Home  5  Books  5  GBEzine  5  News  5  HelpDesk  5  Register  5  GreenBuilding.co.uk
Not signed in (Sign In)

Categories



Green Building Bible, Fourth Edition
Green Building Bible, fourth edition (both books)
These two books are the perfect starting place to help you get to grips with one of the most vitally important aspects of our society - our homes and living environment.

PLEASE NOTE: A download link for Volume 1 will be sent to you by email and Volume 2 will be sent to you by post as a book.

Buy individually or both books together. Delivery is free!


powered by Surfing Waves




Vanilla 1.0.3 is a product of Lussumo. More Information: Documentation, Community Support.

Welcome to new Forum Visitors
Join the forum now and benefit from discussions with thousands of other green building fans and discounts on Green Building Press publications: Apply now.




    • CommentAuthorChendy
    • CommentTimeDec 14th 2022
     
    Hello Green Builders,

    Any recommendations on which brands/models to look at or avoid?
    Naturally, I want all the good stuff, like high ACTUAL efficiency, low cost etc.
    Recondemations along this line are helpful.

    But, thinking people here can provide guidance to the less google-able aspects.
    Like, reliability, service support, flexibility/ability to interface with third party controls etc.

    Any tips appreciated!
    • CommentAuthortony
    • CommentTimeDec 14th 2022
     
    Boulder
  1.  
    I was recommended (by a sales guy) to go for Nuaire AB WM1 but I haven't made any decisions yet. £800-£1k ish

    Default would be vent axia hr100r which is very basic. £250ish


    Some high end options here https://database.passivehouse.com/en/components/list/ventilation_small
    • CommentAuthorMike1
    • CommentTimeDec 15th 2022 edited
     
    Posted By: WillInAberdeenSome high end options here https://database.passivehouse.com/en/components/list/ventilation_small
    This is where I'd go too, though it will almost certainly blow the budget. All those on the their list are independently certified under the same lab conditions, so the efficiency they give is a good guide and you can directly compare like-with-like.

    More generally, don't spec it too small - get a unit with enough capacity to run on low speed during regular use, with a summer bypass to minimise overheating.
    • CommentAuthorborpin
    • CommentTimeDec 16th 2022 edited
     
    I am extremely happy with my Komfovent unit from BPC especially in this cold weather as it has not needed to be switched off due to freezing (it would have been off for about 3 days).

    I can connect it to my HomeAssistant (HA) locally.

    I have fitted CO² monitoring to it, but manage the fan speed by HA rather than feeding the value into it. I'd recommend some form of CO² monitoring as it is more important in my situation than RH.

    Efficiency is good if the figures reported by it are correct.
    • CommentAuthorChendy
    • CommentTimeDec 16th 2022
     
    Thanks all.

    Great, independently verified units is exactly what I'm after.

    https://database.passivehouse.com/en/components/list/ventilation_small
    Is the data here from testing or from the manufacturers?


    I hope somebody tests the cheaper models.
    Does anybody want to create a youtube channel, where people/manufacturers send theirs in to test?! ; )

    @borpin
    I liked the referenced to the amazing open source HomeAssistant project. I'm a electronic engineer - I will be hopefully digging into that automation stuff in due course!
    • CommentAuthorMike1
    • CommentTimeDec 16th 2022 edited
     
    Posted By: Chendyhttps://database.passivehouse.com/en/components
    Is the data here from testing or from the manufacturers?

    The manufacturers pay a passivhaus-accredited lab to do the assessment and the database contains the certified results from the labs.

    If a manufacturer chooses not to have a unit assessed, then it won't appear.

    The minimum standard for all units is that they should meet EN 308:1997.
    • CommentAuthorChendy
    • CommentTimeDec 17th 2022
     
    Excellent, thanks for the info.

    I will begin google for prices.
    If anybody can guide me towards the cheaper brands/models in the database, that would be helpful.
  2.  
    Unfortunately, anything marketed as intended for PH, tends to have an extra grand added to the price tags. It's still a niche market in the UK, you might be able to import something from Europe cheaper.

