish as u-values are reduced? At what point do steady state calculations predict that the otimum level of insulation will be reached?

    Anyone care to have a stab at some ball park figures?
    • CommentAuthortony
    • CommentTimeOct 12th 2007
     
    10% is too high. Very little saving is made by introducing insulation, Define optimum and steady state.

    The problem I have at the moment is that the temperature of the ground under a building is taken to be that of the world arround and it is not it is much warmer than that and as a consequence the heat losses are a lot lower. Un-traditional thinking this is.
    • CommentAuthorMike George
    • CommentTimeOct 12th 2007 edited
     
    Optimum: the level [either finacial or environmental cost] at which increasing the thickness of insulation becomes unviable

    Steady state: calculated according to the methodology used for u-values, IE by reference to conductivity of materials as tested in a hot plate under controlled conditions.

    I'm not a traditionalist either.
    • CommentAuthortony
    • CommentTimeOct 13th 2007
     
    In general no insulation is needed under the middle of the floor slab of a building. So this seems like another case of "belt and braces approach giving rise to excessive wastefulness".

    There is a good case for having insulation round the edge of a floor slab and the place where it is most needed usually is where the cavity insulation or wall insulation stops. This area has for long and still often is a designed in and approval of area of thermal bridging. Disproportionate amounts of heat loss occur here.

    In economic terms looks to me very silly spending on insulation of an even thickness all under any slab. Further having better insulation under the slab than arround the edge is not spending in the right place.

    Good thread Mike. Keep talking about this and we may change the world!
    • CommentAuthortony
    • CommentTimeOct 13th 2007
     
    Insulation will slow the passage of heat but will not set up temperature differentials per say. Thus heat lost through the under slab insulation will warm up the sub strata and once this has happened the insulation is doing nothing ( this statement is not entirely true but very nearly ). Once warm under the insulation then it cant do anything much of use? can it We are back to steady state theories again?

    The above argument does not apply to walls or roofs where the heat is lost to the air surrounding the building and is quickly transported away. There is a substantial temperature differential across a wall but under the house there is not rather a gradual temperature gradient and much slower heat flows result.

    This only applies to ground bearing solid floors.
    • CommentAuthorbayouboy
    • CommentTimeOct 16th 2007
     
    The exception is the case of underfloor heating in a solid build up. There the temperature differential is much greater and you are losing heat directly from your (fossil fuel) heating system.
    • CommentAuthortony
    • CommentTimeOct 16th 2007
     
    The thing is that the stuff underneath will get a lot warmer too indeed in steady state it will get to very nearly the same temperature as the water in the pipes.

    Get out of that!
    • CommentAuthortony
    • CommentTimeOct 17th 2007
     
    No one want to have a try?
    •  
      CommentAuthorfostertom
    • CommentTimeOct 17th 2007 edited
     
    Posted By: bayouboyunderfloor heating in a solid build up. There the temperature differential is much greater and you are losing heat directly
    Posted By: tonythe stuff underneath will get a lot warmer too indeed in steady state it will get to very nearly the same temperature as the water in the pipes
    Not unless the stuff underneath is separated from the outside air by a long path length of adjoining 'stuff', either by downstand insulation, e.g. cavity insulation carried down to top of strip found. Failing that, the stuff underneath will be sucking heat most efficiently out of the pipes and wasting it, ultimately to outside air.
    • CommentAuthortony
    • CommentTimeOct 17th 2007
     
    OK then tell me more about long path length -- how long is long?
    •  
      CommentAuthorfostertom
    • CommentTimeOct 17th 2007
     
    At 1m per month travel-rate of the temp wavefront through the ground, multiplied by what, 6months? of heating season, that's a path length of 6m, before the travel reverses, as the slab heating stops and the ground surface becomes warmer than the slab. That's 3.5m of downstand insulation below slab top (heat travelling down, under the bottom of the insulation and up outside of it to just short of ground surface)! That's why it looks easier to forget downstand for this application, instead do a 6m wide horizontal skirt below topsoil level, around the building's perimeter (or 'umbrella' as the American call it - because they incorporate a membrane along with the insulation, to keep the subsoil dry, preventing rain/snow melt from percolating down, taking the stored heat away with it).
    • CommentAuthortony
    • CommentTimeOct 17th 2007
     
    Not sure that is so relevant but I would be interested to know the U value of 6m of soil.

