Posted By: owlmanPeter, Have a look at these; I imagine the concept would be better than a fan at the bottom of the rad. There are several other variations on the same theme.
https://www.radfan.co/" rel="nofollow" >https://www.radfan.co/
Posted By: WillInAberdeenso we need 240% more output. (Doh! Edit: Should have said we need 140% more output)
So for Peter or I to change our rads from 60 to 40degC, they need to be made (4.3/1.8) = 2.4x bigger
Posted By: WillInAberdeenhelpful, but sadly not transformationalYes, I'm sure there will be niche applications where an extra 18% output will make all the difference, compared to fitting a slightly longer or taller radiator. But can't immediately think of any!
Posted By: WillInAberdeenPosted By: WillInAberdeenhelpful, but sadly not transformationalYes, I'm sure there will be niche applications where an extra 18% output will make all the difference, compared to fitting a slightly longer or taller radiator. But can't immediately think of any!
Posted By: GarethCHowever, in the situation of using a heat pump, I'd imagine we would increase the flow rate of water. In fact, you'd have to, wouldn't you, for any emitter to be able to increase its output due to forced convection, because the rate at which the water can transfer heat is a function of temperature and flow rate?It depends on what the temperature drop from flow to return is. If the heat output and the flow rate is the same at the lower temperature with the fan as it was at the higher temperature without the fan then the drop in temperature will be the same. Of course, that'll be proportionally a larger fraction of the flow temperature but, still, it doesn't necessarily follow that you'll need a higher flow rate.
Posted By: GarethCAlso 2.4 x bigger would be a 140% increase needed I think, not 240%?Oops! You're quite right, my bad sorry!
Posted By: WillInAberdeen
The Myson ivector fan convector moves 180-500 m3/h of air for 1.9-3.7kW output. By comparison the speedcomfort moves 30 m3/h. A bathroom extractor is supposed to move 54 m3/h.