Home  5  Books  5  GBEzine  5  News  5  HelpDesk  5  Register  5  GreenBuilding.co.uk
Not signed in (Sign In)

Categories



Green Building Bible, Fourth Edition
Green Building Bible, fourth edition (both books)
These two books are the perfect starting place to help you get to grips with one of the most vitally important aspects of our society - our homes and living environment.

PLEASE NOTE: A download link for Volume 1 will be sent to you by email and Volume 2 will be sent to you by post as a book.

Buy individually or both books together. Delivery is free!


powered by Surfing Waves




Vanilla 1.0.3 is a product of Lussumo. More Information: Documentation, Community Support.

Welcome to new Forum Visitors
Join the forum now and benefit from discussions with thousands of other green building fans and discounts on Green Building Press publications: Apply now.




    • CommentAuthortreeplanter
    • CommentTimeJul 5th 2016 edited
     
    I am building a new house, 158m2 internal space. I have to meet sustainable regulations as it was on a 'greenfield' site (between two houses, on a road in a village - but it had cows on it), so i am not passive house standard, they call it an 'eco-house' which in reality seems to be only a bit higher than standard building regs.

    There is no town gas here so the SAP report says to use an ASHP to UFH with an electric emersion heater for DHW.
    ….however my preference would be to drop the ASHP altogether and have Calor gas, a PV array and a small wood burner with a back boiler. I have also downloaded all the Accredited Details forms, which i will document as i go, to improve my SAP rating.

    Question is how can i calculate if this is possible? Do i go back to the report writer or can i do it myself? I'm concerned that if i wasn't to pass the SAP rating i wouldn't get my VAT back :sad:
    • CommentAuthorringi
    • CommentTimeJul 5th 2016
     
    Would a A2A heap pump give the required rating?

    A wood burner (unless you got free wood) risks putting up your heating costs, as it is a thermal bridge that cools your living room when not lit.

    Having you costed getting someone like Viking Homes to build to passive house standards and therefore take the problem away from you?
    • CommentAuthorDarylP
    • CommentTimeJul 5th 2016
     
    @treeplanter, ask your 'SAP' assessor to model these changes.... it would take about 30 seconds to tell you the answers you require?
    quote-
    I'm concerned that if i wasn't to pass the SAP rating i wouldn't get my VAT back :sad: -
    No, you would not get your house signed off by LABC / AI, and have other issues to deal with as well !
    Good luck :tongue:
  1.  
    I've found my SAP assessor (bundled in with my building control contract) very happy to model various changes for me. PV and (an approved) wood burner will definitely give you credits. You'll have to work through and see whether it is enough for the targets you are trying to meet.
    • CommentAuthorneilu
    • CommentTimeJul 5th 2016
     
    Richard is right, you should speak to your SAP assessor.
    You are paying him/her to get to a solution that works for you (I say this as a SAP assessor myself).

    Your solution would work fine. I've just tried it on one of my projects although I did assume that the bottled gas boiler would run the full heating and hot water.
    I entered the wood burner as secondary heating only and ignored the back boiler option because I've never seen it used before. Using the wood burner to heat water rather than just as a room heater should improve SAP performance so this would be ok if you wanted to do it.

    By the way it took me longer to write this comment than it did to try out your SAP option.
    • CommentAuthorGreenfish
    • CommentTimeJul 5th 2016
     
    Like the others say with the SAP calc.

    Other comment is from my experience of a new biuld not on mains gas. My initial set-up was based on an approved wood burner with back boiler, PV and solar thermal (all mixed into a thermal store). This works great but takes some careful management during the inbetween days of spring an autumn when there isn't enough sunlight but you don't want a to light a fire. I had no means to get just a bit of hot water (other than boiling a kettle!), so I guess a calour boiler or inline electric boiler would have been useful.

    But, having some unexpected cash (sadly through a family death) I treated the household to an ASHP. It is a luxuary, we don't need it, but I am very happy with it all the same. It fills those gap days, providing both DHW and heating, and is marvelously efficient. Thumbs up to ASHP. I must add that I didn't bother with RHI or MCS apporoveal, just bought the parts and got a good plumber to install it. That no faff approach saved me thousands.