    The more we talk about this the more crazy under slab insulation sounds and the more in favour of down stand insulation I become.

    I think that 5 m of soil gives arround about 0.2 ? so no insulation needed under the middle of almost all floors! QED
    • CommentAuthorNeil K
    • CommentTimeOct 17th 2007
     
    Has there been any monitoring under an uninsulated slab? It would be good to know if this had been proven.

    Only other things that come to mind are:

    Is Fostertom's comment about the ground temperature reversing right? I was not expecting the ground temp to change at the depth below the slab much during the year. Ambient ground temperature below the topsoil level here in Orkney is about 7C all year round. The temperature in the house is unlikely to drop below 19 most of the year, so I am not sure this reversal can take place.

    Second item is about whether the ground is indeed a solid mass. With ground water movement I assume there must be a lateral transport of water. I expect it isn't much as the velocity is likely to be low, but given water has a much greater specific heat capacity than air I would have thought that this might be an issue.

    Finally: Well done for posting this topic up. Checking on 'common wisdom' is always refreshing, and occasionally illuminating.
    • CommentAuthortony
    • CommentTimeOct 17th 2007
     
    Yes water can be a problem but the vast majority of houses are very dry underneath.

    Think about it -- if the house is 19 then the ground immediately under the house will be 19 too. There will be a temperature gradient away from the floor.

    It may well look like a bubble under the house. It will also be dynamic and once the heating goes off some heat will tend to flow back into the house again.
  2.  
    Some papers with research on ground under slab on grade, see page on floor properties.
  3.  
    On wet ground
    • CommentAuthorhowdytom
    • CommentTimeOct 19th 2007
     
    Very interesting links Jeff, found the typeface hard to read on the second one though.
    • CommentAuthortony
    • CommentTimeOct 19th 2007
     
    Thanks Jeff -- paper one is pretty conclusive evidence to support the idea that I have been pushing here for ages that heavyweight houses are more comfortable to live in than lightweight ones in our climates. Please don't start Paul -- you cheat by running your heating/cooling 24/7.

    Very interesting to see that they split the floor slab into two zones -- the edge 0.75m and the central bit. Good case for not insulating under most of the floor, and only a small step away from forgetting it all together and going for perimeter insulation.
    • CommentAuthortony
    • CommentTimeOct 19th 2007
     
    In the first paper the authors have taken the temperature of the ground at one metre below the slab to be the average seasonal ground temperature. This is WRONG in my opinion and will lead to higher heat losses than actual ones. There are lots of reasons that it is not right.

    If we cant get the models right what hope is there for getting it right in the real world?
  4.  
    Posted By: tonyVery interesting to see that they split the floor slab into two zones -- the edge 0.75m and the central bit. Good case for not insulating under most of the floor, and only a small step away from forgetting it all together and going for perimeter insulation.


    Does that mean that a 0.75m insulated external wing allows the slab to be uninsulated (effective R4)?



    Posted By: tonyIn the first paper the authors have taken the temperature of the ground at one metre below the slab to be the average seasonal ground temperature. This is WRONG in my opinion and will lead to higher heat losses than actual ones. There are lots of reasons that it is not right.


    Maybe because the house has a more stable temperature the ground temps at that depth are more stable?
    • CommentAuthortony
    • CommentTimeOct 19th 2007
     
    Temperatures under the house will not be the same as average temps measured away from buildings.
  5.  
    tony,

    correct, we are talking about 1 metre under house!
    • CommentAuthortony
    • CommentTimeOct 19th 2007
     
    Therefore the heat losses through the floor will be less than the model predicts.