    Don't forget to price for the ducts, manifolds, valves etc and any controllers, and the labour fitting them, it can add up to quite a lot. Once you invest on all that, the extra price of a good fan unit compared to a cheap one, might not seem so bad.

    There are actually some different methods in which % heat recovery can be calculated. Some say that the SAP Q method favours the manufacturers by making the performance look better, and that the PH method is more demanding. So if you have % recovery numbers quoted from different sources they might not be directly comparable, that's an advantage of the PH database.

    The elephant in the room is humidity - when you draw air through the house it gets warm (sensible heat) and it carries away humidity (latent heat). MHRV units might recover 90% of the sensible heat, and their sales people talk about that a lot, that's what the testing figures measure. They don't recover (condense) much of the latent heat at all, some recover only a little condensation and some actually recover no condensation at all. (Think of this like how a condensing boiler is more efficient, only at lower temperatures so the condensing is relatively more important for mhrv). So the difference between claimed 80% sensible heat recovery and claimed 90% sensible heat recovery is less significant than it may seem, if neither is recovering much evaporative heat.
    • CommentAuthorChendy
    • CommentTimeDec 17th 2022
     
    Interesting @WilllInAberdeeen.

    What do you estimate the real-world performance of these units are in a passive home then? Factoring in latent heat and any other ignored forms of energy?

    I guess I guess for proof, one can see figures for how little heating energy is required in a good PH.
    But I'm now curious about these efficiency numbers
    • CommentAuthorChendy
    • CommentTimeDec 17th 2022
     
    ... does the PH database testing methods ignore latent heat and any other nicher forms of heat as well??
  3.  
    Just f'rexample:

    If 1kg of outside air at (say) 7⁰/80%RH is drawn into a house at 21⁰/60%RH, then it needs:

    14kJ of sensible heat (80-90% of this is recoverable by a MHRV)

    11kJ of latent heat (not much of this is recoverable by a MHRV)

    Try other combinations yourself with an online psychrometric chart, if of interest? AFAIK the %heat recovery testing methods don't measure the latent heat.

    Other losses come from the electricity consumption, the better units use less electricity per m³ of ventilation.


    For a passivhaus (or any other high performing home) you want the thermal gains from sunshine and people, to balance the thermal losses from ventilation and through the walls etc, to within an allowed tolerance, at all times of the year. If you choose a poorer MHRV, you might need to balance it out by choosing better insulation or more solar gains, that's the fun part! If you're not dealing with such a high performance building then it's more of an economic question whether a better performing Mhrv is worth the extra £ to you, and other factors like noise, controls etc.

    (Edit: not at all intended to be negative about mhrv, sorry if sounded like that!)
    • CommentAuthorMike1
    • CommentTimeDec 18th 2022 edited
     
    Posted By: WillInAberdeenIt's still a niche market in the UK
    It is. Here in France you can buy a selection of lower-spec units from larger DIY stores, from around €750.

    Posted By: WillInAberdeen...you might be able to import something from Europe cheaper.
    It is worth considering this. I may well buy a PH-assessed Zehnder unit for my current project and prices - for the same unit - range from €1,750 to €3,297, depending on the supplier and the country. You may also find that model names (and their stock codes) differ between countries, so some research may be needed to hunt down the best deal, and to make sure that the prices are for the same piece of hardware.

    Posted By: WillInAberdeenfactors like noise
    Particularly important for a flat, if it's going to be above your ceiling or in a cupboard, Chendy.
    • CommentAuthorChendy
    • CommentTimeDec 18th 2022
     
    Thanks both,

    I'm also totally sold on MHRV.
    Watching people heat whilst keeping windows open 'for fresh area' seems insane to me.

    @WillInAberdeen
    More surprises, so electrical efficiency isn't factored into the declared efficiency numbers? The efficiency of the fans is ignored?!

    @Mike1
    Cheers, yes will be in a cupboard. Am thinking about the physical aspects also.
    • CommentAuthorMike1
    • CommentTimeDec 18th 2022 edited
     
    Posted By: ChendyThe efficiency of the fans is ignored?!
    No, passivhaus certification requires that the total electrical power consumption of all fans, controls and any essential external systems do not exceed 0.45 W/m³/h when operating at (passivhaus's assessed) full throughput, with an external pressure of 100 Pa. The best units use less than half of that, as you can see from their database.