    So not sure why you want to "drop the ASHP", but maybe reconsider that?
  2.  
    Thanks for all the replies, its very helpful. I will contact the SAP report firm and ask them to re-model it.

    I am project managing the build myself and hoping to bring it in at around £875-900/m2 so having a passive house 'built for me' isn't an option.
    And I don't want an ASHP as they are an expensive piece of kit and don't feel as eco friendly as 'proper' renewable sources like PV and solar thermal. I think having the gas boiler and wood burner should be enough back up for very cold weather. I'll see what the SAP guy says.

    (...and i'm lucky enough to have access to some space in darkest norfolk to plant some hazel for firewood, so in 5 years it will be free! :)
    • CommentAuthorGreenfish
    • CommentTimeJul 6th 2016
     
    I've a free wood fuel source too, acres of gorse to "manage" and it is a super-fuel joules per kilo. Rather than burn on the hillside we harvest it.

    Cold weather is no problem with a solar/PV/WBS system nor is sunny days, but DHW on cloudy spring/autumn days could be. My solar thermal provides low grade heat through the winter, but I can only depend on it for DHW during the summer months. Using PV to drive an immersion is also limited unless it is sunny. You get weeks when it is warm enouth that you don't want to light a fire, but solar/PV isn't making hot enough water every day. Now you could fill that gap with a bottled gas boiler, lpg or oil but despite the embodied energy in ASHP I found that the numbers make it worthwhile. Also if the PV is generating then the ASHP makes more efficient use of it than any "immerson" device.

    The other gain with the ASHP is that I can use it to warm up the house when we are away. The WBS is great, we love it, and I don't get the thermal bridge losses some people say I could. But it only heats when we are there to light a fire. After a winter holiday entropy wins despite the airtightness and insulation, and you come back to a colder house that then takes an age to heat up.

    Just sharing experiences in the hope it will help you. Not quite a passive house either, and lots of hands on during the build to help the budget too. Ordinary builder implemented good standards and details as we requested, no expensive experts involved just lots of great advice and discussion on this site (thanks again guys)
    • CommentAuthorGreenfish
    • CommentTimeJul 6th 2016
     
    Oh yes, the £10-15k we were quoted for a ASHP system when we started in 2013, was down to £3k when we fitted one this year. Still not cheap, but prices are down and it is worth ignoring the MCS approved route. The money the gov may give back eventually for an approved system is stuck on the price up front.

    I don't mean to sound like a salesman for ASHP, but it has been a revelation for me.
    • CommentAuthordickster
    • CommentTimeJul 6th 2016
     
    We fiited calor gas driven combi boiler and underfloor heating so that when we're old and infirm we have a source of heating. We never use the heating, just our woodburner as planned. The SAP considers the UFH as the primary source of heating, so shot ourselves in the foot (feet?) on this one.
    • CommentAuthorsnyggapa
    • CommentTimeJul 6th 2016
     
    my SAP assessor let me play "what if" games to see what would work. His gut feeling was that I would need a GSHP but we managed to find a solution with PV, direct electric heaters and electric immersion, MVHR and a wood stove that satisfied the requirement. just !
    • CommentAuthorringi
    • CommentTimeJul 6th 2016
     
    Why are people with free wood using an indoor wood burner instead of a wood boiler outside of the property, so as to get hot water etc without overheating?
    • CommentAuthorFlubba
    • CommentTimeJul 6th 2016
     
    Log boilers, thermal stores and ancillaries are expensive and it's still nice to have a wood stove anyway.
  3.  
    Had the SAP report re-done and he's lowered everything to the minimum levels so i can see what i need to do to scrape by. I'm hoping to get better than the predicted 'C'. He has said i can go with a Calor Gas boiler, a wood burner and 1.5KW of PV to pass.

    Interesting that the MCS cert puts the price of an ASHP up so much, one quote i had said it was about £1-2k more if certified.

    My biggest concern with the ASHP is the enormous amount of electric it uses. I spoke to a self build owner today who said hers works beautifully but when i asked about running costs (3 bed detached house) it's using £1500-2000/p.a in electricity, which is terrible!! I've heard similar things about others. I realise that the PV would off set this.

    The other problem is that i may want to rent the house out for a few years while we work abroad, and if i have an ASHP, PV, Solar Thermal, Woodburner and a Gas Boiler the tenants are going to need a diploma just learn to run it (….my experience of tenants tells me to make it flipping simple).

    Dictster i think i may end up with a similar result, being given an officially poor energy rating, but in actual usage a pretty eco-friendly house. It would be interesting to see houses re-assessed three years after their initial rating, based on the utilities bills they generated, that might give us all a better idea which technologies are really efficient in the real world :cool:
    •  
      CommentAuthorSteamyTea
    • CommentTimeJul 8th 2016
     
    Posted By: treeplanterMy biggest concern with the ASHP is the enormous amount of electric it uses. I spoke to a self build owner today who said hers works beautifully but when i asked about running costs (3 bed detached house) it's using £1500-2000/p.a in electricity, which is terrible!! I've heard similar things about others.
    I suspect that is because they are using it to heat water to 65°C+. As the water temperature goes up, it relies more and more on the built in resistance heater, this reduces the CoP to 1. It will also be defrosting more often and for longer.
    Ideally you want to set the water temp to 40°C and then use an inline modulation electric heater to lift the temperature up to 65°C when it is needed.
    The other advantage of storing water at 40°C is that the cylinder losses are lower.

    If you are serious about renting the place out, you are better off with just one fuel source. You only need one safety certificate then.

    And do you really want a dirty woodburner with all the pollution issues they cause (see Mikee thread on here about them).
    • CommentAuthorEd Davies
    • CommentTimeJul 8th 2016
     
    Posted By: treeplanterbut when i asked about running costs (3 bed detached house) it's using £1500-2000/p.a in electricity, which is terrible!!
    Maybe Steamy's right about the water heating. Or maybe they're the sort of people who heat to 25 °C then leave the windows open in winter. Without looking carefully at the actual way in which a house is used the headline numbers are close to meaningless.

    Going on 100 kWh/m²/a for space heating and 3 kWh/person/day for 4 people for hot water with a COP of 3 and electricity at £0.15/kWh I make your costs at a tad over to £1000/year.

    I used 100 kWh/m²/a for space heating as that's what I've seen mentioned for “eco” houses. Passivehaus requires a lot lower, less than 15 kWh/m²/a, which would bring your costs down to £340/year (at which point DHW dominates). It'd be interesting to know what your space heating requirement is calculated to be.
  4.  
    Ed, when you ask for the 'space heating requirement' where is that on the SAP report?

    He's put down 59.5 kWh/m2 which is the minimum for a pass, and he used just Calor Gas, a normal wood burner, along with 1.5kw of PV.

    I figure on using more PV and Solar Thermal as i have the roof space, and a back boiler on the woodburner.
    He's set the fabric targets really low too, i will beat all of them - except the floor which stays at 0.13 U-value.

    ...does that help?
    • CommentAuthorEd Davies
    • CommentTimeJul 8th 2016
     
    OK, 60 kWh/m²/a, area 160 m², COP 3, £0.15/kWh comes to £480/a. DHW with a COP of 2 might be about the same again. Better fabric, run the heat pump as much as possible when the PV is generating or off E7 electricity and it ought to be significantly less - e.g., PV via the heat pump, or even directly, ought to do most of your DHW out of the heating season.

    Having the LPG for backup and cold-weather boost seems sensible. Given that you have neighbours I'd agree with Steamy on dropping the woodburner. I just can't see how they can't introduce a significant cold bridge - as Corporal Jones used to say “they don't like the cold steel up 'em”.
    • CommentAuthorringi
    • CommentTimeJul 8th 2016
     
    Posted By: SteamyTeaThe other advantage of storing water at 40°C is that the cylinder losses are lower.


    You must NOT store water at 40c unless it is in a closed system, so if you want to do this use a thermal store rather then a normal hot water cylinder.
    • CommentAuthorEd Davies
    • CommentTimeJul 8th 2016
     
    Also, think hard about solar thermal. If it's just for DHW (not space heating) then it's really not obvious that the extra complexity and maintenance is worthwhile over just spending the same amount of money on a bit more PV if, as you say, you have plenty of roof space.