    Posted By: Chendyelectrical efficiency isn't factored into the declared efficiency numbers?
    The passivhaus 'efficiency ratio' does take into account electrical efficiency, and other factors, to show 'the amount by which the energy demand caused by ventilation can be reduced.' For full details, you can read the assessment criteria yourself: https://passivehouse.com/downloads/03_Reqs_and_testing_procedures_ventilation_en.pdf

    Outside the Passivhaus scheme, getting reliable numbers for either of the above is difficult.
    • CommentAuthorjms452
    • CommentTimeDec 29th 2022 edited
     
    Appropriately sized Vent Axia sentinel kinetic like this one:

    https://www.efans.co.uk/products/vent-axia-sentinel-kinetic-bh-right-hand-with-humidistat-and-summer-bypass-443319

    Can even buy left and right to make the ducting easier!
    • CommentAuthorcjard
    • CommentTimeDec 29th 2022
     
    I bought a load of temperature sensors a few years ago so I could monitor my sentinel kinetic plus B; still haven't got around to fitting them, but I really should as I've always wondered about its efficiency
    • CommentAuthorcjard
    • CommentTimeDec 29th 2022 edited
     
    ps.. "MHRV; Mechanical Heat with Recovery Ventilation"?

    It's MVHR..
    • CommentAuthorborpin
    • CommentTimeDec 30th 2022
     
    Posted By: cjardps.. "MHRV; Mechanical Heat with Recovery Ventilation"?

    It's MVHR..
    IIRC we had a long discussion about that previously...:bigsmile:
    • CommentAuthorjms452
    • CommentTimeJan 1st 2023 edited
     
    Posted By: cjardI bought a load of temperature sensors a few years ago so I could monitor my sentinel kinetic plus B; still haven't got around to fitting them, but I really should as I've always wondered about its efficiency


    the green hexagon polymeric counterflow heat exchanger is virtually the same between lots of mvhr units - circa 90% although some datasheets claim 95%!
    • CommentAuthorcjard
    • CommentTimeJan 10th 2023
     
    The matrix always seemed really small to me, and I still wonder why it isn't made of metal
    • CommentAuthorjms452
    • CommentTimeJan 14th 2023 edited
     
    By the matrix do you mean the heat exchanger?

    If so it's partly manufacturing lead but also because a counterflow heat exchanger made from a highly conductive material reduces the efficiency.

    Plastic can be made very thin enabling good heat transfer through the heat exchanger wall but very low heat transfer along it.

    https://swissrotors.com/blog/the-battle-of-the-counterflow-heat-exchanger-polymer-vs-aluminum/
    •  
      CommentAuthordjh
    • CommentTimeJan 14th 2023
     
    Posted By: WillInAberdeenIf 1kg of outside air at (say) 7⁰/80%RH is drawn into a house at 21⁰/60%RH, then it needs:

    14kJ of sensible heat (80-90% of this is recoverable by a MHRV)

    11kJ of latent heat (not much of this is recoverable by a MHRV)
    I don't understand this. What is the latent heat for? Where is water being evaporated? What I would expect is that the air in the building will not be at 60% but more like 40-50% where the reduction due to fresh air is balanced by emissions from breathing, washing etc etc.
    • CommentAuthorjms452
    • CommentTimeJan 17th 2023
     
    Hi Dave,

    It's the latent heat of water vapour condensed from the outgoing air into the heat exchanger.

    When it's 'very cold' outside some of this becomes available.

    This leads to the intersting scenario where if it's cold outside and outgoing air is high in humidity the incoming air is heated to virtually the same temperature as the outgoing air (but this is not 100% efficiency despite some marketing I've seen).
    •  
      CommentAuthordjh
    • CommentTimeJan 17th 2023
     
    Posted By: jms452It's the latent heat of water vapour condensed from the outgoing air into the heat exchanger.

    When it's 'very cold' outside some of this becomes available.
    Right, but in WiA's chosen scenario it doesn't. But it's not energy consumed anywhere or lost so I'm not sure how it fits in to an MVHR 'efficiency' calculation.