    My house will have solar thermal but I'm intending it primarily for space heating in a rather odd system.
    • CommentAuthorringi
    • CommentTimeJul 8th 2016
     
    Forget about Solar Thermal is it not worth the cost, better to use the PV to heat the water when you are not using all the power the PV generates. Not having Solar Thermal save both capital cost, and maintenance cost.
    If a property I was going to rent out had Solar Thermal, I would consider removing it, so as to reduce issues with tenants!

    Given that tenants often think of heating controllers as being on/off, and ASHP (connected to radiators or UFH) hates this, I would not put a in ASHP if there is any chance the property will be let out!

    A LPG (or oil tank) has issues with you having to check how much is in it when tenants change, you are dependent on a letting agent to do this check, but most letting agent’s staffs are chosen on their ability to charm people, so may have no idea what a LPG tank is!

    I am coming round to A2A heat pumps in the down stairs rooms and simple electrical heaters (fixed to the walls) in the bedrooms, along with a very good level of insulation. Then put on as much PV as you can, with a DHW tank that is heated by excess PV and E7. See what SAP rating that will give you….
    • CommentAuthorsnyggapa
    • CommentTimeJul 8th 2016
     
    If I built another house that was off the mains gas grid, my first port of call would be exactly as ringi describes above. Cheap to install, simple to control and easy to maintain

    -Steve
    • CommentAuthorEd Davies
    • CommentTimeJul 8th 2016
     
    Posted By: SteamyTea: “And do you really want a dirty woodburner with all the pollution issues they cause (see Mikee thread on here about them).”

    Lots of threads this link could go on (and maybe it has but I've missed it) but still this thread's about one which can be prevented:

    http://www.bmj.com/content/350/bmj.h2757/rr-1
    • CommentAuthortreeplanter
    • CommentTimeJul 9th 2016 edited
     
    Oh wow, just read that article!… now massively re-thinking the wood burner :surprised:

    Interestingly from a planning perspective King Lynn require all houses to have a brick chimney, i didn't want a huge brick chimney (i was going to just put a flue through the roof of a single storey area) ...and building regs are making me flue it all. So as i was having had to spend all of that £ already i was thinking the WB was the simple bit!

    Ringi + Ed - Thanks for the advice on the solar thermal and just using PV. It would simplify my heating to just have LPG gas and PV. How much PV would you want to have?

    Do i need a massive immersion tank to store warm water in?
    • CommentAuthorringi
    • CommentTimeJul 9th 2016
     
    Posted By: treeplanter
    Ringi + Ed - Thanks for the advice on the solar thermal and just using PV. It would simplify my heating to just have LPG gas and PV. How much PV would you want to have?


    As much PV as you can, as the inverter is a fixed cost. There is a limit to what the electrical board will allow you to have, so ask them.

    Can you use a GRF fake chimney to keep the planners happy?

    The DWH water tank should hold what you expect to use in a "normal day", so you can mostly heat it all on E7, and only top up on full price electric when you have more people staying. Or put in a thermal store that will hold about 1 or 2 days of PV output, then use the thermal store to preheat the water before it goes into your LPG combi.
  5.  
    Thanks for all the advice - really helpful!! :bigsmile:
    •  
      CommentAuthorSteamyTea
    • CommentTimeJul 12th 2016 edited
     
    Posted By: treeplanterDo i need a massive immersion tank to store warm water in?

    This is always the dilemma.

    A thermal store can hold different amounts of energy depending on the temperature. So you can have a small store at 80°C holding as much energy as one double the size at 40°C. Or you can have two separate stores in series, one that stores at 40°C and another at 80°C (or what ever temperatures you like).
    Ringi mentions having a store that is large enough to hold 1 or 2 days PV output, but which days are those? And would the previous days generation fit in with your lifestyle over the next 2 days. This is why you need to know your normal DHW usage.
    When you use the water is important too. Ideally you need a cold store at the end of the day, then it can take full advantage of the PV during the next day. That pattern is the absolute opposite of what I have (being on E7). In some ways E7 and PV don't work too well together, but in other ways they do. So you may have to change your bathing times a bit.

    So is it possible to calculate the optimal size. Yes, but you need to know the size of the PV array, your DHW usage, desired temperatures and average daily insolation (Met Office can help there).

    It is fairly easy to work out your daily DHW needs. Just a jug, a clock and a thermometer. Work out the flow rate from the taps (jug and clock) and multiply it by the amount of time they run for. Take the temperature (and if your cold is from the mains, take that temperature too). Then you can wok out the amount of energy.
    Specific Heat Capacity of Water in kWh = 0.00117 kWh/(kg.K)
    So say your shower has a flow of 10 lt/min and last 3 minutes, you like the water to be at 38°C and your incoming mains is at 18°C, then:
    kWh = 0.00117 x 30 [kg] x 20 [K]
    kWh = 0.7 kWh

    Now yesterday my local weather station reported that I had a mean solar radiation level of 136.5 W/m^2 over the 24 hours period and on the horizontal plane. This works out as 213.8 W/m^2 during daylight hours (06:04 to 21:13) or 3.9 kWh/m^2.
    Now a PV system looses a lot of that energy in converting it to electricity, people argue over the amounts and get really upset about it (especially if they have forked out a few thousand quid). I work on converting 10%, other may claim 12%, 15%, 20%, but I shall use 10% for this.
    So 1m^2 of PV should deliver around 0.39 kWh, for that one 3 minute shower we needed 0.7 kWh, so 1.8 m^2 of PV was needed (just slightly larger than a standard 1m by 1.6m PV module).
    Yesterday was not a brilliant day down here, but let us look what the 11th of Jan yielded.
    The mean radiance was 15 W/m^2, over just daylight hours (8:34 to 16:00) it was 47 W/m^2, the yield was 0.35 kWh/m^2.
    So to generate 0.7 kWh would need 20 m^2 of PV or around 13 PV modules.
    On the equinox you would have needed about 3 PV modules

    So thermal store size for 1 short shower is 30 lt (think of it as squeezing a bladder at the right temperature) and somewhere between 2 and 13 PV modules to generate all your DHW.

    Now that is all a bit silly as your whole plot would be covered in PV, so what is a realistic level of PV and what size thermal store do you need.
    A 200 lt store, with an operating range of 15°C (40°C up to 55°C, or 50°C to 65°C) will hold 3.5 kWh.
    You can double that by extending the temperature range (40°C to 70°C), but turning on an immersion heater.
    7 kWh should give a family of 4 enough how water for the day even allowing for the baths.
    To get 7 kWh/day from PV will require somewhere between 20 and 200 PV modules.
    If you could fit 20 PV modules (5 kWp), you would generate about 5000 kWh/year, if your water usage is about 3000 kWh/year, then for about 3/5th of the year you are covered for the 7 best months, and you get a saving on the other 4 other months.
    And that is with just a 200 lt thermal store (which I think is a bit small).

    So it really is a matter of finding out the usage, finding out the expected PV yield in your area and doing the sums.
    • CommentAuthorringi
    • CommentTimeJul 12th 2016
     
    One option is to heat a normal DHW tank to 50c with E7 and 85c with PV, (you MUST have a safety mixer on the output if you do this! And should set your controller to automatically heat to 60c on E7 if the tank has not got to 60c in the last few weeks.)

    Remember a larger tank will give more heat loses, and that the PV water heating is the icing on the cake and should be seen as a nice bonus, the electrical output in the main reason for putting in PV. You have to be careful you are not increasing your DHW costs at the times of the year you don’t have enough PV output.

    Personally I would not use a thermal store with E7 unless you have a wood boiler etc, as a normal DHW tank has a much larger operating range (13c to 85c) so can be a lot smaller. A thermal store comes into its own if you have a LPG (or mains gas) combi that can take preheated water, as you don’t need to think about legionnaire’s disease.

    All solar water heating systems work best if you use most of your hot water in the morning.
  6.  
    Watch the capital costs - when we looked at buying a cylinder or TS, and solar panels and a top up instant heater, getting them installed, and building the house several m2 bigger to fit them in - it added up to many many years worth of running costs for a LPG instant DHW heater or combi.
  7.  
    Posted By: ringi a normal DHW tank has a much larger operating range (13c to 85c) so can be a lot smaller.


    If your DHW tank is delivering hot water at 13°C you've got problems! Operating range by definition has to be greater than about 38°C (unless you're going to use a heat pump to raise the delivery temperature when the "hot" water is below this temperature)